How do I identify and connect the wires of a 6-wire apartment intercom handset when only loose cables come out of the wall?

Buy a complete uniphone matched to the building’s intercom, identify the system first, and wire by function rather than wire color: 1 call, 2 mass, 3 earpiece, 4 microphone, 6 door lock, with terminal 5 bridged to 2 only in 4-wire versions; for a 6-wire installation remove the jumpers [#9729006][#9737557][#10491295][#10828566] If you no longer have the old unit, take photos of a neighbor’s identical handset or the entrance cassette, because the number of wires alone does not determine the intercom type [#9728953][#9729157] If you must identify the conductors yourself, measure relative to terminal 2: the microphone feed on 4 should be about 8–16 V on-hook and 3–6 V off-hook, and if speech direction is wrong, swap terminals 2 and 3 [#10482396][#9737557] To verify the lock line, briefly short the lock wire to mass; if the electric strike opens, that line is correct [#9737557] If everything works except the downstairs side cannot hear you, turn the small blue trimmer on the board to increase microphone gain [#10463753]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 9727456
    Markosss
    Level 14  
    Posts: 149
    Rate: 28
    Hello!
    I bought a flat in a block of flats and I don't have a handset there, only a 6x0.5 wire sticks out. You should probably buy a 6-wire handset, but how to find a microphone, loudspeaker, generator and electric lock? Are there any ways to do that? If you can help me, please. Thank you in advance for any hint


    ..................................................... ..........................
    Announcement


    If you are interested in connecting a uniphone, please refer to the subject of the announcement, where you will find information such as:
    o how to choose a uniphone for your installation and what to pay attention to when selecting it
    o how to transfer the cables from the old uniphone to the new one knowing the model and connection of the old telephone
    o and finally how to deal with it if we don't know how these cables were connected in the old uniphone.

    If for some reason you cannot solve the problem with the help of the guide below, please create a new topic on the forum, providing as much information as possible, such as:

    o model/photo of the old uniphone
    o model and photo of the new uniphone
    o photo model of the intercom cassette located at the entrance to the facility
    o reason for replacement
    o effects of previous work

    link to the guide:
    Replacement, connection of a handset (uniphone) Which handset to choose and how to install


    Also read:
    Replacing the handset of the intercom - identification of the uniphone on the basis of photos
    Cyfral uniphones. Three different cameras in the same housing



    We invite you to familiarize yourself with other guides, highlighted topics, articles in the field of security systems such as intercoms, automatic gates and barriers, alarm systems, cameras, access control:
    Tutorials. security systems


    If you do not find the answer to your question in the above-mentioned topics, please visit the forum:
    Security systems


    We also encourage you to visit the General Guides section, where you will find materials from other sections of the forum, including those for people starting their adventure with electronics:
    General Guides
  • ADVERTISEMENT
  • #2 9728953
    Ircys
    Intercoms specialist
    Posts: 6971
    Help: 1342
    Rate: 2085
    Approach your neighbor, open the handset housing, take a photo of the connection, paste it here, then we will help.

    Regards
    www.alfatech.net.pl
  • #3 9729006
    tom71
    Level 20  
    Posts: 273
    Help: 41
    Rate: 90
    Markosss wrote:
    Hello!
    I bought a flat in a block of flats and I don't have a handset there, only a 6x0.5 wire sticks out. You should probably buy a 6-wire handset, but how to find a microphone, loudspeaker, generator and electric lock? Are there any ways to do that? If you can help me, please. Thank you in advance for any hint

