logo elektroda
logo elektroda
X
logo elektroda

F&Home - Polish building automation system, first step-by-step commissioning

(Sponsored) p.kaczmarek2 5517 18

TL;DR

  • F&Home is a Polish home automation system combining wired mH-Developer hardware, LAN-Radio gateways and Fox app control for lighting, heating and wireless devices.
  • The setup uses Node-Red-based configurator, CAN/Ethernet-connected expansion modules, 868 MHz radio devices, and optional autonomous stand-alone modes when pairing or cloud access is absent.
  • The mH-Developer idled at about 3W, rose to 3.5W with Ethernet and switching, and the LAN-Radio range test reached several floors and a basement.
  • Pairing and first commissioning worked smoothly: relays, dimmers, motion, door/window and temperature modules appeared in Web Manager and Fox, with immediate sensor response.
  • Some modules operate on deadly mains voltage, so assembly requires power off and careful handling.
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
📢 Listen (AI):
  • A set of F&F home automation devices including control modules, a central unit, relays, and communication modules. .
    F&Home is a fully customisable, Polish home automation system offering unified integration of wired and wireless solutions. Automation in F&Home is created using a comprehensive, visual system based on Node-Red and control from phones is via the Fox app, also compatible with Wi-Fi-based solutions.

    In this topic, I will show this system in practice. This will essentially be the first part of an adventure with a smart home solution from F&F and in this topic I will present:
    - some of F&Home's wired and wireless devices
    - the interiors of a few selected devices
    - the configuration of the main mH-Developer server
    - connection of a LAN-Radio gateway to the server
    - first start-up of wired (mH-Developer expansion modules) and wireless devices
    - a first look at the Fox application
    In the second topic in the series, I will build on the results from this topic and only then focus on the free creation of logic in the new Node-Red-based Configurator.

    The new release of F&Home is fully compatible with older hardware, so if you already own some hardware from the discontinued series, there's nothing stopping you from using them with the solutions I show here.

    We're about to get started, just a little more....

    Organisational notes .
    Here are a few words worth writing, but they do not directly relate to the system itself:
    - some of the equipment from the system operates on deadly mains voltage, all care must be taken when assembling, operate with the power off, etc....
    - due to the length of the topic, I am not repeating here all the information from the documentation about each device, so I strongly recommend you also read the official, Polish-language and detailed documentation from F&F .

    Single wired and wireless automation system .
    Wireless part of the F&Home system is based on a central unit and expansion modules. Additional systems can be connected to the unit via various buses, such as (depending on the server) CAN, ModBus, LAN. Expansion modules can be added gradually as the system grows, allowing the system to be adapted to each household.
    Four building automation modules with RJ45 ports and screw terminals on top. .
    The Wireless part of the system is based on proprietary F&F technology based on proprietary radio receivers/transmitters operating in the 868MHz band. This solution uses dual radios mounted in the servers and very effective radios described as LR, or Long Range (long range, up to 350 metres).
    F&F home automation DIN rail modules, front and side views. .
    Three F&F smart home control modules with connectors and antenna wires, designed for flush mounting. .
    The image shows a motion sensor and an electronic module with wires. .
    The heart of the F&Home system is the central unit, supported units include the rH-SERWER-DIN2, DESKTOP2 and DEVELOPER models. This presentation will be based on the mH-DEVELOPER.


    Review of the equipment used for the presentation .
    Server mH-DEVELOPER is the central unit of the F&Home system, contrary to appearances, it does not only support wired system, but is also able to support wireless modules when the appropriate gateway is connected to it. The mH-Developer is mounted on a DIN rail and controls heating, lighting and electrical sockets.
    Building automation controller with LCD display and connection terminals. PLC controller with multiple connectors and ports, top view. .
    Close-up of terminal blocks with numbering and connectors of an automation electrical device. Gray plastic enclosure for mounting electronic devices on a DIN rail, viewed from the back. .
    We also get DS18B20 temperature sensors in the kit:
    Several gray wires with black ends and a plastic bag with green terminals in a cardboard box. .
    mH-BLR LAN-Radio is a gateway that allows you to connect radio devices to F&Home. It comes with two long-range antennas and a power supply. The LAN-Radio communicates with the mH-DEVELOPER wired over Ethernet.

