Single Phase 200A Electric Meter Burnt Out on 3-Phase 230V Supply, 30A Load

318 10
Best answers LABEL_AI_GENERATED

Why would a 200A single-phase meter burn out repeatedly on a 30A load connected to a 230V three-phase, three-wire supply?

The meter/base setup is likely not suitable as connected: a small single-phase meter like this is unlikely to be usable directly at 200A or even 30A, and it may need CTs to reduce the input current to 1A or 5A instead [#21684952] The exact meter specification matters, so the nameplate or photo should be checked to confirm whether it is a self-contained meter or a CT-operated setup [#21684954]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
  • Suspected supply fluctuation causing meter burnout

    #1 21684946
    MARWIN GUILLENA
    Anonymous  
  • ADVERTISEMENT
  • #2 21684947
    Alan Gallagher
    Anonymous  
  • Line-to-line 230 V likely burned the single-phase meter

    #3 21684948
    MARWIN GUILLENA
    Anonymous  
  • ADVERTISEMENT
  • Line-to-line 230 V likely caused meter burnout

    #4 21684949
    MARWIN GUILLENA
    Anonymous  
  • ADVERTISEMENT
  • #5 21684950
    Alan Gallagher
    Anonymous  
  • #6 21684951
    MARWIN GUILLENA
    Anonymous  
  • #7 21684952
    Alan Gallagher
    Anonymous  
  • #8 21684953
    MARWIN GUILLENA
    Anonymous  
  • #9 21684954
    Alan Gallagher
    Anonymous  
  • ADVERTISEMENT
  • #10 21684955
    Alan Gallagher
    Anonymous  
  • Single-phase smart meter functions and AMI connectivity

    #11 21684956
    jessewalter375
    Anonymous  

Topic summary

LABEL_AI_GENERATED
A single-phase GE KV2C class 200 electric meter rated for 200A was installed on a 3-phase 3-wire supply with a line-to-line voltage of 230V and a maximum load of 30A. Despite proper installation with tight terminals and a new 200A 5-jaw meter base, the meter and base repeatedly burnt out after several months of use. The supply voltage is 115V phase-to-ground, but the meter is connected across the 230V line-to-line voltage. The meter is self-contained without current transformers (CTs). Concerns were raised about the suitability of a small self-contained meter for this application, as such meters typically require CTs to reduce current input to 1 or 5 amps for accurate and safe operation. The issue may stem from improper meter selection or connection to a 3-phase supply using a single-phase meter rated for different voltage conditions, potentially causing meter damage due to voltage or current mismatches.
AI summary based on the discussion. May contain errors.