ACCel wrote: And this inverter is NC RfG certified at all?
You should be able to report it without any problems with panels below 3.68kW, if someone in the table with parameters signs the power limit setting of 3.68kW.
The limit of 3.68 kW applies to the power in the panels and not in the inverter. Nothing needs to be set in the inverter, no limit, it is enough to show that the sum of the power in the panels does not exceed 3.68 kW.
On the other hand, I will add as a curiosity that electric power plants have started to allow the construction of micro-installations with 1-phase inverters, even if the total power is greater than 3.68 kW per phase. However, in this case, there must be a central protection that turns off the entire micro-installation if there is an asymmetry above 3.68 kW.
Added after 7 [minutes]: kev21 wrote: Hi,
I have a question regarding the first post, i.e. too much inverter power, why is there a refusal?
I am before buying the equipment and I called ZE (PGE) what do I need to know before buying, whether I should apply for the conditions for connecting the installation, etc. I received information that I do not have to ask for the conditions, but only report (the appropriate application) to them after the installation of the finished system. However, it is often read that the energy company refuses to replace the meter with a bi-directional one because the single-phase inverter is larger than 3.6KW, even yesterday the seller where I would like to buy a 4KW inverter asked "do I have conditions in the ZE for a 4KW 1-phase inverter".
I omit the NC RFG standards because only such equipment I take into account, I will do the installation myself, i.e. after installation, the final connection will be made by a licensed electrician (and it was he who warned me about the conditions from PGE before buying anything)
On FV with PGE, I have a contracted power of 11KW, protection 20A.
Thanks
You ask why energy utilities refuse to connect single-phase micro-installations with a capacity of more than 3.68 kW? Because above this power, problems with voltage asymmetry begin, the inverter boosts the voltage too much and the protections start to turn it off. If you have a contractual power of 11 kW, buy either a 3-phase inverter or 3 1-phase inverters and connect panels with a power of no more than 3.68 kW to each.