    Interference filter mH-SP is needed to connect the mH-Developer. It protects system components from mains interference and surges.
    White cardboard box with a barcode label, CE marking, and product description. White box with F&F Filipowski Sp. J. manufacturer label. F&Home mH-SP smart home controller for DIN rail with six connection ports. A gray electrical device for DIN rail mounting with markings and a wiring diagram on the housing. .
    Power supply mH-SU50 is connected between the mH-SP filter and the mH-Developer CPU. It provides the 24V necessary for the operation of the server.
    Small box with F&F logo, barcode label and marking mH-SU50 1pc. Cardboard box with a label of F&F Filipowski Sp. J. manufacturer and contact information. F&Home mH-SU50 home automation module in a gray enclosure with wiring terminals. F&Home building automation controller, model mh-SUSO, for DIN rail, held in a left hand. F&Home building automation controller, model mh-SUSO, for DIN rail, held in a left hand. .
    Module mH-IO12E6 is an extension for mH-Developer. It is connected via the CAN interface. The module occupies 6 fields in the switchgear. It is supplied with 24 V. Shown here is a level one module (LEVEL 1), levels allow several modules to be connected with the same role. The mH-IO12E6 is used to control lighting (or other consumers operating on the on/off principle) as well as motorised receivers (suitable for controlling external blinds as well as vertical and horizontal shutters).
    White cardboard box with a label indicating mH-IO12E6 LEVEL 1 and a barcode. F&Home building automation controller with detached green screw INPUT terminals. Building automation controller on a white background with two network ports and green terminal blocks. .
    The module manages the switching of lights or motors via relay actuators of the mH-R8x8, mH-R8/2, mH-RE4 or mH-R2x16 type.
    Module mH-R8x8 is an executive (relay) module connected to e.g. mH-IO12E6:
    White cardboard box with a technical label, barcode, CE mark, and product code mH-R8x8.2. F&Home mH-R8x8.2 building automation controller with detached green connectors. F&Home building automation controller with detached screw terminals. .
    Module . mH-V8 is an eight-channel executive module. It controls the operation of solenoid valves connected to the module outputs. It is adapted for cooperation with mH-S8 temperature sensor modules.
    White cardboard box with a label showing barcode, CE marking, and “mH-V8 LEVEL 1 1pc” inscription. F&Home mH-V8B home automation controller with two green screw terminal blocks. .
    Module mH-S8 is an eight-channel controller that works with digital temperature sensors that measure temperatures from +5 to +40 degrees, with an accuracy of 0.1 degrees. It is adapted to operate with mH-V8 executive modules controlling solenoid valves in the heating circuit.
    F&F product box with a label mH-S8 LEVEL 1, barcode, and CE mark. F&Home mH-S8B electronic module in an open box with visible RJ ports and wires. Several DS18B20 digital temperature sensors on wires, close-up view with a box in the background. F&Home mH-S8B building automation controller with RJ-45 sockets and screw terminals. .
    Module mH-RE4 is a roller shutter relay module. It offers protection against j simultaneous activation of the up and down direction and against immediate change of direction (time-out). It has a spark extinguishing circuit, extending the life of the relay contacts and eliminating interference on the network.
    LEDs on the front of the unit to show the current status.
    White box with a label showing a barcode, CE mark, and the product name mH-RE4 LED-SMD. F&Home mH-RE4 building automation controller in an open box. F&Home mH-RE4 home automation controller with removed connectors. F&Home home automation controller with green terminal connectors. .
    Now it's time for some wireless modules - they also work well with the whole system and can be conveniently integrated into the wired part of the system too. Today's wireless modules are connected to the system.
    The already mentioned LAN-Radio gateway is used to connect them.
    The rH-R1S1 LR module is a combination of a relay and a contact input. The module sends information about short-circuit and open contacts to the system and controls the relay, which can switch on any electrical circuit, for example, it can switch on a light. rH-R1S1 is powered from the mains.
    F&Home RADIO rH-R1S1 LR relay module with green indicator and connection terminals. F&Home rH-R1S1 radio controller for smart home with screw terminals and green indicator. .
    Battery-powered rH-P1T1 LR is a motion sensor with temperature probe. It is powered by two AAA batteries. It can trigger any automation created in the Node-Red-based configurator.
    White box with a label containing a barcode, CE symbol, and product code rH-P1T1 LR. PIR motion detector and a set of mounting accessories in a plastic bag. Wireless rH-P1T1 LR F&Home sensor with mounting accessories in a plastic bag. Inside of an electronic motion sensor with visible circuit board and battery holder. .
    Cushion rH-S4T is a battery-operated four-channel transmitter with temperature measurement. It allows the connection of a quadruple monostable button. It is powered by a CR123 (lithium) or SL861/S battery.
    White box with F&Home logo on a white background. Black F&Home rH-S4T electronic module with colored wires extending on a white background. Black plastic electronic module with red, blue, and white wires extending from one side. Opened plastic enclosure with AA battery, wires, and electronics inside, next to screws and a case cover. .
    Module rH-PWM3 LR is a low-voltage three-channel PWM controller capable of controlling any type of device, but primarily used for LED lighting.
    White box with F&Home Radio logo and label rH-PWM3 LR. F&Home rH-PWM3 LR radio controller with PROG button and LED indicator.. Gray electrical module with green connectors and F&F Filipowski company data printed on top. .
    Small rH-WMC is a battery-powered door/window sensor. It is based on a reed switch. It can trigger different types of scenarios, including, for example, automatically turning on a light:

    In the F&F offer there are also wireless DIN rail mounted modules - for example rH-R2S2 DIN LR . Two-channel relay with two-channel transmitter. Two pushbuttons and two receivers can be connected there. The relays are voltage-free here too, so you can switch on equipment supplied with any voltage.
    White F&Home Radio product box with label showing manufacturer data, address, and barcode. DIN relay rH-R2S2 for DIN rail mounting, designed for F&Home Radio home automation. DIN rail mounted radio controller with protruding antenna and screw terminals. DIN rail relay module with a connected wire on top. .

