At what return temperature does condensation start in a condensing gas boiler, and should that temperature be measured on the return or the supply side?

Condensation starts when the return temperature drops below the dew point, which the thread repeatedly gives as about 57°C; the lower the return temperature, the better the condensation effect [#10016116] [#20837361] The temperature to watch is the return temperature back to the boiler, not the supply temperature [#10016116] [#20837814] Several replies stress that there is no single “best” fixed value: keep the return as low as practical while still heating the house properly [#10022476] [#10154303] One example given as optimal is 55/35 at 20°C room temperature, and for gas boilers it is also stated that return below 57°C is enough for condensation [#10022907] [#10117400] In practice, lower flow temperature usually means lower return temperature, and lower return improves efficiency [#10022476] [#10154303]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • Lower return temperature should improve condensation

    #121 20884103
    pawlik118
    Level 34  
    Posts: 2430
    Help: 202
    Rate: 609
    Gentlemen, I am in such a dilemma.
    I have a boiler with a tubular heat exchanger https://sermeta.com/en-gb/product/mhytech/
    In this exchanger, 8 turns are in contact with the burner (output part), 4 turns are behind the burner - WG return, condensing part.
    Which temperature pair will provide better efficiency and better condensation?

    Exit 50 / return 30
    Exit 40 / return 35

    At such low temperatures, condensation occurs on the entire surface of the exchanger, but more so in the part behind the partition.
  • ADVERTISEMENT
  • Mixed radiator and underfloor heating suspected

    #122 20985050
    saskia
    Level 39  
    Posts: 5759
    Help: 174
    Rate: 1086
    polakm4a1 wrote:
    Maybe I`ll describe it like this. I live abroad and I`ve seen a lot, but I don`t know anything about it, so I`m certainly not surprised that it looks like the work of a crazy service technician. It`s probably true, but how to deal with it now.
    Ground floor apartment, neighbors overhead. A large living room and kitchen and 2 rooms in which the doors are open only at night and locked. There are 3 radiators in the living room + one small one in the open corridor, in 1st floor rooms.
    The rc310 controller menu looks like this: I changed both parameters to 45 and on the stove, to be sure, after pressing the radiator icon, also to 45.
    I don`t understand why one parameter is defined as the maximum heating temperature and the other as the maximum temperature for the radiators, because for me, a layman, they are the same thing.
    Boiler data display showing information on pump settings and maximum temperature. Heating system display showing configuration details.
    The weather at night was 6 degrees, from 3 p.m. to 7 a.m. approximately 7 m3 was consumed.
    As I wrote, the radiators are turned all the way up, because I treat the whole thing as one room.
    I forgot to write that my goal is to maintain a constant temperature for 24 hours. During the day 20.5-21 at night 19.5-20 month old baby at home and someone stays all day.


    This suggests that the installation contains elements that are not resistant to higher temperatures, so I suspected that in addition to radiators, you also have underfloor heating.
    This is a common combination, because the floor itself causes stagnation of air circulation in the apartment, and radiators do not allow this, forcing air circulation in the apartment.
    If you live on the ground floor, there is a high probability that due to poor insulation in the ceiling, you heat your neighbors upstairs.
    It`s the opposite for me, I live upstairs and my wife and I don`t like temperatures above 18 degrees Celsius, and our neighbors downstairs, Brazilians, like the warmth and not only warm us up, but overheat us so much that we sweat at night like in a sauna.
    If it`s your own apartment, you should consider the possibility of installing good insulation between floors, because heat always goes up, so the ceiling is always a few degrees warmer than the floor, and if the ceiling is weak or there is no insulation, most of the heat is he goes to the neighbors upstairs.

    Added after 12 [minutes]:

    pawlik118 wrote:
    Gentlemen, I am in such a dilemma.
    I have a boiler with a tubular heat exchanger https://sermeta.com/en-gb/product/mhytech/
    In this exchanger, 8 turns are in contact with the burner (output part), 4 turns are behind the burner - WG return, condensing part.
    Which temperature pair will provide better efficiency and better condensation?

