Heating in the block: CO from the city vs own gas boiler room
adamlabedz 21603 46
How can a 180-apartment community determine whether replacing municipal district heating with its own gas boiler room would actually reduce heating costs?
Do not approve a gas boiler room based only on the claimed PLN 4/m² or PLN 2.50/m² figures; recalculate the project from your own PEC invoices, including fuel, boiler efficiency, inspections, repairs, financing, future replacement and connection capacity. The required design must start from the actual peak demand—your ordered power is 0.854 MW—and verify available boiler-room space, chimney/flue arrangements and whether the gas network can supply the load. [#19644537] A boiler cascade with multiple units is technically typical because one boiler can continue operating if another fails, but the final investment cost can only be established after design and feasibility work. [#19644925] Heat allocators do not themselves reduce consumption; savings depend on changing residents’ behaviour, while poor hydraulic balancing, unsuitable or removed radiators and different apartment locations should be investigated first. [#19645482] The prudent first measures are to audit and balance the heating system and reduce the ordered district-heating power after thermomodernization, then compare the cost of the same delivered heat from gas with the complete ownership costs of the boiler room. [#19646519]
  • Correction factors criticized in area-based heating billing
    #31 19650559
    gimak
    Help: 614
    Rate: 1678
    adamlabedz wrote:
    It's hard to disagree with that, Grandma used to smoke in the stove until recently and none of the neighbors looked into her coal-cart,
    This is poorly defined - it should be in this case - none of the neighbors added it to the coal wagon,
    adamlabedz wrote:
    friends have individual gas heating in their block and no one looks at anyone's bills... Everyone looks after their own bills.
    Correction factors have no meaning when billing by area. I guess that's why they were invented, to muddy what is clear and transparent, especially since their values are taken from the ceiling, just like the share of heating costs in common areas.
    People are tossed with substitute topics, correction factors, cold neighbors, etc., and not why, for example, accounting for allocators raises so much controversy, but because for this you need some knowledge, imagination and willingness, and all this is missing and there is only such a justification for the dissatisfied and equally ignorant - spread your hands and say - that's how it turned out.
  • Individual gas heating now favored over boiler room
    #32 19657197
    adamlabedz
    Thank you all for your help and valuable feedback.
    We had another meeting yesterday on this topic, where the manager himself, after re-analysis, stated that the gas boiler room is out due to the negligible and questionable savings in relation to the value of the investment. The topic of allocators was also dropped due to general reluctance, so were heat meters - here the effect is similar to allocators and the cost is much higher. For now, we are reducing the ordered power and in the spring we return to the topic of modernization of the installation and here, to my surprise, a proposal to switch to individual gas heating was made and what is more, it was not bombarded after the first reading.
    I hope that in the spring nothing will change and the co-residents will positively approach the subject despite the much greater nuisance of the investment.
    I suspect the total cost will be a little higher than in the case of a boiler room, but the savings will be about 2-3 times.
  • #33 19657661
    gimak
    Help: 614
    Rate: 1678
    In the case of individual gas heating, not only the heating installation, but probably also the gas installation will have to be modified - increasing the cross-section of the pipes.
    Good luck.
  • #34 19657782
    Szyszkownik Kilkujadek
    Level 37  
    Help: 211
    Rate: 1014
    In addition, each apartment will have to have its own flue adapted to the gas boiler.
    In general, I would start with a feasibility study, especially from the formal and legal point of view.
  • Horizontal flue outlets can avoid chimney rework
    #35 19657796
    DiZMar
    Help: 2892
    Rate: 6652
    Not necessarily. This only applies to gravity boilers.
    Condensation air intake and exhaust can be several dozen cm behind the wall with a horizontal outlet just above the boiler without a pipe up. This is what I see in many cases now.
    gimak wrote:
    for rework ... probably, also gas installation - increasing pipe cross-sections
    There is no need. The gas supply tubes of a gas boiler are very thin. Thinner than any gas installation in a building.
    If the residents agree, they will hire one designer who will take care of all formal matters, and perhaps also one contractor, which will significantly reduce unit costs in bulk. With the current technology of processing and connecting heating to individual boilers, it will not cause many difficulties.
  • #36 19657808
    sylba
    Level 19  
    Help: 24
    Rate: 54
    DiZMar wrote:
    Condensing air intake and exhaust can be several dozen cm behind the wall with a horizontal outlet just above the boiler without a pipe up. This is what I see in many cases now.
    A block of flats, 45 flats, whether bright or dark kitchens are interesting - it can be a challenge.
  • #37 19657819
    DiZMar
    Help: 2892
    Rate: 6652
    Bright or dark kitchens are no problem. A small angle is enough to hang the boiler and above it 20-30 for the intake-exhaust pipe and an even smaller angle for an individual gas meter, if there is not one yet.
