Purmo Radiator & Danfoss 013G5164 Thermostatic Kit Issue: Not Heating Up in Ground Floor Flat

Tobiasz22 14940 17
Best answers

Why does my new Purmo radiator with a Danfoss 013G5164 thermostatic kit stay cold in a ground-floor flat even though it has been vented and the radiator valves seem open?

The radiator is most likely not getting flow because the riser/basement valves are incorrectly adjusted or partly closed, reducing the supply pressure so the ground-floor radiator cannot circulate water [#16872634][#16874018] Another possible cause is a clogged thermostatic/supply valve or sludge blocking the small passages in the Danfoss valve, so checking the pin, opening the head valve fully, or flushing the radiator was suggested [#16870832][#16872423] In this case, the practical fix was made in the basement: someone from the cooperative unscrewed the valves there, and the radiator started heating again [#16876122]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16870714
    Tobiasz22
    Level 9  
    Posts: 12
    Rate: 2
    Hello,
    I have a problem with a new Purmo radiator with Danfoss 013G5164 thermostatic kit installed. I live in a block of flats on the ground floor.
    A few days ago, the heater only warmed up in the top half, the bottom half was cold. It was probably due to the closed return valve. I unscrewed the valve, unfortunately now the radiator does not heat up at all. When I unscrew the vent, the glycol flows from the radiator, it does not foam, it does not hiss, so the radiator is deaerated. I took off the thermostatic head and tried to adjust the RA-N thermostatic valve to open it as much as possible. It did not help, however. The heater is still cold.

    I would like to add that I have built the pipes of the riser behind the GK. I can only touch the piece of pipe which is horizontally off the vertical and to which the radiator is screwed. This morning it was slightly warm, now it is cold. The cooperative says everything is fine with the outside plumbing and riser. In other rooms, the radiators heat up properly and heat up in about 2 minutes.
    Please help. I already lack ideas to solve the problem.
  • ADVERTISEMENT
  • #2 16870796
    kot mirmur
    Level 33  
    Posts: 2131
    Help: 206
    Rate: 556
    Hello, where does this glycol come from ?, the CO installation is filled with it? Big plate + probably black pipes = all the muck from the installation blocked some flow. I do not believe that some cooperative / community would fill the internal heat node with glycol.
  • #3 16870827
    misiekpb
    Level 22  
    Posts: 661
    Help: 35
    Rate: 144
    I suspect you turned the return valve off, not unscrewed.
    If you had it turned off from the beginning, the radiator would not heat up at all. Also check the valve first.
  • #4 16870832
    E8600
    Level 41  
    Posts: 8861
    Help: 525
    Rate: 2474
    What kind of heater is cast iron or aluminum. There must be a valve for the thermostatic head. If you already have the head removed, move the valve pin and press it several times, you can also gently tap the entire valve to make it move.
  • ADVERTISEMENT
  • #5 16870907
    Tobiasz22
    Level 9  
    Posts: 12
    Rate: 2
    Thanks for the answers. Steel radiators (modernization), new, as well as valves. Yellow liquid flows out of the air vent, not water, so probably glycol. The return valve is turned fully open. I screwed it in and unscrewed it to be sure, checked the settings with another radiator. The head valve is not in place, it extends to the maximum and moves smoothly in both directions.

    Interestingly, with another closed and cold radiator, the pipes leading to the radiator are warm. With this feleler, the top tube is cold, and the bottom tube is a few degrees (slightly) warmer. Weird.
  • #6 16870933
    E8600
    Level 41  
    Posts: 8861
    Help: 525
    Rate: 2474
    Tobiasz22 wrote:
    The head valve is not in place, it extends to the maximum and moves smoothly in both directions.

    Just because the pin is moving does not mean the valve is not seated. I rather doubt that there would be glycol, rather water with rust, if they were modernized. It is possible that your radiator was filled with water when they rinsed the installation. This is the first season after modernization?
  • ADVERTISEMENT
  • #7 16871028
    kot mirmur
    Level 33  
    Posts: 2131
    Help: 206
    Rate: 556
    This yellow liquid is interesting, probably yellow that floods the plumbers reading the topic. This is water with an installation sludge - obvious lack of flow, the shell heaters have small supply cross-sections, they could be covered with your> glycol. If you have valves on the supply and return, as you wrote earlier, disassemble this radiator and clean it with pressurized water.
  • #8 16871087
    Tobiasz22
    Level 9  
    Posts: 12
    Rate: 2
    I will contact the cooperative again tomorrow morning. Meanwhile, is anyone able to explain this phenomenon:
    1.The radiator water inlet valve is fully turned on, the water supply pipe is cold at the riser
    2. I turn off the valve
    3.after about 5 minutes, the pipe on the riser becomes warm
    4. unscrew the valve
    5. the pipe becomes cold after about 30 seconds, the heater remains cold
    How is it possible that unscrewing the valve cools the pipe that supplies the water to the radiator?
  • #9 16871093
    kot mirmur
    Level 33  
    Posts: 2131
    Help: 206
    Rate: 556
    Poor circulation in this heating riser. There may also be an obstruction in the horizontal inflow / outflow of your radiator. Riser pipes heat up?
  • #10 16872283
    roman 18
    Level 24  
    Posts: 526
    Help: 66
    Rate: 143
    hello, buddy, I would bet a clogged supply valve, after all these danfos have very small passages, muck is blocking the flow.
  • ADVERTISEMENT
  • #11 16872423
    Zbigniew Rusek
    Level 38  
    Posts: 3610
    Help: 394
    Rate: 1534
    roman 18 wrote:
    hello, buddy, I would bet a clogged supply valve, after all these danfos have very small passages, muck is blocking the flow.

