I have a cable in the ground between the house and the garage and I suspect that it may be damaged and the electricity "leaks into the ground". What`s the easiest way to check this?
Czy wolisz polską wersję strony elektroda?
Nie, dziękuję Przekieruj mnie tammawerix123 wrote:Measurement of insulation resistance with a device intended for this purpose.
kloszi wrote:Better disconnect everything and check the meter to see if there is any consumption on the meter.
arturdip wrote:You can try to disconnect all loads in the garage and turn on the ammeter (a result above zero will confirm the thesis) if it is a single-phase installation. Of course, all precautions must be taken.
Krzysztof Kamienski wrote:CiekawyŚwiata wrote:From PE cable.from the wires of the cable and the ground?
He should (?) be your Land (Promised or Flat)
![]()
KaW wrote:A "mag meter" with a measuring voltage of 250V is used =(...)
Jacek Rutkowski wrote:(...) but the insulation resistance should be higher than 1MΩ. (...)
CiekawyŚwiata wrote:Insulation resistance measurements showed values from 3 to 10MΩ, so it looks like the cable is OK
KaW wrote:A "mag meter" with a measuring voltage of 250V is used and measures the insulation of each wire in relation to the others and to "earth".
KaW wrote:I had occupational health and safety in mind when taking measurements. Well, if the cable - its wires -
If we measure it, there will be an electric charge on the wires.
If we do not discharge this charge, a discharge will occur when we touch (e.g. with fingertips) the ends of the cable wires. If the megometer had a measurement voltage of 2500 V.