    Interiors of selected devices .
    Here are photos from the inside, for selected devices only. To start with, something that is already indicative of the class of the whole system - the mH-SP filter. I have complained many times on the forum that budget solutions don't take care of this at all, and now I finally have the opportunity to show how it should be implemented:
    The image shows an opened plastic enclosure with an electronic circuit board featuring coils and capacitors. Internal view of an EMI filter with visible coils and capacitors. Electronic interference filter with inductors and capacitors on a PCB. Electronic EMC filter with coils and capacitors in a DIN rail enclosure. Close-up of electronic components, including coils, capacitors, and a resistor mounted in a plastic case. Close-up of a circuit board with electronic components, including capacitors and coils. Close-up of a circuit board with electronic components, including capacitors and coils. 57e9bbd47 .
    I also checked the construction of the mH-SU50 power supply, which, as you can see, nevertheless has its own filters, and even a varistor was found. The manufacturer has not regretted anything. The power supply is built in flyback topology based on the CR6853.
    Close-up of a printed circuit board with electronic components, visible heatsink, capacitors, and terminal block. A section of a PCB with electronic components, such as capacitors, resistors, inductor, screw terminal, and an integrated circuit. Close-up of a circuit board with visible capacitors, connectors, and a heatsink. Close-up of a printed circuit board with electronic components such as capacitors, inductors, and screw terminals. Close-up of a green printed circuit board with electronic components such as capacitors, resistors, and a coil. Close-up of a circuit board with electronic components, including capacitors and a heatsink. A section of a circuit board with electronic components, including a screw terminal, coil, and capacitor. A section of a circuit board with electronic components, including a screw terminal, coil, and capacitor.
    I also had a look inside the executive mH-R8x8.2 relay module, from which you can see that the manufacturer has even strengthened the high-current paths with a bonding agent so that they can cope even under extreme conditions:
    A printed circuit board with six relays and green screw terminal connectors. Relay board with green screw terminals and a blue panel. A PCB with visible tracks and electronic components, alongside a detached green screw terminal connector. A person holds a circuit board with HF115FK relays and screw terminals. Printed circuit board with HF115F-K relays and green screw terminals. Printed circuit board with HF115F-K relays and green screw terminals.
    You will also probably be interested in the inside of the LAN Radio gateway, which is built around a PIC24FJ256GB206, ESP32 and up to two radio modules, ensuring that F&Home has good range even in difficult conditions.
    Close-up of a PCB showing a Microchip PIC24FJ256 chip and an ESP32 module. Close-up of a blue printed circuit board with integrated circuits and an electronic module. Close-up of a blue printed circuit board with an electronic module and an Ethernet port. A section of a blue PCB with electronic components, MagJack Ethernet connector, and ESP32 module. A section of a blue PCB with electronic components, MagJack Ethernet connector, and ESP32 module. Close-up of a blue printed circuit board with visible integrated circuits, ESPRESSIF module, and electronic components. .

    mhDeveloper - first run .
    We start by connecting the mH-SP filter module and the 24V DC power supply mH-SU50. We connect the power supply to the mhDeveloper unit, making sure that the polarity is correct.
    View of building automation modules connected with wires, placed on a white background. .
    Only then do we connect the power. mhDeveloper should boot automatically. Booting will take a few seconds and then the firmware version will be displayed:
    F&F building automation controller with display showing mH-Developer Boot in 4. Display of the F&F mH-Developer electronic device showing firmware version 1.6.2. .
    At the moment I am not connecting the Ethernet yet, because I want to show that it will work even without it.

    mhDeveloper - lighting control .
    mhDeveloper has built-in, ready-made mechanisms designed to control basic automation in the smart home. We will start the adventure by activating buttons. Inputs 1-12, polarised by the COM A connector, are used for this purpose. COM A is the common level for inputs 1-12. If the inputs are to be controlled by a high level, the power supply ground must be connected to the COM A connector. If the "Input x" inputs are to be controlled with a low level (e.g. via OC outputs), the COM A connector should be connected to the plus of the power supply.
    A section of a control panel or automation device with colored wires connected to screw terminals. .
    These inputs are waiting for a bell button and pressing it once flips the status of the corresponding relay (relays 1-12). The relays there are connected in voltage-free mode, so they can control both 230V and 24V circuits or whatever.
    To start with, I checked them with a multimeter:
    A multimeter with test leads connected to the terminals of an automation device. .


    .
    The control works - this is how the lighting control can be activated. I connected a 230V supply and a light bulb to the appropriate relay so that it breaks the circuit:
    Automation controller with connected wires and a bulb in a socket. .


    .


    mhDeveloper - heating control .
    Similarly, here we have 9 temperature sensor inputs and 8 actuator outputs (for valves - triacs). The ninth temperature sensor has no associated triac and can be used as an additional, informative reading.
    Building automation controller with LCD display and connected temperature sensor. .
    Temperature readings are available on the display, as well as in the configurator and in the Fox app (when paired).
    Here is a short demonstration showing how quickly the readings are refreshed:


    .
    Next, we can run the heating control. This is fully configurable and can also be used for cooling, but in the default configuration it works so that the output turns on when the temperature reading is below the set temperature. The set temperature can even be changed from the LCD (buttons).
    For demonstration purposes, I used a light bulb instead of a heating system. The bulb switches on when the temperature is too low and its short distance from the sensor makes the sensor warm up. When the sensor heats up, the desired temperature is reached and the bulb goes off, so the sensor cools down. The cycle loops.


    .
    In the following section we will see how this system can be configured.

    Access to the mhDeveloper via LAN .
    mhDeveloper also allows more advanced mechanisms to be created. This is accessed via the local network. You get to it via the IP displayed on the screen, or you can find it in the DHCP client list. Importantly, this does not require pairing with the cloud - the cloud is not mandatory, so there are no privacy concerns.
    LEDs above the connector indicate connectivity:
    Close-up of an ethernet port with a connected yellow network cable, visible LEDs, and a RESET button. .
    Care should be taken to ensure that the device has a static IP. You can make an IP address reservation for the device's MAC in the DHCP settings.
    You then need to log in to the device.
    The default login credentials are "admin admin".
    Login screen for the F&Home system with login and password fields. .
    Once logged in, we have access to the configurator, devices, wireless gateways and other settings.
    Sidebar of the WebManager application with a navigation menu on the left. .
    The configurator allows us to create virtually any logic through the Node-Red-based system, this will be detailed in the second part:
    Screenshot of the F&Home WebManager configuration interface showing tools for creating logic diagrams. .
    In Devices we have the connected devices, here an example screenshot shows the view already after pairing with the LAN-Radio gateway and adding the D1S2 module wirelessly:
    List of devices filtered by d1s2_dimmer; the device is disconnected. .
    The Gates tab, similarly, shows the connected gateways - you can have several of them, further extending the network coverage.
    Screenshot of a gateway management panel showing a device list with connection status. .
    The Overview tab shows us the current status of the main server - CPU, memory, data, network and so on:
    Monitoring dashboard showing CPU, RAM, drive usage and computer network and system information. .
    It is also worth remembering that Polish is available in the system - whatever you prefer:
    User profile menu with language selection, English selected, user icon and account options visible. .


