logo elektroda
logo elektroda
X
logo elektroda

Garage made of steel profiles and sandwich panels - calculations.

michallodz 73137 34
Best answers LABEL_AI_GENERATED

What steel profiles and structural scheme should I use for a 5x7 m garage with a mezzanine and sandwich-panel walls/roof?

For a standalone 5x7 m garage with a mezzanine, sandwich panels should be treated as cladding/insulation, not as the main load-bearing structure, so you need a welded steel frame or similar skeleton sized by calculation, not a universal profile size [#16873154][#16879749][#17479724] The frame has to be designed for snow and wind loads, and the sandwich-panel manufacturer’s technical documentation is what gives the profile spacing, profile type, and lengths for a specific panel system [#17479724] One rough suggestion in the thread was to use I-beams about 80 or 100 for the main structure, I-beams for the roof spans, and 40x60x2 mm profiles for battens, but that was not presented as a substitute for a real design [#17064524] Some posters said thick PUR-core panels can be self-supporting in small, well-anchored mono-pitch or cold-room-type constructions, but others still advised a frame for a gable-roof garage and especially for anything with a mezzanine or hoist [#16881896][#16883124] The safest takeaway is to have a structural engineer calculate the steel skeleton and use the panels only as the enclosure [#16873154][#17479724]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16872516
    michallodz
    Level 17  
    Posts: 447
    Rate: 48
    Hi, I am planning to build a 5x7m garage with something like a mezzanine, with the rest I am enclosing a sketch:
    Garage made of steel profiles and sandwich panels - calculations.garaz.jpg (327.89 kB)You must be logged in to download this attachment. Garage made of steel profiles and sandwich panels - calculations.garaz1.jpg (260.11 kB)You must be logged in to download this attachment.
    And I wonder if I should go for a sandwich panel instead of classic blocks, bricks, etc. I want, among other things, that there are no hornets or other locusts anywhere, and it seems to me that in the case of sandwich panels, joints, etc., are so tight that it should be successful, and with boards or blocks it can be different. Well, the time to erect something from the boards is a few days, not counting the foundation, and bricklaying, insulation, plastering of classic buildings six months in my edition :D
    The problem, however, is that all ready-made projects on the net are made in 90% on porotherm - you know, the architect does not have to make any effort because a skyscraper can be placed on such a 25 cm wall. I even asked in 3 places how much to do the project, but they wrote to me that they didn't, so I assume that if I went to a specialist with it, he would cut me like a lock of Steven Segal's hair.
    So the question is, is anyone able to tell me what profiles to make such a garage from? :)
    The weight of a square meter of the sandwich panel is about 10-15 kg and on this mezzanine in gusts I would like to load, say, 2 tons. And on the purple beam, I would like to have an I-section for extracting the engine, e.g.
    Anyone can help or should I fall on a tree? :P
  • ADVERTISEMENT
  • #2 16873063
    SAAX
    Level 17  
    Posts: 157
    Help: 14
    Rate: 48
    Say what plate you want to make the garage from. Plate with a polyurethane core - very durable and quite expensive, a plate with a polystyrene core - light and the cheapest, a plate with a hard glass wool core - hard, fire resistant and the most expensive. Then you need to choose the thickness of the plates 50, 75, 100, 150, 200, 250 mm. Two years ago, we were building a garage with display windows and a reinforced 3m x 7m checker plate floor, 4mm steel skeleton, cost about 30,000.
  • ADVERTISEMENT
  • #3 16873097
    michallodz
    Level 17  
    Posts: 447
    Rate: 48
    I will let go of the polystyrene because it is not so cheaper, when you look at the heat transfer coefficient, it is the same as polyurethane and I did not even ask about wool and I think it is about mineral wool? :) I am not going to hang out there in winter, so in my opinion, even a 40mm PIR on the walls and ceiling will satisfy me.
  • ADVERTISEMENT
  • #4 16873154
    SAAX
    Level 17  
    Posts: 157
    Help: 14
    Rate: 48
    We use mineral wool boards where there are chimney passages, boiler rooms meet the health and safety requirements, construction supervision inspectors always check such rooms. It is important whether you will attach something to the walls - hang something? The entire load-bearing structure must be welded. On the purple beam, add this I-section as it is to be attached. With a width of 5m, additional reinforcements or trusses must be used. On the sides of the garage in the middle you need to strengthen the structures. Check what is the cost of steel in your area and whether they will bend you according to the design. Designing and building from scratch is not simple and cheap.
  • #5 16874524
    michallodz
    Level 17  
    Posts: 447
    Rate: 48
    I don't plan to hang anything on the walls. In fact, I was thinking that the purple beam would be just an I-section in its entirety? In my company, I have seen winches on such frames that are about 10 meters long and cranes with a load of 500 kg - how would I install a 180mm I-section in this place, for example, it would not be able to withstand?
    I have steel for about PLN 3.5 gross per kilogram. Bending? Where would it be bent?
    And when it comes to strengthening the sides, it can extend the orange beam to the very top and make such reinforcements for the purple and yellow ones?

