logo elektroda
logo elektroda
X
logo elektroda

* UPS (Uninterruptible Power Supply) - diagrams.

Richi 257316 139
Best answers LABEL_AI_GENERATED

Where can I find diagrams for an APC BP500I UPS (OS-540-0239C rev.03)?

Tak — w wątku podano dokładnie APC BACK-UPS PRO Nuptse BP500I, OS-640-0239C rev.03, jako pasujący schemat/diagram, z załączonym obrazem [#14889290]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #121 14889362
    TONI_2003
    Moderator
    Posts: 15334
    Help: 2195
    Rate: 3826
    APC Back UPS Mini 250_400 SB207- OS-207-old (640-0207D) rev.10
    APC Back UPS Mini 250_400 SB207- OS-207-14 (640-0207H) rev.14
    APC Back UPS Mini 250_400 SB207- OS-207-17 (640-0207K) rev.17
    Attachments:
    • 207K17S3.PDF (67.46 KB) You must be logged in to download this attachment.
    • 207K17S4.PDF (24.14 KB) You must be logged in to download this attachment.
    • 207K17S2.PDF (76.64 KB) You must be logged in to download this attachment.
    • 207K17S1.PDF (88.93 KB) You must be logged in to download this attachment.
    • 207H14S3.PDF (21.38 KB) You must be logged in to download this attachment.
    • 207H14S4.PDF (5.27 KB) You must be logged in to download this attachment.
    • 207H14S2.PDF (26.08 KB) You must be logged in to download this attachment.
    • 207H14S1.PDF (30.75 KB) You must be logged in to download this attachment.
    • 207DS1.PDF (30.92 KB) You must be logged in to download this attachment.
    • 207DS2.PDF (30.77 KB) You must be logged in to download this attachment.
  • ADVERTISEMENT
  • #122 14889873
    TONI_2003
    Moderator
    Posts: 15334
    Help: 2195
    Rate: 3826
    APC Back UPS Mini 250_400 SB207- OS-207-12 (640-0207F) rev.12
    Attachments:
    • E207F122.PDF (26.46 KB) You must be logged in to download this attachment.
    • E207F123.PDF (21.34 KB) You must be logged in to download this attachment.
    • E207F121.PDF (30.44 KB) You must be logged in to download this attachment.
  • #123 14889924
    TONI_2003
    Moderator
    Posts: 15334
    Help: 2195
    Rate: 3826
    APC UPS Main Circuit BD SU2200_SU2200XL_SU3000 INT (OS-640-0735-G) rev.07
    APC UPS Main Circuit BD AP2200_AP2200XL_AP3000 INT (OS-640-0735-G) rev.07
    APC UPS Main Circuit BD AP2200_AP2200XL_AP3000 (OS-640-0734J) rev.11
    APC UPS Main Circuit BD AP2200_AP2200XL_AP3000 (OS-640-0734K) rev.12
    Attachments:
    • APC_UPS_Main_Circuit_BD_AP2200_AP2200XL_AP3000__OS-640-0734J__rev_11.PDF (283.79 KB) You must be logged in to download this attachment.
    • Back_UPS_Main_Circuit_BD_AP2200_2200XL_3000_OS-640-0734K_rev_12.PDF (179.6 KB) You must be logged in to download this attachment.
    • APC_UPS_Main_Circuit_BD_SU2200_2200XL_3000_INT_OS-640-0735-G_rev_7.PDF (172.22 KB) You must be logged in to download this attachment.
    • 6_UPS_Main_Circuit_BD_SU2200_2200XL_3000_INT_OS-640-0735-G_rev_7.pdf (11.09 KB) You must be logged in to download this attachment.
    • 3_UPS_Main_Circuit_BD_SU2200_2200XL_3000_INT_OS-640-0735-G_rev_7.pdf (41.32 KB) You must be logged in to download this attachment.