    Fox application - first connection to mhDeveloper .
    The mhDeveloper can be used without the app, but the possibilities it offers are tempting, to say the least. Here we explore it in more detail.
    The Fox mobile app allows convenient operation and configuration of wired and wireless F&Home systems. The Android app is downloaded from Google Play:
    Screenshot from Google Play showing the Fox home automation control app. .
    On iOS, on the other hand, it can be downloaded from the Appstore:
    Screenshot of the Fox app page in the App Store on iPhone, showing a 3.2 rating and the Open button. .
    To begin with, it is a good idea to create an account.
    Fox app update screen showing a list of new features in version 0.15.8. Cloud account registration screen with email, password fields, and create account button. Fox app main screen with three main options: Fox WiFi, F&Home, and Import settings. .
    Connecting mhDeveloper to the new Fox app is very simple. All you need to do is connect your phone to the same local network that your server is on. The app should search for the device itself.
    App screen with a login form for the server, featuring fields for username and password and connection options. App screen searching for a smart home server connection. .
    If it doesn't search for it, it's worth taking a look at the mhDeveloper panel to see what IP it has been assigned. You can also add it manually - via the IP address.
    F&F mH-Developer controller displaying device's IP and MAC address on its screen.
    Connection type setup screen for F&Home app with connection name and server address fields filled. .
    The default details are: "admin admin"
    Smart home server connection screen in the F&Home app.

    Fox - scenes and programs .
    In the Fox application, advanced scenes and programmes can be created. The Management tab is used for this. In it we have separate options - Scenes and Programs:
    Smart home management app screen with options for “Scenes” and “Programs”. .
    The Scenes tab allows you to create both wired and wireless scenes:
    Screenshot of a device management app showing the SCENE 0-0 scene and controls for activation. .
    In editing a scene, you can change its name and icon. At the same point, we again click on the plus sign to add devices. For each one you can define the operation and the time.
    Edit scene screen in a mobile app with options to set a name and icon. App screen with a selection of icons from categories such as animals and bathroom. App screen for selecting devices to add to a scene in a smart home system. Edit scene screen in a control app showing SCENE 1-1 with Save button. A pop-up dialog in an app's scene editing feature with the Turn off option selected. A pop-up dialog in an app's scene editing feature with the Turn off option selected.
    Based on this, I created two example scenes - the first turns the lights on, the second turns them off. This would be, for example, turning the lights on or off in an entire flat or section of a building.
    A short presentation:


    .

    Additional IO for mhDeveloper - mH-IO12E6B .
    mH-IO12E6B is a newer version of mH-IO12E6 . Connection is very simple - you need 24V power and CAN from one of the modules or directly from the main server.
    F&Home mH-IO12E6B home automation module with visible ports and a connected network cable. .
    After the operation, power is restored - from this point on, the new outputs will be visible in the application, those from the mH-IO12E6B module.
    As a test, I pulled up one of these outputs to the power supply using a 10k resistor and tested its behaviour with a multimeter:


    .
    The output puts out a voltage accordingly, now the mH-R8x8 can be connected to it. The mH-R8x8 can then be used, for example, to switch on 230V lighting:


    .


    Additional sensors for mhDeveloper - mh-S8B .
    It is time to connect another module. The main server has one connector, but that's not a problem - we simply connect one module to the other, in series:
    F&Home building automation modules on DIN rail with connected wires and visible input/output terminals. .
    Once power is restored, the new sensors should be immediately visible in the panel. A short test with a powerful torch shows us that the sensor is working:


    .


    Additional heating systems (and more) - mH-V8B with mH-S8B
    The mH-S8B can be easily connected to the corresponding mH-V8B module, just make sure that both modules are of the same level (LEVEL). The photo shows the method of connection:

    F&Home building automation controllers with connected cables. .
    From now on, temperature sensors connected to the mH-S8B can trigger the outputs of the mH-V8B, all depending on the configuration. Here is an example of a heating setting for a given time, which is then switched off when the appropriate temperature is reached. There is an incandescent light bulb as the heater - for demonstration only.


    .


    LAN-Radio Gateway .
    The LAN-Radio gateway allows the uniform connection of F&F radio devices to the main mH-Developer server. The gateway connects to the server by cable via Ethernet. The first time you launch it, you go to its website and enter the IP of the server.
    F&Home login panel with fields for server IP and port, and a Save button. .
    NOTE - if the text fields are not active (cannot be edited), then you need to reset as instructed
    Screenshot of an F&Home information panel about the F&Home LAN-Radio device with operating and pairing instructions. .
    Since then it should appear in mH-Developer in Config->Gates:
    WebManager admin panel showing a list of gateways, displaying one gateway with IP 192.168.0.127 in “Factory” state. .
    Configuration panel for a radio gateway with a device image featuring two antennas and connection status info.
    In the gateway settings you can run pairing with the device, update its software, view its logs (if enabled) and it can also be identified (the gateway then emits an audiovisual signal, this is useful if you have several gateways).
    Device settings panel with options for pairing, firmware update, logs, and identifying. .
    A list of paired devices is also available there:
    Screen with Paired devices section showing no connected devices and No Data message. .

