Formula for Cable Cross-Section Calculation: Emergency Lighting, Fireproof Cables, 437W Power

hakerit1 81268 10
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 9011189
    hakerit1
    Level 11  
    Hello everyone,
    I was looking carefully at all the topics related to the selection of cabling for the installation. However, I cannot translate this into the case that I have to calculate.

    - lighting installation emergency, fireproof cables
    - the necessary formula to calculate the min. cable cross-section S
    - I have the following data: power of all receivers in the circuit P = 437W, Un = 230V, In = 1.88A, circuit length L = 130m, copper -> conductivity 58 S * m / mm2, max. permissible voltage drop in the circuit dU = 3%

    I will have a few such calculations to do, it is mainly about the formula and a short comment on why the cable cross-section is selected in such a way. The case is divided into sections of 1.5-2.5 mm2. However, I have to justify it and present the relevant calculations.

    One of the forum members advised me to calculate it from the formula below, but I don't know where I'm making a mistake

    R = [ro] xl / S
    [ro] - by this I mean the resistivity for copper 1.7 ? 10-8

    after conversion:
    S = ([ro] xl) / R

    R = U / I -> R = 230 / 1.88 = 122.34

    so: S = (1.7 ? 10-8 x 130) / 122.34 = 1.80 x 10-8 mm2 ????? that is nonsense; /


    Colleagues, I am asking for help and possibly some materials.
  • ADVERTISEMENT
  • #2 9011245
    kreslarz
    Level 35  
    Once again:
    - cable length 130 x 2 = 260 m
    with the formula R = U / I you calculated the resistance for which the current 1.88A will flow, i.e. what resistance should you put so that the current 1.88A will flow -> here is the basic error.
    It is necessary to answer the question what can be the maximum resistance of the cable so that there is a decrease of no more than 3% on it, i.e. 230/100 * 3 = 6.9V. This is how the calculations should be. Good luck
  • ADVERTISEMENT
  • #4 9011347
    hakerit1
    Level 11  
    I'm gonna be a total fool, but I just don't get it :cry:
    kreslarz wrote:
    Once again:
    - cable length 130 x 2 = 260 m


    why times 2 ???


    buddy "sq9jjh" I got to this article, the formula R = [ro] xl / S coincides with the information on that page. but I still don't understand it, sorry; /
  • ADVERTISEMENT
  • #5 9011391
    sq9jjh
    Electrician specialist
    hakerit1 wrote:
    I'm gonna be a total fool, but I just don't get it :cry:
    kreslarz wrote:
    Once again:
    - cable length 130 x 2 = 260 m


    why times 2 ??? /

    Probably because the current must flow back and forth, unfortunately.
  • ADVERTISEMENT
  • #6 9011474
    hakerit1
    Level 11  
    Literature: Wiatr, Boczkowski, Orzechowski ...... "Protection against electric shock and the selection of cables and their protection in low voltage electrical installations" 2010 states:
    p. 162 - when Scu
  • #7 9011563
    Miwhoo
    Electric installations specialist
    The current must "flow" to the receiver and "return" to the socket, it travels the path in the cable 2 times, therefore the length times two ...
  • #8 9011672
    hakerit1
    Level 11  
    Miwhoo wrote:
    The current must "flow" to the receiver and "return" to the socket, it travels the path in the cable 2 times, therefore the length times two ...

    That's right, buddy. This "two" is probably already included in the formula ...

    Will it be the correct way if I transform this formula and on its basis the calculation of S. For the calculations I will take my maximal value, ie 3%, as dU, and then the cross-section mm2 will come out, which will not cause voltage drops greater than 3%. The cables are always selected with a greater weight, so dU will always be below 3%.

    For example:

    S = 2 x In x L x 100 / gamma x dU x Un

    S = 2 x 1.88A x 130m x 100/58 (Sxm / mm2) x 3 x 230V = 1.22 mm2

    And now ... 1.5 mm2 is enough or 2.5 mm2 immediately?
    But let's assume 1.5mm2.
    So, at 1.5mm2 the actual voltage drop will be:

    dU = 2 x In x L x 100 / gamma x S x Un
    dU = 2 x 1.88 x 130 x 100/58 x 1.5 x 230 = 2.44%

    Is this approach correct ???? If so, please explain to me what "safety" factor to choose when determining this cross-section ... when it comes out 1.22 is 1.5, should I load bigger ???
  • #9 9011891
    kkknc
    Level 43  
    Here you have the table and formula.
    Formula for Cable Cross-Section Calculation: Emergency Lighting, Fireproof Cables, 437W Power
    Formula for Cable Cross-Section Calculation: Emergency Lighting, Fireproof Cables, 437W Power
  • #10 9012007
    soadfan
    Level 15  
    My friend, from what I remember, the above formula with reactance is used for calculations on a larger cross-section (16 mm? and more) and higher power.

    S = 2 x In x L x 100 / ?x ?U x Un is the correct formula

Topic summary

The discussion revolves around calculating the minimum cable cross-section for an emergency lighting installation using fireproof cables. The user provided specific parameters: total power of 437W, voltage of 230V, current of 1.88A, and a circuit length of 130m, with a maximum permissible voltage drop of 3%. Forum members clarified that the total cable length should be doubled (260m) to account for the return path of the current. They emphasized the importance of ensuring that the resistance of the cable does not exceed the calculated maximum to maintain the voltage drop within the specified limit. A suggested formula for calculating the cross-section is S = 2 x In x L x 100 / (gamma x dU x Un), leading to a calculated cross-section of 1.22 mm². The discussion also touched on the selection of a safety factor when choosing the cable size, with recommendations to opt for a larger cross-section (1.5 mm² or 2.5 mm²) to ensure reliability and compliance with standards.