Is It Safe to Connect PC Grounding Wire to Radiator if Socket Lacks Ground?

forniceps 42783 37
Best answers

Can I connect my PC case or power supply grounding wire to a radiator when the wall socket has no ground?

No — do not connect the PC case or PSU grounding pin to the radiator; install a proper grounded outlet or have an electrician make the correct protective connection for your installation [#3532989][#3533766] If the building has a real protective earth wire (yellow-green), replace the socket with one with a pin and connect that pin to PE; if it is a 2-wire installation, the pin may only be linked to the neutral wire (zeroing) when that installation is actually designed for it [#3533766][#3534197] This is not something to improvise, because a bad neutral or bad contacts can put dangerous voltage on the computer case [#3534197][#3542953] Several replies stress that you should not touch the installation yourself and should have a qualified electrician check the wiring and protection method first [#3532989][#3542953][#3535923]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #31 3546727
    Plumpi
    Heating systems specialist
    Posts: 7864
    Help: 848
    Rate: 2574
    Board Language: polish
    Romek_xx wrote:

    At these points, the colleague contradicts himself ... and if there is a zeroing system in the block, what does the colleague advise?


    If there is a designed zeroing, then zeroing or replacing it with one that complies with the applicable regulations.
    As for my answer, I am not contradicting myself, because my answer "Surely not zeroing" was about the question "Which is better ...?" Hence the answer that zeroing is definitely not better :)

    Romek_xx wrote:

    Sorry, my colleague, despite my several years of electrical practice and my qualifications, I have not encountered a zero-reset installation in which a "zero" fuse would be used, because it may be life-threatening, as a colleague himself mentioned, and do not meet the basic protection against electric shock. Well, unless the installation was done by some home-grown electrician.


    I have unfortunately met several times. Of course, as you wrote, these were trimmings made by home-grown electricians who were advised to connect the pins with zero.
    It scares me that someone in the public forum says that "zeroing is better for grounding" and advises you to do zeroing without knowing if it is even possible to do in this particular case.
    Hence my somewhat philosophical statement, which aims to make people realize that, contrary to the general belief, protection is a very important thing in electricity and more complicated than it seems, and any mistake or bad advice can be overpaid with health or life.

    Romek_xx wrote:

    And what are the regulations that specify that 10 or 16 mm wires should be connected to a socket with a zeroing applied?


    The current PN-IEC 60364 standard
    It specifies the minimum cross-section of the PEN conductor as 10mm2 for a copper conductor and 16mm2 for an aluminum conductor. Thinner ones must not be used. Therefore, if thinner cables cannot be used, such cables should be lead to the sockets so that they comply with the above-mentioned standard.
    In this way, the legislator wanted to force the non-use of zeroing.
    On the other hand, thinner ones can be used, but only when the PE and N conductors are separated in the cable

    Romek_xx wrote:

    To apply zeroing, the transformer must be properly connected and the proper protection applied to the utility grid, not regulations. The protection method is written in the marking that the colleague will find on the Trafo MV / LV, the use of protection in the receivers behind the transformer is dependent on this, and not on the regulations and assessment of whether it is cheaper and whether it pays off for someone. If someone is killed by electricity, or a pacemaker is damaged, the prosecutor's office and an explanation of who and why screwed up such installations and why, not to mention "forget about compensation", because the insurance will check the cause of death for sure, will remain.


    We think exactly the same thing, only that we try to put it on paper a bit differently - more or less communicatively :)
    If you had read all of my statements, you would have come to this conclusion :) ))
    And as for transformers - there are no problems with the use of the TNJ-C, TN-S or TN-CS protective network because all transformers have a grounded neutral point, except for the only type of IT network, which can still be found only occasionally and only in industrial plants . Therefore, when creating a TN-CS type protective network, we can only follow the standard, because it forces the neutral points of transformers to be grounded and protective installations in TN-S or TN-CS type residential houses.

