How do I stop a Buderus Logano G124 gas boiler from locking out every few days with burner fault 1, even after replacing the ionization electrode and cleaning the ignition nozzle?

This is usually not a software problem; the thread points first to flame-detection and burner-cleanliness issues rather than controller programming. Clean the whole burner and especially the ignition-burner nozzle and ionization electrode, and make sure the candle flame reaches clearly past the ionization electrode; one user fixed the recurring fault only after cleaning the nozzle properly with a thin wire and slightly increasing the flame [#20013815][#18992185] Check the ignition electrode position too, because a misaligned spark or wrong hole orientation can make ignition intermittent even when everything looks normal through the sight glass [#5032250][#8852041] Also verify grounding/earth and polarity, since a loose or missing ground electrode or bad earth connection caused the same burner fault for others [#11454030][#20207806] If cleaning, adjustment, and grounding checks do not solve it, then the burner controller/automation is the last thing to replace [#20013815]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • ADVERTISEMENT
  • #32 8856587
    autoas
    Level 42  
    Posts: 9190
    Help: 571
    Rate: 3924
    But they do not sell parts, only parts with the service :)
  • Interrupted ground caused intermittent burner ignition failure

    #33 11454030
    miś55
    Level 1  
    Posts: 1
    Rate: 4
    Hello, I will share my case. The sparkler worked, the flame lit, the spark switch turned off for a second, and then it started again. After a few seconds, the flame went out and the BLA BURNER 1 message appeared. "I fought" for half a day, cleaning, exchanging and nothing. The last element I checked (thanks to this forum) was the lack of land and BINGO. It turned out that during the exchange of the circulation pump, the neutral wires and ground closed. The differential was activated, only that everything was powered by the inverter and the connection to the ground had to be interrupted.
  • #34 12172415
    pedros75
    Level 13  
    Posts: 142
    Rate: 11
    Hello gentlemen!
    I am forced to connect to the topic. For several days, the message BURNER 1 BLA appears to me. After the reset, it starts (but not for the first time) and it comes back some time. Earlier in the topic was discussed the issue of purging elements, could any of your colleagues indicate any instruction or drawing how to do it and what parts (as for a layman in this topic indicated picture method or from Polish to "our"). I would simply like to eliminate this element from the possible calling of a service technician. I would like to add that the problem appeared on the weekend of the night from Saturday to Sunday, then the stove went perfectly to the night on Sunday, and now after the return from work again this message appeared.
  • #35 12847356
    Tadeusz Pończochin
    Level 10  
    Posts: 8
    Rate: 27
    there is also a nozzle on the start-up burner with holes on the perimeter, but not on the whole.
    during the cleaning I did not remember how it was at the beginning
    help me how to set them
    maybe some drawing
  • #36 13216152
    gipsatura
    Level 10  
    Posts: 74
    Rate: 9
    Hello.
    Others join and I will ask. I have read the topic, in my stove, as in others, "bur bla," so I stripped it and cleaned it and the whole day is working properly. At the bottom under the burners there were a lot of sintered crumbs and an element that appears in the picture, and now a question what is it and how it found itself in this place. I will add that the servant cleaned the burners 2-3 years ago. The stove is already 13 years old and has been working so far without any problems. Thanks in advance for your suggestions.
    Attachments:
    • Buderus Logano G124 Ignition: Switching Off Every Few Days - Replaced Ionization Electrode & More DSC08635.JPG (3.15 MB) You must be logged in to download this attachment.
  • ADVERTISEMENT
  • #37 13219390
    _uki_
    Level 11  
    Posts: 14
    Help: 1
    Rate: 13
    on my eye is an element that supports / forms an ignition flame. Either you press the ignition burner and it will work or the ignition burner will be replaced
  • #38 15195904
    luk99elektroda
    Level 2  
    Posts: 3
    Rate: 6
    I have a problem with the morning ignition of the Buderus gas furnace (G134 + Logomatic 2107).
    Practically since it got colder, the palinic does not want to start after the break at night. It lasts almost two months. I note that there is no problem during the day.
    The scenario is like this: the hour comes to turn on the stove to heat up the water (5.30), the spark turns on (you can see it) and after 5 seconds a burner error occurs, after pressing the burner reset the stove is starting normally and is working normally until the evening . On the second day it is the same and it lasts almost two months. Until autumn, there was no trouble, the stove has been over 10 years and it always worked great. I checked grounding, polarity, cleaned electrodes, etc. The only idea that I have is a negative effect of low temperature on the process of starting the burner. In the morning the boiler room is rather chilly and then it does not fire. This confirms yesterday's case, when I took off the furnace cover around noon, I vented the boiler room with cool air and the stove did not fire as in the morning. What to do ? was buying a new Satronic burner machine?
  • #39 15259295
    luk99elektroda
    Level 2  
    Posts: 3
    Rate: 6
    It ended with replacement of the burner's automaton with a new one. So far it has been working for a week.
  • ADVERTISEMENT
  • #40 18193545
    Piorun2002
    Level 15  
    Posts: 269
    Rate: 25
    Hello,
    > I have a problem with the morning ignition of the Buderus gas oven (G134 + Logomatic 2107).
    > Practically, since it got colder the stake doesn't want to start after the night break