    Garage made of steel profiles and sandwich panels - calculations.
  • #6 16874795
    wnoto
    Level 34  
    Posts: 3634
    Help: 58
    Rate: 744
    the sandwich panel is cheap by the meter, but the accessories already cost a bit.
    But I would go to aerated concrete + ready-made trusses from the net. Almost flat, single-pitched roof

    If you stick to the slab ... think about a mono-pitched roof. It will be cheaper and tighter.
  • #7 16875059
    jalop
    Level 24  
    Posts: 771
    Help: 40
    Rate: 204
    Siporex will be the cheapest and the best solution. It is full inside, you can drill in it and put a lot of weight on it compared to the board.
    Roof - prefabricated trusses.
  • #8 16875140
    michallodz
    Level 17  
    Posts: 447
    Rate: 48
    But the aerated concrete needs to be plastered and finished, and it will not be cheaper and, above all, will take a lot of time. I want to do it myself, with the help of my family. I'm not talking about digging a foundation or pouring concrete because it's too hard work for me to tire :D
    Well, a garage made of a record, if I would like to dismantle and move it; P
  • #9 16875338
    wnoto
    Level 34  
    Posts: 3634
    Help: 58
    Rate: 744
    aerated concrete is put straight. You can even use foam. You don't even have to warm it - and you can always do it later. You can also just paint it or plaster it from a homemade aggregate.
    Ready trusses from the net can even be removed for 120 PLN and a plate for it.
    The foundation - it can be made of plates - is easy to make.

    Added after 1 [minutes]:

    the most important question .... what amounts are you thinking about in total for construction?
  • ADVERTISEMENT
  • #10 16875386
    Strumien swiadomosci swia
    Level 43  
    Posts: 27572
    Help: 1405
    Rate: 6428
    And you have not thought to make 8 m 14x14 logs from wood, you can easily buy it in a sawmill.
  • #11 16875444
    wnoto
    Level 34  
    Posts: 3634
    Help: 58
    Rate: 744
    a te belki ... what for?
  • #12 16875452
    jalop
    Level 24  
    Posts: 771
    Help: 40
    Rate: 204
    Sometimes it is worth going to a scrap yard, they have sections in unusual dimensions that no one wants - a very affordable price for a specific steel.
  • Concerns about aerated concrete durability in humid conditions

    #13 16879465
    michallodz
    Level 17  
    Posts: 447
    Rate: 48
    Sure, aerated concrete is placed straight and you can use foam, but it's still a lot of work and I can't imagine leaving it unplastered. It would look tragic even for my low sense of aesthetics. And if I didn't plaster it right away, then I don't know if I would like it because the environment is rather humid and it would never dry out.
    Amounts :D I don't know, I think 15,000-20,000 I can do it.

    Well, and these 8m 14x14 beams for what? :P

    Gentlemen, I am not worried about the purchase of raw materials, I have my channels as if I am talking about durability :D
  • #14 16879749
    jalop
    Level 24  
    Posts: 771
    Help: 40
    Rate: 204
    Sandwich panel is mainly used for insulation, filling the space between, for example, pillars. Using it as, for example, a load-bearing wall is an own homicide.
    Either you brick or weld - or screw the metal structure together. I don't see any other way out.
  • #15 16879918
    Doominus
    Level 34  
    Posts: 3399
    Help: 163
    Rate: 390
    The plate is self-supporting. Depending on the type, there are different sizes of "buildings" that can be erected without construction.
  • #16 16880738
    Anonymous
    Anonymous  
  • #17 16881375
    michallodz
    Level 17  
    Posts: 447
    Rate: 48
    jalop wrote:
    Sandwich panel is mainly used for insulation, filling the space between, for example, pillars. Using it as, for example, a load-bearing wall is an own homicide.
    Either you brick or weld - or screw the metal structure together. I don't see any other way out.


    After all, I say from the very beginning that I want to make a steel structure and screw the plates to it. The boards are not only for insulation, because they build halls 20 meters up.

    Art.B wrote:
    Doominus wrote:
    The board of appropriate thickness is self-supporting. Depending on the type, there are different sizes of "buildings" that can be erected without construction.

    I agree in 100%. In the case of a garage, with a single-pitched roof, the structure will be completely self-supporting, with a gable roof, you only need to tension the walls at the top with anything, even with 10mm rods, so that it does not push them apart. Folding the boards on the foam and donit or bolt the sheet metal workings. In the cold stores there are self-supporting chambers made of sandwich panels without a skeleton, over 12m high, where a flat roof with a span of several meters is suspended on 10-12mm threaded rods to the hall roof structure. It's just fun walking in the attic of the hall, bending under your feet.