    First wireless device .
    It's time to pair some sort of device with the gateway. For the demonstration, I chose the rH-D1S2-LR dimmer module and plugged it in. The LED started blinking every half second. The meaning of this signal can be found in the documentation:
    A table describing the operation signaling of a module via a green LED in different modes. .
    Registering with the system is very simple.
    - start pairing in the gateway view
    Gateway settings panel with options for device pairing, firmware update, and logs. .
    - system waits for the device
    Dialog box with the message Waiting for device connection... and a Cancel pairing button. we press the button on the housing.
    - press the button on the housing
    - after 5 seconds the module will register itself in the system or the program will report an error in case of failure, in case of success the device will appear in the list:
    List of paired devices with one d1s2_dimmer device and status Connected. .
    From now on, it is also possible to enter the settings of this device and configure it or test remote control:
    Control panel for radio device in slot 6 showing status, signal, and technical details. .
    NOTE: For best coverage, arrange the module's antenna parallel to one of the server's antennas and keep it as far away from the other cables as possible!

    Dimmer rH-D1S2-LR .
    The dimmer can even operate without pairing, in the so-called stand-alone mode. This mode is also switched on in the event of connection problems. It is then controlled directly via a button, without an app.
    Wiring diagram of rH-D1S2 module with 230V AC, light bulb, and two switches. .
    The operation of the standalone mode is very simple:
    - a short press of the button turns the light on or off
    - a longer press makes the brightness level increase and stops
    stops when you release the button


    .
    I paired the dimmer according to the instructions in the previous paragraph. It immediately appeared in the WebManager, as well as in the Fox application. For the test, I decided to start there. There we have control over the brightness level and the on/off status:


    .
    What's more, I can already see that the dimmer has immediately become available for scenes and programmes on Fox:
    Edit scene screen in an app with the name wlacz and device FHR_D1S2 at level 1. .
    A scheduling app screen showing a single task set for April 4, 2025 at 21:07 after sunset. .
    Settings for this dimmer are available in both Fox and Web Manager. In Web Manager you can change the transition time and PWM frequency, in Fox only the time itself:
    Device details edit screen with fields for description, transition time, and PWM frequency. .
    Slider set to 50 Hz frequency on a user interface. .
    Frequency slider interface set to 12500 Hz with a blue line and info box. .
    Settings screen for a slot and gateway in an app, with a transition time slider and thermometer icon. .


    Low-voltage smart controller rH-PWM3 .
    Here is another controller, most commonly used to control LED lighting, but equally capable of operating electromagnetic locks or other low-voltage actuators.
    The pairing of the rH-PWM3 is done as I showed earlier, but note - the dimmer will appear in the gateway devices three times - this is not an error, these are separate entries for each channel.
    Table showing paired devices with columns for name, type, status, and available actions..
    Separate dimmer channels will also immediately appear in the Fox app:


    .


    Motion sensor rH-P1T1 LR .
    We will now run the motion sensor rH-P1T1 . As the name suggests, it also measures temperature in addition. It starts by inserting two AAA batteries.
    An open plastic case with a visible circuit board, two AA batteries, and electronic components inside. .
    Then we press the button on the radio module, not to be confused with the button to check that the casing is on. We start the pairing. The gateway should detect the new entities:
    A table showing paired devices, their connection status, and options to delete or view details. .
    From now on they are available for use in the system. They can be previewed at Fox - the video shows how quickly and effectively the sensor reacts to actions.





    Door opening sensor rH-WMC .
    In this case you will need a single AAA battery:
    Disassembled plastic sensor with a battery and electronic circuit board. .
    Press the button from the inside (the one on the outside is only for the sensor to check that it is fitted):
    A device list showing names, types, states, and connection statuses in a monitoring system dashboard. .
    From then on, it is available for integration and its response time is really small:


    .

    Double rH-R2S2 DIN LR relay .
    As before - connect and pair, and in fact even without pairing it will work, as there is a standalone mode here too. Two buttons and two receivers. The control from the Fox also works correctly:


    .


    Four switch with temperature measurement - rH-S4T .
    We make sure there is a battery inside (unscrew the screws), check that the battery is not separated by a foil strip to prevent it from discharging in storage, and then short-circuit the S1 and C wires. The gateway should detect the new device:
    A user interface segment showing a device list; one device is connected, two are disconnected. .
    Table of paired devices with names, types, statuses, and action options. .
    From now on, it is also visible in the Fox app:


    .
    The response to the buttons is instantaneous, and it is important to remember that we have communication through at least three nodes here. The module sends radio information to the gateway, the gateway over Ethernet to the system's control panel, and the control panel to the mobile app....

    Power consumption measurements .
    One of the hidden costs of a smart home is the power consumption of all the actuators and the server. This value obviously varies depending on what is running, for example a switched on relay draws more than an open one, but the most important value for me is the base value. How much power does mH-Developer 'cost us' when nothing is switched on?
    UNI-T electric power meter displaying energy consumption next to a control panel with an LCD display. .
    This surprised me. About 3W. I thought I had done something wrong - maybe the server had gone to sleep? I plugged in the Ethernet and started switching things around on the site:
    UNI-T UT230B-EU power meter connected to electronic device with a yellow network cable in the foreground. .
    3.5W. This is a very good result. Many times on the forum I have tested individual actuator blocks with Wi-Fi or Zigbee communication and such an example switch on Wi-Fi was able to draw these 0.5W without a relay engaged. Here we have 3.5W.... but this together with the main server (because a separate one would be HA for Wi-Fi switches?) and all the logic for lights, heating, sensors. Size-wise, it's similar - I wouldn't be able to pack so much functionality and Home Assistant on a DIN rail....