    I have exactly the same problem, I cleaned the electrodes but nothing improved.
    My furnace is 18 years old - is it worth buying Satronic TFI 812.2 right away, or are there any other elements that I should check first (gas is ok, nothing changed in the electrical system)
  • #41 18193599
    autoas
    Level 42  
    Posts: 9190
    Help: 571
    Rate: 3924
    And the spark starts, the valve opens the gas .... can you hear it?
  • #42 18193614
    Piorun2002
    Level 15  
    Posts: 269
    Rate: 25
    The spark is, the first time when attempting to start Satronic as if it does not detect ionization and there is a BLAD PAL.
    When I wait 30 sec I can press the error reset button on Satronic and the oven tries to restart - 90% succeeds, sometimes the procedure must be repeated.
    So generally the stove works, you just need to 'help' it start - which is a bit tiring.
  • #43 18193622
    autoas
    Level 42  
    Posts: 9190
    Help: 571
    Rate: 3924
    So it doesn't turn on the gas even?
  • #44 18193643
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    The boiler needs cleaning. Nothing more.
    Ew. It may have a damaged earth electrode. A common malfunction in these models.
  • #45 18193729
    Piorun2002
    Level 15  
    Posts: 269
    Rate: 25
    > So it doesn't turn on the gas even?
    Turns on but the second time only (the first is not detected spark - it seems to me that this is the source of the problem)

    > Ew. It may have a damaged earth electrode. A common malfunction in these models.
    The 'earth electrode' is the one on the right (there are two: one on the left creates a spark and the other on the right seems to be an ionization sensor).
    I cleaned both but it didn't bring much results.
  • #46 18193738
    autoas
    Level 42  
    Posts: 9190
    Help: 571
    Rate: 3924
    At home I had to replace the whole Stronic ...
  • #47 18194426
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    # 36 is a photograph of a ground electrode that often falls out of this torch.

    It's like in the middle. If it is loose or has fallen out, the machine will not see the flame every time.
    It also often goes out when the main burner starts.
  • #48 18201258
    Piorun2002
    Level 15  
    Posts: 269
    Rate: 25
    I replaced Satronica (mine was already 18, 35,000h 'run'), for 4 hours it was ok, and then something tempted me to press the 'chimney sweep test' button ... the stove did not start and now I have to manually push it again.

    > # 36 is a photo of the ground electrode that often falls out of this torch.
    Through the small_the sliding door (sight glass) I can see that this electrode is in place - can it somehow burn or loose?

    Please advise how to perform electrode cleaning.
  • ADVERTISEMENT
  • #49 18202196
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    I told you PLN 350 PLN that the boiler needs cleaning.
    At this price, you would have a specific boiler overview with cleaning, security checks, gas tightness, etc.

    Yes, you have two machines, PLN 350 less and the boiler still out of order.

    You need to clean the entire burner. You will clean the electrodes themselves, the boiler will detect the smallest flame and may start to explode because of too small a candle.
    How do you check the gas tightness after the whole procedure?
    I suspect that no one has looked into it for 18 years.
    The boiler flue probably fell apart seven years ago
    Dust on the burner and under it at 20 mm

    If you don't mind spending PLN 350 blindly, take care of your safety and make a review.
  • #50 18202403
    Piorun2002
    Level 15  
    Posts: 269
    Rate: 25
    @piracik
    - the boiler has been rushing for 17 years ... all in all, the problems started after the authorized service did the inspection (I will not go into details as the valve ... anymore)
    - I bought the controller for 200 (someone bought it unnecessarily)
    - my question was how to do cleaning, not how to panic that it will not work

    And by the way, from sending this email at 12 .. to 22 the boiler worked without problems .. and now it has hung up again.