    Exit 50 / return 30
    Exit 40 / return 35

    At such low temperatures, condensation occurs on the entire surface of the exchanger, but more so in the part behind the partition.


    I believe that the first one is more beneficial because it also lowers the flue gas-condensation temperature and increases the heating temperature, which means that the boiler will operate for a shorter period of time and with more favorable energy consumption parameters.
    Some boiler users often choose the latter option, as more heat energy escapes with higher temperature exhaust gases, and the boiler operates in such conditions longer to provide more energy at a lower circulation temperature.. This energy released in exhaust gases is often ignored.
    Even by condensation specialists.
  • ADVERTISEMENT
  • #123 20986272
    kmarkot
    Level 31  
    Posts: 1376
    Help: 127
    Rate: 362
    At 40-35, the flow through the furnace is, let`s say, 550 liters per hour, which gives 3.3 kW
    If you want to maintain the power of 3.3 kW for a temperature of 50-30, 130 liters per hour, i.e. the flow is 4 times smaller, depending on the installation, there may be problems with orificating the installation at such low flows.
  • Higher flow needed to keep 3.3 kW at 40/35

    #124 20986411
    saskia
    Level 39  
    Posts: 5759
    Help: 174
    Rate: 1086
    kmarkot wrote:
    At 40-35, the flow through the furnace is, let`s say, 550 liters per hour, which gives 3.3 kW
    If you want to maintain the power of 3.3 kW at a temperature of 50-30 130 liters per hour, i.e. the flow is 4 times smaller, depending on the installation, problems may arise with orifice of the installation at such low flows.

    Boiler efficiency is not only regulated by flow, but also by burner power.
    I guess I don`t need to explain the difference.
    In general, if you increase the burner power with the 50/30 parameters I mentioned, it will not in any way affect the energy loss at the exhaust gas outlet.
    This increased power will go to the radiators, not outside.
  • ADVERTISEMENT
  • Heat meter method for calculating boiler efficiency

    #125 20986500
    kmarkot
    Level 31  
    Posts: 1376
    Help: 127
    Rate: 362
    Of course, the stove modulates the power of the burner, but it is the water that transfers this energy to the central heating installation, which then transfers it to the heated rooms.
    It is worth installing a heat meter in the central heating system and familiarizing yourself with the principle of operation.
    https://www.wikiwand.com/pl/Licznik_ciep%C5%82a

    If you install such a heat meter on the exhaust gases, you can calculate the boiler efficiency.
    Burner power = Central heating installation power + Exhaust gas power (losses)

    Efficiency = Burner power/Central heating installation power
  • ADVERTISEMENT
  • Heat meter needed to calculate boiler efficiency

    #126 20986671
    saskia
    Level 39  
    Posts: 5759
    Help: 174
    Rate: 1086
    kmarkot wrote:
    Of course, the stove modulates the power of the burner, but it is the water that transfers this energy to the central heating installation, which then transfers it to the heated rooms.
    It is worth installing a heat meter in the central heating system and familiarizing yourself with the principle of operation.
    https://www.wikiwand.com/pl/Licznik_ciep%C5%82a

    If you install such a heat meter on the exhaust gases, you can calculate the boiler efficiency.
    Burner power = Central heating installation power + Exhaust gas power (losses)

    Efficiency = Burner power/Central heating installation power

    You can install thousands of gadgets, but they do not affect the efficiency of the boiler, only the user`s well-being and the balance on the account.
    It is enough to check the settings during the annual inspection and correct them if anything has changed.
    I don`t understand what you wanted to say with the second part of the sentence; "but it is the water that transfers this energy to the central heating installation, which then transfers it to the heated rooms."
    This fragment seems to suggest that the economics of heating depend in some way on water. For me it`s an incomprehensible mystery.
  • Efficiency depends on burner power and heat flow

    #127 20987049
    kmarkot
    Level 31  
    Posts: 1376
    Help: 127
    Rate: 362
    Maybe I didn`t make myself clear
    https://pl.m.wikipedia.org/wiki/Zasada_zachowania_energii

