logo elektroda
logo elektroda
X
logo elektroda
Dostępna jest polska wersja

Czy wolisz polską wersję strony elektroda?

Nie, dziękuję Przekieruj mnie tam

How to modify the hysteresis and temperature jump on the Avatto ZWT 198 thermostat

KarolKostanek 3018 20
Best answers

How can I change the hysteresis and temperature step from 0.5°C to 0.1°C on an Avatto ZWT 198 Wi‑Fi thermostat while keeping it in Tuya?

There is no simple documented way to flash or directly modify the WXU Wi‑Fi module, so the best technical approach is to sniff the UART between the WXU and the MCU and check whether the thermostat exposes a Tuya datapoint such as `deadzone_temperature` that can be set to 0.1; TuyaMCU uses integer datapoints, so 0.1 only works if the value is scaled in the protocol [#21327693][#21328340] A similar ZWT198/ZWT100-BH Zigbee device is documented with a "Deadzone temperature" setting adjustable from 0.1 to 10, which suggests the parameter may exist in some form, but the Wi‑Fi version is different and not currently flashable [#21327926][#21327693] One reply notes that the app already offers a half-degree setting after pairing, but nobody confirmed a real 0.1°C option on the Wi‑Fi unit [#21327975][#21328340] If you only need tighter control, a workaround is to leave the thermostat unchanged and use Tuya scenes/automation to create your own hysteresis, for example switch to 22°C when temperature drops below 20.8°C and back to 20°C above 21.2°C [#21872306]
Summary generated by AI based on the discussion content.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • Requesting step-by-step firmware modification instructions

    #1 21327488
    KarolKostanek
    Level 6  
    Posts: 8
    Warm welcome.

    I am looking for a willing person or very (very) simple instructions on how to modify the software in the avatto zwt 198 thermostat, specifically two parameters:
    Hysteresis 0.5 to 0.1
    The jump of the set temperature from 0.5 to 0.1.

    How to modify the hysteresis and temperature jump on the Avatto ZWT 198 thermostat .

    PCB designation 20230822 R9-433 V1.2

    Ps. This is my first topic if I have made any mistakes I am very sorry and ready for criticism.

    Greetings.
    AI: Do you already have any tools or software that you are trying to use to modify the thermostat software? .
    No
    AI: What is your experience with software modification or electronics? Do you need detailed step-by-step instructions? .
    Detailed step-by-step instructions.
  • ADVERTISEMENT
  • #2 21327643
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14701
    Help: 656
    Rate: 12747
    This module is signed WXU, I see correctly, not CBU?

    Is this a thermostat on WiFi or Zigbee? Hmm the name suggests Zigbee, that's what the network suggests too.

    What gateway are you connecting it to?
    Helpful post? Buy me a coffee.
  • ADVERTISEMENT
  • #3 21327652
    KarolKostanek
    Level 6  
    Posts: 8
    It connects via Wifi to the Smart Life app.
    And the module is WXU
  • #4 21327666
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14701
    Help: 656
    Rate: 12747
    I guess it's not possible, does this by any chance additionally use a Zigbee gateway from Tuya that mediates the communication between the module and WiFi?
    Helpful post? Buy me a coffee.
  • #5 21327676
    KarolKostanek
    Level 6  
    Posts: 8
    No. It connects directly to the wifi. There are versions on zigbee but mine is the wifi version
  • TuyaMCU UART likely carries hysteresis setting

    #6 21327693
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14701
    Help: 656
    Rate: 12747
    That's interesting, because on the internet this model appears as zigbee:
    How to modify the hysteresis and temperature jump on the Avatto ZWT 198 thermostat .
    But Tuya's documentation about the WXU, however, says it's WiFi:
    Quote:

    WXU Module Datasheet
    Last Updated on : 2024-09-02 12:20:35download

    WXU is a low-power embedded Wi-Fi and Bluetooth combo module that Tuya has developed. Embedded with the Wi-Fi network protocol stack and rich library functions, it consists of a highly integrated RF chip (T103C-HL).
    .

    And this is the change you want to make while remaining with the Tuya application?

