Cross-section of wire for 24V step controller (13 outputs, 2A), wire 1mm2, load 26A

jacuss89 795 4
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 20515662
    jacuss89
    Level 2  
    Hello, I bought a staircase controller with 18 outputs to control I used 24V led tape (4 metres of tape per output of about 2 A) I used 13 of the 18 outputs.
  • ADVERTISEMENT
  • #2 20520342
    funzen
    Level 24  
    1.What kind of led strips how many watts per running meter.
    2.What type/model of controller ?
    3.How many meters of led strip in total is there to be ?
    4.Power supply type/model ?
  • ADVERTISEMENT
  • #3 20524647
    jacuss89
    Level 2  
    1 pointless LED strip 10w per meter 24 v
    2 staircase lighting controller Ntronic
    3 Total 52 meters of led strip in the controller I used 13 inputs out of 18 for each input 4 meters of 40 w strip
    4 power supply 1000w impulse 24 v ( I know it's bigger than I need but I needed power for one more project)
    Maybe I asked the question wrong I don't understand why in this controller there is a constant under LED lighting and the - goes to the driver 13 wires 1 mm2 goes with - and one wire from the driver goes with - to the power supply
  • ADVERTISEMENT
  • #4 20524959
    funzen
    Level 24  

    + from the power supply to the split location I would give 4mm2 (max 5m) then to the individual led strips 1mm2 and + to the controller 1mm2
    - from the power supply to the controller 4mm2 (max 5m)
    - from the controller to the led strips 1mm2
    Power supply and controller as close to each other as possible (e.g. up to 1m) so that voltage drops are minimal.
    The load on the power supply depends of course on the program in the controller and the continuous lighting time of all used
    channels in the controller.
    Here you have a calculator to calculate the diameter of the wires for the leds
    https://enterius.eu/wsparcie/kalkulator-przekroju-przewodow-led/
  • #5 20525783
    jacuss89
    Level 2  
    I did exactly the same thing, except that from the power supply I put 3 wires with 4 mm2 to divide From the controller - it can have Max 1.5 mm2 (larger will not fit) as the manufacturer calculated that there are 18 inputs of 4 A with such a small cross-section.