Remote differential switching - how to do it? Methods and equipment.
palmus 2223 20
How can I remotely detect that an RCD has tripped and switch it back on while I am away, for a few critical appliances like fridges and a boiler?
The practical options are an off-the-shelf automatic RCD recloser and, preferably, remote alarm/monitoring rather than blindly restoring power after a trip [#20668750][#20669982] One suggestion is to use an auxiliary contact on the RCD or breaker so a GSM/Arduino setup can send an SMS when the protected circuit loses power [#20670019][#20670008] Another recommendation is to split the fridge/boiler circuits onto separate RCDs so a fault on some other circuit does not take the critical loads offline [#20669982] Several replies warn that automatically re-energizing a tripped RCD can be unsafe if there is a real leakage or short circuit, so the cause should be found and eliminated rather than bypassed [#20669982][#20670391]
  • Remote breaker reset without manual intervention
    #1 20668714
    palmus
    Help: 233
    Rate: 752
    I had this situation happen to me. Just before going on holiday the differential fell down. Luckily not 3 hours later.There are strategic appliances hanging on it: 2 fridges and a central heating boiler.
    It is difficult to say what the reason was, it happened maybe 2 times in 4 years. I thought of a way to inform remotely about the situation, but more importantly to switch it on again but not with the finger of the absentees.
    Anybody has any idea how to solve this?
  • #2 20668734
    hindoos
    Level 36  
    Help: 290
    Rate: 663
    Re-engagement can be done with a phone call to a family member or neighbour with the keys to our house :)
  • #4 20668783
    Adam-T
    Help: 834
    Rate: 1096
    78db78 wrote:
    I used to stock such a vending machine
    And interestingly there are these machines for sale on a regular basis (a colleague gave a link to an archive auction) ;)
  • #5 20668878
    palmus
    Help: 233
    Rate: 752
    Not a bad idea, but I would have to change the switchgear because it's already cramped and this one is probably 2-3 modular.
    In the meantime, I found something like this ( Tuya). The question is whether it has enough power...
    Remote differential switching - how to do it? Methods and equipment. .
  • #6 20669145
    78db78
    Help: 1814
    Rate: 3282
    >>20668783
    this was an example of a device
  • #7 20669157
    palmus
    Help: 233
    Rate: 752
    Yes yes, I am still looking for something like that.
  • #8 20669684
    Strumien swiadomosci swia
    Help: 1405
    Rate: 6428
    Now get an electrician to take measurements and find out what is causing the switch to malfunction !!!!!!!!!!!!!!!!!!!!!!!!!
  • #9 20669716
    palmus
    Help: 233
    Rate: 752
    This is not what I asked. Diagnosis takes time.
    An attachment to the differentiator costs over 1000zl.I probably won't give that much.
  • #10 20669813
    Baskhaal
    Help: 22
    Rate: 182
    Somehow, my pineal gland was pricked and a thought occurred to me - since the differential has tripped is it a good idea to switch it back on without supervision/control/presence? All in all, it's a safety apparatus for a reason
    Apparently nothing but .... somehow a slight uneasiness sets in.
  • #11 20669818
    hindoos
    Level 36  
    Help: 290
    Rate: 663
    That is why, in post #2, I suggested a cheap and safe temporary solution to the problem :)
  • #12 20669874
    palmus
    Help: 233
    Rate: 752
    But I need to know that the differentiator worked.
    I see that the Chinese have electronic.To short-circuit in Tuya Zigbee.
    I will just check their reliability.
  • Separate RCDs are safer than remote reset
    #13 20669982
    Ktoś_tam
    Level 40  
    Help: 505
    Rate: 2903
    palmus wrote:
    But I need to know that the differential worked.
    I'll just check their reliability.
    I still make myself an overcurrent circuit breaker so that it automatically turns on by itself. The differential will not always disconnect the circuit, sometimes an overcurrent circuit breaker will. But why complicate matters? If the RCD is supposed to switch on as it goes off regardless of the reason for the switch off then maybe bypass it, so do the same with the overcurrent circuit breaker, especially as they can't always be lifted? Of course this is such a joke
    Seriously your idea is of the silly kind. You can't always turn it back on if there's a leak or short circuit and then what? Your plan will go...
