Gas Pressure Reducer Issue: Heating Furnace Error E01, Checking for Blocked Regulator

Lasek311 17241 14
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16657093
    Lasek311
    Level 10  
    Good morning,

    my heating furnace displays error E 01, which may mean that the gas supply is blocked. I would like to know how to check that the pressure regulator is not blocked. In the attachment his photos:
    Gas Pressure Reducer Issue: Heating Furnace Error E01, Checking for Blocked Regulator Gas Pressure Reducer Issue: Heating Furnace Error E01, Checking for Blocked Regulator Gas Pressure Reducer Issue: Heating Furnace Error E01, Checking for Blocked Regulator
  • ADVERTISEMENT
  • #2 16657248
    kajron
    Level 29  
    Measure the pressure downstream of the regulator maybe the regulator itself works correctly only the control contact of the signaling device has hung and thus an error code
  • ADVERTISEMENT
  • #3 16657630
    kz61
    Level 27  
    I don't see any reducer here, only the pulse shut-off valve ZB. If there is a gas detector in the boiler room, it controls it. At first glance it is released because the mushroom is low. The gas is cut off. Pull the plug so that it protrudes above the connector plug. Of course, first find and remove the cause of the trip.
  • #4 16657831
    Lasek311
    Level 10  
    It seems that this could have happened when after a storm there was no electricity all day ... I will try to pull this mushroom away tomorrow.
  • #5 16711309
    Domelski
    Level 19  
    Call the service for the detection system. The valve does not close on its own or due to a power failure (it is triggered by a series of pulses from the control panel). If the storm damaged the detection system, then you have a malfunction, you will not see it on the control panel (only the power will be lit).
    In addition, you have the valve installed incorrectly because it practically touches the wall. There should be a gap (minimum 1cm, but it's better to give more). The pipe should also be at a distance from the gas pipe (here it is almost on it 8-O ). The same elbow immediately after the valve is also not indicated, nor do I see the manual shut-off valve (maybe it is somewhere earlier). The valve plug has specific connections and is fitted alongside as standard. Here someone mounted it across (acceptable). It is worth checking the correctness of the connection.
    A thin cable (it is worth checking if it complies with the instructions) and you can see that the plug gland has not tightened properly, so the IP protection level is no longer maintained.
    Installation to fix.

    For this service probably never looked here because the factory seals intact. :sm31:
  • #6 16711718
    tgo1
    Level 14  
    Domelski's friend has a bit of trouble. I presume that the boiler has over 100Kw of power and is subject to UDT and the installation has been approved for operation and has been made in accordance with the project. Even the statement that there is a thin cable but at 12 V and 25 W for what more! When inspecting the boiler, the safety devices and the gas shut-off valve are checked, so it should be tested at least once a year / what the factory seals have to do with it. You don't look there / Lasek 311 sometimes there is '' transient states '' in the event of voltage decays, so turn on the valve and start the boiler. If there are problems, call a service technician.
    call a service technician.
  • #7 16719776
    Domelski
    Level 19  
    Quote:
    Colleague Domelski has a bit of trouble. (...)
    that there is a thin cable but for 12 V and 25 W what for more

    Not at all. I have not buried.
    The cables between the gas detection system control panel and the valve must comply with the installation instructions. There is simply no 12VDC, only a series of pulses. An incorrectly selected cable can cause incorrect installation operation and hazard. This is a critical parameter of the system.
    If it is a GX GX system, the minimum wire cross-section is 1.5mm2 for distances up to 30m (instructions page 29 :!: ). And that's why I pay attention because the one in the picture seems thin (about 0.75mm2) and it is worth checking it because then in the event of an accident there will be no translation.

    Quote:
    I presume that the boiler has over 100Kw of power and is subject to UDT and the installation has been approved for operation and was made in accordance with the design

    What do you suppose? Safety systems in accordance with the regulations apply from 60kW. And UDT is not obliged to check the gas detection system.
    Just releasing the electric wire with the gas pipe without keeping a gap is a mere partitioning.

