mar_cik wrote: Instead of three-pole B20 for hob and oven, three single-pole B16.
The division into 3 MCBs seems logical but B16 is probably not enough. The induction is 7.2 kW (we finally decided) P = I * U * cos phi = 16 * 230 * 0.95 = 3.496 kW and the induction hob is 3 , 6 kW from one phase. I know, I did not provide information about the power of the induction hob.
mar_cik wrote: Instead of B6 for B10 lighting circuits.
I was just wondering from what I was reviewing, the B 10 protection is often used for lighting circuits. But isn't that too much? One chandelier is approx. 100 - 150 W, with the use of fluorescent lamps 25 - 50 W. So with B6 and the use of incandescent lamps, one could power approx. 8-10 chandeliers. So it seems sufficient.
mar_cik wrote: If possible, replace the three-pole pre-meter B25 with C25.
Unfortunately, the Power Plant imposed such a security.