    Hello ,
    I would like an explanation when and where FR 303 or FR 304 should be used as
    main switch in a 3-phase installation?
  • ADVERTISEMENT
  • #2 8022998
    Akrzy74
    Rest in Peace
    Posts: 7910
    Help: 363
    Rate: 1504
    You raised a very important point - I am curious about other colleagues' opinions. According to the applicable regulations, fire protection switches in TN-S installations should disconnect all working conductors, i.e. L1, L2, L3 and N, while in receiving installations?
    It is known that in fire protection, all current paths should be disconnected, and in installations located in explosion hazard zones, or if such are the requirements of the manufacturer of a device. The second issue is the selection of the apparatus - is the N pole disconnected last - and connected first?
    In the PN-IEC 60364-4-473 standard Overcurrent protection measures (473.3.3) - there is a provision:
    If disconnection of the neutral conductor is envisaged, the disconnection and reconnection should be carried out in such a way that the neutral conductor cannot be disconnected earlier than the disconnection of the phase conductors, and the neutral conductor should be connected at the same time as the phase conductors or earlier.
    So closing is allowed if all contacts of the switch are switched on and off by a common lever - simultaneously.

    In my opinion, the use of the FR 304 disconnecting the N (neutral) wire as the main switch in the "normal installation" is a mistake. I do not know about other colleagues, but I see a difference in the markings 3+N and 4-pole. Sometimes, however, logical thinking related to technical knowledge is missing - just like in the quoted standard.
  • ADVERTISEMENT
  • #3 8023069
    Piciu1
    Level 12  
    Posts: 29
    Help: 4
    Rate: 5
    Hello.

    I agree with Akrzy74, I have had many cases that with 4-pole FR the contacts were unevenly connected. This, of course, caused damage to the receivers.

    Regards.
  • #4 8023141
    Akrzy74
    Rest in Peace
    Posts: 7910
    Help: 363
    Rate: 1504
    For comparison - this photo - Using FR 303 vs FR 304 as Main Switch in 3-Phase Installation: When and Where?

    Citation col. Piciu1
    Quote:
    I have had many cases that with 4-pole FR the contacts were unevenly connected. This, of course, caused damage to the receivers.

    Me too. Switching off will occur instantly, but when we switch on, it may happen that we switch on two phases first - and the connection of the N contacts may take place later. Unfortunately, ordinary FRs have contacts that are switched on and off at the same time - just look at the contact diagram on the switch. Many electricians who assemble such devices do not know what the difference is (unfortunately) - let alone an "amateur" of electrics ...
  • ADVERTISEMENT
  • #5 8023154
    remik_l
    Level 29  
    Posts: 1151
    Help: 144
    Rate: 325
    I will quote PN-IEC 60364-5-53:2000
    Selection and installation of electrical equipment. Switchgear and control apparatus.

    531.2.1.1. Residual current protective devices should ensure disconnection of all active conductors of the circuit. In TN-S systems, the neutral conductor is not required to be disconnected if it can be assumed that this neutral conductor is at earth potential under the given supply conditions.

    NOTE - The conditions for verifying that the neutral is at ground potential are under development.

    It is true that this point concerns the RCD, but there is still talk about interrupting the N conductor. Maybe there is an answer here?
  • ADVERTISEMENT
  • #6 8052461
    Akrzy74
    Rest in Peace
    Posts: 7910
    Help: 363
    Rate: 1504
    Maybe "a few more" sentences regarding disconnecting the neutral wire in the installation :)
    Col. rumik_l wrote-
    Quote:
    I will quote PN-IEC 60364-5-53:2000
    Selection and installation of electrical equipment. Switchgear and control apparatus.
    It is true that this point concerns the RCD, but there is still talk about interrupting the N conductor. Maybe there is an answer here?

    Maybe yes, maybe not :wink:
    In TN-S systems, the neutral conductor can be isolated or connected. (60364-4-46).
    If the cross-sectional area of the neutral conductor in a TT or TN network system is at least equal to or equivalent to that of the phase conductors, detection of overcurrents in the neutral conductor or equipping it with a current interruption device is not required.
    If the cross-sectional area of the neutral conductor is smaller than that of the phase conductor, detection of overcurrents in the neutral conductor related to its cross-section is required. The consequence of detecting such a current should be the disconnection of the phase conductors - but not necessarily the neutral conductor.
    Overcurrents are not required to be detected if two conditions are met simultaneously:
    - the neutral conductor is protected against short-circuit current by a protection device for the phase conductors
    - the highest predicted value of the current in the neutral conductor during normal operation is clearly lower than the long-term current carrying capacity specified for this conductor. (60364-4-473)
  • #7 8053151
    retrofood
    VIP Meritorious for electroda.pl
    Posts: 31317
    Help: 1140
    Rate: 4796
    robsonoski wrote:
    Hello ,
    I would like an explanation when and where FR 303 or FR 304 should be used as
    main switch in a 3-phase installation?


    For now, this discussion doesn't explain anything. Because he can't explain. Well, unless Col. robsonski write what he is talking about.

    Akrzy74 wrote:
    I do not know about other colleagues, but I see a difference in the markings 3+N and 4-pole.


    It probably means that N is then understood as the neutral pole, intended only for switching operations in the neutral line, incapable of making and breaking the short-circuit current.
    In general, circuit breakers are divided into dependent and independent circuit breakers. In dependent, the speed of closing the contacts depends on the speed of moving the drive element. According to the standard, the N pole should close earlier and open later than the other poles. In circuit breakers with independent operation, the speed of closing the contacts does not depend on the speed of moving the drive element, and there it is required that all poles close practically simultaneously.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around the appropriate use of FR 303 and FR 304 as main switches in 3-phase installations, particularly in relation to fire protection and electrical safety standards. Key points include the necessity for fire protection switches to disconnect all conductors (L1, L2, L3, and N) in TN-S installations, and the importance of the sequence in which the neutral conductor is disconnected and reconnected. The PN-IEC 60364-4-473 standard emphasizes that the neutral should not be disconnected before the phase conductors. Concerns were raised about uneven contact connections in 4-pole FR switches, which can lead to equipment damage. The discussion also touches on the conditions under which the neutral conductor can be isolated or connected, depending on its cross-sectional area relative to the phase conductors. Overall, the conversation highlights the complexities of selecting the appropriate switch and ensuring compliance with electrical safety regulations.