    Let me guess, you have 1 RCD for the whole thing? Even if you don't, it's much more sensible to protect sensitive circuits with separate RCDs, then flooding a circuit outdoors/field won't cause the fridge to switch off. It's so simple, reliable and functional, but no, it's better to put in a prosthesis which may not work anyway.
    Fuses very rarely switch off without reason.
  • #14 20670008
    hindoos
    Level 36  
    Help: 290
    Rate: 663
    palmus wrote:
    But I need to know that the differential tripped.
    SMS notification implemented on Arduino + GSM module via relay which will let off as the power goes out in the socket with the fridge.
  • Auxiliary contact on breaker for Zigbee monitoring
    #15 20670019
    Adam-T
    Help: 834
    Rate: 1096
    hindoos wrote:
    through a relay which will let go when the power goes out
    And if the power goes out from the utility will there be a notification too? ;)
    Instead of a relay, add an auxiliary contact to the differential or fuse, depending on what is to be monitored.
    palmus wrote:
    To be wired in Tuya Zigbee.
    Is this a differential only for the kitchen or for the whole flat? Because if the whole flat then I'm guessing the internet will be gone too....
  • #16 20670025
    hindoos
    Level 36  
    Help: 290
    Rate: 663
    Adam-T wrote:
    And if the power supply disappears will there be a notification too?
    Powering the Arduino from the battery, it's quite obvious :) in principle it could simply switch on after a power outage and immediately after logging on to the GSM network send an SMS notification, the problem with the module hanging up would be eliminated.
  • #17 20670029
    Adam-T
    Help: 834
    Rate: 1096
    You misunderstood me, I meant the notification (redundant) after a mains power failure. ;) .
  • #18 20670038
    hindoos
    Level 36  
    Help: 290
    Rate: 663
    In my opinion, even if the entire power grid is down, this information is as sensible and useful as possible :) all the more so if the power goes down for a longer period of time and thaws (and then re-freezes in our absence) our food - a potentially health-threatening situation. You could say it's such an extra feature ;) .
  • #19 20670391
    Help: 1405
    Rate: 6428
    The whole topic going in the direction of powdering the syph, heading for the bin.... This is not what we do. If the RCD is working, there is a cause and it must be found and eliminated....
  • RCDs can fail and must be tested
    #20 20671038
    pikarel
    Help: 410
    Rate: 1848
    Strumien swiadomosci swia wrote:
    The whole subject going to powder syph, heading for the bin.... This is not how we do things. If the RCD is working then there is a cause and it must be found and eliminated....
    .... including the possibility that the RCD itself may be allowed to fail, just like any other product containing electronics inside.
    Unless I am unaware of something, that e.g. the EU and other sentient beings have recognised the RCD as perpetually working - then there is no need.
  • Differential should only protect kitchen and cellar
    #21 20671049
    palmus
    Help: 233
    Rate: 752
    Let's not go in the direction of absurdity.The differential protects only the kitchen and the cellar.And there are 3 important appliances.A boiler and 2 fridges.I described it at the beginning.And it's the only thing I'm concerned about.If the power supply fails,so be it.I can't do anything.If something causes a short circuit,so be it (hasn't happened for years). It's only supposed to work when you're away for a long time and in case of a " strange" tripping of it.There's nothing to expand other theories.
The discussion revolves around the need for remote differential switching to manage critical appliances like fridges and a central heating boiler. The original poster experienced a differential switch failure and seeks solutions to remotely monitor and reset it without physical presence. Suggestions include using a GSM module with Arduino for SMS notifications, employing smart devices like Tuya for remote control, and considering automatic reset devices. Concerns about safety and the reliability of such solutions are raised, emphasizing the importance of diagnosing the underlying issues causing the differential to trip. The conversation highlights the balance between convenience and safety in managing electrical systems remotely.
TL;DR: RCDs trip at 30 mA, and “RCDs are life‑saving devices.” Here’s how to get alerts and safer recovery while away. [HSE, 2020]
Why it matters: For homeowners with fridges/boiler on an RCD, this helps prevent food loss and unsafe auto‑reclosing.
Is it safe to remotely switch an RCD back on after it trips?