  • System heat often costs more than gas boiler rooms
    #38 19657870
    kris8888
    Help: 537
    Rate: 1930
    jdubowski wrote:
    In large cities, system heat is usually cheaper
    I would rather risk saying the opposite, system heat in large cities is usually more expensive. Due to the extensive heating network and heat energy losses occurring in it. These losses are covered by everyone using the network.
    System heat is largely an unavoidable and by-product of electricity production in a combined heat and power plant. This heat is generated anyway, regardless of whether it is needed or not, also in summer. It should be relatively cheap, unused and so it is wasted and unfortunately it is not cheap. I can see this after comparing the cost of heating m2 in a block connected to the network to a similar block heated from a local gas boiler house in my area.
    Of course, as already mentioned, there is also the cost of building, maintaining and repairing the local boiler house, which should be taken into account in the overall calculation.
  • Insulation cut heating costs by one third
    #39 19657954
    gimak
    Help: 614
    Rate: 1678
    Such a remark came to my mind, at the in-laws in the block, at the beginning there was heating with tiled stoves. When they were laying the gas installation, only my father-in-law decided to switch to gas heating (inserts for tile stoves) and only his apartment has a gas pipe, with a diameter approximately half that of the other apartments.
    After a few years, a heating network was connected to the block and a heating installation adapted to heat meters was installed in the block, but there were no such meters for several years, because the residents did not agree to it. Similarly, they did not agree, despite the manager's suggestion, to insulate the block, but they complained about the high heating costs.
    The block has been insulated for several years and heat meters have been installed. After insulating the block, heating costs fell by about 1/3 already in the first year after the insulation.
  • #40 19658331
    Level 37  
    Help: 211
    Rate: 1014
    In multi-family housing too? :-D
  • #41 20609707
    Setral
    Rate: 11
    I'm coming back to the idea of switching from district heating to gas. What is the current cost of heating a building with gas and with a district heating network? The annual demand for heat is approx. 1300 GJ. The price for 1 GJ is approx. PLN 123 gross.
  • Gas heating cost estimate from tariff and boiler efficiency
    #42 20610929
    jdubowski
    Tube devices specialist
    Help: 2511
    Rate: 2804
    Setral wrote:
    I'm coming back to the idea of switching from district heating to gas. What is the current cost of heating a building with gas and the heating network? The annual demand for heat is approx. 1300 GJ. The price for 1 GJ is approx. PLN 123 gross.
    https://www.farmer.pl/energia/pgnig-od-cena-z...owych-nie-wzrosnie-od-nowego-roku,126418.html :
    "The gas fuel tariff of PGNiG Obrót Detaliczny, approved by the President of the Energy Regulatory Office by decision of December 17th 2022, will be in force from January 1st 2023 to March 31st 2023. The price for gaseous fuel was set by the Energy Regulatory Office at less than PLN 650/MWh. The difference between the maximum price resulting from the above-mentioned act and the tariff for gaseous fuel for PGNiG Obrót Detaliczny approved by the President of the Energy Regulatory Office, will be covered by compensation paid to PGNiG Obrót Detaliczny from the Price Difference Payment Fund. subject to tariff protection, the maximum price of which will be PLN 200.17/MWh."
    1 MWh equals 3.6 GJ, so the above-mentioned prices are PLN 180/GJ and PLN 56/GJ. Now multiply it by the efficiency of the boiler and the cost of the loan for the construction of the boiler house.
  • PGNiG business gas prices suggest lower household tariff
    #43 20611190
    Wojewoda82
    Help: 118
    Rate: 392
    I wouldn't look at the current price from the tariff sent to us by PGNiG (which is off the charts, I think there was an update to PLN 0.51 in May), but I wouldn't look at the frozen price we pay as customers at the moment.
    Because the current price from the tariff is burdened, among others, with higher gas purchase prices last year, i.e. also with gas pumped to storage facilities at recently higher prices.
    There is also some inertia between the current gas market prices in Europe and prices for individual customers. The current tariff is a kind of subsidy for last year's unprofitable gas sales to households by PGNiG. And the surcharge comes from the taxes of everyone, including those who do not have gas.
    The price of kWh from gas for household tariffs is currently PLN 0.51 net, and the frozen tariff is PLN 0.20 net (that is over 2.5 times less) for the gas fuel alone, the transmission is less than PLN 0.4. Market gas prices have returned to those from before the gas blackmail.
    However, a good indicator of the real gas price that should be included in the individual tariff is the price for companies. And on March 15, it fell from 65gr to 35.3gr per kWh, at the start of 2023 it was almost 80gr. From May 1, less than 30.2 PLN/kWh
    https://www.e-hotelarz.pl/artykul/89556/pgnig-obniza-cene-gazu-dla-biznesu/
    https://www.muratorplus.pl/biznes/news-z-rynk...-kogo-czy-trzeba-zlozyc-wniosek-aa-JFSZ-f46o- 1imo.html
    So since PGNiG sells gas to companies for PLN 0.30, it actually buys it much cheaper.
