Choosing a contactor for domestic circuits - 20A AC1 sufficient?

mariusz-g 864 1
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 17232817
    mariusz-g
    Level 9  
    Welcome,

    I would like to cut off electrical circuits in the house using a contactor.
    What kind of contactor will ensure long term operation ?
    I have up to 8 sockets on one circuit. On which will be typical household sockets from TV, radio, computer, hair dryer, iron ?
    I have standard 16A B fused circuits.

    Will a 20A AC1 contactor be sufficient ?
    A 4 pole contactor, one pair of contacts per circuit.

    What experience do you have on this subject.

    Thank you
    Regards
  • ADVERTISEMENT
  • #2 17232823
    brofran
    Level 41  
    mariusz-g wrote:
    I have standard 16A B protected circuits.
    Will a 20A AC1 contactor be sufficient ?
    .
    It will be OK.