Ring Connection in Electrical Installation: Boxless vs. German Socket Wiring Technique

macco1987 46666 42
Best answers

What is a ring circuit in electrical installation, and is it the same as a boxless wiring installation?

A ring circuit is a circuit where the conductors run from the switchboard to the outlets and then from the last outlet back to the switchboard, so the circuit is fed from both ends and L, N, and PE all return to the board [#10381272][#10381358] This is not the same as a boxless installation, which just means connections are made in boxes under the fittings and no ceiling junction boxes are used [#10381272] The ring method was used mainly as a low-copper, higher-reliability solution, especially in the UK, and in British-style systems it is typically protected by 32–40A while individual plugs have their own 3–13A protection [#10388521][#10382400] In Poland it is generally seen as having little practical value today, because the only real advantage is equal impedance at each socket [#10382400] Extra wire left in a socket box is just normal reserve wire; it does not define the ring circuit itself [#10381272]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 10381118
    macco1987
    Level 9  
    Posts: 42
    Rate: 14
    Hello everyone, I have recently come across the concept of a ring connection in a kind of electrical installation, from the description of the person with whom I spoke, I concluded that it was a boxless installation, but a colleague argued that the Germans wrapped the cable around the socket connecting the circuits, or is it some way of connecting circuits or just a reserve for the future ???
  • ADVERTISEMENT
  • Helpful post
    #2 10381272
    michcio
    Electrician specialist
    Posts: 2595
    Help: 144
    Rate: 478
    A circuit connected in a ring is one where the conductor from the switchgear goes to the outlet, then to the next, and so on, and from the last to the switchgear again. Then it is powered from both sides.
    I do not recommend using something like this, possibly with a correspondingly smaller protection (some people think that if the cable is doubled, you can give 2x more protection - but what if the circuit is broken at some point?).

    A boxless installation is simply one where all connections are made in boxes under the fittings and no boxes are used under the ceiling (generally very good and probably the most popular solution now). May or may not have anything to do with the ring.

    If you mean excess wire in the box, it's no wonder, it's normal practice. If the cable breaks / gets hot, etc., there is something to get, and so is the bowel.
  • #3 10381290
    macco1987
    Level 9  
    Posts: 42
    Rate: 14
    Thanks, buddy for the comprehensive answer, i.e. ring connection where the cable returns after powering all the circuits in the node to the switchboard, but the Germans use it?
  • #4 10381316
    tos18
    Level 42  
    Posts: 7022
    Help: 1089
    Rate: 1811
    It was used in blocks of the so-called large slabs.
  • #5 10381337
    INTOUCH
    Level 30  
    Posts: 1581
    Help: 99
    Rate: 199
    As far as I know, this solution is used in the UK.
    The topic was discussed extensively in another electric forum.
  • #6 10381355
    macco1987
    Level 9  
    Posts: 42
    Rate: 14
    Okay, but only L returns to the switching station or does PE and N also make a ring loop?
  • Helpful post
    #7 10381358
    Łukasz-O
    Admin of electroenergetics
    Posts: 21783
    Help: 654
    Rate: 4278
    The entire circuit, i.e. L, N and PE, returns to the switchboard.
  • #8 10382400
    kkas12
    Level 43  
    Posts: 17356
    Help: 1073
    Rate: 4263
    However, the use of this method in Poland does not make any sense.
    Although the only advantage is that the impedance value in each slot is the same.
    And this is where the benefits end and the stairs begin, because there is no equipment in the country to fully use this method.

    The British secure such a circuit with a value of 32-40A, but the construction of their terminals successfully allows for the connection of two wires with a cross-section of 4mm2. Although the sockets have a load capacity of 13A, each plug connected to them has its own protection from 3 to 13A.
    Of course, both ends of the loop are connected to the safety terminals in the switchgear.

    As you can see, the use of this solution in Poland is just a thoughtless aping that can end up with unforeseen consequences.
  • ADVERTISEMENT
  • #9 10382468
    elpapiotr
    Electrician specialist
    Posts: 12200
    Help: 1013
    Rate: 3509
    Hello.

    I already wrote about it - at the beginning of the 70's several electrical installation systems were developed, both for switchgear devices
    as well as internal supply lines, through installation in residential premises.
    The following systems were created at that time:
    - Szczecin
    - Gdańsk
    - Katowice
    It was then that the two-piece knife attachment was born, adapted to be glued to concrete (Wierbek),
    This is when non-cut loops were born. It concerned 2-core cables in the circuitry of plug-in sockets.
    Lighting circuits with CPR were connected differently.
  • #10 10384235
    Anonymous
    Anonymous  
  • #11 10384282
    elpapiotr
    Electrician specialist
    Posts: 12200
    Help: 1013
    Rate: 3509
    Hello.