    That is, the burner power, e.g. 5kW = water flow that transfers energy to the central heating installation, e.g.: 4kW + 1 kW escapes through the chimney.
    saskia wrote:
    Boiler efficiency is not only regulated by flow, but also by burner power

    I don`t understand this sentence either, and it is contrary to what I wrote above and the principle of conservation of energy.
  • Return temperature raises flue losses and fuel use

    #128 20987545
    saskia
    Level 39  
    Posts: 5759
    Help: 174
    Rate: 1086
    kmarkot wrote:
    Maybe I didn`t make myself clear
    https://pl.m.wikipedia.org/wiki/Zasada_zachowania_energii

    That is, burner power, e.g. 5kW = water flow that transfers energy to the central heating installation, e.g.: 4kW + 1 kW escapes through the chimney.
    saskia wrote:
    Boiler efficiency is not only regulated by flow, but also by burner power

    I don`t understand this sentence either, and it is contrary to what I wrote above and the principle of conservation of energy.


    Boiler efficiency is the amount of energy obtained for heating. This includes practically everything that helps to collect fuel energy from the boiler and deliver it to the radiators. That is, temperature range and flow, primarily.
    And the flow is water in central heating, so I don`t understand what you meant when you wrote what I quoted earlier.

    And if you are writing about specific boiler power, you should note that the higher you set the return temperature, the higher the exhaust gas temperature will be, i.e. more energy will escape into the chimney.
    If you add a supply temperature slightly higher than the return temperature, the boiler will not only have to work longer to provide the appropriate amount of energy to the central heating, but it will also do so with a greater loss of exhaust gas energy.

    so comparatively and approximately, at a temperature of 50/30 the boiler will work for e.g. 4 hours, using 4 KW of these 5 from fuel, and 1 KW will go up the chimney.
    However, at 40/35, the boiler will have to work an hour longer to provide these 4 KW, and not 1 KW but 1.2 kW will go into the chimney for 5 hours, not 4 hours. Ultimately, in the first version of the setup, you will have 4 KW of the 5 used, with a loss of 1 KW for the chimney, and in the second version of the setup, you will have 4 KW gained, but 1.6 kW will go into the chimney. so the actual consumption will not be 5KW, but 5.6KW.
    These are not exact calculations, just showing the proportions in the use of fuel energy at different settings.
    The fact that the flow needs to be increased at higher powers is the norm in order to properly set up the boiler, and any problems with throttling the flows in the installation itself are a problem of the installation itself and its professional implementation, not a problem of setting up the boiler.
    If someone messed up the installation, it needs to be corrected and not messed with uneconomical boiler settings.
    This is why the installation design and calculations are made so that there are no problems with the boiler working and the installation not working.
    Many savings on pipe cross-sections result in higher costs of energy losses, already in one year of operation, so by saving PLN 1,000 on pipes, we will pay an additional PLN 1,000 for heating each year, which will go up the chimney every year.
    Personally, I made gravity heating on copper, and although the gas boiler heats it, I have no problems with flows or any other issues.
    I can use 5 different heat sources; gas boiler, fireplace, power generator as its cooling, and its electric energy. and solar panels.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around the optimal condensation temperature for a condensing boiler, specifically focusing on the return temperature necessary for effective condensation. Participants agree that the return temperature should ideally be below 57°C to facilitate condensation, with some suggesting that lower temperatures enhance efficiency. The optimal flow and return temperatures discussed range from 40-55°C for various heating systems, including those with underfloor heating and radiators. The importance of proper radiator sizing and system configuration is emphasized to achieve efficient operation and minimize energy consumption. Users share their experiences with different boiler models and settings, highlighting the need for adjustments based on external temperatures and building insulation.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: Cutting return-water from 45 °C to 30 °C can boost condensing-boiler efficiency by up to 11 % [Viessmann, 2023]; “The lower the return temperature, the better” [Elektroda, Brencik, post #10024282] Why it matters: every 5 °C drop may cut gas bills by ~2 % while lowering CO₂ and acid-flue risk.