    I think that ultimately, after frostbite, the price for individual customers will be between 30 and 40 PLN/kWh net with transmission.
  • Reducing ordered heating power and considering gas conversion
    #44 20611228
    vodiczka
    Help: 1185
    Rate: 4311
    sylba wrote:
    If the installation layout is difficult to measure, and the allocators raise a lot of doubts because they allow you to manipulate the indications, then the division of costs by area seems to be the most reasonable.
    Exactly, that's how it is with us and there was never a proposal to install allocators at a community meeting. Proper insulation and a good weather automaton controlling the node, taking into account not only air temperature but also wind strength, solve the problem.
    adamlabedz wrote:
    and some are indignant when the radiators are cold outside at +16C.
    our radiators are cold at +14°C, and if someone is too cold in the apartment, they warm up with a heater and do not jojczy.
    Earlier (after the modernization of the node) we set the heating switch-off to +12°C, but it was too little.
    Added after 14 [minutes]:
    Winters are getting lighter and the maximum power is not used with us and we currently have 80kWh for a four-story terraced house, insulated. From what I remember, the maximum power demand oscillates around 72 kWh. The usable area of all 14 apartments is approx. 1100m². Since the creation of the community in 2001, we have reduced the ordered power three times. The original was over 150 kWh.
  • #45 20611615
    Level 37  
    Help: 211
    Rate: 1014
    What is the annual savings?
  • #46 20611921
    vodiczka
    Help: 1185
    Rate: 4311
    I don't remember but the first reduction was high and significantly reduced bills, the next two are rather cosmetic.
  • Need gas connection conditions before planning heating
    #47 20613733
    W.Wojtek
    Phones specialist
    Help: 245
    Rate: 430
    So much writing and no specifics..
    Loose remarks.
    Is there room for a boiler room with a suitable chimney??? I doubt.
    Boiler room - several boilers in a cascade. As far as I remember, a boiler room with a capacity of more than 100 kW requires CONSTANT service!
    Individual boilers in apartments?? That is, a completely new installation of CO and CW in EVERY apartment at the expense and efforts of the resident??
    As far as I remember, the installation of gas boilers (regardless of whether condensing or with a closed combustion chamber) with one common chimney in multi-family housing in Poland is unacceptable!
    And, of course, chimney sweep reviews.
    And the most important thing!!!!!!!!!!!!! Will you get PGNiG's consent for such a huge gas consumption, or is the gas network adapted to such a need - practically a high-pressure gas pipeline.
    As far as I know, the issuance of NEW gas heating permits has been blocked (until the end of the PIS authority??)
    Start by asking if you will get permission from PGNiG for gas. Connection conditions, pressure and expected consumption. Peak and medium.
    So, stop beating old eggs and start with gassers and chimney sweeps.
    It would be reasonable to insulate the building and install heat meters (you have to redo the entire CO installation. Or the meter has every radiator. Allocators make no sense.
    And finally-
    Our community - a building of 800 m2 (8 units of about 100 m2 each) boiler room 2 atmospheric boilers, 49 kW each in a cascade.
    The whole "de novo" installation. Before that, either tiled coal-fired or small etagere with a boiler in the hall. Everyone has a heat meter. ZW and CW. Thermostats on radiators.
    Cost - costs of gas + electricity and inspections of the boiler room (pumps, etc.) / the number of GJ used, the price is 1 GJ. Separately, the cost of heating water is calculated in a similar way. In addition, we have CW heated by the sun. 8 panels, 2 m2 each. In hot weather, the cost of heating 1 m3 is about PLN 2..
    After the initial problems, the radiators do not heat! Check if you have heat in the apartment and not if the radiator is warm.
    Why do I pay some money and you pay half of it?? 'Cause I'm wearing a sweater and you're only wearing shorts.
    It helped. there is peace. It has been operating for 30 years
    WW chairman of the board of the community
Residents of two prefabricated apartment blocks heated by a municipal network are debating the feasibility of switching to individual gas boiler rooms versus continuing with the current system. The discussion highlights concerns over heating costs, individual comfort levels, and the potential for savings with gas heating. Some residents argue that municipal heating is generally more expensive due to maintenance and transmission losses, while others emphasize the need for thorough economic analysis before making any changes. The manager's proposal for gas boiler rooms was met with skepticism due to high initial investment costs and the complexity of installation. The community is considering reducing the ordered power from the municipal provider and exploring the possibility of individual gas heating, which may require significant modifications to existing infrastructure. The conversation also touches on the importance of heat meters and allocators for fair cost distribution among residents.