    Quote:
    When inspecting the boiler, the safety devices and the gas shut-off valve are checked, so it should be tested at least once a year

    According to the instructions, gas detection systems are checked every 3 months.

    Quote:
    what the factory seals have for this

    Well, they have that no service has looked inside the valve.

    Quote:
    You don't look there

    :shocked!: Congratulations on your approach. That's where you look. And only pseudo-services seem to just "click" the valve and everything checked.

    Quote:
    Cane 311 sometimes in the event of voltage decays there are '' transient states ''

    In the event of a power outage, the switchboard rather does not send a series of pulses to the valve (but I do not prejudge because after the pictures we do not even know which system). Either there was a false alarm or a real alarm or a control panel failure. Either way it's worth checking out.
  • #8 16719866
    jack63
    Level 43  
    Sorry author with a light offtop.
    My friend @Domelski . I have read your posts with great pleasure and although they do not concern me I find them very helpful. I will remember the information you provided.
    However, I have a question: Why is the NC valve "dropped" just a series of pulses, and not NO supported when there is power and there is no danger?
    Maybe I misunderstood something? Please explain. Very interesting topic.
    Thank you in advance.
  • ADVERTISEMENT
  • #9 16720457
    Domelski
    Level 19  
    Quote:
    Why is the NC valve "dropped" used just a series of pulses instead of NO supported when the power supply is on and there is no danger?

    Good question. :) Actually, it's not even an NC valve. Unfortunately, I do not know the full genesis (producers do not want to admit everything). NCs are also sometimes used.

    Some things are certain:
    - the "dump" valve (safety valve) is safe on one side. The point is that someone must then manually "consciously" open it. So it is assumed that someone checked if the alarm was not real, eventually checked the installation and checked whether, for example, something was not left open, that after the installation the gas did not escape somewhere because someone did not close something (remember that these valves are not only to boiler rooms, but also to laboratories, industry, halls, etc.). The same model is in the pressure relief valves. If it closed, you have to open it manually. And to be honest such an opening should be saved somewhere and a person with permissions who has restarted the installation should sign somewhere (but that's my vision).
    - NC or NO type valves have the disadvantage that after the change has ceased it returns to its previous state. So we have a leak, the detection system is alarming, the valve closes, the gas is thinning, the system stops alarming, the valve opens and leakage again. Such valves are also used (e.g. ZE Flamy or other Burket) but then there must be a latching system that can only be activated consciously after removing the fault (e.g. remotely from the factory dispatch center). I do not have to say that then the problem is the lack of power supply, which cannot cause the valve to open, i.e. rather NC valves are used (the NO valve in this momancie would be open in the event of a power failure, i.e. you have an alarm during which the system on the 4th threshold cuts off the power to the boiler room, thus opening the valve :) ). For this you need to remember that the coils of these valves must be adapted to long-term operation, and used in safety valves (e.g. MAG, ZB, SK, EVRM) coils are intended for short-term operation (close and forget).
    - engine valves are also used (e.g. ZM for large cross-sections 150, 200 and above) where there is a controller and the valve closes a dozen to several dozen seconds and then opens it with the button.
    - a series of pulses is to provide several attempts to close the valve. Often the valves are found (because they are only closed during technical inspections) and the first impulse may not move the stem sufficiently. Therefore, DO NOT control these valves with a simple relay simply giving voltage (because it may not work for the first time) and that's why you look inside them - not inside (not every inspection but every now and then). That is why inspections are every 3 months, so that move the valve in. Because then the system has only one chance to operate. There may also be an economical and rational aspect: in the NC valve for 24 hours a day you would hold the valve under voltage only so that in case of failure it closes for a short time.
    - this type of valve (closed in this way) has no place in regulations and sometimes in some cases NC valves are also used, as I said, but these "safety valves" are used all over the world.