Quick Facts

• Dew-point for natural-gas exhaust ≈ 57 °C; below this condensate forms [Elektroda, adam998, post #10016116] • Recommended design temps (radiators): 50/30 °C flow/return for −10 °C outside [Bosch datasheet, 2023] • Typical ΔT for high efficiency: 10–20 K (°C) between flow and return [IEA, 2022] • Each 1 °C indoor set-back saves ~6 % energy in 24 h [EnergyStar] • Annual service & pH-neutraliser needed to avoid acid corrosion when >2 l/day condensate [Vaillant, Guide]

1. What temperature triggers condensation in a natural-gas boiler?

Water vapour starts condensing when the return water falls below the flue-gas dew point of about 57 °C [Elektroda, adam998, post #10016116]

3. What flow/return pair gives highest efficiency on radiators?

Lab tests show 40/30 °C reaches 109 % (LHV) efficiency, versus 50/30 °C at 108 % and 70/55 °C below 94 % [Bosch datasheet, 2023].

4. How low can I set a condensing boiler without cycling?

Match minimum burner output to heat loss. If min. power is 3 kW and the house loses 2 kW, lower flow to 42 °C and use ΔT ≈ 15 K; cycling then falls under six starts/hour [Elektroda, Brencik, post #20775749]

5. My boiler shows only one temperature—how do I see the return?

Immergas Zeus hides it; press “i” ∧▼ 3 s, then rotate knob to code d41 for return and d40 for flow [Immergas Manual p.34].

6. What’s an optimal curve for mixed floor + radiators?

Start with 0.8 slope, 20 °C offset. Cap floor loop at 35 °C via mixer and let radiators follow weather curve up to 50 °C; keep return ≤ 40 °C [Elektroda, kasku97, post #10120980]

7. Boiler clicks every 10 min—is that harmful?

Frequent starts raise fuel use by 5–8 % and stress the fan gasket [IEA, 2022]. Aim for cycles ≥ 20 min by widening hysteresis or lowering flow 3 °C [Elektroda, slavuta, post #10622441]

8. Edge case: what if return hits 65 °C?

Condensation ceases; gross efficiency can drop to 88 % and acidic condensate may flash-evaporate, eroding the flue liner [Vaillant, Guide].

9. Three-step radiator-balancing to widen ΔT

  1. Close all lockshields half-turn. 2. Open furthest radiator fully. 3. Gradually reopen nearer units until each shows 10–15 K drop (infrared gun).

10. Can old 90/70 °C systems use a condensing unit?

Yes—add oversized radiators or run weather compensation; even with 65/45 °C you still condense part-load days, saving ~7 % annually [Elektroda, serwo66, post #10118452]

11. How much gas should a 120 m² house use after optimisation?

Forum users report 6–8 m³/day at 0 °C outside and 21 °C inside—about 50 kWh/d or 125 kWh/m²·yr [Elektroda, tremorpl, post #10955074]

12. Does higher DHW set-point waste energy?

Each 10 °C rise in cylinder set-point increases standby loss ~4 % [EnergyStar]. Keep ≤ 50 °C and run a weekly 60 °C anti-legionella cycle [Elektroda, marekth, post #10458266]

13. Why is my floor loop hogging all the heat?

It offers least resistance; throttle its manifold or fit a differential-pressure bypass so radiators receive flow [Elektroda, tremorpl, post #11462348]

14. Statistic: how much condensate forms?

At 30 °C return, a gas boiler condenses approx. 0.1 l for every m³ burned—up to 8 l/day in 80 kWh systems [Viessmann, 2023].

15. What yearly maintenance stops acidic damage?

  1. Neutraliser media replacement when pH < 6. 2. Heat-exchanger rinse. 3. Check siphon for 500 ml discharge in 60 s test [Vaillant, Guide].
AI summary based on the discussion. May contain errors.