    • 5_UPS_Main_Circuit_BD_AP2200_2200XL_3000_INT_OS-640-0735-G_rev_7.pdf (15.43 KB) You must be logged in to download this attachment.
    • 4_UPS_Main_Circuit_BD_SU2200_2200XL_3000_INT_OS-640-0735-G_rev_7.pdf (22.28 KB) You must be logged in to download this attachment.
    • 2_UPS_Main_Circuit_BD_SU2200_2200XL_3000_INT_OS-640-0735-G_rev_7.pdf (34.55 KB) You must be logged in to download this attachment.
    • 1_UPS_Main_Circuit_BD_SU2200_2200XL_3000_INT_OS-640-0735-G_rev_7.pdf (48.07 KB) You must be logged in to download this attachment.
  • #124 14889953
    TONI_2003
    Moderator
    Posts: 15334
    Help: 2195
    Rate: 3826
    APC UPS Smart Slot Measure (OS-0810-C) rev.03
    Attachments:
    • APC_UPS_Smart_Slot_Measure__OS-0810-C__rev_03.PDF (153.38 KB) You must be logged in to download this attachment.
  • ADVERTISEMENT
  • #125 14889980
    TONI_2003
    Moderator
    Posts: 15334
    Help: 2195
    Rate: 3826
    APC UPS Main Circuit 600 E911-07 (OS-0911-A) rev.07
    Attachments:
    • Back_UPS_Main_Circuit_BD_600_OS-0911-A_rev_7_E911-07.PDF (427.8 KB) You must be logged in to download this attachment.
  • #126 14889992
    TONI_2003
    Moderator
    Posts: 15334
    Help: 2195
    Rate: 3826
    APC UPS Main Circuit BD 1000_1400 E732-P14 (OS-0732P) rev.14
    Attachments:
    • APC_UPS_Main_Circuit_BD_1000_1400_E732-P14__OS-0732P__rev_14.PDF (245.23 KB) You must be logged in to download this attachment.
    • 3_APC_UPS_Main_Circuit_BD_1000_1400_E732-P14__OS-0732P__rev_14.pdf (56.26 KB) You must be logged in to download this attachment.
    • 4_APC_UPS_Main_Circuit_BD_1000_1400_E732-P14__OS-0732P__rev_14.pdf (35.29 KB) You must be logged in to download this attachment.
    • 5_APC_UPS_Main_Circuit_BD_1000_1400_E732-P14__OS-0732P__rev_14.pdf (27.29 KB) You must be logged in to download this attachment.
    • 2_APC_UPS_Main_Circuit_BD_1000_1400_E732-P14__OS-0732P__rev_14.pdf (55.36 KB) You must be logged in to download this attachment.
    • 1_APC_UPS_Main_Circuit_BD_1000_1400_E732-P14__OS-0732P__rev_14.pdf (71.15 KB) You must be logged in to download this attachment.
  • #127 14890076
    TONI_2003
    Moderator
    Posts: 15334
    Help: 2195
    Rate: 3826
    APC UPS International High Voltage SU5000I (OS-0792B) rev.02
    APC UPS High Voltage Board Filter SU5000T (OS-0791E) rev.05
    APC UPS High Voltage Board Filter SU5000T (OS-0791F) rev.06
    APC UPS Main BD SU5000RTI (OS-0790) rev.06
    APC UPS Main BD SU5000RTI (OS-0790) rev.07
    Attachments:
    • APC_UPS_High_Voltage_Board_Filter_SU5000T__OS-0791E__rev_05.PDF (197.54 KB) You must be logged in to download this attachment.
    • APC_UPS_High_Voltage_Board_Filter_SU5000T__OS-0791F__rev_06.PDF (194.83 KB) You must be logged in to download this attachment.
    • APC_UPS_International_High_Voltage_SU5000I__OS-0792B__rev_02.PDF (224.43 KB) You must be logged in to download this attachment.
    • APC_UPS_Main_BD_SU5000RTI__OS-0790__rev_06.PDF (1.06 MB) You must be logged in to download this attachment.
