  • Tasmota relay grouping limited to one relay

    #1 21399257
    Pete0815
    Level 7  
    Posts: 34
    Help: 1
    Rate: 3
    Hello

    hope it’s ok to ask for some Tasmota help/ideas.

    Guess everybody knows e.g. the 4ch relay boards available and I like to combine 3 relays at such a board to act as 1 relay for e.g. a 3 phase (3x230V) consumer.

    So 3 relays should be switched on/off always synchronised by one gui button or one command sent by mqtt.

    I searched for a solution and seems that grouping is a method for this, but the documentation says that only 1 relay can be involved in a device group.

    So I tried to map 3 gpios to one relay but this does not work.

    Kindly ask for your help
    Kind regards and big thanks
    Screenshot of Tasmota settings for a 4-channel relay
  • ADVERTISEMENT
  • Rules suggested to mirror one relay to the others

    #2 21399378
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14796
    Help: 659
    Rate: 12953
    Are you really sure that having 3 Relay entries with index "1" does not work? That's strange...

    Added after 3 [minutes]:

    EDIT: It seems you are right! It only toggles one relay:
    Tasmota interface with GPIO settings for a Sonoff Basic module.

    Ok it seems we need to use rules?

    Added after 2 [minutes]:

    Probably Rules can help?
    https://tasmota.github.io/docs/Rules
    Do something like, when switch 1 is on, turn on switch 2 and switch 3. If switch 1 is off, turn off them...
    Helpful post? Buy me a coffee.
  • ADVERTISEMENT
  • Questions rule reliability for relay synchronization

    #3 21399448
    Pete0815
    Level 7  
    Posts: 34
    Help: 1
    Rate: 3
    Thanks for your help.
    Do you think that rules are fast and reliable enough for this purpose?
    I´m struggling because rules are based on triggers. Just in case one relay becomes different because of boot state or sth like this, this is not synchronized by a rule until a state change of any relay, right?

    Guess I have to create rules triggered for the state ON of each relay and rules triggered for the state Off of each relay, right?

    I also had a look at the interlock function which is available for shutters. Guess that it is possible to put 3 relays into this interlock group but of course the function of an interlock is different. But from the general idea of usage very similar. So sth not like an interlock more like a sync group would be great but seems not to be available :(
  • ADVERTISEMENT
  • #4 21400215
    ferbulous
    Level 18  
    Posts: 419
    Help: 8
    Rate: 56
    Device group is for linking with other tasmota devices.
    You could use rules with backlog for it

    Something like this

    Rule1
    on power1#state=1 do backlog power2 1;power3 1 endon
    on power1#state=0 do backlog power2 0;power3 0 endon
  • ADVERTISEMENT
  • Helpful post
    #5 21400365
    TvWidget
    Level 39  
    Posts: 4429
    Help: 472
    Rate: 700
    3-phase appliances tend to draw a lot of current. Perhaps the solution would be to use a 3-phase contactor externally.
    Alternatively, you could rework the board and connect three relays to one output.
    There are devices that are sensitive to missing one phase for a long time. For this reason, controlling 3 independent channels is not a very good solution.
  • Tasmota relay rules can loop into endless toggling

    #6 21402019
    Pete0815
    Level 7  
    Posts: 34
    Help: 1
    Rate: 3
    Thank you very much and you are right. I have to test if this is really sth. to be used in practical application.

    As you can see the result is clearly sequential and not in parallel, so this should not be a problem for the 3phase device:

    https://streamable.com/fqlur3

    In addition I added for the gui operation to this:

    Rule2
    on power1#state=1 do backlog power2 1;power3 1 endon
    on power1#state=0 do backlog power2 0;power3 0 endon
    on power2#state=1 do backlog power1 1;power3 1 endon
    on power2#state=0 do backlog power1 0;power3 0 endon
    on power3#state=1 do backlog power1 1;power2 1 endon
    on power3#state=0 do backlog power1 0;power2 0 endon
    Rule2 1

    But it’s possible due to rule execution time and by fast button usage that the rule has not finished the last execution and the result is an endless sequence of relay/light on/off in various combinations.

    Only way to stop this is a power shutdown and reboot. In case of a connected 3phase device such behavior is of course unacceptable....