Treat every RCD trip as a fault until proven otherwise. Auto‑reclosing without inspection risks masking dangerous leakage or shorts. Prioritize diagnostics and root‑cause removal before any automation. “If the RCD is working, there is a cause and it must be found and eliminated.” Use alerts plus human verification during absences. [Elektroda, Strumien swiadomosci swia, post #20670391]
I just want alerts. What’s a simple way to get notified if my fridge socket loses power?
Use a small Arduino (or similar) with a GSM module, powered from a battery. Sense mains presence with a relay at the target outlet. On loss, send an SMS, then another when power returns. Battery power avoids missing messages during blackouts. This approach is inexpensive and independent of home internet. [Elektroda, hindoos, post #20670025]
How do I tell if the trip was an RCD event or a utility blackout?
Add an auxiliary contact to the RCD or breaker to signal its actual position. If the whole flat is on that RCD, your router dies and cloud/Zigbee alerts fail. Power your notifier from a separate circuit or a battery to maintain reporting. This distinguishes local trips from grid outages. [Elektroda, Adam-T, post #20670019]
Are there automatic RCD reclosers, and do they fit small boards?
Yes, auto‑reclosing attachments exist and can re‑engage after a trip. Many take about 2–3 DIN modules, so cramped boards may need upgrades. Verify compatibility with your RCD brand and type. Consider safety interlocks and trip‑count limits if you pursue this path. [Elektroda, palmus, post #20668878]
How much do auto‑reclosing add‑ons cost?
Expect pricing above 1000 zł for branded recloser attachments. Factor in any enclosure expansion, wiring, and electrician labor. Compare this cost to splitting circuits or adding monitoring only. Sometimes segmentation plus alerts offers better value and safety. [Elektroda, palmus, post #20669716]
Would splitting circuits across multiple RCDs help keep fridges and the boiler on?
Yes. Put sensitive loads on dedicated RCDs so outdoor or damp circuits don’t drop everything. This reduces cascade effects and nuisance downtime. It’s often more sensible and reliable than an auto‑reclosing “prosthesis.” Plan loads and labeling for clarity. [Elektroda, Ktoś_tam, post #20669982]
Can I use a Tuya Zigbee relay to restore power remotely?
Be cautious. It must handle full circuit current and any inrush properly. If the RCD feeds your router, cloud or Zigbee control won’t work during an outage. Prefer modular, appropriately rated devices and local GSM alerts for resilience. Validate ratings and installation with an electrician. [Elektroda, Adam-T, post #20670019]
Could the RCD itself be faulty, not the load?
Yes. RCDs can fail like any other electronic product. Intermittent or unexplained trips justify testing and possible replacement. Schedule professional testing before depending on reclosers. Keep test logs for future troubleshooting. [Elektroda, pikarel, post #20671038]
What low‑tech backup should I set up before traveling?
Give a trusted neighbor or family member keys and instructions. A phone call can get the RCD re‑engaged with eyes on‑site for safety. This is cheap, practical, and avoids blind auto‑reclosing risks. Leave a checklist and contact numbers near the panel. [Elektroda, hindoos, post #20668734]
How long can food stay safe in a fridge without power?
About four hours if you keep the door closed. After that, discard perishable foods to avoid illness. Timely alerts help you act within this window. Consider a freezer thermometer and notifications for redundancy. [USDA, 2021]
Should I automate reclosers for overcurrent breakers too?
No. Auto‑raising breakers without investigating faults is unsafe and defeats protection. The same logic applies as with RCDs. Diagnose and fix the cause instead of masking it with automation. Safety comes before convenience. [Elektroda, Ktoś_tam, post #20669982]
What should an electrician check to find the trip cause?
Request insulation resistance tests, leakage current checks, and an RCD test. Document results and correlate with appliance usage and events. Fix the root cause before considering remote re‑engagement. “Now get an electrician to take measurements and find out what is causing the switch to malfunction!” [Elektroda, Strumien swiadomosci swia, post #20669684]
How do I build a basic SMS power‑loss notifier?
  1. Power an Arduino (or similar) and GSM module from a battery or UPS.
  2. Use a relay at the target outlet; monitor its coil or contacts for mains presence.
  3. On loss, send an SMS; on restore, send another. Test weekly and label the sensor point clearly. [Elektroda, hindoos, post #20670008]