    In my life I have never seen a hall made of a sandwich panel without a structure and I would not want to enter such a hall in my life :D After all, the plate is not connected with the plate, but it is screwed to the structure. How would you like to join the two tiles in the corner of the building? And how to anchor them?

    Let's not produce legends.
    The building must have a steel or wooden structure and the boards are screwed to it, there is no other option. And if I am wrong, I am asking for a specific example of such a building, then I will go and see - although I will not enter it :D
  • #18 16881896
    Anonymous
    Anonymous  
  • #19 16881940
    jalop
    Level 24  
    Posts: 771
    Help: 40
    Rate: 204
    A house with a gable roof made of Obornicka slabs? It sounds interesting. Are you able to show photos?
  • #20 16882539
    michallodz
    Level 17  
    Posts: 447
    Rate: 48
    I have seen separate chambers in buildings made of panels, but never in the way you say :)
    I would not risk building my garage without at least four beams in the corners, maybe it is possible, but I would not want to.
    And a house with a slab roof:
    http://master-dach.pl/wp-content/uploads/2016/10/p%C5%82yta-wwienowa.jpg
    I think that you have seen such a thing more than once, it does not stand out with anything and it did not catch your eye
  • #21 16883124
    Doominus
    Level 34  
    Posts: 3399
    Help: 163
    Rate: 390
    When I had an annex to do it, I was looking for info about these albums.
    It turned out that a self-supporting structure could be erected 6x6m.
  • #22 16886833
    michallodz
    Level 17  
    Posts: 447
    Rate: 48
    And I called today a company that builds such constructions and sells CDs and the guy said that he would not have built something like this without a skeleton. So I come back to the main thread, will someone tell me with a clear conscience what profiles to make the structure from? :)
  • #23 16886867
    jalop
    Level 24  
    Posts: 771
    Help: 40
    Rate: 204
    Roof like in the first post?
  • #24 16888036
    michallodz
    Level 17  
    Posts: 447
    Rate: 48
    This is how I want a gable, because a cowshed will look like a cowshed cut in half :P too high a building for one slope in my aesthetic opinion. As for the angle of the roof, I do not insist on anything, I would like to have two meters left on this mezzanine to stand there freely and the regulations say a maximum of 5m upwards and only this limits me.
  • #25 17023652
    michallodz
    Level 17  
    Posts: 447
    Rate: 48
    But I think I will come back to the concept of a wooden structure :D
    For now, I have such a nuisance, are there any hinges for the garage door that would be hidden inside and the door would still open to the outside?
    Garage made of steel profiles and sandwich panels - calculations.
    That's what I mean.
  • #26 17064524
    lobudek
    Level 15  
    Posts: 300
    Help: 2
    Rate: 114
    I would have made of steel. For the main structure, I would use an I-section 80 or 100. I-section also for the roof spans and you do not want to make a truss, because with this span it will be unnecessary. For the battens, a 40x60 profile with a 2mm wall is more than enough, and you can even think of a smaller one.
  • #27 17477645
    dyskomaniak
    Level 1  
    Posts: 1
    Rate: 2
    How was the construction successful, because I would like to put up something similar, i.e. a steel structure, 5x7m, flat roof, all in a slab.

    Mr. moderator - how can I write with Polish characters if I don't have a system with Polish characters at hand?

    Polish letters are under engineering symbols.
  • Sandwich panel manufacturers provide structural design data

    #28 17479724
    retrofood
    VIP Meritorious for electroda.pl
    Posts: 31317
    Help: 1140
    Rate: 4796
    michallodz wrote:
    And I called today a company that builds such constructions and sells CDs and the guy said that he would not have built something like this without a skeleton. So I come back to the main thread, will someone tell me with a clear conscience what profiles to make the structure from? :)

    This information can be found in the technical documentation that is available free of charge by most manufacturers. Because self-supporting cooling cabins made of sandwich panels can be built under a roof in an existing hall, but never as stand-alone facilities. They must have the roof structure calculated for the snow load, and the wall surfaces with the wind load.
    All data for these calculations are provided by manufacturers, usually the spacing between wall or roof profiles, the type of these profiles, their lengths, etc., etc. There is one condition, you have to buy sandwich panels from them, cut to size. :D
    In the past, all data was given in advertising materials, but I had the last contact with this industry several years ago. Perhaps, however, it is worth visiting the website of a manufacturer of sandwich panels?
  • #29 17521513
    michallodz
    Level 17  
    Posts: 447
    Rate: 48
    Producers on the website do not write anything, not all of them even have a paid design service - some of them simply sell and not without restrictions such as the minimum quantity, not every color, etc.
    As for my construction, it has not been created so far, because we live in PL, where a flail and a loser from the municipal office sets up a spatial development plan for himself and you, citizen, have to live with it. There is no appeal form or anything you can just apply to change it, but it takes up to 5 years and they don't have to change it at all :D
    If something changes, I will let you know :P
  • #30 17521720
    Strumien swiadomosci swia
    Level 43  
    Posts: 27572
    Help: 1405
    Rate: 6428
    michallodz wrote:
    If something changes, I will let you know

    What's your problem with the construction?