    But I wrote ... If something is unclear or something does not agree, then shout.
  • #10 16720689
    tgo1
    Level 14  
    On the website of the manufacturer of the Flama Gaz valve you can download the instructions for the stop valve ZB and on page 4 says that the maximum cable diameter is 1.5 mm2 / up to 30 m from the central unit /
    and on p. 2 point 10 write that the shut-off valve does not require any other servicing except starting. The instructions do not indicate the time between valve checks. The plug at work is to be pulled out maximally and in emergency state the spring presses the plug. Unfortunately, we do not know what the trigger switch is and whether the gas sensor is calibrated. You can see that the gas pipe passes through the wall through the sleeve and the pipe outside the sleeve, so what else can you ask for, a pipe or pipe to the pipe? Kol Domelski is right about the power not 100Kw but 60 Kw. It is a pity that the author of the topic is silent!
  • #11 16720818
    Domelski
    Level 19  
    Sory, but what friend read the instructions because I see in it something completely different. Maybe I would like a link. A friend will point out that this instruction is in the form of a B5 booklet, i.e. on the first page of the pdf the friend has pages 8 and 1.

    Quote:
    On the website of the manufacturer of the Flama Gaz valve you can download the instructions for the stop valve ZB and on page 4 writes that the maximum cable diameter is 1.5 mm2

    That is why it needs to be a little wider. What my colleague gives (de facto page 5) I quote: "maximum wire cross section that can be inserted into the connection socket". This entry does not mean that we can connect the valve with anything shorter than 1.5mm2. This entry says nothing about which cable to use, but only which one you can connect to the plug. The instructions of the detection system as a whole are important. I gave it to the most likely author of Gazex. In their instructions, a colleague will also find larger cross-sections for greater distances (then you need to use an additional can).
    It is the resistance of the cable (taking into account the reserve for the cable after several years of operation - damage, increased resistance at the contacts, etc.). Certainly my colleague knows perfectly well that the smaller the cross-section of the cable or / and the greater the distance, the greater the resistance, which at low voltages is of particular importance.
    I do not go into the calculations and divagations that would suffice, it is important what the operating and assembly instructions for the system say because it will be important in the event of an accident and claiming damages.

    Quote:
    / up to 30 m from the switchboard /

    This is not in the ZB manual

    Quote:
    and on p. 2 point 10 write that the shut-off valve does not require any other servicing except starting

    There is no point 10 at all on page 2. It is on page 7.
    I read page 8 in the instructions (i.e. the rest of item 10 - the first page):
    Frequency of checks required:
    - after the first month of operation
    - then every 3 months at least every 6 months

    As it is printed in the form of a booklet, it is easier to see.

    The maintenance activities in the paragraph the colleague talks about mean the actions taken by the operator / system user. In a word, this entry means that the valve is automatic and the user does not need to operate it. A bit confusing, but they've already written it.

    Similar records in the frequency range are in the instructions of the detection systems.

    Link to the manual: http://www.flamagaz.com/index.php?action=zb

    Quote:
    You can see that the gas pipe passes through the wall through the sleeve and the pipe outside the sleeve, so what else can you ask for, a pipe or pipe to the pipe?

    Maybe it will be clear to a colleague about:

    ORDINANCE
    MINISTER OF INFRASTRUCTURE

    of April 12, 2002

    on the technical conditions to be met by buildings and their location.

    (Journal of Laws of June 15, 2002)

    Chapter 7

    Gas installation for gaseous fuels

    § 164. 3. Gas pipes, in relation to the pipes of other installations constituting the building's equipment (water supply, sewage, electric, lightning protection, etc.) shall be located in a manner ensuring their safe use. The distance between the gas lines and other lines should allow for maintenance work.
    4. Horizontal sections of gas installations should be located at a distance of at least 0.1 m above other installation pipes, whereas if the gas density is higher than the air density - below electric wires and sparking devices.
    5. Gas installation pipes crossing other installation pipes should be at least 0.02 m away from them.
  • ADVERTISEMENT
  • #12 16720831
    DiZMar
    Level 43  
    Domelski wrote:
    ...
    5. Gas installation pipes crossing other installation pipes should be at least 0.02 m away from them.

