New Chinese Power Generator: Voltage Regulator Breaks & Replacement - Causes & Solutions

makada 16038 14
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16455786
    makada
    Level 12  
    I warmly welcome.

    In my new Chinese aggregate the voltage regulator has broken (I thought so),
    so I ordered a new one (cost PLN 48).
    After connecting the new one, it worked for about 10 seconds (voltage on the voltmeter about 230 V.).
    And my question: was this new regulator defective or is the winding damaged and it damages the voltage regulator.
    I will also write that no receiver was connected to the device after replacing the regulator.
  • ADVERTISEMENT
  • #2 16456764
    soniak2
    Level 21  
    Write something more, what about an aggregate? What winding (aluminum or copper)? What power rating? Does it have stable turnover?

    It is worth to attach photos of winding leads together with measurement of their resistance
  • #3 16459945
    Staszek49
    Level 35  
    Check what voltage the voltage regulator is supplied with (constant or variable and size). During the connection of the regulator, did you mistake the cables (plus and minus), which could also have an impact on the damage.
  • #4 16461590
    makada
    Level 12  
    Hi.
    For sure I didn't make any mistakes, as for power supply, I thought that these regulators are universal.
    After below I put some photos of this aggregate.
    As for the questions @ soniak2, the resistance on all 4 outputs (these 4 shafts) is 0 ohm
    New Chinese Power Generator: Voltage Regulator Breaks & Replacement - Causes & Solutions New Chinese Power Generator: Voltage Regulator Breaks & Replacement - Causes & Solutions . New Chinese Power Generator: Voltage Regulator Breaks & Replacement - Causes & Solutions
  • ADVERTISEMENT
  • #5 16469719
    soniak2
    Level 21  
    0 ohm between each connector on the cube?
    It would be best if you wrote all the combinations on the photo
  • #6 16496631
    makada
    Level 12  
    I'm sorry I haven't written back for so long - no time.
    I have a question. Maybe I used a module with too low power?
    4.2 kW is written on the aggregate housing, and the module supports from 2 to 4 KW.
    I would like a link, which module to buy.
  • #7 16497540
    Staszek49
    Level 35  
    If you still have trouble with this aggregate, in particular with the regulator (for the condition of the windings you guarantee), then disconnect the regulator. Instead of a regulator, connect a smaller 12 V battery (e.g. scooter), observing polarity and start the generator. If the aggregate (except for the regulator) is operational, it should work and generate voltage of approx. 150 V, due to too low power supply to the rotor. Performing such a test (observing the safety rules), you will make sure whether the generator is junk or just a regulator.
    You were supposed to check and provide the result of the measurement of the voltage supplying the regulator, in particular whether it was powered by direct or alternating voltage, which could have affected the regulator damage.
  • ADVERTISEMENT
  • #8 16515700
    makada
    Level 12  
    Hi.
    I'm sorry that it takes so long. Recently, the seller sent me a new regulator, but after connecting it to the aggregate, the output voltage is lacking.
    So I connected the charger to the generator and the output appeared voltage of about 120 V.
    So I guess it's the regulator's fault and I'm probably unlucky and the seller sends me damaged regulators.
  • ADVERTISEMENT
  • #9 16530761
    makada
    Level 12  
    I'm sorry that I write a post under the post, but the repair of my aggregate is a bit delayed.
    I will add a photo of the voltage regulator. I hope someone will tell me which regulator I should order.

    New Chinese Power Generator: Voltage Regulator Breaks & Replacement - Causes & Solutions New Chinese Power Generator: Voltage Regulator Breaks & Replacement - Causes & Solutions New Chinese Power Generator: Voltage Regulator Breaks & Replacement - Causes & Solutions
  • #10 16530863
    tolo
    Level 35  
    If it wasn't for this resin, yours could be repaired.
  • #11 16531324
    makada
    Level 12  
    Will you advise my friend what regulator should be bought?
  • #12 16540011
    wmazek
    Level 18  
    Hello !
    I suggest checking the generator carefully. You must also have voltage supplying the regulator / about 90 V idling speed / and voltage at the measuring tap / 16-18 V /. The main winding is important but also the rotor winding is important.
    Good luck.
  • #13 16541676
    makada
    Level 12  
    Hi.
    Please write on which pins of the regulator these voltages should appear.
    Today I have connected the rectifier again and the output has 220V.
    When I touched the regulator's negative wire in place of the negative connection of the brushes, there was a spark on the contact, so the power supply to the regulator seems to be.
  • #14 16542240
    wmazek
    Level 18  
    Welcome back!
    The regulator is usually powered by yellow wires and there should be about 90 V, and the other two wires are a measuring tap - voltage control and there should be 16-18 V. Check all connections carefully.
    Good luck.
  • #15 16573587
    makada
    Level 12  
    This 90 V should be between wires or to "ground". Because it is by all means and I get around 6 V.
    but if I attach the regulator, it connects to the brushes, and so the current goes to the brushes.

Topic summary

The discussion revolves around issues with a new Chinese power generator, specifically concerning a faulty voltage regulator. The user initially replaced the regulator, which functioned briefly before failing again. Participants suggested checking the generator's specifications, including the type of winding (copper or aluminum), power rating, and ensuring correct wiring during installation. The user later suspected that the replacement regulator might be defective or that the generator's windings could be damaged. Suggestions included testing the generator with a lower voltage source and measuring the voltage supplied to the regulator. The user reported receiving a second regulator, which also failed to provide adequate output voltage. The conversation emphasizes the importance of verifying the generator's operational parameters and the compatibility of replacement parts.