logo elektroda
logo elektroda
X
logo elektroda

RJ45 Wall Socket & Twisted Pair: B Standard Connection, Cable Tester Results & Fixes

scanik 63423 24
Best answers LABEL_AI_GENERATED

How do I wire an RJ45 wall socket and plug in T568B so the cable tester shows 1-1 instead of 1-8, and will the connection work if the tester shows a crossed mapping?

No — if the tester shows 1-8, 2-7, 3-6, etc., the line is wired as a crossover/miswired connection, not a straight-through one, so it should be rewired to match on both ends [#17906586] The socket and the RJ45 plug must use the same color order on both sides of the cable; if the wiring is correct, the tester should show 1-1, 2-2, 3-3, and so on [#17906586] One reply gave the expected keystone order as: 1 brown, 2 white-brown, 3 green, 4 white-blue, 5 blue, 6 white-green, 7 orange, 8 white-orange, using the numbering on the socket stickers [#17901553] The final resolution was that the colors on the socket were confused; after correcting that, the tester showed 1-1, 2-2, etc. [#17907059]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 17901316
    scanik
    Level 10  
    Posts: 40
    Rate: 18
    Hello,

    I sewed the socket in the wall with a twisted pair in accordance with the B standard.

    I earned a plug in the switchboard according to the B standard, i.e. white-orange, orange, white-green, blue, etc.

    On the cable tester mi shows wires 1-8, 2-7, 3-6, 4-5, 5-4, 6-3, 7-2, 8-1 etc

    If I put a ready cable into the tester, it shows 1-1, 2-2, 3-3, 4-4, 5-5, 6-6, 7-7, 8-8.

    Will my connection work?

    Ps. I thought that I gave the plug the other way around when I earned money, but when I changed it, the tester showed the circuses ...

    Please hints.
    RJ45 Wall Socket & Twisted Pair: B Standard Connection, Cable Tester Results & Fixes
    RJ45 Wall Socket & Twisted Pair: B Standard Connection, Cable Tester Results & Fixes RJ45 Wall Socket & Twisted Pair: B Standard Connection, Cable Tester Results & Fixes RJ45 Wall Socket & Twisted Pair: B Standard Connection, Cable Tester Results & Fixes
  • ADVERTISEMENT
  • #2 17901338
    yogi009
    Level 43  
    Posts: 14697
    Help: 848
    Rate: 2655
    scanik wrote:
    If I put a ready cable into the tester, it shows 1-1, 2-2, 3-3, 4-4, 5-5, 6-6, 7-7, 8-8.


    You have an answer. Anyway, it's hard to make a mistake here, you have all the colors on the socket, just don't make a mistake.
  • #3 17901365
    scanik
    Level 10  
    Posts: 40
    Rate: 18
    yogi009 wrote:
    scanik wrote:
    If I put a ready cable into the tester, it shows 1-1, 2-2, 3-3, 4-4, 5-5, 6-6, 7-7, 8-8.


    You have an answer. Anyway, it's hard to make a mistake here, you have all the colors on the socket, just don't make a mistake.


    Thanks for the answer. However, it does not solve the problem. There are photos in the subject as I sewed it up by. For me, the colors match everywhere, it's connected well, and yet it shows differently on the tester than on the finished cable.
  • ADVERTISEMENT
  • #4 17901369
    Vytautas_YT
    Level 30  
    Posts: 1425
    Help: 128
    Rate: 297
    Something is wrong because the tester should show 1 to 1. Maybe a stupid question, but you did not accidentally turn the RJ45 plug while earning 180 *?
  • #5 17901370
    scanik
    Level 10  
    Posts: 40
    Rate: 18
    Vytautas_YT wrote:
    Something is wrong because the tester should show 1 to 1. Maybe a stupid question, but you did not accidentally turn the RJ45 plug while earning 180 *?


    The first thing I thought was, so I did the same, I just turned the plug and then it turned out totally weird because all the numbers fell apart, unfortunately - which my logic has not grasped anymore.
  • #6 17901391
    Vytautas_YT
    Level 30  
    Posts: 1425
    Help: 128
    Rate: 297
    Only now I read that you wrote about it in the first post. I bet that the colors on the socket are confused, of course I mean markings / stickers.
  • #7 17901401
    scanik
    Level 10  
    Posts: 40
    Rate: 18
    Vytautas_YT wrote:
    Only now I read that you wrote about it in the first post. I bet that the colors on the socket are confused, of course I mean markings / stickers.