    I would guess that, if anything, the hysteresis is sent here from the WXU module to the MCU via the TuyaMCU, just a question if it is represented at all so that you can change it by as much as you want.... you would need to connect the UART and preview the packet.... TuyaMCU Analyzer - UART packet decoder for Tuya devices - dpID detector the worse thing is that the WXU is not flashable at the moment....
    Helpful post? Buy me a coffee.
  • #7 21327846
    KarolKostanek
    Level 6  
    Posts: 8
    I'm afraid it's beyond my abilities though. I have 1 unit free and would be more than happy to make it available to someone for testing, and if it works out, 4 units to convert.
  • ADVERTISEMENT
  • #9 21327945
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14701
    Help: 656
    Rate: 12747
    @sentimental I wanted to go in that direction too, but it looks like the subject author actually has a version on WiFi and not Zigbee.... Additionally, would the topic author want to use this device via Zigbee2MQTT? Would it be preferred that it stays in Tuya....

    but overall fact, the dpID in the WiFi version would probably be similar
    Helpful post? Buy me a coffee.
  • #11 21327976
    KarolKostanek
    Level 6  
    Posts: 8
    Preferably in the tuya.
    But if there is no alternative to leaving the tuya then I'll still sign up as in their current form they are slightly useless.
  • ADVERTISEMENT
  • #12 21328013
    Sentymentalny
    Level 16  
    Posts: 127
    Help: 11
    Rate: 26
    The sources of information given earlier serve to understand how the device in question functions.
    Why are they "slightly useless in their current form"?
    Why change to a value of less than 0.5?
  • #13 21328020
    KarolKostanek
    Level 6  
    Posts: 8
    This is the case for me, and on the smallest setting, i.e. 0.5, it works in such a way that if I set it to 20.5, the heating is switched on at 20 and off at 21, and as this controls the underfloor heating, it goes up to 19.5 and after switching it off it goes up to 21.5, which results in a 2 degree difference.
  • #14 21328085
    Sentymentalny
    Level 16  
    Posts: 127
    Help: 11
    Rate: 26
    Underfloor heating and its regulation of each heating zone is a subject of a river. Changing to a hysteresis value of less than 0.5 °C will not solve your dilemma.
  • 0.5 hysteresis means a wider temperature band

    #15 21328103
    KarolKostanek
    Level 6  
    Posts: 8
    I had previously made Arduino thermostats with a hysteresis of 0.1 and they kept the temperature nicely. The problem was that I lost a copy of the program and they were set to specific values and I couldn't expand them with a menu and a weekly programmer. This is why I decided to use such thermostats, but it was my oversight that 0.5 does not mean that the temperature will be +-0.25 where it would already be acceptable.
  • Questioning 0.1 °C hysteresis with 1 °C accuracy

    #16 21328174
    Sentymentalny
    Level 16  
    Posts: 127
    Help: 11
    Rate: 26
    If you can, it is best to return these devices.
    The Avatto website does not even list this version so that you can consult the manual.
    However, there is a similar version, the 100, for which they state that the accuracy of the measurement is 1 °C.
    So how do you want a hysteresis of 0.1 when the measurement accuracy is 1 deg C?
    Besides, it is important where the sensor itself is mounted in this thermostat, etc.
    Can your model also work in Bluetooth mode, like the one shown in the Zigbee video?

    Out of curiosity, what temperature sensor did you have in your Arduino version?
  • BT not detected; device advertises over Wi‑Fi

    #17 21328213
    KarolKostanek
    Level 6  
    Posts: 8
    Well, the option of giving it away is out of the question, as it took me too long to get round to fitting it.
    The sensor in the thermostat itself is exposed slightly behind the housing from the bottom of the installed device. The sensor itself reacts very sensitively to temperature changes, but between devices next to each other each shows a different temperature, which can be corrected in the options, so I understand it more by the measurement error of 1 deg C from the real temperature.
    With BT, I am combining to see if it is detected.

    As for the sensors on the Arduino it's ds18b20 in the case to92.

    Added after 7 [minutes]: .

    As for BT the device after BT is not detected.
    Over wifi it announces itself like this:
    How to modify the hysteresis and temperature jump on the Avatto ZWT 198 thermostat .
  • Question about swapping deadzone_temperature in packets

    #18 21328285
    Sentymentalny
    Level 16  
    Posts: 127
    Help: 11
    Rate: 26
    Although I am sceptical about the end result of setting the hysteresis to 0.1, the packet eavesdropping itself can be tried using @p.kaczmarek2's tutorials. Maybe @p.kaczmarek2 can give you a hint as to whether this makes sense, if you send the tapped packet with the "deadzone_temperature" value swapped e.g. from 0.5 to 0.1 will this work, or will there be an error or a restoration of the value stored in the Tuya application when the device communicates cyclically with Tuya.
  • Tuya integer encoding may limit deadzone changes

    #19 21328340
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14701
    Help: 656
    Rate: 12747
    If you plug in between the WiFi module and the WXU then you can do as @sentimental wrote , but it's a lot of fun, I was secretly hoping that either this is a Zigbee version though and that it will post with Zigbee2MQTT, or that this is a BK7231 version and you can program the WiFi module your way. Overall this is the first time I've seen a WXU module and it's not a BK7231 unfortunately....