    I will be very grateful if someone will tell you how to do 'cleaning the electrodes'
  • #51 18202506
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    Piorun2002 wrote:
    my question was how to do the cleaning and not how to panic that it will fail


    I do not panic that you can not. The question you have posed indicates that you are not fit for it.
    How to clean the electrodes?
    Unscrew the starter torch being careful not to tighten the screw.
    Clean the electrodes, e.g. with a soft brass brush
    Check the condition of the electrodes, check that the massage electrode is not loose.
    If necessary, or rather is, replace the damaged starter burner gasket
    Insert and screw on the starter burner
    Check gas tightness.

    When cleaning the electrodes, clean the torch nozzles and the mesh in front of the nozzle.

    If the service has damaged something, it should take responsibility for it. If something is not working after the site they should fix it.
  • #52 18202906
    Piorun2002
    Level 15  
    Posts: 269
    Rate: 25
    Thank you for the substantive description, I would just like to clarify if I understand correctly.

    > Unscrew the starter torch being careful not to tighten the screw
    So first remove the wires from both electrodes (E1 and E2), then unscrew the metal wire (Torch - taking care not to tighten the screw) and disassemble the whole by unscrewing the screws S1 and S2

    > Check the condition of the electrodes, check that the massage electrode is not loose.
    Which electrode is it?
    Earlier I took out E1 and E2 - I cleaned it but it did not help much.

    > replace the damaged starter burner gasket
    > clean the burner nozzles and the mesh in front of the nozzle.
    I understand that these elements are visible after unscrewing the burner nut.

    Did I interpret your description correctly? (I prefer to ask twice just in case)
    Attachments:
    • Buderus Logano G124 Ignition: Switching Off Every Few Days - Replaced Ionization Electrode & More Buderus_Palnik_Startowy.jpg (200.54 KB) You must be logged in to download this attachment.
  • #53 18203020
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    Buderus Logano G124 Ignition: Switching Off Every Few Days - Replaced Ionization Electrode & More

    Unscrew the entire burner. The ground electrode is clamped in the torch housing.
    Under this tube is a nozzle that needs to be cleaned.
  • #54 18386259
    Piorun2002
    Level 15  
    Posts: 269
    Rate: 25
    My experience:
    - cleaning helped :)
    - I did not listen to my friend and instead of explaining the whole burner, I only dismantled the handle with electrode mounting to make it faster, but:
    one from fixing the screw broke (they are terribly corroded)
    the gasket (in Figure 9) was probably already cracked and spilled after being removed

    To sum up: it is better to disassemble the entire burner (I wanted to avoid it because I don't have a gas sensor to check the gas supply connector after assembly)
  • #55 18386636
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    Piorun2002 wrote:
    - I did not listen to my friend and instead of explaining the whole burner, I only dismantled the handle with electrode mounting to make it faster, but:
    one from fixing the screw broke (they are terribly corroded)


    piracik wrote:
    Unscrew the starter torch being careful not to tighten the screw


    Piorun2002 wrote:
    the gasket (in Figure 9) was probably already cracked and spilled after being removed


    piracik wrote:
    If necessary, or rather is, replace the damaged starter burner gasket


    Unscrewing the entire burner will not help much. There will be no access to the ground electrode.
    You didn't read what I wrote to you.
  • #56 18988500
    gipsatura
    Level 10  
    Posts: 74
    Rate: 9
    It will reheat the topic.
    The topic "BLA burner" came back to me
    I replaced the satronics, the ionization electrode, cleaned the candle nozzle, cleaned the igniting electrode and continued to light it again and not the next one. Sometimes when the burner is ignited, it is as if the blast extinguishes the candle and the entire burner goes out, and other times the candle goes out before giving the gas to the burners.
    Please indicate how the nozzle of a candle with a few holes should be positioned.
    I will add that I blown the gas pipe in front of the gas machine with the compressor, the machine and the thin tube behind the machine leading to the candle.
    Thanks in advance for your suggestions.
  • #57 18988582
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    Take a picture of the ignition burner.
  • #58 18988675
    gipsatura
    Level 10  
    Posts: 74
    Rate: 9
    I have just assembled everything, I want to see how it will be until morning, I'll take a picture tomorrow. The nozzle at the end of the candle / burner has it seen as it is seen standing in front of the stove
    one horizontal opening facing the inside of the furnace
    three small holes directed to the sides
    one larger opening pointing to the side
    two small invisible holes after screwing the entire torch
    I just found a pictorial photo of the set
    Attachments:
    • Buderus Logano G124 Ignition: Switching Off Every Few Days - Replaced Ionization Electrode & More de-dietrich-do-dtg-palnik-zapalajacy.jpg (45.77 KB) You must be logged in to download this attachment.
  • #59 18988965
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    I know what the burner should look like.
    I meant a photo of your burner.

