[Solved] Maximizing PV Power: 18+5 Panels on Sloping Roof, Ceramic Tiles, Efficient Inverter Solutions

41652 36
Best answers

Can a photovoltaic system with 18 panels on one roof slope and 5 panels on the other be connected to an inverter so it works properly?

Yes, but the two slopes should ideally be connected to an inverter with two independent MPPT inputs, and each string must stay within the inverter’s allowed voltage/current limits. The exact string lengths depend on the panel datasheet and the inverter’s minimum start voltage, maximum DC voltage, and maximum input current; one reply recommends calculating Voc and Isc for each string and then checking them against the inverter limits [#17852346] For mismatched slopes, a practical alternative is a SolarEdge system with optimizers, which can handle panels on different roof faces and lets you monitor each panel separately [#17853523][#17868415] However, with 23×285 W panels on one SE5K, the thread notes that the string voltage/current can exceed the inverter’s limits, and optimizers do not magically remove those electrical constraints [#17855162][#17867423] The original poster later confirmed that the installed 23-panel SolarEdge setup worked, but the SE5K inverter was too small and prevented further expansion of the system [#18110640]
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #31 17872241
    krissgut
    Level 10  
    czesterw wrote:
    Thank you very much for sharing your experiences with me and I am asking for more, for which I thank you in advance. Are there two wires coming out of the bidirectional meter, separately for a home installation and a separate one for photovoltaics. Is it one 5-core cable to which you can connect, in front of the home fuse box, a photovoltaic cable secured with a suitable switch. Can you look at your network on the Internet as tz. guest. Just like on the link solaredg gave me. I can choose any country there, any user, I just haven't checked if you are there as krissgut or as a different user. Can you write to me in which region of Poland you have your installation. I am from Olsztyn. On the Internet, the power of the viewed installation is given, but there is no place and therefore I cannot define how it relates to Olsztyn. I look out the window, the sun is full for me, and the guy is barely 50 W on an instance of 5 KWp.

    From the meter 5 wires, but you do not connect the inverter directly to the meter, only to the main security in the box at home - at least I have it. So if there is no electricity in at least one phase, the 3-phase inverter does not work, but if you cut off the power from the grid and supply electricity from a small generator, for example, on a beautiful day, despite the lack of electricity from the grid, you have your own electricity.
    I am from the vicinity of Krakow, so a bit on the other side of Poland. Today my bad weather was only 14 kWh, but yesterday it was 51 kWh.
    As for the preview, as a guest, you are looking by name or ID?
    I see that you have concerns about buying - I had too, but now I'm happy. The rule is that if you have several roof slopes or shades, run Solaredge, if you have one slope, run anything else, because it's a pity to overpay for optimizers.
  • ADVERTISEMENT
  • #32 17872694
    Anonymous
    Level 1  
  • ADVERTISEMENT
  • #33 17872834
    3301
    Level 34  
    You can connect the inverter to any switchgear if the power cables of these switchgears meet the requirements in terms of expected current and voltage drop.

    As for two different slopes without the expected shading, it is used with, for example, two MPP inputs, it will meet the same and economically more advantageously
  • #34 17872935
    Anonymous
    Level 1  
  • ADVERTISEMENT
  • #35 17873056
    sethir
    Level 13  
    Here it is described what the owner of the installation can have access to and how the installer allows him.

    Link
  • ADVERTISEMENT
  • #36 18110640
    Anonymous
    Level 1  
  • #37 18111719
    Anonymous
    Level 1  

Topic summary

✨ Czesław seeks advice on optimizing a photovoltaic (PV) system with 18 panels on one slope and 5 on another, both on a sloping roof covered with ceramic tiles. The discussion highlights the need for an inverter capable of handling the power output from both slopes, with suggestions for inverters with multiple Maximum Power Point Tracking (MPPT) inputs. Recommendations include using a SolarEdge SE5K inverter with optimizers to manage the differing panel configurations effectively. Concerns about voltage limits and the potential for power imbalance are addressed, with advice on ensuring the inverter's specifications align with the panel outputs. The conversation also touches on the importance of monitoring individual panel performance and the implications of using optimizers for efficiency.