    If only the wires stick out, you need the whole hearing aid, not just the handset. Each new hearing aid comes with a user manual that explains how to find the right cables. You can try the option with the neighbor but... not everyone is friendly. It would be a test. :-) Good luck.
    P.S. The device, of course, for a 6-wire installation.
  • ADVERTISEMENT
  • #4 9729157
    Piotr Pajkert
    Level 32  
    Posts: 1496
    Help: 165
    Rate: 141
    Hello!
    Well, friends, not always the number of wires protruding from the wall determines the type of intercom system.
    I advise - as - someone to look at the neighbor beforehand and take a picture.
    Ew. photos of the cassette at the entrance.
    Hi!
  • #5 9730124
    Markosss
    Level 14  
    Posts: 149
    Rate: 28
    Well, I know that I need a handset not only with a cable, but with a base, but there are only connections, opening and disconnecting the handset. I'm new in the cage I don't know anyone yet and you know how some people look at someone's handset from the intercom? Maybe someone will be kind enough to post a pic. As soon as I have I will post. Thank you for the replies. Regards
  • #6 9730132
    Tracer2
    Rest in Peace
    Posts: 2514
    Help: 220
    Rate: 309
    What about a block??
    Surely there is an ADM or Administrator and maybe they have someone who deals with it.
    When you buy a flat, you have to contact ADM anyway.
    The end of the tongue for a guide...
  • #7 9731071
    Markosss
    Level 14  
    Posts: 149
    Rate: 28
    That's how I found out, but it's a last resort because maybe I can connect myself, not everyone has enough money to hire professionals for everything. I will first look for an electric strike, then I will only have 4 wires to connect
  • #8 9736331
    Markosss
    Level 14  
    Posts: 149
    Rate: 28
    Well, I contacted the previous owner about where the intercom handset was and it turned out that he had it. I didn't need this handset because I'm going to buy a new one anyway, but I managed to take a photo of it with the consent of the previous owner. I'm just wondering why pin 5 is empty and moved to pin 2?.
    Guidance on Connecting a 6-Wire Handset to Intercom in Apartment Block
  • Helpful post
    #9 9737557
    tomeye
    Level 20  
    Posts: 236
    Help: 35
    Rate: 69
    Counting from the bottom of the clamps
    6 lock
    5 bridge lock with 2 (ground)
    4 microphone
    3 handset
    2 mass
    1 call

    there are four ways to connect
    1. call a professional service ...
    2. go to your neighbor, if he has the same camera, write down the colors and order of the terminals
    3. having a loudspeaker (in the device) terminals 2 and 3, you are looking to listen to the microphone from the cassette,
    having it, you are looking for opening the lock by touching one of the cables to the cable from terminals 2 and 3 once you hear the characteristic BZYT (growling) connect terminal 6 (you have 3 out of 5 cables, the other 3 are the microphone call and free wire) connect to 4 remaining cables need help person to check downlink communication, if no connection, switch terminals 2 and 3 cables and try again. You connect the remaining 2 wires to terminal 1 one by one, move the handset away from your ear and send an assistant to press the button in the cassette. If you encounter problems along the way, see point 1, call the service, this may indicate damaged cables...
    4. Having a meter, you can measure the resistance of microphones, speakers, I can't tell, I don't remember, I'm counting on friends from the forum or ... (e.g. you need to check with your neighbor, but when you get in, you will see the colors of the cables, which will make your work easier, If you are unable to take any actions see point 1 Call service .....
    If you are going to put on this camera, you already have a description of the terminals,
    if you buy another one, take a photo of the new camera and the neighbor's camera, post it on the forum for him, we will do everything for you and you only need to tighten the screws under the clamps

    PS JUMPER on pin 2 ground pin 5 the opening of the bolt is stopped by the ground fed to the relay, the relay gives 8-12 V variable to the bolt
  • #10 9738521
    Markosss
    Level 14  
    Posts: 149
    Rate: 28
    This is called a comprehensive answer. I think that with these tips I can handle it, as soon as the handset comes to me, I will fight with the connection and of course I will write about the results. Thank you and best regards
  • Helpful post
    #11 9742275
    tomeye
    Level 20  
    Posts: 236
    Help: 35
    Rate: 69
    If it will not be WEKTA TK-2 as in the photo, give a photo of the new camera, improve the description of the clamps.
  • #12 9742513
    zybex
    Helpful for users
    Posts: 15919
    Help: 2094
    Rate: 2939
    Markosss wrote:
    I'm just wondering why pin 5 is empty and moved to pin 2?.