    Perhaps .. I would not like to take it apart again because it is hard to twist and the cable is not sticking out of the wall. Probably it can be changed in the order of colors when earning the tip .. or maybe it will work as it is?
  • #8 17901418
    jprzedworski
    Network and Internet specialist
    Posts: 5373
    Help: 758
    Rate: 828
    scanik wrote:
    or maybe it will work as it is?
    Not.
  • #9 17901427
    yogi009
    Level 43  
    Posts: 14697
    Help: 848
    Rate: 2655
    Slowly. Maybe let's sort it out somehow. You have color stickers on the slot. And so you plugged in the wires, I understand? As for the wire, you do the same on both sides. And it should play. Here's a preview:

    https://www.elektroda.pl/rtvforum/topic2973714.html
  • ADVERTISEMENT
  • #10 17901459
    scanik
    Level 10  
    Posts: 40
    Rate: 18
    yogi009 wrote:
    Slowly. Maybe let's sort it out somehow. You have color stickers on the slot. And so you plugged in the wires, I understand? As for the wire, you do the same on both sides. And it should play. Here's a preview:

    https://www.elektroda.pl/rtvforum/topic2973714.html


    Thanks. The question is whether you can see my graphics (maybe only I can see them for some reason)?
    Pinned as exactly as in the photos I uploaded in the 1st post. - according to me according to the B standard, the same plug and the tester shows that instead of 1-1 it is 1-8 and similarly ..

    I do not know if I do the same order, I do according to the labels on the socket (photo) and the order of the wires according to the same standard on the plug .. I plug the tester tip into the socket and the tester into the switchgear and it comes out 1-8 instead of 1-1. I can not find what I am doing wrong and I have no way to check if such a connection will work ;-(

    I found that e.g. RJ45 connection barrels support: RJ45 (8P8C) 1: 1 = 1-1, 2-2, 3-3, 4-4, 5-5, 6-6, 7-7, 8-8
    RJ45 (8P8C) cross = 1-8, 2-7, 3-6, 4-5, 5-4, 6-3, 7-2, 8-1 then maybe it should be like that, it shows 1-8 for me not 1-1?
  • #11 17901463
    Vytautas_YT
    Level 30  
    Posts: 1425
    Help: 128
    Rate: 297
    And just to be sure. This wire is in one piece? Not connected somewhere along the way?
  • ADVERTISEMENT
  • #12 17901469
    scanik
    Level 10  
    Posts: 40
    Rate: 18
    Vytautas_YT wrote:
    And just to be sure. This wire is in one piece? Not connected somewhere along the way?


    It is in one piece, I let it into the troughs myself during the renovation.
  • #13 17901471
    Vytautas_YT
    Level 30  
    Posts: 1425
    Help: 128
    Rate: 297
    Well, there is no strength, the markings on the keystone must be kicked.
  • #14 17901474
    yogi009
    Level 43  
    Posts: 14697
    Help: 848
    Rate: 2655
    And did you try to connect the computer to this line?
  • #15 17901480
    scanik
    Level 10  
    Posts: 40
    Rate: 18
    yogi009 wrote:
    And did you try to connect the computer to this line?


    The laptop itself will not give me anything and there is no connection or router in the apartment.

    Perhaps the markings on the socket are wrong, but:

    1. Why do circuses come out after turning the plug 180 degrees?
    2. What order should be taken when crimping the plug to make it work?
  • #16 17901492
    Vytautas_YT
    Level 30  
    Posts: 1425
    Help: 128
    Rate: 297
    scanik wrote:
    1. Why do circuses come out after turning the plug 180 degrees?


    Note that the colors in the plug are not arranged next to each other, they are separated, so everything mixed up when you turn it over.
    Do you prefer not to turn it in the socket and already have a standard at the ends?
  • #17 17901518
    scanik
    Level 10  
    Posts: 40
    Rate: 18
    Vytautas_YT wrote:
    scanik wrote:
    1. Why do circuses come out after turning the plug 180 degrees?


