Maximum number of 150W LED streetlights on 100A breaker with 12 AWG THHN wire?

372 14
ADVERTISEMENT
  • #1 21677818
    joey martin
    Anonymous  
  • ADVERTISEMENT
  • #2 21677819
    April Grace Ranario
    Anonymous  
  • ADVERTISEMENT
  • #3 21677820
    David Ashton
    Anonymous  
  • ADVERTISEMENT
  • #4 21677821
    Elizabeth Simon
    Anonymous  
  • #5 21677822
    joey martin
    Anonymous  
  • #6 21677823
    Elizabeth Simon
    Anonymous  
  • #7 21677824
    joey martin
    Anonymous  
  • #8 21677825
    joey martin
    Anonymous  
  • #9 21677826
    Elizabeth Simon
    Anonymous  
  • #10 21677827
    joey martin
    Anonymous  
  • #11 21677828
    Elizabeth Simon
    Anonymous  
  • #12 21677829
    joey martin
    Anonymous  
  • ADVERTISEMENT
  • #13 21677830
    Jayaprakash JP
    Anonymous  
  • #14 21677831
    Elizabeth Simon
    Anonymous  
  • #15 21677832
    joey martin
    Anonymous  

Topic summary

✨ The discussion addresses the maximum number of 150W LED streetlights that can be connected on a 100A breaker using 12 AWG THHN wire, considering a 240V supply and lights spaced approximately 25 meters apart. Each 150W LED light at 240V draws about 0.625A. Voltage drop is a critical factor, with a recommended maximum of 3-5%. For 12 AWG wire (5.21 Ohm/km resistance), the voltage drop per 25-meter segment carrying 0.625A is approximately 0.1625V per light segment. Calculations show that up to 8 lights can be strung on 12 AWG wire before exceeding a 3% voltage drop (~7.2V). Beyond the 8th light, upgrading to 10 AWG wire is advised to maintain voltage drop within limits. The total circuit length can reach 250-300 meters with series wiring, but voltage drop and current decrease along the run must be considered. Using multiple branches or loop/ring circuits can reduce wire gauge requirements and improve fault tolerance. Underground conduit with concrete encasement is used for wiring. The choice of wire gauge from underground conduit to the steel post can be smaller (e.g., 14 AWG) depending on current and distance, but must comply with voltage drop and safety standards. Wire sizing tables and Ohm’s law calculations are essential tools for design optimization.

FAQ

TL;DR: At 240 V with 25 m pole spacing, 12 AWG supports about 8×150 W LED streetlights before exceeding a 3% voltage drop. “Increase wire size closest to the power to go farther.” [Elektroda, Elizabeth Simon, post #21677831]

Why it matters: This helps you size conductors economically while keeping lights bright and within drop limits.

Quick Facts

How many 150 W LED streetlights can 12 AWG carry at 240 V with 25 m spacing?

Eight fixtures keep total drop near 7.2 V (3%). The ninth span pushes cumulative drop past 3%, so stop at eight on straight 12 AWG. “Increase wire size on sections closest to the power” if you need more distance. [Elektroda, Elizabeth Simon, post #21677831]

What current does one 150 W, 240 V LED draw, and what about ten lights?

One lamp draws 0.625 A at 240 V. Ten identical lamps in one run draw 6.25 A at the source segment. Use this current to estimate voltage drop per segment. [Elektroda, Elizabeth Simon, post #21677823]

Why does the first cable segment near the breaker drop the most voltage?

That segment carries the sum of all downstream currents. With N lamps, its drop is Rsegment × I × N, making it the largest contributor. [Elektroda, Elizabeth Simon, post #21677831]

What voltage-drop limit should I design to for streetlighting?

Target 3% when uniform brightness is critical. Some projects accept up to 5%. Confirm your luminaire’s tolerance and any local spec. [Elektroda, Elizabeth Simon, post #21677828]

Can I mix gauges along the run to reduce cost?

Yes. Use heavier wire for the first spans near the source, then taper to 12 AWG later. This cuts total drop and material cost. [Elektroda, Elizabeth Simon, post #21677831]

How far can I continue after the 8th light if I switch to 10 AWG?

Upgrading wire at the source segments lets you add lights beyond eight. Calculate again with lower resistance for those early spans to stay under 3%. [Elektroda, Elizabeth Simon, post #21677831]

What is a ring (loop) circuit and does it help?

A ring uses two parallel feeds forming a loop, alternating connections to balance current and cut drop. It also adds fault tolerance if one leg opens. [Elektroda, David Ashton, post #21677820]

How do I calculate segment-by-segment voltage drop quickly?

  1. Compute lamp current (I = P/V).
  2. Get round-trip resistance per span.
  3. Sum drops: span k drop = Rspan × I × lamps downstream, then total and compare to 3%. [Elektroda, Elizabeth Simon, post #21677831]

Is 12 AWG THHN appropriate between poles 25 m apart underground?

For load, 12 AWG works up to eight fixtures at 240 V, 25 m spacing. Confirm conduit fill and thermal conditions separately for compliance. [Elektroda, Elizabeth Simon, post #21677831]

What gauge should I use inside the steel pole up to the luminaire?

Match conductor size to the branch-circuit design and drop target. If the run from base to head is short, 14 AWG may suffice by drop, but keep it consistent with upstream protection. [Elektroda, Elizabeth Simon, post #21677828]

How many 150 W fixtures can a 100 A breaker support by load alone?

By load math alone, many. Ten fixtures draw 6.25 A, far below 100 A. Sizing should still respect conductor limits and voltage-drop design. [Elektroda, Elizabeth Simon, post #21677823]

What failure edge case should I plan for on a long straight run?

If the source-near segment opens, downstream lights go dark. A ring configuration keeps lights on by feeding from the other side. [Elektroda, David Ashton, post #21677820]