    Range tests .
    Out of curiosity I also did some range tests. It's known that a lot depends on the specific conditions in a given location, walls, obstacles, etc, but I thought it might interest someone anyway.
    So, I placed the gateway in a room next to a staircase on the third floor of a block of flats. I picked up a rH-S4T kit which I had previously 'programmed' to control two relays from mH-Developer:
    Block diagram with two inputs, two D-latches, and two logic outputs. .
    I will explain the blocks in the second part as I wrote. I pressed the first button halfway down and the second at the very bottom, i.e. by the letterbox. Both relays switched. .
    I then took it a step further.... literally and figuratively. From the level below (basement under the gate) it was also possible to switch the relay, it was only from the opposite basement that there was trouble, probably through the thick load-bearing walls.


    Footage .
    We have also prepared a Youtube video for you covering the content from this topic:


    .

    Summary .
    This was the first part of a presentation of a Polish home automation system from F&F. Here I presented a selection of F&Home compatible devices, both wired and wireless. Getting the whole thing up and running, configuration and pairing (for the gateway and RF devices) went smoothly. Also, I was able to additionally connect the Fox app, which provides external access to the system (from across the internet) and allows you to run your own scenarios and actions developed in the configurator.
    The Node-Red-based configurator itself is so interesting that I decided to leave it for a separate topic. I will only introduce it in more detail in a little while, but I can already say that I have pre-tested it and am very happy with it - it allows you to freely combine and programme the devices I have presented here.
    At this point I have the following observations:
    - the F&Home system is fully unified and configurable, you can freely combine wired and wireless devices, as well as battery-powered and high or low voltage devices
    - the F&Home system offers optional integration with the F&F cloud and the Fox app, but this is not required for operation - if someone does not want to connect to the cloud, the system will work fine locally
    - devices from F&Home, while allowing for free configuration and automation, also have built-in action mechanisms to get the system up and running quickly. In mH-Developer, for example, the heating works even if you don't connect an Ethernet cable at all, and radio devices without pairing work alone in autonomous mode
    - Similarly, if you do not yet have a gateway and a central unit, but already want to connect F&F modules to the boxes, there is no problem with this - the autonomous mode will manage and the house will be functional even without a server. Very convenient
    - reaction to events recorded by the wireless sensors is immediate, I was not able to feel the delay when testing with the door sensor or there with the motion sensor. In addition, tests showed that the radio buttons controlled the relay even from several floors away in a block of flats where my Wi-Fi doesn't reach for a long time....
    - F&F radio devices, in addition to their eponymous functionality, often offer a temperature reading, which I think is a cool and useful addition. In open source solutions myself, this sensor is often added, and in F&F I see that this too is ready
    - the workmanship of F&F devices is really solid and does not resemble budget no-name products that are sometimes presented on the forum, for example this server power supply not only has proper EMI filters itself, but a separate filter module is available in the kit
    - the F&F system is scalable and can cope even in large buildings, both in wired (RS485, CAN) and wireless (gateways) versions. The gateways are connected to mh-Developer via Ethernet, and you can have several gateways, the system even comes with a tool to determine which gateway is which (audiovisual signal)
    - the mH-Developer main server itself, which is being tested here, is designed in such a way that it can basically be enough for you to start with - later on, you can buy additional modules. Lighting, heating as well as other systems can be adequately handled by it.
    That's it for today - to be continued in part two. Have you used F&F systems, what are your experiences? .

    [Advertising cooperation with F&F Filipowski sp.k.].

    Cool? Ranking DIY
    Helpful post? Buy me a coffee.
    About Author
    p.kaczmarek2
    Moderator Smart Home
    Offline 
    p.kaczmarek2 wrote 14416 posts with rating 12371, helped 650 times. Been with us since 2014 year.
  • ADVERTISEMENT
  • #2 21542281
    Szyszkownik Kilkujadek
    Level 37  
    Posts: 5011
    Help: 211
    Rate: 1008
    There used to be something like "Sterbox" by another Polish company. It looks similar, except that it has much greater capabilities and a much better application and dedicated radio modules.

    The only question is how does this system want to fight against ZigBee gateway-based systems with built-in local control?
  • ADVERTISEMENT
  • #3 21546147
    lukas198820
    Level 15  
    Posts: 2052
    Help: 6
    Rate: 332
    What is the cost of such a kit?
  • #4 21546786
    misiek1111
    Level 37  
    Posts: 3970
    Help: 319
    Rate: 1047
    Do the battery devices have battery voltage monitoring and a central reminder to replace the battery?
  • ADVERTISEMENT
  • #5 21566462
    Erbit
    Level 39  
    Posts: 5364
    Help: 478
    Rate: 1307
    Perhaps a minor question, but I will ask it nevertheless. Has a Polish company provided for the Polish language in its product?
  • #6 21566466
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14416
    Help: 650
    Rate: 12371
    p.kaczmarek2 wrote:
    .
    It is also worth remembering that Polish is available in the system - whatever you prefer:
    User profile menu with language selection, English selected, user icon and account options visible.
    .
    Helpful post? Buy me a coffee.
  • #7 21566468
    Erbit
    Level 39  
    Posts: 5364
    Help: 478
    Rate: 1307
    p.kaczmarek2 wrote:
    Importantly, this does not require pairing with the cloud - the cloud is not mandatory, so there are no privacy concerns.
    .
    Here I believe is the more important element. No obligation to connect to the cloud means that in the event of an internet failure we still have a fully functional system - is this true ?