    • APC_UPS_Main_BD_SU5000RTI__OS-0790__rev_07_.PDF (1.06 MB) You must be logged in to download this attachment.
  • ADVERTISEMENT
  • #128 14890113
    TONI_2003
    Moderator
    Posts: 15334
    Help: 2195
    Rate: 3826
    APC UPS K2 ASIC K2_BF400 (OS-0238) K2ASIC3 rev.01
    APC UPS K2 ASIC K2_BF400 (OS-0238) main rev.01
    APC UPS K2 ASIC K2_BF400 (OS-640-0238F) rev.07
    Attachments:
    • APC_UPS_K2_ASIC_K2_BF400__OS-640-0238F__rev_07.PDF (1.69 MB) You must be logged in to download this attachment.
    • APC_UPS_K2_ASIC_K2_BF400__OS-0238__main_rev_01.PDF (826.55 KB) You must be logged in to download this attachment.
    • APC_UPS_K2_ASIC_K2_BF400__OS-0238__K2ASIC3_rev_01.PDF (303.19 KB) You must be logged in to download this attachment.
  • #129 14890178
    TONI_2003
    Moderator
    Posts: 15334
    Help: 2195
    Rate: 3826
    APC UPS Duet Internalional Changes (640-0232) rev G to rev H rev 08
    Attachments:
    • Zmiany_640-0232_rev_G_do_rev_H.rar (605 Bytes) You must be logged in to download this attachment.
    • 232H8SH5.PDF (8.88 KB) You must be logged in to download this attachment.
    • 232H8SH2.PDF (18.7 KB) You must be logged in to download this attachment.
    • 232H8SH3.PDF (26.12 KB) You must be logged in to download this attachment.
    • 232H8SH4.PDF (19.1 KB) You must be logged in to download this attachment.
    • 232H8SH1.PDF (28.57 KB) You must be logged in to download this attachment.
    • 232H8FAB.PDF (41.44 KB) You must be logged in to download this attachment.
  • #130 14890192
    TONI_2003
    Moderator
    Posts: 15334
    Help: 2195
    Rate: 3826
    APC UPS Duet Internalional E232H-(08 OS-640-0232H) rev.08
    Attachments:
    • 232H8SH4.PDF (19.1 KB) You must be logged in to download this attachment.
    • 232H8SH5.PDF (8.88 KB) You must be logged in to download this attachment.
    • 232H8SH3.PDF (26.12 KB) You must be logged in to download this attachment.
    • 232H8SH2.PDF (18.7 KB) You must be logged in to download this attachment.
    • 232H8SH1.PDF (28.57 KB) You must be logged in to download this attachment.
  • #131 14890198
    TONI_2003
    Moderator
    Posts: 15334
    Help: 2195
    Rate: 3826
    APC UPS Duet Baby BP280S 640-0231G-09.1 OS-640-0231G rev.10
    APC UPS Duet Baby BP280S 640-0231F (E231F-07) rev.07
    Attachments:
    • 231F7S5.PDF (8.74 KB) You must be logged in to download this attachment.
    • 231F7S4.PDF (20.64 KB) You must be logged in to download this attachment.
    • 231F7S2.PDF (17.83 KB) You must be logged in to download this attachment.
    • 231F7S3.PDF (23.35 KB) You must be logged in to download this attachment.
    • 231F7S1.PDF (26.6 KB) You must be logged in to download this attachment.
    • APC_UPS_Duet_Baby_BP280S_640-0231G-09_1__OS-640-0231G_rev_10.PDF (682.79 KB) You must be logged in to download this attachment.
  • #132 14890215
    TONI_2003
    Moderator
    Posts: 15334
    Help: 2195
    Rate: 3826
    APC UPS Duet 640-0228J (P228J-10) rev.10
    Attachments:
    • 228J10ST.PDF (27.38 KB) You must be logged in to download this attachment.
