How should an open central-heating and domestic hot-water installation with a 25 kW solid-fuel boiler be piped so it is safe, correctly sized, and uses the right pump and differential-valve layout?

The installation can be made safe, but as drawn it needs changes: the second version is preferred and the differential valve should be omitted [#16230457] The open expansion vessel must be connected correctly, with the safety pipe coming from above and the vessel connection from below, using a tee on the safety pipe [#16230457][#16230542] Put check valves behind both pumps, and on a manifold-based radiator system there is no need for a pump bypass [#16230457] Do not reduce the boiler circuit and 4-way valve to 28 mm unless you add a boiler pump; otherwise use pipe and valve sizes equal to the boiler outlet, and if you want a 1" valve then place a pump between the 4-way return and the boiler [#16230457] Add thermometers on the boiler return and on the radiator supply behind the pump [#16230647] Several replies also warned that the boiler may be oversized for this house [#16230429][#16230704]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • Questions about boiler safety, pipe sizing, and valve placement

    #1 16230408
    webfreak
    Level 10  
    Posts: 11
    Rate: 1
    Hello,
    I am asking someone who is knowledgeable in the subject to assess the correctness of the attached scheme of the CO + CWU installation
    Open installation, all-flammable boiler (mainly coal, walnut and wood) 25kW. Boiler room in the basement, heated ground floor + part of the 1st floor, a total of approx. 140m2. Everything on radiators, without a floor.
    The main part of the installation (all 'thick' lines in the diagram) is 28mm copper. From manifolds to 16mm PEX radiators.

    The expansion vessel will be open about 5-6m above the boiler.

    Basic questions:
    1. Would the installation be safe?
    2. Is something missing / too much?
    3. Are the pipe diameters in the installation appropriate?
    4. Which version will be more correct and why? In the first version, the pump and the differential valve are connected to the same four-way valve output, in the second version the differential valve is before the four-way valve, and the pump at the four-way valve output.

    I will be grateful for your help :)
    Central heating installation - the diagram to be checked - Please check the diag Central heating installation - the diagram to be checked - Please check the diag
  • ADVERTISEMENT
  • #2 16230429
    nowackahelena
    Level 17  
    Posts: 425
    Help: 16
    Rate: 47
    Differential valve as in version 1. Why two pumps? One on a common central heating and domestic hot water circuit without a four-way valve. No pump control after reaching the right temperature on the boiler. The tube for the dish from the highest point and can be thin. The boiler is supplied from the central heating pump before the manifold. I think the boiler is too big.
  • ADVERTISEMENT
  • Correcting safety vessel piping, pump valves, and boiler circuit sizing

    #3 16230457
    gersik
    Level 33  
    Posts: 1717
    Help: 164
    Rate: 639
    1. Installation is secure. Only the safety pipe is to be connected from above with an empty space of the expansion vessel, and from below the vessel well. So there must be a tee on the RB and the joint must be connected from the bottom and top of the vessel.
    2. Check valves are to be behind both pumps. There is no need to bypass the pump on the radiator system because the system is made of manifolds (no gravity).
    3. If there is no boiler pump, the installation in the boiler circuit and the 4d valve must be the same size as the boiler outlet. Certainly not 28. If you want to make a circulation and a 1 "valve, there must be a pump between the return from the 4d valve and the boiler.
    4. Second version only without differential valve.
  • Questions about four-way valve sizing and pump requirements

    #4 16230458
    webfreak
    Level 10  
    Posts: 11
    Rate: 1
    Why version 1 valve? I mean explain the differences in action.

    Two pumps because if I turn the four-way valve so as to cut off the radiator circuit (summer), then the boiler circuit + DHW circuit will remain, and thanks to the pump the water will actually go through the DHW tank, and not on the shortest route on the boiler circuit itself. If I'm wrong and CWU works the same way, please correct me.

    I can't get rid of the four-way valve, I care about the right temperature to return to the boiler.

    The control of both pumps will of course be, perhaps the four-way valve itself, I have not only placed on the controller diagrams.

    Added after 15 [minutes]:

    Quote:
    1. Installation is secure. Only the safety pipe is to be connected from above with an empty space of the expansion vessel, and from below the vessel well. So there must be a tee on the RB and the joint must be connected from the bottom and top of the vessel.


    Apparently in low power systems the overflow pipe can act as a safety pipe. I found something like this:
    Central heating installation - the diagram to be checked - Please check the diag .
    it's the version on the right. If this is incorrect or complete nonsense then please correct me :)

    Quote:
    Check valves are to be behind both pumps.

    Indeed, I forgot about it.