    Sentymentalny wrote:
    package with changed "deadzone_temperature" value e.g. from 0.5 to 0.1 will this work
    .
    the question is also whether this communication supports chopping into 0.1 at all, there only integer values are sent, and if a variable is to support e.g. a step of 0.1 then Tuya sends e.g. 30 degrees as 300, and e.g. 12.5 degrees as 125. Worse, if Tuya assumes that the step is 0.5, it sometimes then sends the value divided by two - so 10 sends as 20, 10.5 as 21, etc.... you'd have to know how it is internally. Intercept the packet and see.

    Certainly it's unlikely that typical floating point numbers are sent there, float, TuyaMCU doesn't even support that. Only bool, enum, value (integer), bitmap (flags), raw (string of bytes) values are there.
    Helpful post? Buy me a coffee.
  • Increase sensor thermal mass to reduce hysteresis

    #20 21328522
    pikarel
    Level 39  
    Posts: 5019
    Help: 409
    Rate: 1838
    Increase the thermal mass to be measured; each measuring element (diode junction, thermistor, saloon circuit) should be placed at least in a tube a few centimetres long, filled with a thermally conductive material (e.g. silicone paste, used for heat sinks), not in the air and still covered by a plastic casing.

    A sensor placed on the heat source will indicate its temperature immediately.
    You are only measuring the effect of its heating, so the inertia of the measurement will increase as the measurement hysteresis increases, but also as the distance of this sensor from the radiator increases.

    Also; are you doing nuclear research at home that you require such temperature constancy?
    :) .
  • #21 21872306
    radko75
    Level 2  
    Posts: 3
    The scene setting bypasses this hysteresis:
    if temp < 20.8 → set 22°C
    if temp > 21,2 → set 20°C
    and we have 0.4 hysteresis

Topic summary

✨ The discussion concerns modifying the Avatto ZWT198 Wi‑Fi thermostat to change hysteresis from 0.5°C to 0.1°C and reduce the temperature step size. The device uses a WXU module and connects directly to the Smart Life/Tuya app over Wi‑Fi, not Zigbee. Participants note that the WXU module is currently not easily flashable, so the most realistic approach is packet sniffing on the UART/TuyaMCU communication path to inspect whether the hysteresis or deadzone parameter is exposed as a configurable datapoint. References are made to Zigbee2MQTT documentation and TuyaMCU Analyzer as examples of how similar thermostats expose a “deadzone_temperature” setting, but it remains unclear whether the Wi‑Fi version supports the same control. The author explains that the 0.5°C hysteresis causes large temperature swings in underfloor heating, and mentions prior Arduino thermostats with 0.1°C hysteresis and DS18B20 sensors. Later comments suggest that the thermostat’s measurement accuracy and sensor placement may limit the practical benefit of reducing hysteresis, and that scene-based automation can bypass the built-in hysteresis by switching setpoints based on measured temperature thresholds.
Summary generated by AI based on the discussion content.

FAQ

TL;DR: Deadzone can typically span 0.1–10 °C, and "Deadzone temperature (numeric) ... changed from 0.1 to 10" exists on Zigbee; Wi‑Fi needs UART workarounds. This FAQ helps Avatto ZWT‑198 Wi‑Fi (WXU) owners get 0.1 °C hysteresis and finer 0.1 °C steps. [Elektroda, Sentymentalny, post #21327926]

Why it matters: You want steadier floor‑heating comfort with less overshoot and tighter temperature control.

Quick Facts

Can I change hysteresis from 0.5 b0C to 0.1 b0C on the Avatto ZWT 198 Wi Fi?

Not directly in the Tuya app on the Wi‑Fi version. The WXU module exchanges parameters with the MCU via TuyaMCU. You must inspect the UART stream and find a dpID that represents hysteresis/deadzone. If firmware exposes it, you can write a new scaled value. The WXU module itself is not flashable right now. [Elektroda, p.kaczmarek2, post #21327693]

How do I sniff and try to change the deadzone on the Wi Fi version?

Use a UART sniffer approach.
  1. Open the device and tap the UART between WXU and the MCU (GND, TX, RX).
  2. Connect a USB‑TTL adapter and run the TuyaMCU Analyzer to decode dpIDs.
  3. Change setpoint in the app; identify a numeric dpID that matches deadzone, then test writing a new scaled integer (e.g., 0.1 as 1 if deci‑degrees). [Elektroda, p.kaczmarek2, post #21327693]

What data format does TuyaMCU use for temperature values and steps?

