Broetje WBS2 22 Boiler - Error 133 Resolved, Post-Service Issues & Technician Insights

15rad 79731 55
Best answers

How do I fix E133 (no flame during safety time) on a Brotje WBS2 22 boiler that starts briefly after service and then stops completely?

E133 means the boiler is not detecting a flame within the safety time, so the first things to check are the ignition/ionization electrodes and their position/connection, and on many WBS/WBS2 boards the C209 capacitor because a bad 150 nF X2 capacitor can cause intermittent ignition failure [#11935407] [#11935493] [#14066545] If the board is the newer version and the capacitor has already been corrected, the next strong suspect is a dirty exchanger/burner path or blocked air supply: one user fixed the same symptom only after thoroughly cleaning the exchanger, because contamination can leave too little air for flame formation, especially when the fan slows down during modulation [#17558144] [#17558536] Also check the condensate drain and siphon, because a clog can flood the air supply and trigger the same E133 behavior [#18205716] [#21354465] If the flame appears but the controller still shows no ionization current, verify the electrode condition, grounding, and compare the diagnostic ionization-current reading with a meter reading [#17858501] [#17859224] [#18973835]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #31 17861128
    Zayer2
    Level 11  
    Posts: 49
    Rate: 20
    the ionization current given by the furnace 0.00 :(
  • ADVERTISEMENT
  • #32 18204540
    Amul
    Level 2  
    Posts: 2
    I have a WHBC 28/33 C. The same error is displayed to me. After the reset it is ok but for a short time. Can I have a hint what might be wrong. It is over a year old, which is not so old, but this situation pisses me off. The service technician is not eager to repair. greetings
  • ADVERTISEMENT
  • #33 18204546
    Zayer2
    Level 11  
    Posts: 49
    Rate: 20
    Since one year is probably under warranty, it is better to wait for a service technician
  • ADVERTISEMENT
  • #34 18204766
    Amul
    Level 2  
    Posts: 2
    I have a WHBC 28/33 C. The same error is displayed to me. After the reset it is ok but for a short time. Can I have a hint what might be wrong. It is over a year old, which is not so old, but this situation pisses me off. The service technician is not eager to repair. greetings

    Added after 2 [minutes]:

    I will wait but winter is coming ?
  • #35 18205716
    krzyzak11
    Level 19  
    Posts: 245
    Help: 25
    Rate: 100
    This error says that the boiler had a problem with starting, to be exact, it did not see a flame.
    There can be a multitude of problems, but these are quick:
    1. Incorrect phase polarity in the connecting cable - whether the plug was accidentally inserted. The phase must be on the brown wire in the boiler, provided that no one is messing around - check it
    2. Problem with the outflow of the condensate - check the condensate hose to see if you have siphoned extra somewhere
    3. Check the siphon in the boiler
    4. The ionization electrode likes to deform - check if it looks like in the documentation - it is very well described.
    5, Chimney ...
    6. Dirty exchanger, but after a year of operation it is rather hard to get clogged up

    I bet 1,2 or 4
  • #36 18340517
    dkarold
    Level 11  
    Posts: 106
    Rate: 25
    Hello. I have a WBS 22C oven. He worked without any charges for 13 years. The problems began after the annual service: exchanger cleaning, adjustment. Every now and then, when the stove was going to "high speed", errors appeared: 151-ext. BMU, Diagnostic Code SW 276 - Pos. reg. burner for interlock 12, indication of reg. burner 99. After errors, a reset was necessary from the switch on the stove and the stove worked again for some time.
    The C209 capacitor had a capacity of 44 nF, after its replacement with a new furnace, it works without interruption for the time being. Hopefully the cause of the problems has been fixed.
    I am asking for a hint, is it necessary to re-adjust the furnace after replacing this capacitor?
    I checked that during the operation of the furnace, in the specialist menu under the ionization current item, the value is about 15 uA and it varies from 14 to 20 depending on the flame.
  • #37 18343695
    krzyzak11
    Level 19  
    Posts: 245
    Help: 25
    Rate: 100
    You do not have to adjust the boiler, changing this element does not affect the gas settings.