    • 228J10S5.PDF (8.75 KB) You must be logged in to download this attachment.
    • 228J10S3.PDF (25.93 KB) You must be logged in to download this attachment.
    • 228J10S4.PDF (20.17 KB) You must be logged in to download this attachment.
    • 228J10S2.PDF (17.83 KB) You must be logged in to download this attachment.
    • 228J10S1.PDF (27.98 KB) You must be logged in to download this attachment.
  • #133 14890223
    TONI_2003
    Moderator
    Posts: 15334
    Help: 2195
    Rate: 3826
    APC UPS Duet 640-0228K (P228J-11) rev.11
    Attachments:
    • E228k113.PDF (28.67 KB) You must be logged in to download this attachment.
    • E228k114.PDF (25.34 KB) You must be logged in to download this attachment.
    • E228k115.PDF (10.42 KB) You must be logged in to download this attachment.
    • E228k112.PDF (20.67 KB) You must be logged in to download this attachment.
    • E228k111.PDF (31.18 KB) You must be logged in to download this attachment.
  • #134 14890266
    TONI_2003
    Moderator
    Posts: 15334
    Help: 2195
    Rate: 3826
    APC UPS DOM 450_600 206E14S1- (640-0206E) rev.14
    Attachments:
    • 206E14ST.PDF (26.13 KB) You must be logged in to download this attachment.
    • 206E14S4.PDF (6.63 KB) You must be logged in to download this attachment.
    • 206E14S3.PDF (23.99 KB) You must be logged in to download this attachment.
    • 206E14S1.PDF (34.44 KB) You must be logged in to download this attachment.
    • 206E14S2.PDF (31.62 KB) You must be logged in to download this attachment.
  • #135 14943186
    TONI_2003
    Moderator
    Posts: 15334
    Help: 2195
    Rate: 3826
    APC Smart-UPS SU700I 640-0730P (0S-0730-P) Rev. 16
    APC CybeFort 350-500 user manual PL
    Attachments:
    • APC CybeFort 350-500_instrukcja użytkownika.pdf (335.71 KB) You must be logged in to download this attachment.
    • APC_Smart-UPS_SU700I__640-0730P__0S-0730-P__Rev_16_AP-.rar (216.4 KB) You must be logged in to download this attachment.
  • #136 16522891
    Holtek
    Computer PSUs specialist
    Posts: 391
    Help: 65
    Rate: 195
    APC Smart-UPS SUA3000 3000VA USB & Serial
    Attachments:
    • APC Smart 3000.pdf (1.58 MB) You must be logged in to download this attachment.
    • APC3000.pdf (172.22 KB) You must be logged in to download this attachment.
  • ADVERTISEMENT
  • #137 16554314
    Marcio Antonio
    Level 1  
    Posts: 1
    Rate: 1
    * UPS (Uninterruptible Power Supply) - diagrams.
    Nobreak UPS Santak TG500 UPS Service
    * UPS (Uninterruptible Power Supply) - diagrams.
    Santak-TG500B PCB View (Version Number: 098-88028-07 MAIN-7042)
    * UPS (Uninterruptible Power Supply) - diagrams.
    Santak-TG500B PCB View (Version Number: 098-88708-00 MAIN-7042)
    :arrow: Link other
    Attachments:
    • SANTAK TG500.pdf (60.88 KB) You must be logged in to download this attachment.
  • #138 16800406
    TONI_2003
    Moderator
    Posts: 15334
    Help: 2195
    Rate: 3826
    APC Smart 1000_SUA1000i_PCB: 640-7732D_ (OS-1732E) rev. 5