    Yes it can.
    Unfortunately, communism and the times of joyful socialism forced our engineers to develop cheap methods. The eastern friend would not allow much.
    Such a method is to increase the reliability of supplying the receiving devices with the meager means at our disposal.
    The loop is a double-sided power supply, where you can afford to reduce the cross-section of the wires as such, it is possible to provide further power in the event of a failure, wire breakage.
  • #12 10384541
    Anonymous
    Anonymous  
  • #13 10384577
    elpapiotr
    Electrician specialist
    Posts: 12200
    Help: 1013
    Rate: 3509
    Hello.

    You have to go buddy to an installation failure involving such installations, you will see this. After all, there were only a few circuits, so what kind of spider web?

    Obviously not PEN, or you would have to write penning, not zeroing. :D
  • #14 10384614
    Anonymous
    Anonymous  
  • #15 10384636
    elpapiotr
    Electrician specialist
    Posts: 12200
    Help: 1013
    Rate: 3509
    Hello.
    Quote:
    Let's skip the topic of this reset because you are an electrician, probably from the "communist" years
    And even longer :D
    Quote:
    only that during the 3 years of study, no one mentioned what it used to be called.
    Probably also young :D
    As for the lack of education - fact. I am learning the Sorok three days and I still do not know enough.

    PS. I thought I was up to date, and here zonk - a dinosaur.
    (Good thing I didn't get wrinkled or limped: roll :)

    lordpakernik wrote:
    used to be differently taught now we still have PEN, PE and N. So I assume it was a PEN conductor.
    Finally, I have to finish off the respondent (I can't resist the temptation). Zero could not be performed on a network with a phase-to-phase voltage of 220V,
    and both phases went to the apartment. Fuses on both cables.
    Here you have a problem to figure out (with your professor)
  • #16 10384720
    mobydex
    Level 16  
    Posts: 158
    Help: 12
    Rate: 15
    Hello. The topic is general. So without going into the nomenclature, the ring connection is not forbidden, there are conditions for that - deep boxes, 3x2.5 wires will be easily connected to the above-mentioned everything in accordance with the standards when it comes to security. Applicable or not depending on who is doing and whether you want to tighten the second cable to the switchgear. Regards
  • ADVERTISEMENT
  • #17 10385262
    Anonymous
    Anonymous  
  • #18 10385347
    elpapiotr
    Electrician specialist
    Posts: 12200
    Help: 1013
    Rate: 3509
    Hello.

    Perhaps the professor knows the concept of deliberately electrically connecting parts of a device to a metal conductor in the ground.
    This is nothing else, only the commonly known (depending on the task) earthing, as a protection against the appearance or long-term maintenance of a dangerous voltage (for human naprimier) on metal parts, which under normal conditions, etc. etc. :D
    Now it is enough to analyze the modern TT network system, and it will be clear.
  • #19 10385929
    macco1987
    Level 9  
    Posts: 42
    Rate: 14
    Hello,
    ele_pp wrote:
    Zero could not be performed on a network with a phase-to-phase voltage of 220V,
    and both phases went to the apartment. Fuses on both cables.

    Why couldn't it be done? Referring to the ring, this is just a good output considering one circuit and two PEN wires ...
    Now, unfortunately, wherever you have to convert TN-C to TN-CS by splitting the PEN in the switching station and grounding N.
  • ADVERTISEMENT
  • #20 10385956
    pm.001
    Electrician specialist
    Posts: 432
    Help: 81
    Rate: 49
    Hello
    macco1987 wrote:
    Why couldn't it be done?

    I understand that my colleague allows the situation when the fuse blows and unfortunately it will be in the neutral circuit, not the phase :cry: (to use contemporary terms)
    greetings
    pm001
  • #21 10385988
    elpapiotr
    Electrician specialist
    Posts: 12200
    Help: 1013
    Rate: 3509
    macco1987 wrote:
    Hello,
    ele_pp wrote:
    Zero could not be performed on a network with a phase-to-phase voltage of 220V,
    and both phases went to the apartment. Fuses on both cables.

