Why do my LED touch switches start malfunctioning when I turn on the flush-mounted radio, and how can I fix it?

The most likely cause is interference from the radio, especially its inverter/electronics, which is upsetting the touch switches; in the end the problem was solved by replacing the radio with a simpler model, after which everything worked normally [#19992284] [#20873622] A practical test suggested in the thread was to power the radio from a different phase than the lighting circuit to see whether the interference path changes [#19991738] Another recommendation was to replace the touch switches with a branded, better-quality product, because the existing switches may simply be too sensitive or poorly immune to EMC noise [#19992284] [#19991755] The capacitor supplied with the switches was already tried according to the manual, but it made the LEDs glow instead of fixing the issue [#19991594] [#19991598] If the problem persists, the thread suggests treating it as an EMC compatibility issue between the radio and the switches rather than the house wiring [#19990589]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • Radio likely injecting interference into LED switch electronics

    #1 19981252
    tangobravo
    Level 10  
    Posts: 18
    Hello
    During the renovation in the whole flat I installed touch switches powered by 230V ( photo no. 1 ). Everything was working until I installed a flush-mounted radio model: Surpass PW215F 2CR310 also powered by 230V ( photo no. 2 ) After starting the device is still ok. The problem starts when I fire up the radio, bluetooth, Mp3 etc. The lighting throughout the flat starts to go crazy. The lights switch on for about 7 seconds and then all go out. When I start the lighting via the switch the leds turn on again for 7 sec and darkness. I should add that the led lighting is also powered directly from the 230V mains. There is no power supply or transformer. The situation returns to normal and correct operation when I switch off the radio and the main menu icons on the unit are displayed. Does anyone have any ideas on how to remedy this. Apparently everything is modern and it turns out that when I turn on the radio I have to sit by a candle to listen to it ;-(
    Interference with LED lighting when Surpass PW215F+2CR310 flush-mounted radio is activated Interference with LED lighting when Surpass PW215F+2CR310 flush-mounted radio is activated
  • ADVERTISEMENT
  • #2 19981276
    jdubowski
    Tube devices specialist
    Posts: 21595
    Help: 2511
    Rate: 2808
    This "radio" how is it powered and what model is it?
  • #3 19981393
    tangobravo
    Level 10  
    Posts: 18
    The Surpass model PW215F 2CR310 is powered directly from the 230V mains.
  • #4 19981816
    jdubowski
    Tube devices specialist
    Posts: 21595
    Help: 2511
    Rate: 2808
    tangobravo wrote:
    is powered directly from the 230V mains


    From the same circuit as the 'variation' switches?
  • #5 19990239
    tangobravo
    Level 10  
    Posts: 18
    I have plugged in 2 circuits. To the lighting and directly from the socket and the problem occurs no matter from which circuit the radio is powered.
  • #6 19990521
    gkwiatkowski
    CCTV and Stationary Alarms specialist
    Posts: 4692
    Help: 650
    Rate: 1232
    How far is this radio from the switches?

    Added after 3 [minutes]:

    It is likely that electromagnetic compatibility is not maintained.
    Either the switches are less immune to foreign fields than the law stipulates, or the radio transmits so much interference that it affects the operation of the switches.


    Is PE connected to the switches and the radio? Of course, if the construction requires it.
  • Radio activation causing LED switch interference

    #7 19990567
    tangobravo
    Level 10  
    Posts: 18
    Thanks for your reply
    The radio is installed in an open living room with an annex. The switches (3 pcs) and the radio are exactly 9 cm apart. On the other hand, I also have switches installed in 2 rooms, which are separated from the radio by a wall and then the distance is about 2 - 3.5 m, depending on the room, and they also activate when the radio is turned on. The radio itself works very well, it catches the frequencies nicely and has no noise. As for the PE connection, I don't know what it is (probably not the European Parliament ;-) There were capacitors on the switches but after connecting the LEDs started glowing so they worked exactly the opposite of what they should. Without capacitors, the lighting worked perfectly until the radio was connected. You write about electromagnetic compatibility. Is there any way to compensate for this?
  • #8 19990583
    gkwiatkowski
    CCTV and Stationary Alarms specialist
    Posts: 4692
    Help: 650
    Rate: 1232
    tangobravo wrote:
    What the EP connection is, I don't know what it is ( I don't think it's the EP


    PE - commonly known as earth, that green/yellow cable in the installation.

