[Solved] Seeking Table for Connection Power and Pre-Meter Protection Values - PGE Zamość Branch

pawlo_1 35418 4
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 18459902
    pawlo_1
    Level 17  
    Hello. Someone has a table specifying the connection power and the value of the pre-meter protection that corresponds to it. I mean mainly PGE Zamość Branch.
  • ADVERTISEMENT
  • #2 18460173
    retrofood
    VIP Meritorious for electroda.pl
    It should be on the PGE website.
  • ADVERTISEMENT
  • #3 18463196
    pawlo_1
    Level 17  
    Unfortunatelly it is not available.
  • ADVERTISEMENT
  • Helpful post
    #4 18464133
    stonefree
    Level 27  
    1 Phase:
    1kW - 6A
    2kW-10A
    3kW-16A
    4kW-20A
    5kW-25A

    3 Phase
    1-4kW-6A
    5-6kW-10A
    7-10kW-16A
    11-13kW-20A
    14-16kW-25A
    17-21kW-32A
    22-26kW-40A
    27-32kW-50A
    33-40kW-63A
    41-52kW-80A
    53-64kW-100A
    65-81kW-125A
    82-103kW-160A
    etc, calculated from the formula.
  • #5 18465131
    pawlo_1
    Level 17  
    Solved. Thank you.