[Solved] Standard Tightening Torque for 32A Power Plug & Electrical Connection Bolts Explained
LiutenetMaria 36784 4
  • #1 10751178
    LiutenetMaria
    Help: 59
    Rate: 210
    Is there a standard that specifies the tightening torque for bolts in electrical connections?
    It is, for example, the tightening torque of the screws in the 32A power plug.
  • #2 10751322
    LightOfWinter
    Help: 369
    Rate: 935
    To my knowledge, the plug manufacturer should specify the torque with which the bolts should be tightened. It depends on the material used and the mechanical structure of the joint - stamping.
  • #3 10753918
    nuszek
    Level 30  
    Help: 123
    Rate: 389
    From the manual:
    11.1.5 Bolt tightening torques
    The following moments are recommended for use
    Thread size
    Device or contact fixing bolts, second value from M6 - Tightening (for rails without lubrication)
    M3 0.5 ÷ 0.56 Nm
    M3 * 0.8 ÷ 0.9 Nm
    M3.5 1.0 ÷ 1.1 Nm
    M4 1.4 ÷ 1.5 Nm
    M5 2.7 ÷ 3.0 Nm
    M6 5.4 ÷ 6.0 Nm; 8 Nm ? 10%
    M8 14.0 ÷ 16.0 Nm; 20 Nm ? 10%
    M10 23.0 ÷ 26.0 Nm; 40 Nm ? 10%
    M12 36.0 ÷ 40.0 Nm; 70 Nm ? 10%
    M16 54.0 ÷ 60.0 Nm; 140 Nm ? 10%
    When at least 60% of the proposed values are used, it can be assumed that the connection is made correctly. In the case of lower torque values, all bolts during inspection should be re-tightened in accordance with the proposed torques.
  • #4 10754857
    LiutenetMaria
    Help: 59
    Rate: 210
    krzysztofer5 wrote:
    And will you tighten with a torque screwdriver and issue a protocol on tightening the connectors? :D
    I just want to buy a pneumatic screwdriver and I do not know what torque range to buy, so that it has the greatest versatility.
  • #5 18795689
    LiutenetMaria
    Help: 59
    Rate: 210
    Thank you for your help.