    To clean it, remove the head, set the initial setting (crimping) to the "N" position, so that a greater flow was washed out of silt, sand and dust. After approx. 20 minutes, restore the old crossings, or set it slightly higher than it was (but not N, unless it is the last floor - then you can set "N").
  • #12 16872557
    Tobiasz22
    Level 9  
    Posts: 12
    Rate: 2
    Thanks again to everyone for the answers.
    I called the cooperative this morning, they say the problem is not on their side since the riser is warm. There is no glycol in the system, only treated water. I also spoke by phone to the plumber who installed the valves for me and he told me to check the valves as follows:

    1.unscrew the top and bottom valves, the radiator is full of water
    2. I turn off both valves
    3.open the vent, drain the water, after a while the water should stop flowing, it means that the radiator above the vent has emptied and that the valves are tight. This is also what happened in my case.
    4. Then I only opened the top valve. I heard water pouring rapidly into the radiator. The water supply pipe to the radiator has become hot. The valve is clogged.
    5. I closed the top valve (both valves were closed). Then I opened the vent again and drained the water from the radiator.
    6. I opened the top valve. After literally a quarter of a turn. water began to fill the heater and flow from the vent. The bottom valve is not open.

    Now the most interesting.
    At the moment when I released the water from the radiator with the valve turned off again with the vent, then turned off the vent and opened the upper valve, the pipe got hot as the first time. Then I opened the lower valve a bit and immediately the upper pipe, carrying the water to the radiator, became cold! This means that for some reason the pressure is more on the down tube than on the top tube.

    I live on the ground floor. Other vertical radiators on the returns do not have valves (unless someone replaced the radiator and put them on). I currently have the R-AN valve set to 7. I tried with different settings (the upper valve was set to 1, the lower valve was only slightly unscrewed), unfortunately to no avail. In the morning I spoke to my neighbor upstairs, his living room heater heats up. Other radiators (e.g. kitchen, bathroom) in my apartment heat well.
  • #13 16872634
    E8600
    Level 41  
    Posts: 8861
    Help: 525
    Rate: 2474
    I ask again which year it is after this modernization? There are 2 options either a colleague messed up something or a clogged / incorrectly set thermostatic valve in the basement. In the cellars, they can also install thermostatic valves, which are connected with a "heat-pipe" (copper pipe), if there is warm water on the return from the riser, the valve on the supply riser is closed (such heat saving). There is probably a problem on the return valve in the basement that has stuck and all the water in the mountain comes back to you back. Such charms of the ground floor can be similar to the sewage system as the riser becomes blocked, e.g. a fountain from the toilet. :)

    Here you have valve adjustment.


  • #14 16872651
    Tobiasz22
    Level 9  
    Posts: 12
    Rate: 2
    This is the first heating season after the modernization of radiators in my apartment. I saw the movie, I have an identical valve.

    I don't know what the installation in the basement looks like and how it is built. Tomorrow I will call the cooperative again, I hope they won't put me off.
  • #15 16872663
    E8600
    Level 41  
    Posts: 8861
    Help: 525
    Rate: 2474
    Tobiasz22 wrote:
    This is the first heating season after the modernization of radiators in my apartment.

    So they probably got something wrong.

    You will find something similar in the basement.
    Purmo Radiator & Danfoss 013G5164 Thermostatic Kit Issue: Not Heating Up in Ground Floor Flat
    This is a differential pressure regulator, but I have seen it somewhere with a thermostat.
  • #16 16874018
    Zbigniew Rusek
    Level 38  
    Posts: 3610
    Help: 394
    Rate: 1534
    I suspect one thing. The riser valve (in the basement) on the supply riser can be slightly screwed on, so that the pressure on the above riser has been reduced to the value of the return pressure (if not even lower) and the heater does not heat up. Screwing the riser valves on is - unfortunately - quite a common practice, performed "by feel", without any pressure measurements. This usually results in non-heating radiators on the upper floors of a given riser.
  • #17 16874034
    Tobiasz22
    Level 9  
    Posts: 12
    Rate: 2
    Yes, the problem is most likely in the basement and it could be the supply and return valves. Today someone from the cooperative is to check it. I will let you know.
  • #18 16876122
    Tobiasz22
    Level 9  
    Posts: 12
    Rate: 2
    The radiator heats up. Someone from the cooperative had to unscrew the valves in the basement.

