Residual current device in the TN-C photovoltaic installation

eclipse99 36021 35
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #31 14494130
    jekab
    Level 23  
    WojcikW wrote:
    I also do not know why the RCD would malfunction?


    If you disassemble it here and install it correctly in a switchboard, it should work properly.

    Mounted according to this diagram after the inverter serves for nothing.
  • ADVERTISEMENT
  • #32 14495396
    stomat
    Level 38  
    Why do you say it's mounted "after an inverter"? It is in front of the inverter and protects against electric shocks in the event of "breakdown", eg in an inverter. I agree with my colleague Wójcik and I also see no reason why it should not work. I see that some of my colleagues have so much inherent rules for the most popular solutions that in slightly atypical cases they get lost like children in a fog.
  • ADVERTISEMENT
  • #33 14495446
    Wirnick
    Level 30  
    stomat wrote:
    I agree with my colleague Wójcik and I also see no reason why it should not work. I see that some of my colleagues have so much inherent rules for the most popular solutions that in slightly atypical cases they get lost like children in a fog.

    I also agree with my colleague Wójcik with the following conditions:
    1- double breakdown in the inverter,
    2- permanent metallic connection of PE and N in the receiving circuits, then condition 1- does not have to be met,
    3- the inverter is adapted to TN-C conditions - then the RCD is at the "output" and cannot work with the TN (...) network (PE and N short-circuit on both sides).


    PS.
    So many years on Elektroda - we have to finally find out!
    Is there 3x400V, 400V to 230V or 3x230V in the 3F electrical system?
    As for 50Hz, there is no doubt about it.
  • ADVERTISEMENT
  • #34 14495871
    jekab
    Level 23  
    stomat wrote:
    Why do you say it's mounted "after an inverter"? It is in front of the inverter and protects against electric shocks in the event of "breakdown", eg in an inverter.


    Before or after? It all depends on your point of view.

    Perhaps plugging the RCD into the inverter's output makes some sense.
    And it will have to be revoked that it is useless.
    Maybe the whole secret is in the surge protection of the inverter output that may arise from the network.

    Maybe some transils are installed at the output between the phases and the inverter body?

    In the event of an overvoltage, the RCD would disconnect it from the power supply.

    Prerequisite is insulation in the inverter between N and PE.

    Electric shock protection is provided by RCDs that are common for the inverter and the network.
  • ADVERTISEMENT
  • #35 14496108
    BILGO
    Level 38  
    Here, an example connection diagram for a Fronius inverter, as shown, the RCD should only be installed when the regulations / standards dictate it. The question is, is there an order to install an RCD next to PV inverters in PL, is it regulated somewhere?
    Residual current device in the TN-C photovoltaic installation
  • #36 14496780
    Anonymous
    Anonymous  

Topic summary

The discussion revolves around the use of a 4P 40A / 300mA Type B residual current device (RCD) in a TN-C photovoltaic installation. Participants express concerns about the appropriateness of using RCDs in TN-C systems, highlighting a ban on their use in such configurations. The original poster questions whether the installation diagrams represent a design error, given that PE and N are connected in the main switchboard. Various responses clarify the role of RCDs, with some suggesting that RCDs are not necessary for inverter protection, while others debate the correct placement of RCDs in relation to inverters. The conversation also touches on the cost of RCDs and the need for precise definitions of protection requirements in photovoltaic systems.