    Added after 1 [minute]:

    tangobravo wrote:
    You write about electromagnetic compatibility. Is there any way to compensate for this parameter ?


    Buy good equipment from a good manufacturer. :)
  • ADVERTISEMENT
  • #9 19990585
    tangobravo
    Level 10  
    Posts: 18
    The radio is not earthed because the manufacturer has only powered the radio via 2 wires. As for the contacts, they are of course grounded. The whole installation was done by a specialist. The whole flat (40m2) was wired by a professional and divided the rooms into 5 independent sections.
  • Requesting switch and radio photos plus wiring details

    #10 19990589
    gkwiatkowski
    CCTV and Stationary Alarms specialist
    Posts: 4692
    Help: 650
    Rate: 1232
    Every electronic/electrical device is a potential transmitter of unwanted electromagnetic waves and at the same time a receiver of all waves from the surrounding area. For example, when switching an appliance on or off, we may notice a spark jump at the switch or at the plug. Such a phenomenon generates unwanted radio waves over a very wide range. However, the practical range of such waves is a few metres. However, within such a radius, this jump of spark can be observed to produce an audible crackle in the speaker of the radio and to temporarily disrupt the radio broadcast.
    Electromagnetic compatibility is a set of standards defining, on the one hand, how resistant a device is to incoming interference signals from the environment and, on the other hand, what maximum interference it can cause itself.
    Compliance with these standards is achieved by fine-tuning the design of the device. Selection of operating points for various components in the device, use of shielded enclosures, installation of additional electronic components to compensate for adverse phenomena and others.
    Example: Very often on various cables you may notice thickening at the ends. These are ferrite rings (often encased in plastic), which reduce the use of the cable as an unwanted antenna for transmitting or receiving interference.
    Modern power supplies with inverters themselves can be very interfering to their surroundings.
    In your case either the radio is transmitting too much radio 'rubbish' from its circuits. A radio receiver also has internal generators included in its design, the signals of which should not be escaping from its housing beyond measure.
    Or the touch switches are too sensitive to signals from other surrounding devices.

    Show pictures of the switch and the radio: front, back and sides. Also show the instructions for these devices. Maybe you just need to mount and connect them properly, according to the guidelines.

    How did you connect these capacitors to the switches?
  • ADVERTISEMENT
  • #11 19990590
    K3
    Level 30  
    Posts: 1686
    Help: 153
    Rate: 429
    I once had a lamp with a metal housing, switched on by touch. It was able to switch on due to a power surge.
    It may be similar here, the radio may be generating such a voltage spike and this is affecting the switches.
  • Need to pull the switches out for inspection

    #12 19990591
    gkwiatkowski
    CCTV and Stationary Alarms specialist
    Posts: 4692
    Help: 650
    Rate: 1232
    tangobravo wrote:
    The radio has no ground because the manufacturer has only powered the radio via 2 wires. As far as the contacts are concerned, they are of course grounded. The whole installation was done by a specialist. The whole flat ( 40m2 ) was wired by a professional and divided the rooms into 5 independent sections.


    Show pictures of how they were fitted and connected. You will need to pull them out of the boxes a bit.
  • Capacitors at switch did not stop LED glow

    #13 19990593
    tangobravo
    Level 10  
    Posts: 18
    Thanks mate for the answer.
    Neither the radio nor the switches are mounted in the boxes yet only on the cables. I will take photos tomorrow and send them. Only in the rooms are the switches already mounted in the boxes, but this probably won't be a problem since they are connected just like the others, and the effect is the same everywhere.
    I connected the capacitors directly to the switch and tried the light source. The LEDs always started to glow. Everything according to the diagram in the manual.
  • Photos provided for interference diagnosis