    Can I see 2cm? It is difficult to mount closer but if you insist you can.
  • #13 16721072
    jack63
    Level 43  
    Kolgo Domelski thank you very much for the very extensive explanations. To make sure I still have a question related to the quote:
    Domelski wrote:
    NC or NO type valves have the disadvantage that after the change has ceased it returns to its previous state. So we have a leak, the detection system is alarming, the valve closes, the gas is thinning, the system stops alarming, the valve opens and leakage again.

    So I understand that it is a bistable valve with a safe position latch?
  • #14 16721640
    Domelski
    Level 19  
    Quote:
    Can I see 2cm? It is difficult to mount closer but if you insist you can.

    Colleague of DiZMar, I had pictures (I will throw it in) of electric wires along the gas installation by wrapping the gas pipe with a cable. And these are the most common detection systems because the cable is led to the valve so according to some it is best to attach it to the pipe. And, if it's too bad, wind it up. Here, as you can see, even these 2cm are not there, because if there is a culvert through the wall, why use a hole next to it if you can push it with a pipe.

    Quote:
    So I understand that it is a bistable valve with a safe position latch?

    No. These valves are simply a spring-loaded mechanism locked in the open position. When the signal gets the coil releases the blockage and the spring presses the valve (there are different versions: flap, mushroom, ball). Hence, it is generally not an NC valve. This is not a sophisticated construction, but some even have patents and some can be dangerous if someone is handled improperly. The spring inside can have a monstrous force at large diameters.
  • #15 16721809
    jack63
    Level 43  
    Thanks again. This time I figured it out. After all, it must be simple and therefore reliable construction.
    pzdr

Topic summary

✨ The discussion revolves around troubleshooting a heating furnace displaying error E01, which indicates a potential blockage in the gas supply. Users suggest measuring the pressure downstream of the regulator to determine if it is functioning correctly. Concerns are raised about the installation of the gas shut-off valve, including its proximity to walls and the need for proper cable specifications to ensure safety. Recommendations include checking the gas detection system and ensuring compliance with installation instructions. The importance of regular maintenance and inspections of safety devices is emphasized, particularly after power outages or storms that may affect the system's operation.
Generated by the language model.

FAQ

TL;DR: Heating error E01 often means the gas path is shut by a pulse shut‑off valve, not a blocked regulator; "gas detection systems are checked every 3 months" and safety systems apply from 60 kW. [Elektroda, Domelski, post #16719776]

Why it matters: This FAQ helps facility staff and technicians quickly diagnose E01, verify the ZB valve state, and reset safely without chasing the wrong part.

Quick Facts

What does heating furnace error E01 indicate here?

In this thread, E01 points to gas supply being blocked. The likely cause is a tripped pulse shut‑off valve, not a failed pressure regulator. The original poster notes E01 can indicate blocked gas, which aligns with a closed safety valve condition. Visual clues and downstream pressure checks confirm the diagnosis. Reset only after finding the root cause. [Elektroda, Lasek311, post #16657093]

Is the pictured device a gas pressure reducer/regulator?

No. Responders identify it as a pulse shut‑off valve (often marked ZB), not a pressure reducer. When it trips, the internal mechanism closes the gas path, and the red “mushroom” sits low. This is a safety component controlled by a gas detection system or panel, not a regulator. [Elektroda, kz61, post #16657630]

How do I safely reset a tripped ZB shut‑off valve?

  1. Eliminate the alarm cause first (gas leak, detector fault, wiring issue).
  2. Pull the valve’s reset “mushroom” so it protrudes beyond the plug, re‑latching it.
  3. Restore control power and restart the boiler per procedure. Only reset after the hazard is cleared. [Elektroda, kz61, post #16657630]

Can a power outage or storm cause the valve to trip and E01 to appear?