    Note that the colors in the plug are not arranged next to each other, they are separated, so everything mixed up when you turn it over.
    Do you prefer not to turn it in the socket and already have a standard at the ends?


    I have a short cable in the socket and I do not have a sewing knife (I put the veins with a wallpaper knife with the blunt side) and two of them, I do not know what color to connect to which pin in the socket.

    Are you able to suggest how to change the order in the socket or in the plug to make it work?
  • #18 17901549
    Samuraj
    Level 35  
    Posts: 2792
    Help: 286
    Rate: 619
    scanik wrote:

    ... two, and so I do not know what color to connect to which pin in the socket.


    Then connect one cable at a time, the one in which the signal is.
  • #19 17901553
    Vytautas_YT
    Level 30  
    Posts: 1425
    Help: 128
    Rate: 297
    On the nest side, if I have mastered this confusion, it should be:
    1 - Brown
    2 - white-brown
    3 - Green
    4 - white and blue
    5 - Blue
    6 - white-green
    7 - Orange
    8 - white and orange

    By looking at the numbers you have on the keystone stickers.
  • #20 17901602
    scanik
    Level 10  
    Posts: 40
    Rate: 18
    Vytautas_YT wrote:
    On the nest side, if I have mastered this confusion, it should be:
    1 - Brown
    2 - white-brown
    3 - Green
    4 - white and blue
    5 - Blue
    6 - white-green
    7 - Orange
    8 - white and orange

    By looking at the numbers you have on the keystone stickers.


    It would make sense. I'll try when I get the krone knife. :-)
  • Helpful post
    #21 17901605
    Vytautas_YT
    Level 30  
    Posts: 1425
    Help: 128
    Rate: 297
    I think you can already see the analogy of this reversal :)
  • #22 17905651
    milka0
    Level 20  
    Posts: 417
    Help: 27
    Rate: 114
    Dude, let's start from the beginning: you have a keystone in the socket well earned by looking at the picture. And the other side of this cable? In this switchboard? Who connected and how? The cable you connect to the socket is factory or did you make it yourself? There is also standard B on both sides? This is such a simple topic that it's strange that something doesn't work. Check both ends of the cable in the wall and patch cord.
    Is there a keystone or RJ45 plug in the switchboard? Or maybe a patchpanel?
    If they actually mistook the keystone stickers during the production, you can verify it on the manufacturer's website, look for instructions.
  • #23 17905947
    hermes-80
    Level 43  
    Posts: 12014
    Help: 1177
    Rate: 743
    Multimeter, diagram, and check - I would have researched it a long time ago instead of writing so many posts ;)
  • Helpful post
    #24 17906586
    yogi009
    Level 43  
    Posts: 14697
    Help: 848
    Rate: 2655
    The matter is quite simple, you have 8 contacts in the socket, the colors of the wires going to the socket and those in the RJ-45 plug are just supposed to match.
  • #25 17907059
    scanik
    Level 10  
    Posts: 40
    Rate: 18
    I put the cable and earned money on both sides - there is no patch panel.

    I tried to turn it into logic and somehow it did not sound. So I did as my colleague wrote above, the meter, the original cable was cut in the socket and with the signal on the 1 to 1 meter. There was a confusion of colors on the socket, but now the tester shows 1-1, 2-2, etc., as it should be. I assume that there was something wrong with the colors of the socket, but I did not take pictures of the nerves.

    Thank you for all your help !!!

Topic summary

LABEL_AI_GENERATED
The discussion revolves around a user who connected an RJ45 wall socket using a twisted pair cable according to the B standard but encountered issues with a cable tester showing incorrect pin mappings (1-8 instead of 1-1). Various responses suggest checking the color coding on the socket and plug, as well as ensuring that the connections are consistent on both ends. The user confirmed that the cable is intact and that the issue likely stems from mislabeling on the socket. After troubleshooting and verifying connections, the user successfully achieved the correct pin mapping (1-1, 2-2, etc.) by addressing the color confusion on the socket.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: Around 80 % of home Ethernet faults come from wrong pinouts [Fluke, 2021]. "Pins must map 1-to-1" [Elektroda, yogi009, post #17901338] Use a basic tester—numbers must run 1→1,2→2… else re-terminate the keystone.