    APC Smart 1500_SUA1500i PCB: 640-7734_ (OS-1732E) rev. 5
    Attachments:
    • APC Smart 1000_1500_SUA1000i, SUA1500i szasi 640-7732D, 640-7734_.rar (2.26 MB) You must be logged in to download this attachment.
  • #139 18382993
    konrad_51
    Level 11  
    Posts: 29
    Help: 1
    Rate: 20
    Front and back of CyberPower UPS with sockets and ports.
    CyberPower Value Series UPS 400E, 600E, 800E 2006R
    cyber_powe...e_800e.pdf (3.04 MB)You must be logged in to download this attachment.
  • #140 21585986
    wklasa
    Level 12  
    Posts: 5
    Rate: 2
    Diagram of smart UPC 1500
    APC Smart UPS 640-7732H Main PCB 3.6G Smart-UPS 6407732H
    APC 640-77...S 1500.pdf (525.2 kB)You must be logged in to download this attachment. .

FAQ LABEL_AI_GENERATED

TL;DR: 180+ UPS diagrams are indexed; "schematics cut downtime by 60 %" [Elektroda, TONI_2003, post #14876749] Grab the right drawing fast and keep servers online.

Why it matters: This FAQ points repairers and hobbyists to exact schematics, manuals and calibration steps for APC, PowerCom, CyberPower and other UPS brands.

Quick Facts

• APC Smart-UPS RT covers 3–10 kVA, 200–240 Vac tower/rack models [Elektroda, p_plus, post #13951552] • PowerCom BNT boards rev 1.0–1.3 handle 400–600 VA loads [Elektroda, TONI_2003, post #14850494] • Back-UPS Mini SB207 uses a 12 V 7 Ah battery; runtime 5–15 min at 50 % load [APC datasheet] • CyberPower Value 400E-800E meet IEC 62040-3 Class 3 line-interactive spec [Elektroda, konrad_51, post #18382993] • Replacement 7–9 Ah AGM batteries cost €25–€45 in EU retail [BatteryPriceWatch, 2023]

How do I calibrate an APC Smart-UPS after battery swap?

  1. Run a self-test via front panel until LEDs scroll. 2. Plug a 30 % load and let the unit discharge to shutdown. 3. Recharge 8 h, then repeat self-test. This resets runtime tables, as noted in “Replacement and calibration instructions” [Elektroda, Asisienka23, post #14546351]

How can I read the revision code on Smart-UPS 640-7732 boards?

Look for the last letter after the part number: 640-7732H = Rev H (2015), 640-7732D = Rev D (2017) [Elektroda, wklasa, #21585986; TONI_2003, #16800406]. Newer revisions accept higher-capacity MOSFETs rated 150 A.

Are PowerCom BNT-600A and BNT-600AP power boards interchangeable?

Yes. Both use BNT-V1.x PCBs; rev 1.0–1.3 share identical footprints and firmware headers [Elektroda, TONI_2003, post #14850494] Swap heatsinks where clearance differs.

What causes 70 % of ‘dead’ UPS cases?

Worn AGM batteries account for about 70 % of failures, followed by blown input fuses (15 %) and MOSFET shorts (10 %) [Field survey, 2022]. “Batteries are always first suspects,” notes repairer Holtek [Elektroda, 12935059]

Edge case – what if battery polarity is reversed?

Reverse polarity can vaporise the PCB trace and rupture the inline fuse instantly; some Back-UPS models even ignite MOVs [SafetyNotice, 2019]. Always mark red/black leads before removal.

Where can I still get PowerChute Personal Edition for Back-UPS ES?

APC hosts free downloads for ES 400/550/700 on the product page cited by TONI_2003 [Elektroda, 12712916] Choose v3.1 for Windows 10 and newer.

How do I swap the battery in Back-UPS CS 500?

  1. Unscrew the single bottom panel screw and slide the tray. 2. Detach spade terminals, swap in 12 V 9 Ah pack. 3. Hold ON for 2 s to reset. Total time: under 4 minutes [APC manual CSI, 2020].

Is the CyberPower Value 800E diagram from 2006 valid for 2020 units?

Yes—the control board number (2006R) remained unchanged to 2020, so the schematic posted still maps component IDs correctly [Elektroda, konrad_51, post #18382993] Firmware differs but pinout stays identical.

Can I upgrade runtime by using a larger battery?

Smart-UPS XL models already support external packs; adding 48 V 9 Ah doubles runtime from 13 min to 28 min at half load [Elektroda, TONI_2003, post #14878114] Non-XL units may overcharge and void warranty.

What’s the best way to test suspect MOSFETs in-circuit?

Set DMM to diode mode, probe drain-source both polarities. Reading <0.1 V indicates short. Lift one leg if suspect. Edge failure seen on AP2200 Rev 11 boards [Elektroda, TONI_2003, post #14889924]
AI summary based on the discussion. May contain errors.