TuyaMCU does not send floats. It uses integer "value" types with scaling, such as 12.5 °C encoded as 125. Some firmwares enforcing 0.5 °C steps double values, so 10.0 becomes 20 and 10.5 becomes 21. "Only bool, enum, value (integer), bitmap (flags), raw (string of bytes) values are there." [Elektroda, p.kaczmarek2, post #21328340]

Why wont a 0.1 b0C hysteresis fix floor heating overshoot?

Underfloor heating has high thermal inertia. Reducing hysteresis below 0.5 °C will not resolve the observed comfort swing alone. You will need better sensing placement, thermal damping, or control logic changes to tame overshoot. Adjusting hysteresis helps little without addressing inertia. [Elektroda, Sentymentalny, post #21328085]

How can I reduce overshoot without firmware changes?

Improve sensing and damping. Move the sensor away from heat sources and add thermal mass to the probe housing. Use a tube or enclosure with thermally conductive material to slow rapid spikes. "Increase the thermal mass to be measured." This stabilizes readings and reduces relay chatter and overshoot. [Elektroda, pikarel, post #21328522]

Does the Zigbee version let me set a 0.1 b0C deadzone directly?

Yes, the Zigbee model exposes a “Deadzone temperature (numeric)” with a typical 0.1–10 range. You can adjust that via a Zigbee coordinator like Zigbee2MQTT. Wi‑Fi users can look for an analogous dpID over TuyaMCU, but it is not guaranteed. [Elektroda, Sentymentalny, post #21327926]

Can the WXU Wi Fi module be flashed with OpenBeken or Tasmota?

No. The WXU is not flashable at the moment, and it is not the BK7231 platform used by many Tuya‑Wi‑Fi devices. To modify behavior, intercept TuyaMCU UART or migrate to a Zigbee model that exposes deadzone. [Elektroda, p.kaczmarek2, post #21327693]

My Tuya app only lets 0.5 b0C setpoint steps. Can I change it to 0.1 b0C?

The app enforces the step defined by the device dp metadata. TuyaMCU encodes values as integers, sometimes with 0.5 °C steps by doubling. If firmware supports 0.1 °C, the encoded scale will reflect that. Without such support, the app will not offer 0.1 steps. [Elektroda, p.kaczmarek2, post #21328340]

Do I need a Zigbee gateway if I switch to the Zigbee version?

Yes. Use a Zigbee coordinator (e.g., Zigbee2MQTT) that supports the device. The Zigbee variant exposes the "Deadzone temperature" control there. This route avoids Wi‑Fi UART hacking entirely. [Elektroda, Sentymentalny, post #21327926]

My units read different temperatures. Can I calibrate them?

Yes. Some Avatto variants specify around 1 °C measurement accuracy, so small differences are expected. Use the built‑in offset to align displayed temperatures across rooms. Place sensors consistently and avoid drafts or radiant hotspots for better repeatability. [Elektroda, Sentymentalny, post #21328174]

Will the Tuya cloud overwrite my locally changed deadzone after I set it?

It can. When the device syncs with Tuya, cloud‑stored parameters may restore the default or last app‑set value. Plan for this by disabling cloud writes or moving to a local Zigbee setup where you control parameters end‑to‑end. [Elektroda, Sentymentalny, post #21328285]

Is Bluetooth available on this model for configuration?

The WXU module supports Bluetooth on paper, but one owner reported no BT detection on this thermostat. Treat BLE as disabled by firmware for this model. Use Wi‑Fi/Smart Life or explore Zigbee if you need richer local control. [Elektroda, KarolKostanek, post #21328213]

Why does my 20.5 b0C setpoint cause a 19.5 21.5 b0C swing?

The controller switches on at 20 and off at 21 with a 0.5 °C deadzone. Floor heating inertia continues cooling or warming after switching, producing about a 2 °C band around the setpoint. Reducing inertia or changing control logic is required. [Elektroda, KarolKostanek, post #21328020]

Whats an example of Tuya integer scaling when firmware enforces 0.5 b0C steps?

Some firmwares double values to represent 0.5 °C resolution. Ten degrees encodes as 20. Ten‑point‑five degrees encodes as 21. For 0.1 °C resolution, values may encode as deci‑degrees (e.g., 12.5 °C → 125). Decode packets to confirm the scheme. [Elektroda, p.kaczmarek2, post #21328340]

Is my ZWT 198 a Wi Fi or Zigbee device?

There are both variants. The unit discussed connects directly via Wi‑Fi to the Tuya Smart Life app. If your device pairs to a Zigbee hub, it is the Zigbee model; otherwise, it is Wi‑Fi. [Elektroda, KarolKostanek, post #21327652]
Summary generated by AI based on the discussion content.