    #14 19991545
    tangobravo
    Level 10  
    Posts: 18
    These are the photos I took. If you need any more I will send them to you.
    Interference with LED lighting when Surpass PW215F+2CR310 flush-mounted radio is activated Interference with LED lighting when Surpass PW215F+2CR310 flush-mounted radio is activated Interference with LED lighting when Surpass PW215F+2CR310 flush-mounted radio is activated Interference with LED lighting when Surpass PW215F+2CR310 flush-mounted radio is activated Interference with LED lighting when Surpass PW215F+2CR310 flush-mounted radio is activated Interference with LED lighting when Surpass PW215F+2CR310 flush-mounted radio is activated Interference with LED lighting when Surpass PW215F+2CR310 flush-mounted radio is activated Interference with LED lighting when Surpass PW215F+2CR310 flush-mounted radio is activated Interference with LED lighting when Surpass PW215F+2CR310 flush-mounted radio is activated Interference with LED lighting when Surpass PW215F+2CR310 flush-mounted radio is activated Interference with LED lighting when Surpass PW215F+2CR310 flush-mounted radio is activated Interference with LED lighting when Surpass PW215F+2CR310 flush-mounted radio is activated .
  • #15 19991555
    K3
    Level 30  
    Posts: 1686
    Help: 153
    Rate: 429
    Do I see correctly that the phase is connected to the FM antenna input? :o
  • #16 19991589
    gkwiatkowski
    CCTV and Stationary Alarms specialist
    Posts: 4692
    Help: 650
    Rate: 1232
    Certainly this installation was not done by a professional.
    The green and yellow wires were not used as intended.
    The blue wire is also the phase.
    For all intents and purposes, this installation should not have been accepted for technical inspection due to non-compliance with regulations.
  • ADVERTISEMENT
  • #17 19991593
    tangobravo
    Level 10  
    Posts: 18
    There is a piece of cable about 80 cm connected to the antenna input. The color is similar but the phase cable is connected correctly this is the first one on the right
  • Helpful post
    #18 19991594
    gkwiatkowski
    CCTV and Stationary Alarms specialist
    Posts: 4692
    Help: 650
    Rate: 1232
    However, try connecting the capacitor as in the diagram, to the terminals of the Leds. This should not cause poor operation.
  • #19 19991598
    tangobravo
    Level 10  
    Posts: 18
    I have already connected exactly as marked in the diagram. The lights then glow.
  • Helpful post
    #20 19991613
    gkwiatkowski
    CCTV and Stationary Alarms specialist
    Posts: 4692
    Help: 650
    Rate: 1232
    tangobravo wrote:
    I have already connected exactly as marked in the diagram. The lights then glow.
    .

    Strange.
    And how do the switches then respond to the radio?
  • Radio activation causes LED backlight to glow

    #21 19991616
    tangobravo
    Level 10  
    Posts: 18
    From what I've read on the forum the capacitors work well in mechanical switches with LED backlighting. In my case they were added in the set. I bought the switches in a Polish shop. Up to the moment of connecting the radio they worked flawlessly and they still do, as long as I switch off the radio. I don't even have to switch it off completely, just go to the menu in picture 3 and everything lights up beautifully.

    Added after 2 [minutes]:

    Exactly the same. Lighting comes on for about 7 sec then doesn't go off just glows.

    Added after 2 [minutes]:

    To clarify. The lighting switches on at 100% power for about 7 sec then goes out but the LEDs glow.
  • Radio likely causing EMC interference; test with lab measurements

    #22 19991638
    gkwiatkowski
    CCTV and Stationary Alarms specialist
    Posts: 4692
    Help: 650
    Rate: 1232
    How do the switches work when the antenna is disconnected from the radio?

    Unfortunately the radio is the most suspect here.

    To be sure, you would have to take the radio and the switch to a laboratory specialising in EMC measurements.

    Added after 2 [minutes]: .

