Sofar 5.5K Grid Errors OVP, UVP, OFP, UFP: Troubleshooting Differential Tripping Issues

bobo 44 74190 19
ADVERTISEMENT
Treść zostaÅ‚a przetÅ‚umaczona polish » english Zobacz oryginalnÄ… wersjÄ™ tematu
  • #1 19115309
    bobo 44

    Level 18  
    Hello
    Such errors have been popping up for some time regardless of the time of day. When such an error occurs, the main differential at home goes out. I understand the errors, but why is the differential blowing out, the installation is connected right after the differential in the switchboard.
  • ADVERTISEMENT
  • #2 19115414
    kosmos99
    Level 38  
    There is some current leakage somewhere. For inverters, a differential with a leakage current of 100mA is recommended. The one you have should have a value of 30mA, which is three times more sensitive.
  • #3 19115449
    bobo 44

    Level 18  
    That's right, mine is 30 mA and there is no other one in the installation.
  • #4 19115748
    kosmos99
    Level 38  
    An extra one should only be added to the inverter circuit.
    Of course, it's best to check if everything is fine with the installation and the inverter.
  • #5 19115915
    Cytro12
    Level 26  
    I also have 30mA and there is nothing wrong, I need to check the installation and grounding.
  • ADVERTISEMENT
  • #6 19116147
    noja102
    Level 24  
    @bobo 44, post photos of the boxes next to the inverter.
  • ADVERTISEMENT
  • #7 19116524
    3301
    Level 34  
    Grid OVP, UVP, OFP, UFP means too high and too low AC voltage and too high and too low frequency, perhaps there are some anomalies in the grid.
    The inverter power supply should be connected before the residual current circuit breaker, of course through overcurrent protection.
    Download the AC voltage and current parameters from the inverter and check whether these parameters differed from the time when the inverter was working correctly before the error occurred.
  • #8 19116594
    prose
    Level 35  
    In Sofar, such errors appear when the AC is disconnected. I checked it on my own.
  • #9 19117877
    bobo 44

    Level 18  
    There were machers from the company and they said that they would connect a 100mA differential on the set, I'll see what it will do. When this error appears, the differential goes out, but after turning off the inverter, everything works fine.
  • #10 19117915
    Cytro12
    Level 26  
    If the RCD trips, something is wrong, maybe the insulation is damaged somewhere and there is a short between N and PE, or a bad connection of the differential switch and/or inverter. Have them check the type of network you have with the instructions for connecting the inverter. Increasing the sensitivity may mask the problem, but it will not solve it.
  • #11 19117949
    kosmos99
    Level 38  
    bobo 44 wrote:
    There were machers from the company and they said they would connect a 100mA differential

    But I understand that this will be an additional differential, not the existing one?
  • ADVERTISEMENT
  • #12 19118004
    prose
    Level 35  
    100mA is recommended for some inverters.
  • #13 19118017
    bobo 44

    Level 18  
    Yes, it will be an additional differential only on the set, bypassing the one in the normal installation.

    Cytro12 wrote:
    If the RCD trips, something is wrong, maybe the insulation is damaged somewhere and there is a short between N and PE, or a bad connection of the differential switch and/or inverter. Have them check the type of network you have with the instructions for connecting the inverter. Increasing the sensitivity may mask the problem, but it will not solve it.

    The set is connected directly with a cable to the home switchboard behind the differential switch. If the cable connecting the inverter to the grid were damaged, it would trigger all the time, and this could be called "spontaneous".
  • #14 19118908
    Cytro12
    Level 26  
    bobo 44 wrote:
    if the cable connecting the inverter to the grid were damaged, it would trigger all the time, and this could be called "spontaneous".

    Maybe the RCD is connected incorrectly, a common error is incorrect N pairing.
  • #15 19299204
    bobo 44

    Level 18  
    I ended up replacing the inverter with a new one with new software.
  • #16 20137324
    gawkosg
    Level 1  
    I have the same problem with two inverters, both of them behave this way independently. Sometimes it trips the RCD on one, sometimes on the other and sometimes both at the same time 😞. There are 11 panels under each inverter with a total power of 4.95 kWp. Maybe someone can suggest what to do about it?
  • #17 20231145
    e_majsterkowicz
    Level 10  
    The differentials used were 30mA or 100mA?
  • #18 20541806
    Przemek22tex
    Level 14  
    I have a problem with the Sofar 3 kW 1-phase inverter. Often, when the sun comes out from behind the clouds at noon, Grid OVP, UVP, OFP, UFP errors appear. I switched to a phase with a lower voltage, but during operation the installation does not exceed 240 V. I don't know what the problem is anymore, because it can trip the inverter several times a day, and since it is in the attic, it is annoying to have to constantly run and reset it. Could this be the fault of the inverter itself? I will add that the differential and protection devices have never tripped for me.
  • #19 20541923
    3301
    Level 34  
    These errors result in: too high and too low AC voltage and too high and too low frequency. Maybe the network is working on the generator, but you need to download the parameters from the inverter from the export tab and analyze when the shutdown occurred and at what indications.
  • #20 20555013
    somzol1981
    Level 1  
    Hello Guys. I have the same issue. Every now and then shows a OVP alarm. Installer blames the manufacturer. Manufacturer blames the installer. Do you have any solution?

Topic summary

The discussion revolves around troubleshooting differential tripping issues related to Sofar inverters, specifically errors such as OVP (Over Voltage Protection), UVP (Under Voltage Protection), OFP (Over Frequency Protection), and UFP (Under Frequency Protection). Users report that these errors cause the main differential to trip, often linked to current leakage or grid anomalies. Recommendations include using a 100mA differential for the inverter circuit, checking installation integrity, grounding, and ensuring proper connections. Some users suggest that the inverter may be at fault, while others emphasize the importance of analyzing AC voltage and current parameters during operation. The conversation highlights the need for thorough checks of the installation and potential issues with the grid supply.