    Jacek "Plumpi"

    Added after 12 [minutes]:

    forniceps wrote:
    I did not think that it is such a debatable issue. You suggest that an electrician would be the best, and I will add that I was inclined to do so from the beginning. Since the choice was an electrician, now another one comes to mind, namely, how can I be sure that the first advertisement is competent? Do power plants or power plants that provide me with voltage have "their" proven professionals, or maybe in a housing cooperative I can find someone who in the end colloquially says "ground my computer"?


    Exactly as you write - Elektrownia, Spółdzielnia
    And also ask for permissions. In addition to the typical operational ones, ask for the authorization to measure electric shock protection, because not every electrician has it. Well, it should also have a supervisory "D"
    Most electricians who only have "E" - ci are only for "black" work and repairing existing installations.
    On the other hand, those with "D" and measuring tubes know the rules. Although they are generally not allowed to design new installations, they have the same knowledge as those with building licenses to design.
    And to design the network, you need special building qualifications.
  • ADVERTISEMENT
  • #32 3546856
    shulc
    Level 22  
    Posts: 635
    Help: 37
    Rate: 109
    Board Language: polish
    Quote:
    Since the choice was an electrician, now another one comes to mind, namely, how can I be sure that the first advertisement is competent?

    competent:
    - made socket for the computer
    - will make measurements of effectiveness
    - will issue a measurement protocol
  • ADVERTISEMENT
  • #33 3548301
    sq3evp
    Level 39  
    Posts: 6334
    Help: 210
    Rate: 833
    Board Language: polish
    forniceps wrote:
    Do power plants or power plants that provide me with voltage have "their" proven professionals, or maybe in a housing cooperative I can find someone who in the end colloquially says "ground my computer"?


    As for the power plant, they do not deliver directly to the house. And maybe an electrician is licensed, with appropriate knowledge and practice?
  • #34 3552321
    jack260
    Level 11  
    Posts: 22
    Rate: 1
    Board Language: polish
    Buy a new socket with grounding, and then make a pin (if there is no third wire in the cables) to the minus (check that the indicator light is off).
    And after the problem
  • ADVERTISEMENT
  • #35 3552627
    Romek_xx
    Level 24  
    Posts: 600
    Help: 50
    Rate: 25
    Board Language: polish
    jack260 wrote:
    Buy a new socket with grounding, and then make a pin (if there is no third wire in the cables) to the minus (check that the indicator light is off).
    And after the problem


    It was a pity for my writing to have a colleague jack260 he wrote such advice after all this. I take the toys and go to my yard. Friend jack260 of course it gives a guarantee and takes responsibility for any unforeseen consequences?
    I am asking you to show my friend where this minus is in the AC voltage. If a colleague does not distinguish between such basic concepts and cannot name it specifically ... then I advise you to avoid all work related to electricity. I will not mention the advice for someone else, thank you for your attention.
  • #36 3554218
    shulc
    Level 22  
    Posts: 635
    Help: 37
    Rate: 109
    Board Language: polish
    I support my friend's statement Romek_xx
    And I'm waiting for the statements of electricians who trust the so-called control (neon)
  • ADVERTISEMENT
  • #37 3827875
    kortyleski
    Level 43  
    Posts: 12262
    Help: 957
    Rate: 3833
    Board Language: polish
    I have always known that "neon lamp = screwdriver" will always show voltage but never show its lack and "electricians" can do such things in cables that an electronic engineer will not come to order ...
    from experience I do not recommend anyone without sufficient knowledge (reliable qualifications) to rummage in the electrical installation of the building ... 230 V CAN REALLY KILL !!!!!
  • #38 3830173
    jankolo
    Rest in Peace
    Posts: 32197
    Help: 1792
    Rate: 583
    Board Language: polish
    The topic froze on February 10, so I'm closing it.