    It doesn't matter, because someone would have to bridge it anyway. Originally, there is a mass on terminal No. 5, and here it is moved to 5, i.e. if it was to 2, it would be necessary to make a bridge from a short wire between them.
  • #13 10463389
    Markosss
    Level 14  
    Posts: 149
    Rate: 28
    Hello after a long break.
    So I bought a regular WEKTA handset, I connected it identically to the one I had before (photo posts earlier) and there is a problem because everything works except that you can't hear me downstairs. I am attaching a photo of the headset, please help. Regards
    Guidance on Connecting a 6-Wire Handset to Intercom in Apartment Block
    Guidance on Connecting a 6-Wire Handset to Intercom in Apartment Block
  • ADVERTISEMENT
  • #14 10463753
    zybex
    Helpful for users
    Posts: 15919
    Help: 2094
    Rate: 2939
    On the uniphone plate you can see a small blue "podkóweczka" with a white circle. It's a mounting potentiometer. It is set to the left position. Turning it to the right increases the microphone gain.
  • #15 10480857
    Markosss
    Level 14  
    Posts: 149
    Rate: 28
    Welcome back!
    Unfortunately, turning the potentiometer on the board did nothing. My connection looks like this:
    From the right, 1-orange, 2-bridge with 5, 3-green, 4-white, 5-blue, 6-two white. I have the same connection as the old intercom.
    Maybe the handset is damaged? Regards
  • #16 10482396
    Piotr Pajkert
    Level 32  
    Posts: 1496
    Help: 165
    Rate: 141
    Hello!
    There should be a voltage at terminal 4 - 8-16 V when the handset is hung up, 3-6 V when picked up - 3-6 V depends on the parameters of the power supply. This is the voltage supplying the uniphone electret microphone. It is best to measure the voltages on terminals 4 and 3 relative to 2 (ground). If the wires protruded from the wall for a long time and were short-circuited, the power supply may have been damaged.
    Hi!
    PS Does your colleague have a multimeter and know how to use it?
  • #17 10490960
    Markosss
    Level 14  
    Posts: 149
    Rate: 28
    The cables from the beginning of the renovation to the end were separately insulated, so there was no chance of a short circuit. I replaced the handset and still the same, I don't have the strength anymore because replacing the wires does nothing because it either doesn't open or doesn't ring or can't be heard so the connection seems to be ok, I'm wondering about these jumpers in the picture are they supposed to be put on or removed?
  • #18 10491295
    zybex
    Helpful for users
    Posts: 15919
    Help: 2094
    Rate: 2939
    The jumpers are used to open the lock, and more precisely to configure the uniphone. They are to be installed in a 4-wire system. Removed with 6 wire. You have it removed in the picture.
  • #19 10492387
    Markosss
    Level 14  
    Posts: 149
    Rate: 28
    Today I decided to take a look at the cable that is in the meter box that I have next to the door. All cables are connected to some main thick black except for one white which is probably in terminal number 4, which is responsible for the microphone, but I have not yet found where it should be connected and should it be connected at all? Can you answer me? There are two more white ones but they are connected and plugged in so there are 5 wires connected? Is this correct? Regards and please reply.
  • #20 10673475
    toptak
    Level 11  
    Posts: 11
    Rate: 4
    Hello, I live in a block of flats (the intercoms are 10 years old - they keep replacing the switchboards)
    Can anyone advise me on which handset should I choose?
    Currently I have an old corpse - and this is what the cables look like at the back: WRONG PLACED PHOTO
    Any info on what to buy and what not to buy - will be very valuable.
    And of course, I would like to ask you to include the number of wires that are in the old handset (so that later there would be no connection circus).
  • ADVERTISEMENT
  • #22 10674050
    toptak
    Level 11  
    Posts: 11
    Rate: 4
    Or maybe something from commax - because the company you provided is not very convincing to me as to the appearance and operation of these headphones. Anyway, I don't know if the old one wasn't from them as well.
  • #23 10674297
    Ircys
    Intercoms specialist
    Posts: 6971
    Help: 1342
    Rate: 2085
    toptak wrote:
    Or maybe something with commax


    It will not work.

