[Solved] Boiler heater control 3 kW - selection of programmer and 16 A fuse

tomek.dziekonski 6738 4
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 14643262
    tomek.dziekonski
    Level 8  
    Posts: 20
    Rate: 2
    I have an electric boiler powered by a 3 kW electric heater as the idea is to have a night electric tariff I plan to install a simple control system.

    At the moment there is a normal grounded socket.

    I plan to purchase something like this

    http://www.conrad.pl/Programator-tygodniowy-c...n%C4%99-DIN.htm?websale8=conrad&pi=198520

    Add a fuse/switch to this and mount in a box on the rail in front of the socket.

    My question is whether 16 A is sufficient for a 3 kW heater?
    What is the best fuse contactor for the kit?
    Will the kit mentioned work well and how best to mount it?

    What is a possible alternative. The device must not be too expensive or the whole operation will lose its meaning.

    Best regards
  • ADVERTISEMENT
  • #2 14649307
    zibuch
    Level 10  
    Posts: 43
    Rate: 1
    I have the same tank and the same heater in the middle. i have a 6kW heater. With 3kw you have to set the temperature so that you always have a supply of water, don't expect it to heat you up when you need it. For a family of 2+2 it is easily enough.
    Of course, you forgot about the thermostat which will cut off the heating when it reaches a certain temperature, because I don't suppose you want to do that
    I don't know if you shouldn't look for a dedicated controller with hours of operation, a thermostat that has a weekly overheating of the water right away. Unless you're oiling the legionella subject
  • ADVERTISEMENT
  • #3 14649368
    tomek.dziekonski
    Level 8  
    Posts: 20
    Rate: 2
    The thermostat is in the heater and it is the one that keeps an eye on the temperature independently of the other devices. I am interested in using the night-time tariff to heat water.
    i recently found something like this
    http://www.conrad.pl/?websale8=conrad&pi=614900&&gclid=CP7G37SXlsUCFaLMtAodGUkAtQ

    As far as legionella is concerned, during the winter period (from the beginning of September to the end of May) the water is heated from the central heating boiler and has a temperature of 55-60 degrees (non-stop) so there should be no problem. With the heater I plan to heat also to some 55-60 degrees and once a week a higher temperature can be given.
  • ADVERTISEMENT
  • #4 14683926
    kosmos99
    Level 38  
    Posts: 4188
    Help: 338
    Rate: 816
    tomek.dziekonski wrote:
    My question is 16 amp power sufficient for a 3 kW heater?


    It is sufficient.

    If the controller is only to be used for this, then a simple controller with a timer and a socket for a dozen or so zlotys will suffice. You insert it into the socket and the plug from the boiler into its socket. Controllers are both electronic and mechanical clocks.
  • #5 17232153
    tomek.dziekonski
    Level 8  
    Posts: 20
    Rate: 2
    I purchased a German 16A socket, which will take a 3 kW heater. The only inconvenience is that I had to change the socket to the German one, because the Polish one could not be plugged in. The advantage of the German one is that Polish appliances can be plugged in without any problems.