qbart_gt wrote: Does my scheme make sense?
NO.
From the beginning:
qbart_gt wrote: This is a single-phase installation on the plot
I see the counter 3f.
You mark the connections with dots and the PEN hangs in the air or on the ground.
Are you moving from where? from the earth electrode? PE too? This is what it looks like from this diagram.
No information about the network system from ZE.
Is a 3m pin supposed to guarantee a transfer resistance of less than 10 ohms? Any data for such a statement (soil resistivity)?
Why is there a ban in ZK? 160A and pre-meter bills. is unmarked? Why pre-meter is a circuit breaker? (there will probably be a lack of selectivity).