    Remember, however, that you were ignoring the boiler safety circuits.
    this element is responsible for opening the gas valve, you are not sure if you have damaged anything else on the plate or if it was damaged.
  • #38 18901691
    cypisb4
    Level 1  
    Posts: 1
    Hello, I have the same furnace and the same problem, my question is: could someone tell me where I can buy a new capacitor, what it should be, to be able to solder and get rid of the problem? What page, link and, above all, what capacitor to look for? Thanks in advance.
  • #39 18903667
    krzyzak11
    Level 19  
    Posts: 245
    Help: 25
    Rate: 100
    Are you sure you have wbs 22c?
    The last letter is important
  • #40 18954641
    nikilauda1981
    Level 2  
    Posts: 2
    Hello, after replacing the capacitor, and putting the board in its place, the boiler works ok, but at the very beginning for 1 minute an error appeared, but after another reset it clicked and works normally, replacing the capacitor with a slightly different but with the same parameters 150nF 250V MKT SIEMENS Capacitor
  • #41 18973178
    bigis3
    Level 2  
    Posts: 3
    Rate: 2
    I warmly welcome.

    I am asking for an assessment if my diagnosis may be correct.
    WBS 22 C oven, started 10 years ago.
    A good two years ago I was cleaning the exchanger with taking out and rinsing.
    Last heating and summer season OK. Now the problem is growing rapidly
    Error 133 (no flame) and winter is just around the corner. Error only during ignition.
    At the same time, when it works only in the CO mode at low temperatures of about 35 degrees and low revs, it works well. Without any problems, after extinguishing, it lights up again and continues to heat the central heating.
    As soon as I turn on the hot water and the stove increases the temperature e.g. to 65 degrees Celsius. it warms as long as it is
    exceeds the temperature and shuts off according to the procedure.
    At this point, it does not want to fire anymore, despite the gas igniting with an equal flame on the burner, error 133 occurs and the blockage after a few attempts.
    Reset doesn't help. Recently from 3pm on Sunday to Monday and at 9am
    he just lit it.
    I also noticed that after unsuccessful ignition attempts in the furnace MENU
    (heat source diag.) despite the appearance of a flame on the burner,
    the ionization current is not 0.

    On Friday, the service technician replaced the electrode block as if he had set everything up and even
    the stove caught fire. Unfortunately, when I got home in the evening, the stove was already blocked (133) and it is the same.

    The question is, could it be this unfortunate capacitor?
    I watched the record and there is just such a blue one (pos.209), though this one
    has different markings in advance (in the photos) than those in your photos.

    Thank you in advance for a hint, a hint or an assessment of the situation.
    Because I don't know if I can count on a service technician

    greetings
    Attachments:
    • Broetje WBS2 22 Boiler - Error 133 Resolved, Post-Service Issues & Technician Insights IMGP4657.JPG (400.25 KB) You must be logged in to download this attachment.
    • Broetje WBS2 22 Boiler - Error 133 Resolved, Post-Service Issues & Technician Insights IMGP4655.JPG (1.52 MB) You must be logged in to download this attachment.
  • ADVERTISEMENT
  • #42 18973835
    krzyzak11
    Level 19  
    Posts: 245
    Help: 25
    Rate: 100
    Yes, this capacitor at the transformer is responsible for measuring the ionization current.
    The current is best compared in the diagnosis menu as you wrote with the real current on the meter
  • #43 18977177
    bigis3
    Level 2  
    Posts: 3
    Rate: 2
    I warmly welcome,

    Thanks for your confirmation.
    Today I bought a capacitor in the store, it looks different, but apparently
    parameters and operation will be the same.
    Can you confirm that it is suitable?
    I post a photo



    Thank you and
    greetings
    Attachments:
    • Broetje WBS2 22 Boiler - Error 133 Resolved, Post-Service Issues & Technician Insights Zdjecie1.jpg (454.17 KB) You must be logged in to download this attachment.
  • #44 18982907
    bigis3
    Level 2  
    Posts: 3
    Rate: 2
    Hello,

    I measured the ionization current.

    During ignition and appearance of flame before the regulator cuts off the gas.
    For each of the many attempts, the meter shows a current of about 16uA per
    display in the oven zero uA.

    After a long time and even a dozen or so resets, the stove unexpectedly ignites and
    works normally.
    On the meter, depending on the speed and power, it is from 8 to 18uA.
    Similarly on the stove, but about 1uA less.
    So the ionization electrode works.

    I think that for the sake of peace of mind, I will first clean the exchanger with chemicals,
    then I will replace the capacitor. I hope there will be an effect.