TL;DR: Average district heat in the thread costs 123 PLN / GJ while gas can be as low as 56 PLN / GJ [Elektroda, Setral, #20609707; Elekt...
• Ordered thermal power for the two 90-flat blocks: 0.854 MW [Elektroda, adamlabedz, post #19644576] • Draft cascade boiler house: 2 rooms × (3–4) condensing units ≈ 500 kPLN each [Elektroda, adamlabedz, post #19647240] • District-heat tariff quoted: 123 PLN / GJ (≈ 443 PLN / MWh) [Elektroda, Setral, post #20609707] • Protected gas ceiling: 200.17 PLN / MWh = 56 PLN / GJ [Elektroda, jdubowski, post #20610929] • Typical condensing boiler life: 10-15 years [Viessmann, 2023]
How much cheaper is gas versus district heat in mid-2023?
Using the current ceiling tariff, 56 PLN / GJ gas under a 92 % boiler gives 61 PLN / GJ delivered. That is about 50 % of the 123 PLN / GJ district rate quoted in the thread [Elektroda, Setral, #20609707; Elekt...
What budget must a 2-block community set aside for its own boiler house?
Forum costings show two cascaded rooms priced near 1 M PLN total (≈500 kPLN each) [Elektroda, adamlabedz, post #19647240] Add 10 % for design and 5 % for commissioning. A 5-year 6 % loan would mean ≈19 kPLN per month; the OP’s saving forecast was 15.4 kPLN, so cash-flow looks tight.
Is staying on municipal heat compulsory?
Polish Energy Law allows disconnection if safety, emissions and neighbourhood plans are met. “Someone somewhere whispered” that mandatory connection exists, but contributors called it “just farts” [Elektroda, misiek1111, #19646064; DiZMar, #19646095]. Always obtain written conditions from the local utility and municipality.
What space and chimney rules apply to a shared gas boiler room?
• Dedicated room with fire-rating EI 60 and floor drain. • Separate access route—no flats above according to PN-B-02411. • Flue sized for full cascade; stainless insert often needed in old shafts [Elektroda, vojtas1985, post #19644925] • >100 kW rooms require permanent on-site or contracted 24 / 7 service [W.Wojtek, #20613733].
How much can reducing ordered power save?
One 1,100 m² block cut power thrice—from >150 kW to 80 kW—and saw the first reduction “significantly” lower bills [Elektroda, vodiczka, post #20611228] Savings depend on the utility’s capacity charge, typically 15-25 % of the annual bill [URE, 2022].
Does insulation really cut communal bills?
After façade retrofit, one block’s charge dropped from 3 PLN / m² to 2 PLN / m² (-33 %) even before meters were fitted [Elektroda, gimak, post #19657954] Energy audits predict 15-40 % savings for 1970s slabs [KAPE, 2022].
How can a community estimate required boiler size from old invoices?
  1. Locate the coldest billing month and its GJ figure. 2. Divide GJ by 0.277 to get MWh, then by hours in the month to obtain average load. 3. Multiply by 1.3 for safety margin. “Read the PEC invoices from when the frost was crackling” [Elektroda, jdubowski, post #19644537]
Why does district heat include CO₂ costs?
CHP plants surrender EU ETS allowances; 2023 certificates trade near 90 € / t. Utilities allocate this to tariffs, raising city heat prices [Szyszkownik Kilkujadek, #19646719]. Small building boiler rooms under 20 MW avoid ETS, so their gas price lacks direct CO₂ surcharge.
Edge case: what if gas again spikes to 2022 levels?
At 300 PLN / MWh wholesale (≈83 PLN / GJ), delivered gas could exceed current district heat. The community must model worst-case prices and maintain dual-fuel clauses or return-to-grid option, as oil-switchers learned after 2000 price hikes [Elektroda, Inkwizycja, post #19645082]
How often must a >100 kW boiler room be serviced?
Polish Reg. Dz.U. 2019-E0027 requires quarterly checks and annual full maintenance. W.Wojtek notes continuous attendance if capacity exceeds 100 kW, though many firms subcontract 24 / 7 monitoring [Elektroda, W.Wojtek, post #20613733]
Can horizontal concentric flues be used in multi-family buildings?
Yes for sealed-chamber or condensing units ≤21 kW, if the terminal is ≥0.5 m from openings and local zoning allows; however, large-scale use may pepper façades and is often refused by architects [Elektroda, DiZMar, #19657796; Szyszkownik Kilkujadek, #19658331].
Are there financing programmes for community energy upgrades?
Poland’s BGK Thermo-Modernisation bonus refunds 16 % of eligible costs if 25 % energy savings are achieved [BGK, 2023]. The OP’s projected 1 M PLN boiler room could reclaim 160 kPLN, improving payback to under six years at today’s price gap.