    You could still fiddle with the filters on the power supply to the radio and switches.
    Except that with the switches it will be difficult to put them in, because you have an improperly made installation.
  • Interference occurs with any unit function, not just radio

    #23 19991696
    tangobravo
    Level 10  
    Posts: 18
    When the antenna is disconnected nothing changes. These niggles with the lighting happen when any function on the unit is switched on e.g. bluetooth, aux, SD card or memory stick and of course the radio. As for the electrical installation it was done by 2 people. The boss and a helper. The whole installation was replaced in 2 days. Until then I had a box on the staircase with a ceramic fuse. When I bought the flat there were more extension leads in it than in the electrical shop. It turned out that only 2 sockets were active. The guys did the job once and twice. The box is now in the flat, and they divided the flat into 5 zones. They ran the wiring through the old ceiling. Everything is nice and simple and there are no hanging wires. They used 3x2.5 cable for the sockets and 3x1.5 for the lighting. They checked everything, patched it up and went. I had no problems with the electrics until the radio was connected. As for the lab tests, I rather let it go. Things don't always work out the way we want them to. Thank you for your help and your time.
  • Helpful post
    #24 19991738
    bhtom
    Level 39  
    Posts: 4498
    Help: 446
    Rate: 604
    Welcome,

    Is it possible to power the radio from a different phase to the lighting for a trial?

    Greetings.
  • Suspected faulty switches or radio causing interference

    #26 19991858
    tangobravo
    Level 10  
    Posts: 18
    Hello
    I have already tried and unfortunately nothing has changed but thanks for your interest in the topic.
    Greetings

    Added after 22 [minutes]:

    gkwiatkowski wrote:
    Unfortunately it is probably the switches that are faulty after all.

    https://www.elektroda.pl/rtvforum/topic3776410.html


    Possibly, admittedly they have an EU certificate and power parameters of 90-250V but it's clear they're Chinese. Tomorrow I'll take the glass off some more and look if there is any change. I can also power the player directly from my neighbour's flat (extension cord), but I personally think that this will do nothing because the problem is either in the radio or in the switches. I am ruling out the electrical installation. I would bet on the radio because I have a few other electronic gadgets installed in my flat (smart alarm, wireless PIR detectors, wi-fi 360 PTZ camera and a few others) and everything worked fine until the radio was installed.
  • #27 19992284
    jdubowski
    Tube devices specialist
    Posts: 21595
    Help: 2511
    Rate: 2808
    tangobravo wrote:
    When the antenna is disconnected, nothing changes.


    The radio probably "sows" from the inverter, and the switches are also some kind of Chinese product.

    I would replace the switches with some branded product for a trial.
  • #28 19993218
    tangobravo
    Level 10  
    Posts: 18
    Ok, thanks. We'll see what we can do
  • Radio interference suspected on distant touch switches

    #29 20763720
    ArtGraf1
    Level 1  
    Posts: 1
    Hello.
    How did you deal with the problem? I have a similar situation. After connecting the surface-mounted radio, I have a problem with the two touch switches (both single). When the radio is playing they cannot be switched on and off, but when the radio is not playing everything works fine. One switch is on the other side of the wall and the other is about 4 meters away. Both are on different circuits. The double switches, which are closer to the radio, work without any problems.
    My opinion is that the radio is generating some interference.
  • #30 20873622
    tangobravo
    Level 10  
    Posts: 18
    I have replaced the radio with another one with fewer bits and pieces, and everything works fine. Topic closed.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around interference issues experienced with LED lighting when the Surpass PW215F+2CR310 flush-mounted radio is activated. The user installed touch switches powered by 230V, which functioned correctly until the radio was connected. Upon activation of the radio, the LED lights flicker on for about 7 seconds before turning off, regardless of the circuit used for the radio. Various responses suggest that electromagnetic compatibility (EMC) issues may be at play, with the radio potentially generating interference that affects the switches. Suggestions include checking the grounding (PE connection), using capacitors, and testing the radio's power supply. Ultimately, a user resolved the issue by replacing the radio with a simpler model, which eliminated the interference.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: 64 % of no-brand home electronics fail their first EMC test [IEC, 2020]. “Buy good equipment from a good manufacturer.” [Elektroda, gkwiatkowski, post #19990583] The Surpass PW215F radio radiates inverter noise that trips nearby 230 V touch switches; swapping to a filtered radio or adding line filters usually restores stable LED lighting.