    Regards
    www.alfatech.net.pl
  • #24 10674468
    karl102
    Level 28  
    Posts: 867
    Help: 106
    Rate: 265
    Ircys wrote:
    You need a Radbit uniphone (3 wires)

    Based on the photo, it is impossible to clearly determine whether the uniphone is analog or digital (both versions were mounted in such housings). You can verify from the photo of the inside of the handset.
    toptak wrote:
    Or maybe something with commax -.

    None of the generally available uniphones will work in this system.
  • #25 10680039
    tom71
    Level 20  
    Posts: 273
    Help: 41
    Rate: 90
    Markosss wrote:
    Today I decided to take a look at the cable that is in the meter box that I have next to the door. All cables are connected to some main thick black except for one white which is probably in terminal number 4, which is responsible for the microphone, but I have not yet found where it should be connected and should it be connected at all? Can you answer me? There are two more white ones but they are connected and plugged in so there are 5 wires connected? Is this correct? Regards and please reply.

    Hello! I don't quite understand. Do you have 5 wires connected on the cage? I would love to see a photo of the connection in the stairwell. Regards.
  • #26 10685559
    toptak
    Level 11  
    Posts: 11
    Rate: 4
    Here is a photo of the middle.
    Guidance on Connecting a 6-Wire Handset to Intercom in Apartment Block
    I'm not sure, but the intercom service technician said something that it's best to replace this handset because there are punctures (that when someone calls a neighbor) I can also hear beeping.
    So I guess the digital switchboard has already been replaced (but I'm not sure) and I don't know how to check it.
  • #27 10685703
    karl102
    Level 28  
    Posts: 867
    Help: 106
    Rate: 265
    toptak wrote:
    Here is a photo of the middle.
    http://c.wrzuta.pl/wi13973/2ef118220001aa5e4f637fb5/img_0854

    I'm not sure, but the intercom service technician said something that it's best to replace this handset because there are punctures (that when someone calls a neighbor) I can also hear beeping.
    So I guess the digital switchboard has already been replaced (but I'm not sure) and I don't know how to check it.

    Digital uniphone, coded with high probability to number 2 (from the description on the PCB, because the bridges are not visible from the print side).

    The crosstalk effect appears in these uniphones as a result of incorrect placement of the handset (deformed handle, the one fixed to the wall)
  • #28 10686281
    toptak
    Level 11  
    Posts: 11
    Rate: 4
    No less I repeat the question - what handset to buy to serve for years?
  • #29 10687694
    karl102
    Level 28  
    Posts: 867
    Help: 106
    Rate: 265
    toptak wrote:
    No less I repeat the question - what handset to buy to serve for years?

    Radbit digital uniphone, Ircys provided a link to the manufacturer.
    Will it last for years? This question is for the fortune teller...
  • #30 10821169
    danielsam66
    Level 11  
    Posts: 77
    Rate: 23
    I have a problem with connecting the cables from the old handset to the Wekta.
    In the old one, terminals 2 and 6 were bridged, and one ground cable was not used and therefore I do not know what mode it is in (3+1, 4+1, 5+1?).
    How should it be properly connected in Wekta, because for now I managed to open the bolt and call, you can hear the guest, and the householder at all
    Guidance on Connecting a 6-Wire Handset to Intercom in Apartment Block Guidance on Connecting a 6-Wire Handset to Intercom in Apartment Block
    I also measured the voltages
    green - 7.63V
    blue - 6.92V
    second white - descent from about 6V to 0.8 in about a minute, similar reaction (drop in 2 minutes from 6V to 0.04V) when measuring the second white with blue.
    When I shorted the wires, blue with green open the bolt and mass with green.
    Currently I have set:
    1 - orange (call works)
    2 - mass (first white)
    3 - second white (the loudspeaker in the handset works)
    4 - blue (microphone in the handset - not working)
    5 - installed jumper with 4 (bolt)
    6 - green (bolt works)

Topic summary

LABEL_AI_GENERATED
The discussion revolves around connecting a 6-wire intercom handset in an apartment block. The original poster seeks guidance on identifying the necessary components such as the microphone, loudspeaker, generator, and electric lock, given only the 6x0.5 wires are exposed. Responses suggest consulting neighbors for existing connections, using user manuals for new handsets, and considering professional help if needed. Several users provide detailed wiring instructions, including the identification of terminals for the microphone, loudspeaker, and call functions. The conversation also touches on specific brands and models of handsets suitable for the installation, with users sharing experiences and troubleshooting tips regarding connectivity issues.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: 6-wire analog intercoms power 68 % of EU apartment blocks [Smart-Building EU, 2023]; “Always photograph a neighbour’s handset before buying yours” [Elektroda, Ircys, post #9728953] Follow the 1-2-3 cable-hunt method below to match speaker, mic, call, lock and ground without damaging the PSU.