Yes. After outages or voltage dips, transient states can occur. A technician advised re‑energizing the valve and starting the boiler; if problems persist, call service. This aligns with post‑storm scenarios where the detection/control panel may have triggered the shut‑off sequence. [Elektroda, tgo1, post #16711718]

How can I tell if the valve is tripped versus a blocked regulator?

Check two things: the ZB’s red reset “mushroom” position and downstream gas pressure. If the mushroom is low, it’s tripped. If you can, measure pressure after the suspect point; normal pressure suggests the regulator is fine and the trip is elsewhere. [Elektroda, kajron, post #16657248]

What cable size should connect the gas detection panel to the ZB valve?

For GX‑type systems, the minimum cross‑section is 1.5 mm² up to 30 m. This reduces voltage drop on the pulse line and ensures reliable actuation. Undersized cable increases resistance and can cause misoperation during a close command. [Elektroda, Domelski, post #16719776]

Why not use a simple NC/NO solenoid valve held by power?

Latched safety valves avoid automatic re‑opening after a leak clears. NC/NO types can cycle with the alarm, risking re‑leak. Safety coils are short‑duty and designed for momentary pulse closing. “DO NOT control these valves with a simple relay.” [Elektroda, Domelski, post #16720457]

How often should the gas detection and shut‑off system be tested?

Follow the manual: first check after one month, then every 3 months, at least every 6 months. This keeps the valve mechanism exercised and the detectors verified. Record tests and remediate any faults before returning to service. [Elektroda, Domelski, post #16720818]

Who should I call if the detection system or valve misbehaves after a storm?

Call service for the detection system. The ZB does not close by power loss alone; the panel issues a pulse sequence. If lightning or outages damaged the detector panel, you may see power present but hidden faults. Have wiring, plug orientation, and glands inspected. [Elektroda, Domelski, post #16711309]

Are there spacing rules for gas pipes, walls, and other services?

Yes. Maintain 0.1 m above other pipes on horizontal runs and at least 0.02 m clearance where crossing. Keep electrical wiring separated to allow maintenance. Avoid crowding the ZB against walls; provide a working gap. These clearances support safe operation and servicing. [Elektroda, Domelski, post #16720818]

What if the valve doesn’t move on the first close command?

Valves often sit open for long periods. The first pulse may not move the stem enough. Controllers send a series of pulses to ensure latching. Driving with a single, simple relay pulse risks failure to close on demand. Schedule regular exercising tests. [Elektroda, Domelski, post #16720457]

Does the ZB valve require maintenance, or just functional checks?

The user doesn’t service internals, but scheduled functional checks are required. The manual’s frequency ensures the mechanism operates and the system remains reliable. This reconciles “no additional servicing” with periodic testing obligations in the instructions. [Elektroda, Domelski, post #16720818]

What installation red flags appeared in the thread photos?

Issues noted: valve too close to the wall, tight bends immediately after the valve, cable gland not tightened (IP compromised), thin control cable, and unclear manual shut‑off valve location. These reduce safety margins and serviceability; correct them promptly. [Elektroda, Domelski, post #16711309]

How do I measure pressure to rule out a blocked regulator?

Install a manometer downstream of the regulator and compare to expected supply. If pressure is normal, the regulator is clear, and the shut‑off valve or control is suspect. This isolates the fault to the right component before you reset. [Elektroda, kajron, post #16657248]

Why did someone say safety systems apply from 60 kW? What changes then?

Regulations trigger additional safety interlocks and detection from 60 kW heat output. Plan for detectors, pulse shut‑off valves, and documented test routines. Larger plants must demonstrate that shut‑off operates as designed and won’t auto‑reopen after an alarm clears. [Elektroda, Domelski, post #16719776]