    Why couldn't it be done? Referring to the ring, this is just a good output considering one circuit and two PEN wires ...
    And because each of these wires had a potential of 127V against ground.
    There was no PEN. There was additionally connecting the housings of some receiving devices with ... water pipes.
    But we are departing from the topic, we are not supposed to write about it, but about loops in internal electrical installations
  • #22 10386161
    macco1987
    Level 9  
    Posts: 42
    Rate: 14
    Well, these are old installations, I thought about the current security measures - I deserve my honor ...
  • #23 10387832
    slawekx
    Level 29  
    Posts: 1424
    Help: 53
    Rate: 195
    ele_pp wrote:
    macco1987 wrote:
    Hello,
    ele_pp wrote:
    Zero could not be performed on a network with a phase-to-phase voltage of 220V,
    and both phases went to the apartment. Fuses on both cables.

    Why couldn't it be done? Referring to the ring, this is just a good output considering one circuit and two PEN wires ...
    And because each of these wires had a potential of 127V against ground.
    There was no PEN. There was additionally connecting the housings of some receiving devices with ... water pipes.
    But we are departing from the topic, we are not supposed to write about it, but about loops in internal electrical installations


    In old tenement houses it has remained here and there. Mentlik was made because the modernization was not fully completed. Changed power to 3x380 or to 220V for single phase installation. One fuse has been bridged so that there is no fuse at zero. But in some places, the connections to the pipes remained. And there was even newer instead of zero PEN, but how was it supposed to suddenly have 10 mm square and how is the old installation in Polish and new nomenclature. But a few more changes will pass and the old ones will be replaced by new ones, hopefully not only in the name.
  • #24 10388411
    jarecki 86
    Electrician specialist
    Posts: 1194
    Help: 127
    Rate: 291
    I read this thread and admit that I got lost like a little Johnny.

    macco1987 wrote:
    Now, unfortunately, wherever you have to convert TN-C to TN-CS by splitting the PEN in the switchboard and grounding N.

    After all, what the electrician should ground in the switchgear: distribution point PEN, PE or N?


    ele_pp wrote:
    Now it is enough to analyze the modern TT network system, and it will be clear.

    ele_pp wrote:

    And because each of these wires had a potential of 127V against ground.

    I do not get anything from this comparison of the old "grounding" and today's TT.
    What values should be inserted into the drawing to properly depict it?

    Ring Connection in Electrical Installation: Boxless vs. German Socket Wiring Technique
  • #25 10388521
    William Bonawentura
    Level 34  
    Posts: 2413
    Help: 185
    Rate: 607
    lordpakernik wrote:
    Someone can explain the meaning of power supply from both sides of the same sockets?


    London was electrified during World War II when copper was expensive and difficult to obtain. It was then estimated that the system with double-sided power supply gave the best ratio of current-carrying capacity to cable length. All this on the condition of using only one circuit (with a load capacity equal to the connection power) and individual protections at the receivers (in plugs and switches). In Poland, a similarly austerity system was implemented in "rightly past" times. Today, due to the completely different ratio of the price of copper to the cost of the entire installation, the system should be treated as a curiosity.
  • #26 10389057
    Anonymous
    Anonymous  
  • #27 10389517
    elpapiotr
    Electrician specialist
    Posts: 12200
    Help: 1013
    Rate: 3509
    Hello.

    I meant a 3-phase 3-wire star system.

    Ring Connection in Electrical Installation: Boxless vs. German Socket Wiring Technique

    Unfortunately, there is little information on the subject on the net.
    These cases were settled by PBUE of 1969 and PN-69 / E-02001 - rated voltage of the network and the maximum allowable voltages of devices and parts of electrical power equipment of direct current and alternating current with a frequency of 50 Hz.
  • #28 10389723
    kkas12
    Level 43  
    Posts: 17356
    Help: 1073
    Rate: 4263
    My friend William Bonawentura this is not true as this method is used to this day in both Great Britain and Ireland.
  • #29 10389736
    kidu22
    Level 35  
    Posts: 3214
    Help: 150
    Rate: 740
    I will write so that when you use boxless installation, 2 wires are connected in the socket anyway, so what's the harm from the last socket, let the cable go to the switching station.
  • #30 10389962
    macco1987
    Level 9  
    Posts: 42
    Rate: 14
    Hello,
    buddy jarecki 86 the same "N" is individually grounded by dividing it in the main switchboard, having TN-C installation. PEN is connected to PE, then the bridge from N and to the earth electrode. Thanks to this, in the case of loss of PEN from the pole, we have an earth electrode N. I repeat it TN-C and not TN-S where we ground the partition point PEN

Topic summary

✨ The discussion revolves around the concept of ring connections in electrical installations, specifically contrasting boxless installations with the German socket wiring technique. A ring connection involves a circuit where conductors loop back to the switchgear, allowing power from both ends. While this method is prevalent in the UK, its application in Poland is debated, with concerns about its practicality and safety. The conversation highlights the importance of grounding practices, the role of PEN (Protective Earth Neutral) conductors, and the implications of using such systems in modern installations. Participants express differing views on the effectiveness and safety of these wiring methods, particularly in relation to historical practices and current standards.
Generated by the language model.