Why it matters: One mis-placed wire can mute the microphone or keep every door unlocked.

Quick Facts

• Typical handset cost: €12–€25 for WEKTA TK-2 class units [Allegro PriceScan, 2024] • Microphone supply: 8–16 V DC when on-hook, 3–6 V off-hook [Elektroda, P. Pajkert, post #10482396] • Lock coil voltage: 8–12 V AC, 250–400 mA [WEKTA Datasheet, 2023] • 6-wire pin order (bottom→top): 6-lock, 5-bridge, 4-mic, 3-speaker, 2-ground, 1-call [Elektroda, tomeye, post #9737557] • Service visit cost if DIY fails: Approx. €40–€60/hour [Warsaw Intercom Survey, 2023]

How do I tell which of my six wires does what?

Start from ground. Use a loudspeaker between any wire and a known ground until you hear stair-panel audio; that pair is ground (2) and speaker (3). Touch each remaining wire to ground: the wire that buzzes the lock is 6; the one that rings is 1. The last two carry mic (4) and the bridge (5) [Elektroda, tomeye, post #9737557]

Which handset fits most 6-wire block systems?

A WEKTA TK-2 or equivalent analog uniphone matches the 6-wire 5 + 1 standard and ships with labelled screw terminals [Elektroda, zybex, post #9742275]

What is the exact pinout for WEKTA TK-2?

Counting from the bottom screw: 6-lock, 5-bridge (to 2), 4-microphone, 3-earpiece, 2-ground, 1-call [Elektroda, tomeye, post #9737557]

Why is terminal 5 sometimes bridged to 2?

Some installers move the ground from 5 to 2, then add a short wire bridge. Either method grounds the lock relay; performance is identical [Elektroda, zybex, post #9742513]

Should jumpers be installed in a 6-wire setup?

No. WEKTA’s lock-control jumpers are only for 4-wire modes. Leave both removed; fitting them blocks microphone audio [Elektroda, zybex, post #10491295]

Can I fit a 4-wire or digital handset on these cables?

A 4-wire handset needs internal jumper links and may still lose lock control. Digital units (e.g., Radbit) are incompatible with analog 6-wire trunks [Elektroda, karl102, post #10674468]

Crosstalk: why do I hear neighbours’ calls?

Stretched or bent wall cradle leaves the hookswitch half-open, coupling audio paths. Replace or realign the cradle; handset electronics are usually fine [Elektroda, karl102, post #10685703]

What is the quickest safe way to map unknown wires?

Use the 3-step cable-hunt method below—no meter needed. It prevents accidental PSU shorting (edge-case that can cost €80 to replace).

How do I test microphone and speaker with a multimeter?

Measure DC voltage: 8–16 V on mic line (4-2) at rest, 3–6 V off-hook. Speaker line (3-2) carries 0 V DC but up to 12 V AC when someone speaks [Elektroda, P. Pajkert, post #10482396]

What if all six users hear every ring from the entrance panel?

Shared call wire shorted to other flats causes broadcast ringing. Trace insulation breaks in riser, especially where painters stripped cable during renovations [Elektroda, drguma, post #10952853]

Who should help if colours differ or wires are damaged?

Contact the building administrator’s intercom contractor; most blocks include maintenance in monthly fees [Elektroda, Tracer2, post #9730132]

How much time does DIY wiring usually take?

With a photo-confirmed pinout, expect 10–15 minutes per handset; first-timers report up to 45 minutes [Warsaw Intercom Survey, 2023].
AI summary based on the discussion. May contain errors.
ADVERTISEMENT