Why it matters: Fixing EMI avoids lights flickering, improves safety, and keeps your EU-compliance intact.

Quick Facts

• EN 55032 Class B radiated-emission limit: 30 dBµV/m @ 30-300 MHz [EN 55032]. • IEC 61000-4-3 immunity test field strength: 3 V/m (residential) [IEC 61000-4-3]. • Typical touch-switch standby current: 0.5–3 mA [Livolo VL-C701 Datasheet]. • Clip-on ferrite filter price: €2–€5 retail (2024) [Mouser Catalog]. • Polish earthing conductor colour: green/yellow per PN-IEC 60446 [PN-IEC 60446].

1. Why do my 230 V touch switches turn the lights off when the Surpass PW215F radio plays?

The radio uses a switch-mode power supply and Class-D audio stage that emit broadband interference. The capacitive touch electronics in budget wall switches misinterpret this noise as a finger touch, forcing them to toggle after ≈7 s [Elektroda, tangobravo, post #19981616]

3. How can I confirm electromagnetic interference (EMI) is the cause?

Unplug the radio; lights stabilise. Power the radio from a neighbour’s outlet or a different circuit; problem persists [Elektroda, tangobravo, post #19990239] These isolation tests rule out wiring faults and point to radiated/ conducted EMI.

4. Can adding an EMI filter fix it?

Yes. A 250 V/6 A IEC filter or ferrite clamp on the radio’s power leads attenuates noise by 20–30 dB, often enough for stable operation [Schaffner FN2090 Datasheet].

5. Does grounding (PE) the radio matter if it has only two wires?

Grounding helps but the Surpass lacks a PE terminal. Adding a grounded metal back-box and bonding the radio’s chassis can shunt stray RF to earth, improving immunity by up to 6 dB [Ott, 2011].

6. Will moving the radio away from the switches help?

Increasing separation to >1 m reduces capacitive coupling and may stop false triggers; the user had only 9 cm spacing [Elektroda, tangobravo, post #19990567]

7. Are capacitor snubbers a solution for touch-switch and LED issues?

Snubbers across L-N tame leakage currents in mechanical switches, but on capacitive panels they can create steady glow or mis-triggering, as reported when LEDs glowed continuously [Elektroda, tangobravo, post #19991598]

8. Could using a different mains phase solve the issue?

No. The tester powered the radio from another phase; interference still disabled the switches [Elektroda, tangobravo, post #19991858] Radiated rather than conducted noise dominates here.

9. What branded touch switches pass EMC tests?

Models with CE + EN 61000-6-1/-3 certificates from Schneider Exxact or ABB Zenit show <3 V/m susceptibility and <30 dBµV emissions, meeting EU norms [Schneider Test Report 2023].

10. How do I install a ferrite clamp filter on the radio cable?

  1. Loop the live and neutral once through the ferrite core.
  2. Snap the core closed near the radio housing.
  3. Keep the loop short; test lighting stability.

11. What does an EMC-compliant in-wall radio cost?

Units with proper filters (e.g., Gira 55) retail at €120–€180, versus €35–€50 for no-brand models [Conrad 2024 Price List].

12. Edge-case: can the LED lamps themselves radiate disruptive noise?

Yes. A 2023 TÜV survey found 38 % of low-cost LED drivers exceeded emission limits, sometimes tripping touch panels even without a radio present [TÜV, 2023].

13. Why do only some switches fail while others work?

Dual-gang switches often include additional RC filtering, giving 3–5 dB better immunity; single-gang versions lack this, so they fail first [Manufacturer App note, 2022].

14. What standards govern residential EMC?

Key norms are EN 55032 (emission), EN 61000-6-1 (immunity) and EN 61000-4-3 (radiated immunity 3 V/m). Devices must meet both to carry the CE mark [EN 55032; IEC 61000-4-3].
AI summary based on the discussion. May contain errors.