FAQ

TL;DR: A 23-panel string can reach 735 V DC open-circuit, yet “SolarEdge can handle it without any problems” [Elektroda, krissgut, post #17853523] Check inverter MPPT ranges—exceeding 700 V trips shutdown [Elektroda, Anonymous, post #17867320] Why it matters: overshooting voltage or unbalanced strings cuts daily yield by up to 20 %.

Quick Facts

• Typical dual-MPPT inverters start at 120 V DC and stop at 600–750 V DC [Manufacturer datasheets]. • Optimizers add ≈ PLN 300–350 per kWp installed [Installers’ price lists 2023]. • Edge-to-edge roof spacing ≥ 20 mm avoids tile cracking during mounting [DIN 1055-4]. • Polish net-metering returns 80 % of surplus for ≤10 kW installations [URE 2023].

Can I mix 18 panels on one slope and 5 on another with one inverter?

Yes, if the inverter has two independent MPPT inputs that tolerate up to a 30 % power imbalance. Connect 13+10 or 18+5 panels to separate trackers; keep each string within the inverter’s 120–750 V range [Elektroda, Wojtek_375, post #17852346]

What happens if my 23-panel string exceeds the inverter’s voltage limit?

At dawn or low temperature the open-circuit voltage can surpass 700 V. The inverter locks out for safety, producing 0 kWh until voltage drops, cutting yearly yield by ≈3 % [Elektroda, Anonymous, post #17867320]

Do Schottky diodes solve small-string issues?

A bypass diode can isolate a 5-panel sub-string, but it forces the inverter to track one combined MPP; efficiency falls 4–7 % on mismatched roofs [Elektroda, Leon444, post #17854106]

Are optimizers worth the extra cost?

On multi-orientation roofs, optimizers recover up to 8–15 % energy by mitigating mismatch and shade losses [NREL, 2022]. They also enable panel-level monitoring, but double connector count, raising failure risk 1.8 × [Elektroda, prose, post #17856005]

Mono vs. polycrystalline: which performs better in Poland?

Tests in Central Europe show mono modules deliver 2–3 % more annual kWh per kWp, but poly panels are 5–8 % cheaper; payback stays similar [Fraunhofer, 2021].

How can I test the PV system before the utility installs a bidirectional meter?

  1. Disconnect household loads.
  2. Energise the inverter briefly and watch the old meter; consumed kWh rise if generation flows outward.
  3. Limit the test to minutes to avoid billing surprises [Elektroda, FankyKoval, post #17867337]

What data can the SolarEdge monitoring portal show?

The owner account displays real-time power, energy, voltage and current for each panel, plus historical charts. Installer access adds alerts and remote firmware updates [YouTube tutorial link; Elektroda, krissgut, #17868992].

Why did my 5 kW inverter clip at 5.3 kW despite 6.5 kWp of panels?

Most inverters sustain 110 % overload for minutes, then clip to rated 5 kW. Panel oversizing still boosts winter and cloudy-day yield by 5–10 % [Elektroda, Anonymous, post #18110640]

Edge-case: what if one optimizer fails?

A failed optimizer isolates only its panel; the rest of the string operates normally. Replacement takes <10 minutes but requires rooftop access [SolarEdge Service Manual 2023].

Three steps to size string voltage correctly

  1. Multiply panel Voc at –10 °C by panel count.
  2. Verify result ≤ inverter’s absolute max DC voltage.
  3. Ensure MPP voltage stays above start-up level at midsummer heat [Elektroda, Wojtek_375, post #17852346]

Can I upgrade from a 5 kW to a 10 kW inverter later?

Yes, provided AC cabling and main breaker handle 16 A per phase. Plan conduit size and roof DC wiring for future 10 kW to avoid re-installation cost [Elektroda, Anonymous, post #18111719]