    Quote:
    There is no need to bypass the pump on the radiator system because the system is made of manifolds (no gravity).

    That's right, it won't push through distributors :oops:

    Quote:
    If there is no boiler pump, the installation in the boiler circuit and the 4d valve must be the same size as the boiler outlet. Certainly not 28. If you want to make a circulation and a 1 "valve, there must be a pump between the return from the 4d valve and the boiler.

    Could you explain why? I care about understanding the topic.

    One more question - will it be warm enough there without an additional pump?
  • #5 16230521
    Anonymous
    Anonymous  
  • #6 16230528
    nowackahelena
    Level 17  
    Posts: 425
    Help: 16
    Rate: 47
    Do as you like, I do not agree with gersik. Why are you complicating this?
  • Small boiler loop prevents gravity circulation and return protection

    #7 16230542
    gersik
    Level 33  
    Posts: 1717
    Help: 164
    Rate: 639
    https://www.is.pw.edu.pl/~pawel_kedzierski/ZabezpieczenieNWotwarte.pdf
    Because gravity will not work on such a small diameter of the boiler circuit, and there will be no return protection. This topic is rolled out all the time, just look.

    Added after 2 [minutes]:

    http://sas.busko.pl/pl/images/stories/sas/pro...rty_zamkniety/uklad_otwarty/ukl_otwarty_1.jpg
    This is how the vessel should be connected.
  • #8 16230570
    nowackahelena
    Level 17  
    Posts: 425
    Help: 16
    Rate: 47
    Central heating installation - the diagram to be checked - Please check the diag

    Added after 1 [minutes]:

    This installation works for my parents 10 years you close manual for summer and that's it.
  • ADVERTISEMENT
  • #9 16230606
    webfreak
    Level 10  
    Posts: 11
    Rate: 1
    Unfortunately, I will definitely not decide on such a solution. Maybe it works 10 years, but the expansion vessel connected behind the valve and pump?
    The regulations make it clear that this can't be the case. Besides, I would be afraid for my parents' life when the power goes out and the valve grows stone and doesn't let go.
  • ADVERTISEMENT
  • #10 16230616
    Anonymous
    Anonymous  
  • #11 16230618
    nowackahelena
    Level 17  
    Posts: 425
    Help: 16
    Rate: 47
    Yes, if you run out of electricity, you boil water. The vessel after the pump or valve is not a problem. The pump is not tight as you know its construction is a centrifugal pump like in a car.
  • #12 16230647
    gersik
    Level 33  
    Posts: 1717
    Help: 164
    Rate: 639
    "nowackahelena" could you not comment on heating installations?
    "webfreak" do not forget about the thermometers on the return to the boiler and on the supply to the radiators behind the pump.
  • #13 16230659
    nowackahelena
    Level 17  
    Posts: 425
    Help: 16
    Rate: 47
    Ryszard_to_wie wrote:
    Please do not show such dangerous schemes, someone else will use them and the accident is ready.

    Why? write us all?
    I remind you of an oversized coal boiler "for everything" and you can't just turn it off, and at least one receiver should work in gravity. Unless it has a second cooling coil.
  • #14 16230692
    Anonymous
    Anonymous  
  • #15 16230704
    gersik
    Level 33  
    Posts: 1717
    Help: 164
    Rate: 639
    In one "... helena" is right. The boiler is too big.
  • #16 16230730
    webfreak
    Level 10  
    Posts: 11
    Rate: 1
    The house is not insulated, and I do not exclude the possibility of smoking I had, and then the efficiency will not be as high as on basic fuel, hence the boiler power. The area also may increase slightly in the coming years due to the development of most of the floor.
  • #17 16230857
    nowackahelena
    Level 17  
    Posts: 425
    Help: 16
    Rate: 47
    Ryszard_to_wie wrote:
    This question has already been answered by the author himself, you can see that he is more stranger than you.

    Yes. Is more.
  • #18 16239358
    webfreak
    Level 10  
    Posts: 11
    Rate: 1
    Thank you for any advice. I close the topic.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around the assessment of a central heating installation diagram for a coal, walnut, and wood boiler rated at 25kW, intended to heat a 140m² area. Key concerns include the safety of the installation, adequacy of pipe diameters, and the configuration of the pump and differential valve. Responses indicate that the installation is generally secure but requires specific adjustments, such as proper connections for the expansion vessel and check valves behind the pumps. There is debate over the necessity of two pumps and the implications of the four-way valve's placement. Some participants express concerns about the boiler's size and the potential risks associated with the proposed configurations, particularly regarding safety during power outages. The conversation concludes with the author deciding to close the topic after gathering insights.