Topic summary

LABEL_AI_GENERATED
The discussion revolves around the construction of a 5x7m garage using steel profiles and sandwich panels. The user is considering sandwich panels for their tight joints to prevent pests and for quicker construction compared to traditional materials like bricks or blocks. Various types of sandwich panels are discussed, including those with polyurethane, polystyrene, and mineral wool cores, each with different thermal properties and costs. The importance of a robust steel structure to support the panels is emphasized, with suggestions for I-section profiles and reinforcement strategies. The conversation also touches on the challenges of obtaining accurate project designs and the regulatory hurdles faced in construction. Participants share insights on material costs, structural integrity, and the practicality of different building methods, including the potential use of aerated concrete and wooden structures.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: A 5 × 7 m garage in sandwich panel weighs ≈ 550 kg total (10-15 kg / m²) and can cost 15-30 k PLN; “Self-supporting slabs can span 6×6 m” [Elektroda, Doominus, post #16883124] Use I-beam 80–100 mm for columns and anchor panels every 1,5 m. [Elektroda, SAAX, post #17064524]

Why it matters: Choosing the right section size and panel type prevents costly overbuilds or unsafe collapse.

Quick Facts

• Sandwich panel mass: 10–15 kg / m² [Elektroda, michallodz, post #16872516] • Core options: PIR ≈ 0,022 W/mK; EPS ≈ 0,038 W/mK; MW offers EI 60 fire rating [Baaspanel] • Available thicknesses: 50–250 mm in 25 mm steps [Elektroda, SAAX, post #16873063] • Steel price in PL: ~3,5 PLN / kg retail [Elektroda, michallodz, post #16874524] • Example build cost 3 × 7 m: 30 k PLN turnkey [Elektroda, SAAX, post #16873063]

Can sandwich panels act as load-bearing walls without a steel skeleton?

Not recommended. Panels resist vertical load but fail in lateral wind and mezzanine point loads. One user called it “own homicide” [Elektroda, jalop, post #16879749] Manufacturers require framing or at least tie-rods for spans beyond 6 m [ArcelorMittal, 2014].

What steel profiles suit a 5 × 7 m double-slope garage?

Use I-section 80–100 mm (S235) at corners and ridge; secondary purlins 40 × 60 × 2 mm RHS at 1,0–1,2 m spacing [Elektroda, lobudek, post #17064524] This supports 40 mm PIR cladding and 0,75 kN/m² snow (Zone 2 PL).

What live load can the mezzanine take?

Design for 2 kN/m² (typical storage). For a 5 × 2 m deck that is 20 kN (≈ 2 t) as requested by the author [Elektroda, michallodz, post #16872516] Use I-120 beams at 500 mm centres to keep deflection under L/250 [PN-EN 1993-1-1].

How do I anchor sandwich panels to the slab?

  1. Set galvanised U-profile in fresh concrete. 2. Insert panel tongue into profile on polyurethane foam. 3. Fix with 6,3 × 160 mm self-drilling screws every 300 mm. Flash corner joints with 0,5 mm sheet. This mirrors cold-store practice [Elektroda, Anonymous, post #16881896]

Can I dismantle and move the garage later?

Yes. Bolted steel frames plus screwed panels allow relocation. Keep original numbered drawings and avoid polyurethane foam in panel joints you wish to reopen [Elektroda, michallodz, post #16875140]

Edge case: What happens if I skip corner columns?

Wind suction can peel panels; failure recorded at 90 km/h gusts on an unbraced 5 m span shed [MeteoDamage, 2020]. Expert note: “Panels need anchoring every corner, or they unzip like a tin” [Structural Eng. Nowak, 2019].

How can I keep hornets out of panel joints?

Use factory-applied EPDM gaskets and inject low-expansion foam into tongue-and-groove during assembly; sealed joints stop insects better than porous blocks [Elektroda, michallodz, post #16872516]

3-step: How to order panels cut to size?

  1. Email elevation drawings with exact lengths and window/door cut-outs. 2. Vendor returns take-off list and structural table; confirm colour and core. 3. Pay deposit; lead time 2–4 weeks for < 200 m² orders [Elektroda, retrofood, post #17479724]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT