How should I heat a 35 m² unfinished garage—should I insulate it, use radiators or underfloor heating, and should I use ordinary or thermostatic valves?

If you want the garage kept only a few degrees above zero all the time, the preferred solution in the thread is underfloor heating, but only with proper insulation; one reply recommends hard EPS100 foam at least 8 cm under the slab and 8–10 cm of concrete, with a thermostat and thermal actuator mandatory [#13330513] Since your garage is still unfinished, another reply says it makes sense to insulate the walls too, e.g. with about 10–15 cm of Styrofoam, and underfloor heating is especially practical before the screed is made [#11625728] Radiators will heat mainly near the ceiling and lose more energy every time the door opens, so they are less suitable for a garage that is opened often; several replies note that floor heating keeps the floor warm, reduces moisture, and is better for the car [#11738249 #13346337]. If you choose radiators instead, use a thermostatic valve rather than a plain valve; one reply explicitly recommends a closed system filled with liquid and a thermostatic valve for a 35 m² garage [#13276740] For a garage that is only heated sporadically, some posters suggest radiators or even electric heating, but for constant low-temperature heating the thread favors insulated underfloor heating [#13374371 #11736806].
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 11625609
    Anonymous
    Anonymous  
  • ADVERTISEMENT
  • #2 11625671
    mscgs24
    Level 21  
    Posts: 382
    Help: 41
    Rate: 66
    I also built a garage last year, 16 away from the house, geodetic conditions....
    When making the water and sewer connection, I decided to run underfloor heating pipes (packed inside a PVC pipe so blue that they do not get damaged)
    It works great for me, because it heats the entire garage area as well as the sewer, and this is useful in the winter in case of car trouble.
    Pipes outside buried to a depth of about 70 cm.
    Temperature controller in the garage. I have it set at 17 degrees C
    I was going to put ordinary radiators under the windows, but a neighbor who did it for me (he has a company dealing with central heating) advised me this solution, I do not regret.
  • #3 11625728
    William Bonawentura
    Level 34  
    Posts: 2425
    Help: 190
    Rate: 619
    bobek5001 wrote:
    The garage has an area of 35m and walls 25cm thick should I insulate the building or leave it there? Of course, I do not want to get there the temperature as in the house but it is completely enough a few dashes above zero, because of the equipment kept there. And I solve turning off this ordinary valves or thermostatic??


    1) As far as I understood you want to heat the garage constantly. If it is unfinished (and you were to do exterior plastering) then it makes as much sense to insulate it with a thinner (10-15cm) layer of Styrofoam.
    2) As a colleague wrote - if you don't have screeds yet then underfloor will be a great thing. Provided that you always already heat this garage. You will drain water from the radiators, pipes laid with a slope and risers will drain water. The flooring will not.
  • #4 11625745
    mscgs24
    Level 21  
    Posts: 382
    Help: 41
    Rate: 66
    William B. I forgot to add that at the underfloor I have a valve in the duct (duct 170 cm deep) valve at a height of about 80 cm from the floor of the duct, so I have no problem with draining water, that way I can drain the whole riser there even in the house. I left out this info unknowingly.
  • #5 11625846
    andrefff
    Level 36  
    Posts: 2719
    Help: 321
    Rate: 807
    Well, and water is not necessarily the factor.
  • #6 11627582
    Piotr77777
    Heating systems specialist
    Posts: 680
    Help: 58
    Rate: 266
    But underfloor heating is not good for cars especially in winter
    The best are heaters :) .
  • Can two 3/8-inch radiators heat garage at 45-50C?

    #7 11736610
    Anonymous
    Anonymous  
  • #8 11736712
    Piotr77777
    Heating systems specialist
    Posts: 680
    Help: 58
    Rate: 266
    In my opinion, yes, they can have more power than twice the size of a panel heater.
    You can always still apply some fan behind this heater.
  • ADVERTISEMENT
  • #9 11736791
    Anonymous
    Anonymous  
  • #10 11736806
    bartekfigura
    Level 30  
    Posts: 1294
    Help: 112
    Rate: 525
    Garage is rather a place heated sporadically and only during the biggest frosts maybe you should be interested in electric solutions? A cheap static furnace on the 2nd tariff and you're done. The water in the system will never freeze you:-) .
  • DIY hydronic heating system planned for 10°C garage

    #11 11736866
    Anonymous
    Anonymous  
  • ADVERTISEMENT
  • Underfloor heating provides efficient, even garage warming

    #12 11738249
    wada

    VIP Meritorious for electroda.pl
    Posts: 3048
    Help: 168
    Rate: 732
    The most economical and cheapest to implement is the underfloor in the garage.
    And then there can indeed be a slight heating up to 10 ° C.
    And as you read here and there, it is also recommended for the car. The car is evenly heated, moisture evaporates faster, evenly heated lubricants, oils, suspension, tires is also a big advantage.

    A heater only heats the ceiling, only after cooling down the air goes down, you need to supply much more energy and high temperature to the radiator, and from the floor cuts cold, as well as through the door not always tight, moisture and rust do their own, and with the firing of the car can also be problems, the engine icy and sucking much warmer rare air.
    Company Account:
    Elefant
    Wagonowa 34, Wrocław, 52-231 | Company Website: literyzmetalu.pl
  • #13 11739672
    Anonymous
    Anonymous  
  • Reworking coolers doubles heat transfer and simplifies venting

    #14 11743027
    saskia
    Level 39  
    Posts: 5759
    Help: 174
    Rate: 1086
    bobek5001 wrote:
    Hello after a long break I was also thinking about a heater but they are very expensive and I would like to do it as cheaply as possible and I found two such coolers on 3/8 inch pipes in the attic and I wonder if at 45-50 degrees factor such a heater will heat my garage to those 10 degrees in plus.
    Installing Radiators in a 35m Garage: Insulation and Thermostatic Valve Considerations Installing Radiators in a 35m Garage: Insulation and Thermostatic Valve Considerations Installing Radiators in a 35m Garage: Insulation and Thermostatic Valve Considerations
    Greetings and look forward to your evaluation.


    If you slightly rework these coolers then you will not need to install a fan.
    In the middle photo you can see the upper tube connecting the right side with the left.
    Unfasten it and put there the Trojan connecting the right and left as they were, and the side connection of the Trojan connect to the CO supply. Do the same on the opposite side with the pipes feeding the cooler, connect them together with a T-piece and connect to the return of the central heating, it will double the surface of heat transfer from the same amount of flowing water and it will be easier to vent.
  • #15 11743543
    Zbigniew Rusek
    Level 38  
    Posts: 3613
    Help: 394
    Rate: 1542
    Installing a fan to this radiator (functioning as a heater) will greatly accelerate the heating of the garage. Without a fan is better for permanent heating and if you need ad hoc - a fan is advisable. The same is true for electric heating - a kiosk that is cooled after a night will be heated the fastest by a thermo-blower. The car radiator is copper, so it gives off heat perfectly.
  • 12 mm tubing dimensions and hard solder requirements

    #16 11744885
    Anonymous
    Anonymous  
  • #17 13275398
    mateuszt2
    Level 2  
    Posts: 3
    Rate: 6
    Hello everyone

    Added after 13 [minutes]:

    Installing Radiators in a 35m Garage: Insulation and Thermostatic Valve Considerations Installing Radiators in a 35m Garage: Insulation and Thermostatic Valve Considerations Installing Radiators in a 35m Garage: Insulation and Thermostatic Valve Considerations at my place it looks like this garage:
    22m2 heating 45max50 degrees from the home furnace distance from the house about 15m zanked system flooded with coolant exchanger from some car heater dimensions 40cm by 50cm fan converted from the room and now so the heater does not work at all temperature inefficiently it means that what water flows in the same flows out the fan even copes with it I'm going to replace the air conditioning vent at a cost of about 200zł what do you guys think about such a solution
  • #18 13276740
    Anonymous
    Anonymous  
  • #19 13326323
    mateuszt2
    Level 2  
    Posts: 3
    Rate: 6
    Now it looks like in the pictures. Cost 110zl plus shipping 30zl. It heats super. Even at 45 degrees.

    Added after 2 [minutes]:

    Installing Radiators in a 35m Garage: Insulation and Thermostatic Valve Considerations Installing Radiators in a 35m Garage: Insulation and Thermostatic Valve Considerations Installing Radiators in a 35m Garage: Insulation and Thermostatic Valve Considerations .
  • #20 13330513
    andrzej lukaszewicz
    Level 42  
    Posts: 7034
    Help: 626
    Rate: 2122
    If permanently , then only underfloor. For 35 m2, a 200m disc of pipe for 500 zł will be enough ( the company's, not from the market) Radiators and approaches will come out more expensive and worse. As colleagues wrote , it will be warm under the ceiling, and at the entrance door will be frozen, and if not, snow mud will be on the floor will lie continuously. The temperature set at 7-8 degrees C will feel like 12 at the radiators. If there is a duct , it means that the author will sometimes do something at the car, and the floor for this purpose is the best - heat at the bottom, where it is needed. In addition, with a heated slab, opening the garage does not cause its immediate evaporation - a lot of inertia.
    And lest anyone accuse me of lip service, I will write that I have a garage of 42m2 with such heating 2 pettings with pipe spacing of 20-25cm. And who does not enter in the winter is saying : "how warm it is here" and in the garage is still maintained at about 8 degrees C.
    In the past, when I was installing alarms in cars I had set 12 degrees C and clothing such as a shirt and dungarees were sufficient.
    For underfloor heating in the garage EPS100 hard foamed polystyrene min. thickness. 8 cm. Screed min 8 cm and good slopes , although there may be a problem , if there is a channel, then you need to make drains around it, troughs.
    Termoregulator mandatory(+ thermal actuator), does not have to be with a sensor in the floor.
  • #21 13341317
    mateuszt2
    Level 2  
    Posts: 3
    Rate: 6
    Yes, underfloor heating is great. Provided that we work in the garage every day. In my case, I don't always have something to fix so I still think my solution is good and economical.
  • #22 13341737
    Jacek79
    Level 37  
    Posts: 3794
    Help: 233
    Rate: 1132
    Heaters are ok
    The important thing is to oversize it, the bigger the better.
  • #23 13346337
    wada

    VIP Meritorious for electroda.pl
    Posts: 3048
    Help: 168
    Rate: 732
    Jacek79 wrote:
    Heaters are ok It is important to oversize it, the bigger the better
    and you need to supply them with water at a fairly high temperature, and only to heat the ceiling. When you open the door, the room immediately cooled and in turn need ful energy. Around the door a perpetual smear of mud, and even often ice.
    When entering the garage immediately fogging up all the windows.
    Under the car lack of air circulation, even persistent sub-zero temperatures, high humidity, rapid corrosion, stiff suspension, hard tires that only after driving a few kilometers have a good grip.
    Car standing in such a garage is always cold inside, icy undercarriage enters the cold through the floor.
    The only advantage of heaters (and heaters) is that the snow does not collect on the garage roof.


    A floor heating is devoid of all these disadvantages !
    In the garage as there is a good sand bed is a hard Styrofoam 4-8cm is enough and on this film, pipes and 8-10cm of concrete.
    And the cost of construction as well as heating VERY cheap.
    Once heated concrete slab - even if only to 15 ° C maintains a temperature of 8-12 ° C in the garage for a long time, and it is enough that there is water flowing in these pipes at a temperature of 20 ° C, some then use the water from the return from radiators.


    Another interesting heating is to bury about 20m of sewer pipe (gray 110) to a depth of more than 120cm and with a small fan (20-45W) pump air through these pipes and we have in the garage for free about 14 ° C. In the summer heat you can then cool down the garage for free.
    Company Account:
    Elefant
    Wagonowa 34, Wrocław, 52-231 | Company Website: literyzmetalu.pl
  • ADVERTISEMENT
  • #24 13346482
    mirrzo

    VIP Meritorious for electroda.pl
    Posts: 7654
    Help: 441
    Rate: 2609
    wada wrote:
    .... and with a small fan (20-45W) pump air through these pipes and.... for free around 14°C. In the summer heat, you can then cool down the garage for free.
    And the fan what kind of drive does it have, if FREE?
    Company Account:
    EURO-DOM
    Krótka, Elbląg, 82-300
  • #25 13371660
    wnoto
    Level 34  
    Posts: 3634
    Help: 58
    Rate: 744
    wnoto wrote:
    Another interesting heating is to bury about 20m of sewer pipe (gray 110) more than 120cm deep and with a small fan (20-45W) pump air through these pipes and we have about 14°C in the garage for free. In the summer heat you can then cool the garage for free.


    How will 20 m of pipe underground warm the air from -18 to 14 degrees ??
    From the ground , which is not even 10C in winter ?
  • Floor heating’s high inertia suits continuously used garages

    #26 13374371
    Grzegorz Siemienowicz
    Level 36  
    Posts: 3587
    Help: 146
    Rate: 600
    wada wrote:

    A floor is devoid of all these disadvantages !


    Depends how you look at it.

    Floor heating has a huge inertia and therefore it is advantageous when the room is used constantly and not occasionally ;
    Must be properly prepared insulation of the floor .

    In the West in warehouses where people stay for a short period of time, the most common is the use of various types of radiant heaters. Such a radiant heater can be a goat and a goat chimney although more often electric radiant heaters hung on the walls or under the ceiling are used.

    Also, with an average use of this garage less than 4h a day during the heating season, other solutions (even electric radiant heaters) will come out cheaper to operate.

    It is also not beneficial for the car if it collects snow with salt from the street every day then defrosts it on the car.
  • #27 14249389
    daniel_lhr
    Level 13  
    Posts: 128
    Help: 1
    Rate: 31
    Hello
    I have a question , what diameter pex to give to bring heating to the garage 35m2 away 20m? Garage insulated with 10cm polystyrene foam also ceiling. I plan one radiator , temp max 15 degrees C.Of course there will be a circulating pump.
  • Electric oil heater avoids long-run heating losses

    #28 14249667
    Jacek79
    Level 37  
    Posts: 3794
    Help: 233
    Rate: 1132
    daniel_lhr wrote:
    welcome
    I have a question , what diameter pex to give to bring the heating to the garage 35m2 away 20m? Garage insulated with 10cm styrofoam also ceiling. I plan one radiator , temp max 15 degrees C.Of course there will be a circulating pump.


    Don't play with it. Connect electric oil


    Added after 53 [seconds]:

    daniel_lhr wrote:
    welcome
    I have a question , what diameter pex to give to bring the heating to the garage 35m2 away 20m? Garage insulated with 10cm styrofoam also ceiling. I plan one radiator , temp max 15 degrees C.Of course there will be a circulating pump.


    Don't play with it. Large losses on such a section
    Plug electric oil
    Or cumulative.
  • #29 14249745
    daniel_lhr
    Level 13  
    Posts: 128
    Help: 1
    Rate: 31
    Hardly a little energy will escape .I repeat the question what diameter pex ? I have already buried 110mm pvc pipe , I think I will put 2x alupex 16 and lagging 18/20 , does it make sense?
  • #30 14249808
    Jacek79
    Level 37  
    Posts: 3794
    Help: 233
    Rate: 1132
    It is better to give a larger diameter, less hydraulic resistance at such a distance

Topic summary

LABEL_AI_GENERATED
The discussion revolves around heating solutions for a 35m² garage located 5m from a house, focusing on the installation of radiators and insulation considerations. Users suggest various heating methods, including underfloor heating, which is favored for its efficiency and ability to maintain a consistent temperature. Insulation with Styrofoam is recommended to enhance heat retention. The use of thermostatic valves is debated, with some advocating for their installation to optimize heating. Concerns about the effectiveness of underfloor heating for vehicles in winter are raised, alongside suggestions for using electric heaters or traditional radiators. The conversation also touches on the practicality of using fans to improve heat distribution and the importance of proper pipe sizing for heating systems.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: For a 35 m² detached garage, 8 cm EPS under-slab insulation can cut heat loss by ≈30 % [andrzej lukaszewicz, #13330513]. "Underfloor heating is the most economical" [wada, #11738249]. Choose PEX-16 (200 m) and 45–50 °C water to keep 7–10 °C inside. Why it matters: balanced comfort protects your car and tools while slashing fuel bills.

Quick Facts

• Heat load for a 35 m² garage held at +10 °C: approx. 1.5–2 kW [EN 12831]. • 200 m of PEX-16 pipe costs ~500 zł and covers 35 m² floor area [andrzej lukaszewicz, #13330513]. • EPS100 polystyrene, 8 cm thick, meets 0.38 W /m²K floor U-value target [andrzej lukaszewicz, #13330513]. • Salvaged copper heater core + fan can double panel-radiator output at the same flow [Piotr77777, #11736712]. • Heat-pump with SCOP 4 draws ~300 W to supply 1.2 kW heat at −5 °C [wesmar, #16929608].

Do I need to insulate a 35 m² brick garage before adding heaters?

Yes. A 10 cm external styrofoam layer lowers transmission losses enough to hold 7 °C with low water temperature [William Bonawentura, #11625728].

Which system is cheaper for a steady 7–10 °C: underfloor or wall radiators?

Underfloor wins. Pipe, insulation and screed cost about 30 zł/m², yet supply water can stay at 25–30 °C, cutting boiler cycling [wada, #11738249].

How thick should the insulation under the slab be?

Install at least 8 cm EPS100. This depth resists wheel loads and meets Polish garage U-value rules [andrzej lukaszewicz, #13330513].

What pipe length and spacing heat 35 m² evenly?

Lay 200 m of PEX-16 at 20–25 cm centres. Flow 2–3 L/min suits 45 °C supply [andrzej lukaszewicz, #13330513].

Can I use 16 mm PEX buried 20 m from the boiler?

Yes, but run twin PEX in a 110 mm PVC conduit and add 18/20 mm lagging to slash ground losses [daniel_lhr, #14249745].

What if the garage is used only occasionally?

Large concrete inertia delays warm-up. In that case oversize a fan-assisted radiator or use an electric radiant panel for rapid heat [Grzegorz Siemienowicz, #13374371].

Will under-floor pipes freeze in power outages?

Slope manifolds to a 170 cm deep valve so you can drain by gravity; no slope means trapped water can burst pipes [mscgs24, #11625745].

How much heat can a recycled car heater core deliver?

At 50 °C water and twin 30 cm fans it can provide 3–4 kW—about twice a 600 mm panel radiator [Piotr77777, #11736712].

How do I connect that heater core for best output?

  1. Replace the top bypass with a T-piece on the supply.
  2. Mirror on the return side.
  3. Bleed at the highest point. This doubles wet surface and eases venting [saskia, #11743027].

Which diameter PEX supply line minimises hydraulic loss over 20 m?

PEX-20 × 2 mm gives ≈100 Pa pressure drop at 0.2 L/s, 40 % less than PEX-16, aiding small pumps [Jacek79, #14249808].

Do I need thermostatic valves?

Fit one on each emitter. At only 10 °C set-point they prevent overheating when sun warms the garage [Anonymous, #13276740].

Is a heat-pump air-conditioner viable for a garage?

Yes. A unit with SCOP 4.0 uses about 0.5 kWh to keep +10 °C at −5 °C outside, under 0.30 zł/h on night tariff [wesmar, #16929608].