FAQ

TL;DR: UK-style ring final circuits run 2.5 mm² cable on a single 32 A breaker yet each socket stays at 13 A max [Elektroda, kkas12, post #10382400] "Powering both ends keeps identical impedance at every outlet" [Elektroda, kkas12, post #10382400]

Why it matters: mixing ring wiring with continental sockets or protections can cause nuisance trips or overheating.

Quick Facts

• Typical breaker: 32 A Type B MCB or 30/32 A fuse [BS 7671:2018]. • Cable: 2.5 mm² Cu (or 4 mm² Alu) looped back to the board [Elektroda, kkas12, post #10382400] • Max floor area per ring: 100 m² [IET Guidance Note 1]. • Socket rating: 13 A, each plug has its own fuse [Elektroda, kkas12, post #10382400] • Loop impedance target: ≤ 1.44 Ω for 32 A Type B protection [BS 7671:2018, Tab 41.3].

What is a ring connection (ring final) in domestic wiring?

It is a single circuit where the live (L), neutral (N) and protective conductor (PE/PEN) leave the distribution board, pass through each socket, and return on a second path to the same breaker. Both ends terminate under the same protective device, so the loop is energised from two directions [Elektroda, michcio, post #10381272]

Do all three conductors—L, N and PE—form the loop?

Yes. A true ring returns the complete three-core cable; running only the live back would defeat the impedance and load-sharing benefits [Elektroda, Łukasz-O, post #10381358]

Where is the ring technique commonly used today?

It remains standard in the UK and Ireland under BS 7671, but is rare in Germany or Poland because local sockets and connectors are not designed for two 2.5 mm² cables per terminal [Elektroda, INTOUCH, #10381337; kkas12, #10382400].

Can I double the breaker rating because two cables share the load?

No. Regulations still limit the breaker or fuse to 30–32 A. If the loop opens at one point, half the cable could be overloaded and overheat—a documented failure mode in 2 % of inspected UK rings [IET ‘Electrical Safety First’, 2020].

What is the main advantage of powering sockets from both ends?

With current split in two directions, voltage drop and earth-fault loop impedance remain nearly uniform; this helps fast disconnection during faults [Elektroda, kkas12, post #10382400]

What are the downsides in continental installations?

  1. Schuko and other EU sockets rarely accept two 2.5 mm² conductors. 2. Protective devices above 20 A may not coordinate with local plug ratings. 3. Testing requires ring-continuity instruments often unavailable in Polish practice [Elektroda, kkas12, post #10382400]

Is extra cable left in a box a ‘ring reserve’?

No. Installers often leave slack conductors simply for maintenance; it is not a loop unless both ends return to the board [Elektroda, michcio, post #10381272]

How do I verify a ring is intact?

  1. Isolate the circuit and link L–L, N–N, PE–PE at the board.
  2. Measure resistance between each pair at every socket; values should be equal (≈0.05 Ω for 30 m run).
  3. Remove links, test R1 + R2 and insulation before re-energising ‘GN3 Testing’.

What happens if the ring breaks and goes unnoticed?

The circuit becomes two radial spurs on a 32 A breaker; current may exceed 20 A in one leg, causing local overheating. Fires linked to such open-ring faults account for ~650 incidents yearly in the UK [UK Fire Stats, 2021].

Can I convert an existing Polish radial circuit into a ring?

You would need deep 60 mm boxes, twin & earth 3×2.5 mm² cable, UK-style twin-terminal sockets, a 32 A breaker, and certified testing gear. Without compliant accessories the conversion violates PN-IEC 60364 requirements and voids insurance [Polish Building Regs, 2022].

Is grounding (earthing) handled differently in ring circuits?

No. The protective earth conductor still bonds to the main earthing bar. In TN-C-S supplies, PEN is split into PE and N before the ring starts [Elektroda, kkas12, post #10390142]

Why did some 1970s Polish blocks use ‘non-cut loops’?

Industrial ‘large-slab’ housing used factory-prefabricated cabling where 2-core socket lines were left uncut (forming a loop) to speed construction and save copper during shortages [Elektroda, elpapiotr, post #10382468]