    Hello :)

    I connect such a flow water heater:
    BIAWAR Oskar OP-5

    I have 3 cable outputs on it:

    PE
    N
    L.

    now at home I have a 2-wire installation (old)
    How do I connect the plug. PE I know it is a protective one, and this one will be connected to the pin in the plug, now N or L is to be shorted with the phase in the socket, because I have "0" in the socket, of course, and the bolt together.

    Sorry, but probably a totally trivial question, but I don't want to fap.

    greetings :)
    Lateralus

    Moderated By skryn:

    I moved from home appliances.

  • ADVERTISEMENT
  • #2 3936503
    VIRUS32
    Level 26  
    Hello. N and PE wire in the socket. Bridge from PE to N, phase separate. Regards.
  • ADVERTISEMENT
  • #3 3936519
    jam_es
    Level 24  
    Hello

    In this case, if you do not have a separate protective conductor, connect as follows:
    - "phase" -> L;
    - "zero" -> N;
    - bridge between N and PE.
    Remember that in this case the connection must be permanent in order not to accidentally change "phase" to "zero", because the full mains voltage will appear on the housing of the device.
    Write down whether the heater has a connection in the form of a plug on the cable or a terminal strip inside.

    greetings
  • #4 3936580
    Lateralus
    Level 10  
    Terminal strip, inside the heater, and lead out the cable and plug. And I just noticed that my electricians did not connect the pin to the zero (they did not make a bridge) specs. :(