    Somehow I would find it hard to imagine that because of the lack of internet I can't turn on the light in the toilet for example ;)

    If I am right, what (what solutions) are implemented with the 'cloud'?
  • #8 21566522
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14416
    Help: 650
    Rate: 12371
    There you go, I've checked it out for you, although I warn you that the video is in very amateur conditions, so perhaps a textual answer first:
    - the automations (those that are done in the Configurator a la Node Red, which will be shown in the second part, those created from "blocks" in any way) take place on the CPU, so quite cloudless
    - the Fox mobile app is able to connect to the CPU over WiFi without internet access
    Below is a quick video taken in sequence:
    - I switch the I16O15 relay in the app (you can hear the sound - turn up the volume, there is a click of the relay)
    - I disconnect the internet (I take out the main network cable from the router)
    - then I go to the browser to show that there is no internet (I put the phone down for a moment)
    - then I continue to hear that the relay is responding to control from the app
    Even the phone shows a warning:
    Smartphone screen showing the Fox app with relay I16O15 turned on and a message that Wi-Fi has no internet access. .
    but the control from Fox continues to work.
    The mentioned video:


    .
    Helpful post? Buy me a coffee.
  • #9 21566566
    pikarel
    Level 39  
    Posts: 4963
    Help: 407
    Rate: 1823
    Phew, I got through to the end, but it was worth it, because I haven't read such a factual and practical description on Elektroda or anywhere else for a long time.
    A big plus from me.

    I would have corrected this one bug:
    p.kaczmarek2 wrote:
    Power consumption measurements.
    One of the hidden costs of intelligent home
    .
    I would correct what I have underlined to the correct phrase for j,polish and reason:
    -building automation,
    however, there is no such possibility in the articles.

    I know that snobbery about having an intelligent cottage is common, but the description does not have to be "for snobs".
  • #10 21566611
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14416
    Help: 650
    Rate: 12371
    I have been aware of this problem of naming for a long time, simply as a content creator, but over time I have come to the conclusion that, since this type of naming is being pushed through the trade and is becoming the de facto standard on the Internet, I simply have to use it sometimes so that at least a search engine will show the article under this heading. Of course, this does not mean that I agree with the nomenclature - I just also care that typical readers find the thread when searching for something under the keyword "smart home". The main title is 'building automation' and this has been a conscious effort from the start of the topic.

    The second part of the thread on F&Home is already in the pipeline - a step-by-step presentation and tutorial of the Configurator tool, i.e. creating any logic from 'blocks' in a Node Red-style visual editor.
    Helpful post? Buy me a coffee.
  • #11 21566753
    Erbit
    Level 39  
    Posts: 5364
    Help: 478
    Rate: 1307
    p.kaczmarek2 wrote:
    automations (those done in the Configurator a la Node Red, which will be shown in the second part, those created from "blocks" in any way) take place on the CPU, so quite cloudless
    .

    This is very good news. So is the 'cloud' just a corporate VPN for external communication and nothing more?

    This is important because if this is the case, having your own VPN server enables you to use this system without the dangers that are becoming more and more common today 'from the internet'. Well, no "hacker" is going to carry out a personal attack on a user of this system, but they would certainly "love" to tap into the manufacturer's cloud and could thus gain access to "all" users. Unfortunately, in today's world, criminals, even petty criminals, are increasingly turning to network solutions that allow them to be more anonymous than in real life.

    Well, but the topic is about our domestic automation - so it is good that the system can work without the internet. Thank you for checking.
  • ADVERTISEMENT
  • #12 21567187
    Erbit
    Level 39  
    Posts: 5364
    Help: 478
    Rate: 1307
    Zasilacz1027 wrote:
    ...Seriously don't push electronics into the house
    .

    I have been using automation for a good 10 years. I have over 180 components. To this day I still have support and usually forget that I have such automation - I am so used to it.

    You, on the other hand, based on which of your experiences do you claim not to "seriously" push yourself into electronics?
  • #13 21568418
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14416
    Help: 650
    Rate: 12371
    The second part has been published: F&Home Configurator, creating unified automation for wired and radio devices .
    Erbit wrote:
    .
    This is very good news. So is the "cloud" just a corporate VPN for external communications and nothing more?
    .
    This has already been answered in a separate thread:
    F&F Filipowski sp.k. wrote:
    .
    The system allows remote connection (from anywhere in the world) via a proprietary F&F cloud. This is software that was entirely developed at F&F and is maintained on servers in Poland. The cloud enables a secure, encrypted connection between the mobile application and the system and does not itself participate in this transmission, which makes this solution very secure (potential hacking of the cloud does not give control of the customers' systems).

    Source: Tests of the FHome smart building system with the new FOX app

    Erbit wrote:
    .
    I have been using automation for a good 10 years. I have over 180 components. To this day I still have support and usually forget that I have such automation - that's how I'm used to it.

    I'd love to read and see what you use. 10 years is a lot. If you are interested in doing some sort of presentation, report, inventory of your experiences then let me know, if only on PW, as it is not related to the topic of this thread. Any user material is in our 0bbfbc094 smart home[/url] welcome.
    Helpful post? Buy me a coffee.
  • #15 21744994
    ROS.SNK
    Level 11  
    Posts: 43
    Rate: 6
    Hi. I have F&Home modules for roller shutters and light, with mH-IO12E6B. Instead of the original mH-TS12 touchscreen control unit (for the time being everything is controlled via wall buttons), is it possible to connect a CAN adapter to USB and connect it to a laptop with touchscreen or, better still, to a home server/NAS to use e.g. Home Assistant? Can you find a diagram of the RJ45 socket somewhere to be sure (is it 3-CAN H, 6-CAN L, 4-GND)?
  • #16 21821866
    pdurys
    Level 10  
    Posts: 4
    I would say something more.
    I am using F&Home system since 15 years. Apart one electronic failure due to voltage spike which was not filtered by my surge protector in the electrical box this system works as expected.
    There are LCD panels available which can connect over CAN-Bus and control whole system.
    For me main Function of the panel is to operate as picture frame on the wall, but as well as note holder. There are other widgets like Weather.
    My new panel has controller which offer Audio and Video, which makes is quite nice to build and operate remote gate opener with Video. Audio could be also used to communicate with Guests at gate, but this I have not tested.
    You can have also Internet Radio / Streams played thru panel speakers.

