Fronius Symo 3.0-3-S Inverter Error 301: Overcurrent, AC Grid Issue, Troubleshooting & Service Cost
czarnu 7503 6
  • Suggesting UPS logging on all three phases to trace error 301
    #1 16870735
    czarnu
    Hello, after the complete failure of the Fronius Symo 3.0-3-S inverter at the end of July and replacement by the service with a new one, a new problem appeared, namely the error 301. In the manual, he says:
    Overcurrent (AC).
    Behavior: Short-term interruption of feeding into the grid. The inverter restarts the system startup.
    Troubleshooting: If the status message persists: Contact a service technician
    trained by Fronius.
    I contacted my installer, after three weeks, the gentlemen from the service called and said:
    "They are ready to repair the inverter, the courier arrives, takes the inverter to the service and makes a diagnosis there, and everything would be great if not for the fact that, if Fronius does not find a fault, I will be charged for about 100 euros (transport and diagnostics).
    In addition, they also sent possible reasons for the error
    301 Current peak on the mains supply detected
    What can cause:
    1. Voltage drop on the public mains
    2. Grid Impedance out of permitted values
    3. Bad contact of the power stack with AC
    4. Measuring error on the power stack
    The problem is so bothersome that when the inverter catches an error, it is not able to restart itself, synchronize and start production, there must be physical interference disconnecting the inverter from the AC side for about 1-3 minutes and the problem disappears.
    I have had the installation for a year earlier, except for the failure of the inverter, the problem never occurred.
    Ad 3, the installation in the house with the connection is new.
    The question of where to start to eliminate the problem?
    Added after 19 [hours] 32 [minutes]:
    Today I learned from an electrician to find a UPS x 3 for each phase, preferably APC, connect via USB or RS232 and start logging with the apcupsd program.
  • #2 16872331
    prose
    Level 36  
    Help: 173
    Rate: 850
    For me, the Fronius ig 60 hv once caught this error and reset itself, but it was only one time. If it does not restart itself, it is an internal error of the inverter, otherwise a defect.
    Added after 4 [minutes]:
    1. Voltage drop in the public supply network
    2. Mains impedance outside the allowed values
    3. Bad contact with the stack of AC
    4. Measurement of error on the power stack
    It will also happen when you use high-power receivers, the voltage drop for me popped up when welding with high current.
  • #3 16872617
    czarnu
    Well, I don't know myself, but thinking logically when the inverter catches an error (it finds that something is wrong with the network parameters), it should be restarted, start checking again and turn on. And for me it is not like that, I have to physically turn it off and it is just starting to work.
    Best of all, I told my installer, he passed the information to Fronius and they said it was a symptom according to the procedure.
    In my case, the error was caught 3 times twice, it was on Sunday around 12-13, so I did not have a heavy load on the network, only the boiler could work.
    Added after 21 [minutes]:
    On the Fronius website I downloaded the pdf manual and it says:
    Code:
    301
    Description:
    Overcurrent (AC)
    Behavior:
    Brief interruption of the mode
    mains supply
    The inverter starts over
    system boot
    Removal:
    If the status message is displayed constantly: Contact the service technician
    trained by Fronius.
    Reasoning, it should reboot and reattach.
  • #4 17127514
    czarnu
    It was calm until today, beautiful sunshine 3:30 PM no production, I went to the inverter and it is in the process of synchronization, the test passed correctly, the production starts and suddenly it crashes error 112 error description in the manual is an RCMU error restart and error 301 again - overcurrent, I did a current restart of the inverter, it started up and by the end of the day it worked without problems.
    I read that the inverter has RCMU in security, while looking on the Internet, I found that it is a module that works like a differential. I do not know if I understand it correctly, but it seems to me that these problems are not the fault of the inverter, but the network.
  • #5 17139984
    taniam
    Help: 28
    Rate: 41
    I agree with this line of reasoning.
    Check:
    - supply line impedance
    - insulation resistance of the wires on the AC and DC side
    - mains voltage at the time of the problem.
    You should find these measurements in the installation commissioning report.
  • #6 17140419
    BILGO
    Help: 393
    Rate: 725
    First, check the entire installation from the AC side. Inverters are very sensitive to poor contacts. Likewise, to be sure, you can perform the above-mentioned measurements to be sure.
  • #7 20145191
    rootkris
    I propose to leave this problem to the installer of the PV installation, you do not lose the warranty, they will find the cause and in the event of a mistake and shipping, you do not bear the costs because the installer pays Fronius for replacing the inverter.
The Fronius Symo 3.0-3-S inverter has encountered error 301, indicating an overcurrent issue related to the AC grid. Users report that this error can result from various factors, including voltage drops in the public supply, grid impedance exceeding permissible limits, and poor AC connections. Troubleshooting steps suggest checking the supply line impedance, insulation resistance, and mains voltage during the error occurrence. Some users experienced the inverter restarting itself, while others had to manually reset it. It is recommended to consult a trained Fronius service technician for persistent issues, as they can diagnose the inverter without incurring costs if no fault is found. Users also emphasize the importance of having the installer handle the situation to maintain warranty coverage.