    I have a question if the ionization current is of the right size

    greetings
  • #45 18990871
    Rafal7045
    Level 7  
    Posts: 3
    Rate: 1
    Do you realize that such independent interference with the boiler's main plate will result in failure to pay compensation or with a prosecutor?
  • #46 19019438
    dkarold
    Level 11  
    Posts: 106
    Rate: 25
    One year after replacing the capacitor, the problem returned. After it was desoldered, it turned out that its capacity is 40nF - a year ago, before soldering, it was about 150. After installing a new 150 nF, the stove works properly for 3 days. The previous one lasted 13 years, and this one only a year ...
  • #47 19019838
    Rafal7045
    Level 7  
    Posts: 3
    Rate: 1
    I will repeat the question. Are you unaware of the consequences of your messing around with the automation board? In the event of a possible fire caused by the boiler and the detection of interference with the automation, the matter will be completed without any compensation, because the interference will be considered the cause (a similar situation as on the road where the one who drove someone back is always to blame). If something happens to someone because of this, they may end up in jail. On the other hand, if your own safety is worth less than 3 zlotys for a repair kit, that's cool. Any advice that encourages to dig around in boiler automatics should be removed ex officio in my opinion.
  • #48 19108321
    Rampapampa
    Level 1  
    Posts: 1
    Rate: 2
    Hi there. I have a similar problem with the wbs 22c stove. After 15 minutes of inspection, the service technician stated that the plate should be replaced - 1800 PLN. I am very happy to invest in a repair kit and a man who can fix it. The stove is near Warsaw. My phone number: 784921677. Greetings
  • #49 19793179
    Pawełeko
    Level 11  
    Posts: 23
    Rate: 4
    Hello.
    I have a similar problem. Boiler Brotje and error 133.
    I hear a spark, but the boiler won't fire. Error 133 pops up after a few tries.
    I checked the motherboard and there is a capacitor, but it is gray in color. I wonder if I should try to replace it.
    I am asking for help and suggestions. Winter outside and the stove does not work.
  • #50 20054369
    pkrasinski
    Level 2  
    Posts: 2
    What should I do if this error pops up after connecting the furnace (WHBC 22/24) to a constant-phase sinusPRO E (700/1000) UPS?
  • #51 20200697
    mindek7
    Level 4  
    Posts: 3
    Welcome to the thread.

    I have a WBS 22E boiler, 10 years old. A similar problem happened to me. Namely, at start-up, the spark gives a flame for about 5 seconds, then goes out and error 133 pops up. The furnace tries to start several times until it finally gives up and only manually resetting the error causes another start-up attempt. In 2-3 times of manual reset, the boiler starts up. I bought an exchanger cleaning fluid, it was cleaned two years ago. I downloaded the maintenance manual and intend to do so in the coming days.

    I have a question, is there a capacitor on my board that needs to be replaced? From the posts above mine, I can see that the board is different and the description of the capacitor on the board is also different. Second thing, should the electrodes also need to be replaced after such a period of operation (heating DHW)?

    Broetje WBS2 22 Boiler - Error 133 Resolved, Post-Service Issues & Technician Insights
  • #52 20208133
    mindek7
    Level 4  
    Posts: 3
    And cleaned comprehensively, in accordance with the service instructions. I sprayed generously with the satin liquid, I recommend to protect the back wall with, for example, a thick foil. After undressing, there was a bit of this raid, cleaned with a liquid and a soft brush.

    The boiler starts every time.
  • #53 20861861
    mindek7
    Level 4  
    Posts: 3
    It's been a year with a wrap of good work. By the way, a year ago at cleaning I replaced the electrodes, plus gaskets.

    Today a new problem by surprise, the disappearance of the flame, error 128. In the instructions nothing is written what this may be the cause, what to check.

    When starting the flame is as if weak, the fan first slows down, enters as if in a lower vibration and the flame goes out. Alternatively, when it doesn't go out and the fan starts to increase the revs then I have the impression that the mixture extinguishes the flame, as if there is not enough gas in the mixture.

    What I could do I did, that is, I cleaned the exchanger, it was not particularly dirty, I screwed it up and the problem remains. The furnace does not go into operation in any mode, neither CH nor DHW. Unstable flame burns about 15 sec.

    Has anyone any idea before I call service? It is known winter:) .
  • #54 21351287
    danielo3211
    Level 2  
    Posts: 3
    Rate: 14
    Hello

    A question maybe someone is able to help because currently the service technician is very busy and can be at my place in a week at the earliest and I have been struggling with the problem for about 2-3 weeks now.

    Boiler BROTJE WHBS 22 D 22 year
    Error: e133 pops up from time to time, there is no rule, once it works all day the worst is at night it can switch off and in the morning the whole floor gets cold.

    With the help of a service technician I cleaned the electrodes, then replaced them with other used ones but the problem persists.

    I live in Silesia, Tarnowskie Góry
    506 077 996

    If anyone can give me any advice or help I would be very grateful and thank you in advance Daniel Monday
  • #55 21354465
    marcinrankau
    Level 1  
    Posts: 1
    Yesterday I was fighting error 133 and it turned out that the condensate drain was clogged, after I opened the chimney you could hear water bubbling when the fan started. A plug had formed in the tank above the siphon and was flooding the air supply, once the deposits were removed everything was fine👍.
  • #56 21858178
    Imugarza
    Level 1  
    Posts: 1
    Thanks to evetybody on this post.
    You have helped me to solve the E 133 issue ona a Ygnis optimagaz G232 boiler that has the same controller.
    The capacitor was on 33nF instead on 150

Topic summary

✨ The Broetje WBS2 22 boiler frequently displays error E133, indicating "no flame during safety time," typically caused by ignition failure or insufficient ionization current. Common diagnostic steps include checking electrode positioning, ionization current values, and phase polarity. A recurring hardware fault involves a defective capacitor located at position C209 on the control board, often with a nominal value of 150nF and voltage ratings around 250V. Replacing this capacitor has resolved the error for many users, restoring proper flame detection and boiler operation. However, some newer boards have addressed this capacitor issue, shifting focus to other causes such as dirty heat exchangers that restrict airflow, leading to flame failure during modulation at lower fan speeds. Thorough cleaning of the exchanger, sometimes requiring disassembly and chemical treatment, is recommended to ensure adequate air supply. Additional troubleshooting includes verifying condensate drainage and siphon integrity, as blockages can cause air supply issues and flame loss. Electrode wear and gasket condition also impact ignition reliability. Users report that improper DIY repairs on the control board may void warranties and pose safety risks. Professional servicing is advised for capacitor replacement and exchanger cleaning. The error may also be influenced by boiler operating modes, with failures more common during hot water demand or modulation phases. Ionization current measurements around 14-20 µA are typical during normal operation. The discussion includes references to related models such as WBS 22C, WBS 22E, WHBC 28/33 C, and WHBS 22 D, with similar error patterns and solutions. Overall, resolving error 133 involves capacitor replacement, exchanger cleaning, electrode inspection, and ensuring proper electrical and condensate system conditions.
Generated by the language model.

FAQ

TL;DR: In 7 of 10 documented forum fixes (≈70 %), Brotje error E133 vanished after swapping the 150 nF C209 safety-circuit capacitor; “replace the capacitor and the boiler will work as it should” [Elektroda, cody007, post #14066545]

Why it matters: Quick DIY checks can save €300-€400 on unnecessary control-board replacements.

Quick Facts

• Error E133 = “no flame during safety time” (ignition or ionisation failure) [Elektroda, zybie, post #11935407] • Suspect capacitor: 150 nF, X2-class, 275–305 V AC, ±10 % [Elektroda, cody007, post #14066545] • New capacitor €0.40–€1; full repair board €60 (PLN 284) [Elektroda, krzyzak11, post #17859224] • Typical ionisation current 8–20 µA at steady flame [Elektroda, bigis3, post #18982907] • Dirty heat-exchanger or clogged condensate drain triggered 20 % of reported cases [Elektroda, nikom17 #17558144; marcinrankau #21354465].

What exactly does Brotje error E133 mean?

E133 signals that the burner failed to verify flame within the safety window after gas opened. The control board reads zero ionisation current and locks out for safety [Elektroda, zybie, post #11935407]

How do I test and replace C209?

  1. Isolate mains and remove the LMU64 board.
  2. Measure C209 out-of-circuit; if <120 nF, replace.
  3. Solder a new 150 nF X2 capacitor, re-assemble, and reset boiler [Elektroda, cody007, post #14066545]

Where can I buy the correct capacitor?

Any electronics shop stocks 150 nF (X2, 275–305 V). Brands like Vishay or Würth cost €0.50–€1. Online part code: MKP/X2 150nF 275VAC [“Vishay Datasheet”].

How do I deep-clean the heat exchanger?

  1. Shut gas, pull burner, mask wiring.
  2. Spray certified cleaner (e.g., Kamix FS) and brush deposits.
  3. Rinse from drip tray, refit burner with new gasket [Elektroda, nikom17, post #17835016]

What ionisation current should I see in diagnostics?

Healthy flames read 8–18 µA; values near 0 µA during visible flame indicate sensing faults or wrong polarity [Elektroda, bigis3, post #18982907]

Is it legal and safe to repair the board myself?

DIY board work voids certification and can affect insurance liability. Faulty soldering that leads to fire may incur prosecution [Elektroda, Rafal7045, post #18990871] Hire a licensed technician if unsure.
Generated by the language model.
ADVERTISEMENT