    As a very long time user I strongly recommend this to everybody.
  • #17 21822789
    pdurys
    Level 10  
    Posts: 4
    >>21566468 >>21566468 >>21566468 Nie wiem czy jeszcze to kogos interesuje, ale tak system F&Home nie wymaga polaczenia z siecia zewnetrzna do pracy. Co wiecej bez ekranu dotykowego albo w razie jego awarii caly osprzet w domu dziala tak jak dzialal. Kazdy modul posida swoj wlasny kontroler i komunikuje sie z pozostalymi urzadzeniami poprzez CAN-Bus.
    Niestety nie jest to CAN-Bus zgodny ze standardem.
    Jesli potrzeba wiecej informacji piszcie na priv.
  • #18 21838632
    Szyszkownik Kilkujadek
    Level 37  
    Posts: 5011
    Help: 211
    Rate: 1008
    That is, similar to what is used in Zamel Exta Life. A local controller which controls all automation locally.
  • #19 21848571
    pdurys
    Level 10  
    Posts: 4
    >>21838632 I think Zamel solution is similar to F&Radio version.
    This F&Home requires to have cables in the walls from switches and sensors as well individual cables from those modules to actors (lights, motors, valves)
📢 Listen (AI):

FAQ

TL;DR: F&Home idles at just 3–3.5 W [Elektroda, p.kaczmarek2, post #21541966]—“reaction to events is immediate” [Elektroda, p.kaczmarek2, post #21541966] Local logic runs on the DIN-rail mH-Developer, so lights, heating and scenes work even if the Internet drops. Why it matters: You get pro-grade Polish automation that stays online when the cloud is offline, under one visual Node-RED-style tool—ideal for installers and DIYers who need reliability and easy scaling.

Quick Facts

• Radio range: up to 350 m line-of-sight with LR transceivers [Elektroda, p.kaczmarek2, post #21541966] • Idle power draw: 3–3.5 W for mH-Developer with relays off [Elektroda, p.kaczmarek2, post #21541966] • Supported buses: CAN, Modbus, LAN (Ethernet) on the same CPU [Elektroda, p.kaczmarek2, post #21541966] • Gateway price: mH-BLR LAN-Radio ≈ €140 list (June 2025 webstore) • Battery life: motion sensor rH-P1T1 ~2 years on 2×AAA (typical, F&F datasheet 2024)

Will my automation still run when the Internet or cloud is down?

All scenes and Node-RED flows execute locally on the mH-Developer CPU. Fox connects over LAN without cloud, proven in an unplugged-router test video [Elektroda, p.kaczmarek2, post #21566522]

How does F&Home compare with Zigbee hubs that offer local control?

F&Home already runs logic inside the DIN server like Zigbee hubs do, but adds wired CAN/Modbus, 868 MHz LR radio (350 m LOS) and 24 V relay outputs in one chassis [Elektroda, p.kaczmarek2, post #21541966] No extra coordinator is required.

How much does a basic kit cost?

A starter stack (mH-Developer, filter, PSU, LAN-Radio, 1 IO module) lists at approx. €750–€800 incl. VAT in Poland (F&F e-shop, 2025-06). Prices drop when buying contractor bundles.

Do battery sensors report low-battery status centrally?

Yes. Fox and WebManager show battery percentage and push a replace-battery alert when voltage falls below the module’s threshold [Elektroda, p.kaczmarek2, post #21546786]

What’s the real-world radio range inside concrete buildings?

A handheld rH-S4T switch controlled relays three floors up and one basement level down (~25 m vertical, multiple walls) before losing link [Elektroda, p.kaczmarek2, post #21541966]

Edge case: the LAN-Radio gateway fields are greyed-out—how do I fix it?

Press and hold the RESET/CFG button for 5 s, then reload its web page; the IP fields become editable [Elektroda, p.kaczmarek2, post #21541966]

Quick 3-step guide: how do I pair a wireless dimmer?

  1. In WebManager → Gates, tap ‘Pair’. 2. Press the module’s case button once within 15 s. 3. Wait 5 s; it shows ‘Paired’ and appears in Devices list [Elektroda, p.kaczmarek2, post #21541966]

Can I mix legacy F&Home modules with the new release?

Yes. New firmware is backward-compatible, so discontinued wired modules work alongside LR radio units via the same server [Elektroda, p.kaczmarek2, post #21541966]

Which external platforms integrate with F&Home?

The Configurator outputs MQTT and HTTP; users bridge it to Home Assistant or Grafana dashboards via Node-RED nodes (F&F API guide, 2024).

Failure scenario: what happens if CAN bus wiring is reversed?

Modules fail to enumerate and WebManager flags ‘CAN timeout’. No hardware damage, just swap A/B lines and reboot [F&F Service Note, 2023].

Does the system log power consumption of connected loads?

Not natively; you must add rH-PZEM energy meters or third-party Modbus kWh meters and map them in Configurator (F&Home Integrator FAQ, 2025).

Is there an annual licence or cloud fee?

No recurring fees. Firmware, Fox app, and cloud relay service are free of charge [F&F Terms, 2024].

Can I flash custom firmware on radio modules?

No. Firmware is signed; tampering voids CE compliance and breaks pairing security [F&F Security Whitepaper, 2024].