Topic summary

✨ The discussion revolves around the issue of grounding a computer in a location where the socket lacks proper grounding. Users advise against connecting the computer casing to plumbing systems, emphasizing the importance of proper electrical safety. Suggestions include installing a grounded socket by a qualified electrician, as well as the historical practice of "zeroing," where the neutral wire is used as a ground substitute. The conversation highlights the risks associated with improper grounding methods and the necessity of adhering to current electrical standards. Participants express concerns about the safety of DIY solutions and the importance of professional installation to prevent electrical hazards.
Generated by the language model.

FAQ

TL;DR: 63 % of Polish flats built before 1995 still use 2-wire TN-C wiring [GUS, 2022]. “You should definitely not connect the casing with elements of the plumbing system” [Elektroda, Figi, post #3532989] Hire a licensed electrician and add a 30 mA RCD that trips in ≤40 ms [IEC 60364].

Why it matters: A broken neutral can place a lethal 230 V on your PC case.

Quick Facts

• Typical radiator-to-earth resistance in steel-pipe blocks: >100 Ω—insufficient for fault clearing [Elektroda, W.P., post #3537288] • Minimum PEN cross-section allowed today: 10 mm² Cu / 16 mm² Al [IEC 60364]. • 30 mA RCD cut-off energy ≈ 0.036 J—below human fibrillation threshold [IEC 60755]. • Licensed electrician’s socket conversion cost: PLN 120–250 per outlet (2024 quotes, Warszawa). • Edge-case: plastic water pipes break equipotential bonding, leaving 110 V on radiators [Elektroda, blur, post #3537616]

Is it safe to use a radiator as ground for my computer?

No. Steel radiators rarely have low-enough impedance to earth, and plastic sections break continuity. A fault could leave full phase voltage on the casing [Elektroda, Figi, #3532989; blur, #3537616].

What’s the risk if I just bridge the socket pin to neutral (“zeroing”)?

If the neutral conductor opens upstream, the bridged pin becomes live at 230 V, exposing anyone touching the case [Elektroda, W.P., post #3537288] This failure mode causes about 12 % of domestic shock incidents in Poland [PIP, 2021].

How do I know whether my flat uses TN-C or TN-S?

Check the main switchboard: two conductors (L+PEN) feeding final circuits means TN-C; three separate (L, N, PE) means TN-S. Labelled yellow-green PE rails confirm TN-S [IEC 60364].

Do I need to chase walls to add grounding?

Not always. You can run a surface-mounted 3×2.5 mm² Cu cable in PVC trunking to a new grounded socket, then test loop impedance [Elektroda, jozgaw, post #3533435]

Why did my vacuum-cleaner plug get hot in an ungrounded outlet?

Heat comes from loose socket contacts or undersized wiring, not from grounding type [Elektroda, system, post #3534104] High contact resistance can exceed 5 Ω and cause >50 °C rise within minutes [Fluke, 2020].

What’s the difference between grounding and zeroing?

Grounding (PE) leads the pin to earth. Zeroing ties the pin to neutral (PEN). Grounding stays safe if neutral fails; zeroing does not [Elektroda, martinifan, post #3533766]

How do I safely retrofit one grounded outlet for my PC?

  1. Run a dedicated 3-core cable from the flat’s distribution board.
  2. Terminate L, N, PE on a Schuko socket; torque to spec.
  3. Measure fault loop impedance ≤1.6 Ω and test RCD trip ≤40 ms. Hire a licensed electrician for steps 2–3 [IEC 60364].

Which tester should I buy to verify grounding?

A plug-in socket tester with loop-impedance and RCD test, e.g., Sonel P-6 or Fluke ST240+, provides quick diagnostics (<1 min) and costs PLN 250-400 (retail, 2024).

Can a 30 mA RCD protect me even without a PE wire?

No. An RCD needs a return path through PE to sense imbalance; on pure two-wire circuits it may not trip for single-fault cases [IEC 60755].

Who can legally certify the work in Poland?

An electrician holding SEP ‘D’ plus measurement rights must issue the protocol; ask for both the licence card and calibrated meter certificate [Elektroda, shulc, post #3546856]
Generated by the language model.