    The biggest hole for ionization.
  • #60 18989835
    gipsatura
    Level 10  
    Posts: 74
    Rate: 9
    Here you are,
    Attachments:
    • Buderus Logano G124 Ignition: Switching Off Every Few Days - Replaced Ionization Electrode & More 20201020_175350.jpg (420.42 KB) You must be logged in to download this attachment.
    • Buderus Logano G124 Ignition: Switching Off Every Few Days - Replaced Ionization Electrode & More 20201020_175524.jpg (504.02 KB) You must be logged in to download this attachment.
    • Buderus Logano G124 Ignition: Switching Off Every Few Days - Replaced Ionization Electrode & More 20201020_175443.jpg (444.7 KB) You must be logged in to download this attachment.
    • Buderus Logano G124 Ignition: Switching Off Every Few Days - Replaced Ionization Electrode & More 20201020_175548.jpg (465.58 KB) You must be logged in to download this attachment.
    • Buderus Logano G124 Ignition: Switching Off Every Few Days - Replaced Ionization Electrode & More 20201020_175318.jpg (885.97 KB) You must be logged in to download this attachment.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around issues with the Buderus Logano G124 furnace, specifically related to the ignition system that intermittently fails, resulting in the "BLA burner" error. Users have shared experiences of replacing components such as the ionization electrode and the ignition nozzle, cleaning the burner, and troubleshooting the Satronic controller. Common solutions include ensuring proper grounding, checking gas pressure, and adjusting the position of the ignition electrode to improve flame detection. Some users have successfully resolved their issues by cleaning or replacing the ignition components, while others have suggested consulting authorized service technicians for further assistance.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: A healthy Buderus G124 needs >3 µA ionisation current [Elektroda, piracik, post #20013983]; “clean the nozzle before buying parts” [Elektroda, TB.PL, post #20013815] Regular maintenance solves most “BLA burner” errors.

Why it matters: This FAQ helps Buderus owners fix random ignition shut-downs without costly guesswork.

Quick Facts

• Ionisation current spec: >3 µA for reliable flame detection [Elektroda, piracik, post #20013983] • Ignition safety time ts: 5 s (mod.5) or 10 s (mod.10) on DKG 972 [Elektroda, marik, post #8845159] • New Satronic TFI 812.2 costs ≈ PLN 350 online [Elektroda, piracik, post #20013983] • Electrode kit price ≈ 10 € (≈ PLN 45) [Elektroda, Soloo, post #4807469] • Nozzle drill size: 0.47–0.5 mm for proper gas jet [Elektroda, antares29, post #5032250]

Why does my Buderus Logano G124 show “BLA burner” and shut down every few days?

The controller loses the flame signal when the ignition “candle” is weak or dirty. Clogged nozzle holes or carbon on the ionisation electrode drop the ionisation current below 3 µA, so Satronic closes the gas and flags “BLA burner” [Elektroda, kunert7, post #4790644][Elektroda, piracik, post #20013983]

What ionisation current should I measure on a working G124?

3 µA is the Buderus service threshold. Below that, flame supervision becomes unreliable [Elektroda, piracik, post #20013983]

Is the DKG 972 mod.21 a drop-in replacement for TFI 812.2?

Yes. Honeywell specifies it as the digital successor; wiring is identical, plus an extra diagnostic function. Follow the datasheet during swap [Elektroda, systemgaz, post #6177727]

Do I need a chimney draft sensor on the G124?

Many G124 installations lack the optional draft sensor; its absence will not trigger “BLA burner”. Temperature and ionisation circuits are the primary safeties [Elektroda, kunert7, post #4790644]

How do I decode Satronic DKG 972 blink codes?

One long + four short blinks = Code 14 (no flame within safety time). One long + six short = Code 16 (no gas to pilot). Full table is in the Satronic OEM PDF [Elektroda, marik, post #8845159]

Edge case: pilot lights but cuts out when main burner opens—why?

The main burner’s airflow can pull the pilot away from the ionisation rod if the ground electrode has slipped or the nozzle delivers too small a flame, causing immediate shutdown [Elektroda, piracik, post #18992185]

Can I buy just the nozzle or electrodes without full service visit?

Yes. Buderus partners sell individual parts, though some insist on fitting them. Independent suppliers list the starter burner gasket, nozzle, and electrodes from PLN 30 upward [Elektroda, autoas, post #8856517]