Topic summary

✨ The discussion revolves around a heating issue with a newly installed Purmo radiator equipped with a Danfoss 013G5164 thermostatic kit in a ground floor flat. The radiator initially heated only the top half, leading to the suspicion of a closed return valve. After unscrewing the valve, the radiator ceased to heat entirely. The user noted the presence of glycol instead of water when venting the radiator, indicating potential blockage or improper flow. Various responses suggested checking the return valve, ensuring the thermostatic head was functioning correctly, and investigating possible obstructions in the riser or supply lines. Ultimately, the problem was resolved when a cooperative technician adjusted the valves in the basement, allowing the radiator to heat properly.
Generated by the language model.

FAQ

TL;DR: Ground-floor Purmo radiator with Danfoss 013G5164 not heating? Try a flush: set RA‑N to "N" and run ~20 minutes; "set the initial setting … to 'N'" first. Many fixes end in balancing or opening throttled valves. [Elektroda, Zbigniew Rusek, post #16872423]

Why it matters: This FAQ helps flat owners quickly diagnose no‑heat issues tied to RA‑N presets, clogged valves, and basement balancing.

Quick Facts

How do I quickly check if my radiator issue is a clogged valve or system balancing?

Close both radiator valves, open the vent to drain, then open only the supply briefly. If the supply pipe heats fast but the radiator stays cold when the return opens, balancing or basement throttling is likely. If no heat returns on supply, suspect a clogged valve. [Elektroda, Tobiasz22, post #16872557]

What does yellow fluid from the vent mean on a new Purmo radiator?

It usually indicates water mixed with installation sludge, not glycol. Sludge can block the narrow passages in panel radiators and valves, starving flow and heat. A pressure rinse or targeted flush often restores performance. [Elektroda, kot mirmur, post #16871028]

How do I free a stuck Danfoss 013G5164/RA‑N valve?

Remove the thermostatic head, press the valve pin repeatedly, and gently tap the valve body to release the seat. A moving pin can still mean a seated valve, so verify flow afterward. “Just because the pin is moving does not mean the valve is not seated.” [Elektroda, E8600, post #16870933]

What is the RA‑N preset “N” and when should I use it?

RA‑N “N” is the full‑flow preset used for commissioning or flushing. Set to “N” and run for about 20 minutes to wash out silt, then restore the previous preset to avoid over‑flow on the riser. [Elektroda, Zbigniew Rusek, post #16872423]

Could the problem be in the basement, not my apartment?

Yes. Throttled or stuck riser supply/return valves or a regulator can starve ground‑floor radiators. In this thread, heat returned only after the cooperative opened basement valves. If others heat normally, escalate balancing checks. [Elektroda, Tobiasz22, post #16876122]

Why does my riser pipe warm after 5 minutes when the valve is closed, then cool 30 seconds after opening?

That pattern signals pressure imbalance. With the valve closed, the riser warms. Opening the valve lets low‑pressure return dominate, pulling cooler water and dropping supply temperature locally. This supports a balancing or throttling fault. [Elektroda, Tobiasz22, post #16871087]

What’s the first thing to check if only the top of the radiator gets warm?

Verify the return valve is open. A closed return can heat only the top via limited convection, leaving the bottom cold. Open it fully, bleed once, and confirm both valves have flow. [Elektroda, misiekpb, post #16870827]

How can I tell if my Danfoss valve body is clogged?

Typical clues: no heat despite open valves, supply cools quickly when return opens, and other radiators heat normally. Danfoss bodies have small passages that silt can block, especially first season after work. [Elektroda, roman 18, post #16872283]

Could a regulator on the riser be closing my supply when the return is warm?

Yes. Some risers use differential pressure or thermostatic controls linked by a heat pipe. Warm return can drive these to restrict the supply, affecting ground‑floor branches. Inspection and reset in the basement fix it. [Elektroda, E8600, post #16872634]

What is a differential pressure regulator in heating risers?

It maintains stable pressure across the riser to balance flow between flats. If mis‑set or stuck, it can starve the lowest branch. The fix requires access and adjustment at the basement manifold. [Elektroda, E8600, post #16872663]

How‑to: Flush a radiator using the RA‑N and vent in 3 steps

  1. Close both valves, open the vent to drain until flow stops.
  2. Open only the supply; let water rush in and out the vent briefly.
  3. Close vent, set RA‑N to “N” for a short run, then restore the prior preset and reopen return. [Elektroda, Tobiasz22, post #16872557]

Edge case: Why do upper-floor radiators heat while mine stays cold?

A riser valve partially closed “by feel” can equalize supply and return pressures at lower floors, halting flow. Upper floors may still heat, masking the fault. Ask building management to measure and rebalance. [Elektroda, Zbigniew Rusek, post #16874018]
Generated by the language model.