Metabo TKHS315C - How to properly connect to the old 4-wire network.

soczi666 14202 8
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 17023267
    soczi666
    Level 11  
    I bought a new table saw with a 3-phase motor. The saw is equipped with a KOA7 (DZ08-3) 400V switch diagram of this switch below. The switch has a 5-pin power plug
    [/ Img]
    Metabo TKHS315C - How to properly connect to the old 4-wire network.

    In the garage, however, I have an old installation with 3 phases and a N cable
    I would like to advise you how to connect it so as not to break the engine.
    I am asking for advice.
  • ADVERTISEMENT
  • #2 17023289
    mar_uda
    Level 23  
    The key question is what is the repetition of the power supply network (to be checked in the power grid or connection conditions attached to the contract).
  • ADVERTISEMENT
  • #3 17023300
    soczi666
    Level 11  
    mar_uda wrote:
    The key question is what is the repetition of the power supply network (to be checked in the power grid or connection conditions attached to the contract).
    this is an old type network, I don't know anything about it, but normally there are 4 links, including 3 phase ones. And the same village has the same installation. I don't want to do anything but connect this device to a 4-pin plug.
  • ADVERTISEMENT
  • #4 17023341
    mar_uda
    Level 23  
    I made it quite clear what information is needed to connect. A colleague did not provide it, and an error in this matter can result in electric shock or even fire (not to mention damage to the equipment).

    If a colleague bought a version with a 5-pin plug, then the socket must be the same. And to connect them, you need to know the type of mains.
    If you do not feel up to a colleague, please call an electrician.
  • #5 17023464
    soczi666
    Level 11  
    I bought with 5 plugs because 4 plugs no longer produce for this type of devices and I have no humor and money to modify a few years of installation. That is why I asked how to connect an induction motor with such a switch to a 4-wire network. I do not have grounding or any differentials, the meter reaches 3 phases and N. I do not know what installation you are because I do not need life, I know that it works and no one hurt electricity.
  • #6 17023513
    mar_uda
    Level 23  
    I asked about the type of mains and gave where it can be checked. If even your friend doesn't feel like it, I suggest calling an electrician to connect the device.

    If a friend does not want to replace the 5-pin socket, how does a friend want to connect the device with such a plug? Wires and adhesive tape? Will it cut the plug and replace it, which, depending on the terms of the warranty, may end in losing it?
    If the device connection system requires connection to a 5-pin socket, such should be used.
  • #7 17023532
    soczi666
    Level 11  
    TN-C network
    I will buy a 5-pin plug, a piece of cable and a 4-pin socket.
  • #8 17023608
    mar_uda
    Level 23  
    It is not allowed to make adapters from a 4-wire to a 5-wire installation. The socket should be replaced with a 5-pin socket and the PEN cable should be separated (or rather zero, because it probably is there). It's even cheaper.

    If devices with a 4-pin plug are also to be connected to the socket, then the adapter from the 5-pin to 4-pin socket can be made without problems (unless there are devices in the "bypass" that are converted by amateurs and require a PEN cable, which is not and was not allowed).
  • ADVERTISEMENT
  • #9 17023619
    Krzysztof Reszka
    Moderator of Electrical engineering
    soczi666 wrote:
    TN-C network

    So you have 3x L and a PEN cable.
    soczi666 wrote:
    I will buy a 5-pin plug, a piece of cable and a 4-pin socket.

    So how do you combine it?
    Leave this plug 5x that the manufacturer gave. Replace the socket with 5 x. Now it would be best if you exchanged this piece of cable from the socket to the socket if you can for 5 x. Deriving 3 x L and PE and N separately. And if you can't do it like the subject here.
    https://www.elektroda.pl/rtvforum/topic423870.html
    Here I quickly drew how to connect this socket.
    Metabo TKHS315C - How to properly connect to the old 4-wire network.

Topic summary

The discussion revolves around connecting a Metabo TKHS315C table saw, equipped with a 3-phase motor and a KOA7 (DZ08-3) 400V switch with a 5-pin plug, to an older 4-wire electrical network. Users emphasize the importance of understanding the type of power supply network before making connections to avoid potential hazards such as electric shock or equipment damage. Recommendations include replacing the existing socket with a compatible 5-pin socket and ensuring proper wiring, including separating the PEN cable. Some users suggest purchasing a 5-pin plug and a 4-pin socket, while others caution against making adapters from 4-wire to 5-wire installations. The need for professional assistance is also highlighted for safety.