De Dietrich MCR II / 24 Stove: E2 Error in Heating Mode & Restart Solution - Maintenance Advice
Danper2 38322 20
Why does my De Dietrich MCR II show E2 in heating mode after a long idle period while domestic hot water still works, and how can I fix it?
E2 is usually caused by the boiler detecting an abnormal temperature relationship, especially return temperature higher than flow temperature, and in this thread the fault was ultimately fixed by replacing a temperature sensor [#12795766][#12920827] First check the simple causes: valve positions, whether 3–4 radiators are open, boiler pressure, air in the boiler, pump operation, and dirty/blocked filters [#12795766][#12795768][#15338064] The original poster later confirmed that a service technician replaced one temperature sensor (part S58733) and the boiler then worked normally [#12920827]
  • #1 12793977
    Danper2
    I have question for you. I have had a De Dietrich MCR II stove for 2 years. The furnace was serviced in June this year and it was ok. On Friday I started the heating and there was an E2 error. After restart it started and it was ok for a while. But after a long time of downtime (when there is no heating on) it is the same. Error E2 pops up and after reboot it starts. I mention that hot water is heated without any problem.
    Could anyone advise me where the problem lies.
  • #2 12795766
    piracik
    Help: 557
    Rate: 1976
    Return temperature higher than flow temperature.
    Do you have a second boiler, e.g. a coal boiler or a fireplace with a jacket?
    Check that the valves are open.
    Check that at least 3 or 4 radiators are set to at least 3.
    You can feel if the return pipe is actually warmer than the supply pipe.
    If all of the above is OK, then you can choose:
    - pump failure
    - defective return or supply sensor
    - supply sensor not installed (e.g. after inspection or repair)
    - air in the boiler
  • #3 12795768
    exeter85
    Rate: 21
    Error E2 can mean several things:
    low system pressure
    problem with boiler sensors
    circulation problem (pump)
    dirty filter what
  • #4 12799811
    Danper2
    Thank you for the hints. Due to the fact that yesterday the problem was repeated again, I called the furnace specialist. The strangest thing about the whole situation is that once it fires up, it then works flawlessly until a long downtime. I'll let the technician know where the problem was.
  • #5 12820289
    exeter85
    Rate: 21
    I bet that the filter in the left hydro block may be dirty
  • #6 12920827
    Danper2
    Suggestions by pirate and exeter85 were confirmed. On October 21, a service technician visited me and after replacing one temperature sensor (in the spare parts catalog item No. 2013 No. S58733) it works ok.
    Regards and thanks for your help
  • #7 15321786
  • #8 15321846
    piracik
    Help: 557
    Rate: 1976
    bernidi wrote:
    most of the season I burn wood or coal in 9kW Stąporków
    Is the solid fuel boiler operating at the time when the error occurs?
  • #9 15321862
  • #10 15321896
    piracik
    Help: 557
    Rate: 1976
    It is possible that the sensor has a gap in its characteristics, which is revealed at higher temperatures (DHW charging)
  • #11 15321922
  • #12 15321957
    piracik
    Help: 557
    Rate: 1976
    This would indicate a low heat exchange capacity. Jacket/coil.
  • #13 15321972
  • #14 15338064
    dobroslaw
    Help: 57
    Rate: 157
    To reduce the power to DHW, change the parameter p 18, see how much p17 is set, i.e. heating, what you definitely have 37 (I don't know what model you have) p18 set from 46 to 40, you will go down with power, instructions can be found on the manufacturer's website. You may have too little pressure in the boiler, the filters may also be dead. In mcr 2 you have a hidden filter on the hot water supply, a plastic thing that is very difficult to remove, but if you don't have a hot water supply, it can be clogged, I usually throw it out because it disturbs more than it protects. It's best to call a service technician because you can only make things worse.
    Term Klima serwis De Dietrich Białystok
    białystok słowackiego 7, Białystok, 15-229 | Tel.: 500XXXXXX (Show)
  • #15 15340475
  • #16 15390152
  • #17 15392666
    piracik
    Help: 557
    Rate: 1976
    bernidi wrote:
    At the time of failure t1 20 degrees t2 40 degrees,
    T1 - supply temperature
    T2 - return temperature
    bernidi wrote:
    is it possible that the valve switching the heating water circuit does not close properly and initially the supply water flows partially from hot water and not only from central heating after switching to central heating?
    Even the question of how it immediately cooled down by 20 * C to swim out cooler.
  • #18 15393144
  • #19 15416753
  • #20 15467426
  • #21 17317439
    Skorpionek1111
    Piec de Dietrich Mcr II, Does anyone know what can cause a change in hot utility water temperature when the co is turned off (when turned on there is also this problem). Cold, warm, then hot, and so on. Changing the temperature doesn't help. And five errors do not show. E7 and E10 have popped up a few times recently but after restarting it doesn't show up anymore. First, it heats the water to the max and then turns off, and so on all the time.
The discussion revolves around the E2 error encountered in the De Dietrich MCR II / 24 stove during heating mode. The user reported that after a service, the stove displayed the E2 error after long downtimes, although hot water heating functioned normally. Responses suggested various potential causes, including issues with return and supply temperature sensors, low system pressure, circulation problems, and dirty filters. A follow-up confirmed that replacing a faulty temperature sensor resolved the issue. Other users shared similar experiences, indicating that the E2 error often occurs when switching between domestic hot water (DHW) and central heating (CO), with suggestions to check sensor functionality and system pressure. The conversation highlighted the importance of proper maintenance and sensor checks to prevent recurring errors.