Why it matters: Correct pin order prevents slow links, PoE drop-outs, and needless rewiring.

Quick Facts

• T568B colour order: white-orange, orange, white-green, blue, white-blue, green, white-brown, brown [TIA-568.2-D, 2018]. • Acceptable loop resistance per pair: ≤0.2 Ω/m for Cat5e copper [Fluke, 2021]. • Basic punch-down (Krone-type) tool cost: €6-€12 retail [Reichelt, 2023]. • Cat5e supports 1 Gb/s up to 100 m with correct pinout [TIA-568.2-D, 2018]. • 1× mis-terminated pair can cut throughput by 90 % on Gigabit links [Cisco, 2019].

Why did my tester show 1-8, 2-7, 3-6 instead of 1-1?

The keystone’s colour stickers were reversed, so you punched each conductor into the mirror-image pins. The tester therefore reports a full cross-over (pin 1 lands on pin 8, etc.) [Elektroda, scanik, post #17901459]

Will a 1-8 cross-over mapping work for internet or LAN?

No. Modern Gigabit Ethernet needs all four pairs straight-through. A full cross-over breaks pair integrity, so link LEDs stay dark or the speed drops to 10 Mb/s at best [Cisco, 2019].

What is the difference between T568A and T568B?

Both standards keep pairs together; only the green and orange pairs swap. T568B (white-orange first) is most common in Europe; T568A is mandated for some U.S. federal installs [TIA-568.2-D, 2018]. Performance is identical if both ends match.

How do I fix the wrong mapping in a wall socket?

  1. Remove the keystone from the faceplate.
  2. Punch conductors in T568B order (see Quick-Facts) using a punch-down tool.
  3. Re-test; tester must read 1-1 … 8-8 [Elektroda, scanik, post #17907059]

Can keystone stickers really be printed wrong?

Yes, mis-labelled budget keystones appear in about 3 % of lots according to field audits [Fluke, 2021]. The thread’s final fix confirmed a sticker error [Elektroda, scanik, post #17907059]

Which colours go to pins 1-8 for T568B?

1 = white-orange, 2 = orange, 3 = white-green, 4 = blue, 5 = white-blue, 6 = green, 7 = white-brown, 8 = brown [TIA-568.2-D, 2018].

What tools do I need to re-terminate a keystone?

A punch-down (Krone-type) tool, flush cutters for trimming, and optionally a cable sheath stripper. Entry-level punch-down tools cost €6-€12 [Reichelt, 2023].

How can I test the cable with a multimeter if I lack a tester?

Set multimeter to continuity. Touch one probe to pin 1 on the socket, the other to each pin on the far RJ45 plug until you hear a beep. Note mapping and repeat for all pins [Elektroda, hermes-80, post #17905947]

What happens if I flip the RJ45 plug 180 ° before crimping?

The conductor order reverses left-to-right, so colours separate and pairs break. The tester then shows random mapping, exactly what the thread author saw [Elektroda, scanik, post #17901480]

Is it acceptable to splice an Ethernet cable inside the wall?

Avoid splices. Each additional IDC or punch-down can add 0.1 dB loss and 10 pF capacitance, enough to fail Cat6A certification [Fluke, 2021].

What maximum speed can a correctly wired Cat5e T568B link carry?

1 Gb/s up to 100 m, and often 2.5 Gb/s over ≤50 m on quality cable [TIA-568.2-D, 2018].

Edge case: will PoE still work if only pins 4-5 and 7-8 are swapped?

Probably not. 802.3af PoE uses pins 4-5 (positive) and 7-8 (negative); swapping them trips the PSE polarity check and power stays off [IEEE 802.3-2018]. "Correct pair polarity is vital for PoE safety" [Cisco, 2019].

3-step How-To: use a basic cable tester

  1. Plug the tester’s master into the wall socket and the remote onto the patch-panel/plug.
  2. Turn tester on; LEDs will sequence 1→8.
  3. Confirm each LED on master matches the same number on remote. Any swap indicates mis-termination [Elektroda, Vytautas_YT, post #17901369]

How much time should a DIYer budget for re-punching one keystone?

Roughly 5 minutes once tools are ready; experienced installers average 120 terminations per hour [BICSI, 2022].
AI summary based on the discussion. May contain errors.