De Dietrich MCR 24 Boiler Error E04: Issues with Ignition, Small Flame & Venting Procedure

tomaki 44838 6
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 13155390
    tomaki
    Level 10  
    Hello,
    I have a problem with the boiler as in the subject. During the venting procedure at the beginning, the boiler tries to ignite 5 times, but it ignites only for 1 second with a very small flame and then goes out. There is a spark, el ignition-ionizac new, gas at ignition 2.5 mbar, and yet it does not ignite. Please help
  • ADVERTISEMENT
  • #2 13155459
    rafal8103
    Level 14  
    check the transformer attached to the gas valve, it seems to be unbreakable and the varistor inside is falling and hence the errors 04 and 06
  • ADVERTISEMENT
  • #3 13155502
    piracik
    VIP Meritorious for electroda.pl
    tomaki wrote:
    gas at ignition 2.5 mbar

    In this boiler, the amount of gas is set for flue gas analysis.
    Check if the phase with neutral is not inverted.
    Check the fuse on the reducer or that the gas pressure does not drop.
  • ADVERTISEMENT
  • #4 13155817
    tomaki
    Level 10  
    The pressure does not drop, checked with a micromanometer at the outlet of the valve 2.5mbar
    on the gas valve. 25 mbar.
  • #5 13158333
    piracik
    VIP Meritorious for electroda.pl
    tomaki wrote:
    checked with a micromanometer at the outlet of the valve 2.5mbar

    And how much was it before you switched to these 2.5 mbar?
    I have already written that the pressure behind the fittings says little because the boiler is regulated for analysis.
    From what it seems to me, there should be negative or zero pressure there.
    It is true that I have never measured it in this boiler, but it is possible that this is how it should be. And an order of magnitude a little smaller 0 -10 Pa, not mbar. However, I may be wrong. I would like to point out that I have never measured the pressure behind the fittings in this boiler.

    Have you checked the phase sequence with zero yet?
    Check the connection of the protective conductor to the panic and transformer.

    Also write what you did with this boiler that it broke down.
  • #6 13159302
    tomaki
    Level 10  
    I understand that it is not regulated, but I have to light it somehow, so it gives more gas to the burner - 4 mbars. I replaced the gas fittings, transformer, electrode and it's the same, it still lights up for 1s and goes out. Phase zero has nothing to do with it.
  • ADVERTISEMENT
  • #7 13159813
    piracik
    VIP Meritorious for electroda.pl
    tomaki wrote:
    Phase zero has nothing to do with it.

    You see. I would start with this before I replace anything and change the gas pressure blindly.

Topic summary

The discussion revolves around the De Dietrich MCR 24 boiler experiencing an E04 error, characterized by ignition issues where the boiler attempts to ignite five times but only produces a small flame for one second before extinguishing. Users suggest checking the transformer connected to the gas valve, ensuring proper gas pressure settings, and verifying the phase and neutral connections. The author confirms that the gas pressure is stable at 2.5 mbar but has replaced several components, including gas fittings and the transformer, without resolving the issue. There is a suggestion to measure the pressure behind the fittings, as it may not be regulated correctly, and to ensure the protective conductor is properly connected.
Summary generated by the language model.