  • Looks at the explosion risk of 3.15A fuses when short-circuit current gets too high, using several fuses from different sources and types.
  • Shows a mains-installation short circuit where the fuse wire burns through, the tube breaks, and the glass shards explode.
  • Advises eye protection when repairing equipment because glass fuses can burst violently during fault conditions.
  • DC short circuits can be explosive and dangerous
    #31 21054639
    TechEkspert
    Editor
    Help: 17
    Rate: 5707
    Well that's right, that + on the ground in the control panels (or -48V power supply if you prefer) has always increased my attention. Interestingly, this power supply scheme has survived and radios for licensed bands still have the + power supply connected to the chassis.
    DC power supplies, but also smaller power supplies with batteries and even UPS and VRLA battery strings also increased my vigilance, the effects of a short circuit could be quite explosive and dangerous due to the temperature and splattering of evaporating metal. At higher voltages on the battery string you have to be careful with shock as DC can lead to electrolysis of the blood, the effects of which can show up in the days to come....
  • Fuse rupture scattered quartz dust and caused ringing ears
    #32 21054845
    Plumpi
    Heating systems specialist
    Help: 875
    Rate: 2685
    Many years ago when I was working on an LV switchgear in the harbour due to a misconnection of a ship, it ruptured two 400 or 600A BMs on the substation. The bang was so powerful that, in spite of several doors being closed, all the workers converged to see what had happened.
    The switchgear became momentarily dark from the dust that arose due to the grinding and scattering of quartz sand with which the fuses were filled. After half an hour the dust settled covering everything with a perfect thin layer of fine dust. The clean-up was days later. My ears were ringing all day.
    From then on I never dared to open the cupboard again without first putting on a mask, gloves and dielectric boots and protective clothing. Previously, it happened to enter in a short T-shirt without a face mask :) .
  • #33 21056350
    Matheu
    Help: 61
    Rate: 306
    web69 wrote:
    telecom equipment has (+) on the ground
    TechEkspert wrote:
    power scheme survives and radios on licensed bands still have (+) power connected to the chassis.
    Does this (+) on the ground on the device chassis:
    1) have any substantive justification?
    2) was it simply- once done like that, and then other devices by necessity had to have it too, so that they could work with the previous ones ?
  • #34 21056397
    web69
    Help: 188
    Rate: 629
    Yes, this is because the true direction of current flow is from - to + . Equipment with + on the ground is less sensitive to interference and emits less of it. It used to be that most vehicles had + on the ground, they corroded much less and the electrical connections did not electro-erode as in modern vehicles
The discussion centers around the risks associated with fuse explosions during short circuits, highlighting the importance of safety measures such as wearing eye protection. Users share personal experiences of component failures, including capacitors and transistors, leading to explosive incidents. The breaking capacity of fuses is emphasized, with Littelfuse mentioned as a manufacturer providing fuses with varying breaking capacities. The mechanism of glass fuse destruction is explored, noting that metal vaporization can lead to voltage breakdown and glass cracking. The advantages of sand-filled fuses over glass fuses in preventing injuries and minimizing damage during failures are also discussed. Additionally, the conversation touches on the dangers of working with DC circuits and the need for proper equipment and precautions.
TL;DR: A 3.15A glass fuse can still explode during a mains short because fault current can far exceed its safe interrupting limit, and one expert warned that sand-filled fuses "extinguish" the arc faster. This FAQ is for repairers and hobbyists who need to prevent shard injuries, arc damage, and avoidable equipment loss during fuse faults. [#21026920]
Why it matters: A fuse rating in amps alone does not tell you whether the fuse will survive a real short circuit without spraying glass, metal vapor, or ceramic fragments.
Fuse / setup Construction mentioned in thread Behavior under high fault current Practical consequence
Ordinary 3.15A glass fuse Glass tube, visible fusible wire Wire burns, glass cracks, shards can fly Eye-injury risk during mains faults
Sand-filled fuse Filler identified as silica/quartz sand Better arc extinction, less surface flashover Limits damage duration and fragmentation
Large ceramic BM fuse Thick ceramic body with sand filling Can still burst under very severe faults Ceramic fragments can be sharper than glass
Key insight: Choose a fuse by breaking capacity and construction, not just current rating. In the thread, both small glass fuses and large sand-filled BM links failed violently when the available fault energy was high enough. [#21026715]
  • Littelfuse fuse breaking capacity was quoted in the thread as 35A to 1500A, with one example rated 10000A at 125V but only 40A at 250V. That shows why voltage rating changes real interruption performance. [#21026715]
  • A reported capacitor accident involved 0.17F charged to 120V; molten metal from a dropped screwdriver fused into safety goggles. That is a direct PPE case for face and eye protection. [#21026610]
  • One workshop-protection idea was a dedicated branch with its own RCD and B16 overcurrent breaker, so a project fault trips only that circuit instead of blacking out the whole room. [#21027306]
  • Extreme DC systems in the thread included 48V / 2500A power plants, 2x1200A battery fuses, and a 24-cell OPzS 2500Ah battery set. Even at low voltage, short-circuit energy was described as explosive. [#21053746]
  • Large-fault examples included 630A BM fuse links in switchgear and 400–600A BM links in a harbor LV installation; both produced blast, dust, and flying fragments despite sand filling. [#21027394]
Why can a 3.15A glass fuse explode and throw shards during a mains short circuit instead of just melting safely?
A 3.15A glass fuse can explode because the short-circuit current from the mains can be far above what its body can interrupt safely. In the thread video, the wire first burned open, then cracks spread across the glass tube, and finally shards flew outward. Another participant explained that large fault current vaporizes metal and sustains an arc, which heats the tube instead of ending cleanly. The ampere rating only states normal current; it does not guarantee safe interruption under every fault level. [#21026812]
What is the breaking capacity of a fuse, and how do voltage and fault current affect it in models like Littelfuse fuses?
Breaking capacity is the maximum fault current a fuse can interrupt without the body melting apart or exploding. One thread example cited Littelfuse parts rated from 35A to 1500A, and one model was quoted at 10000A at 125V but only 40A at 250V. That means the same fuse family can tolerate very different fault conditions depending on voltage. Higher voltage makes arc extinction harder, so safe interrupting current can drop sharply. [#21026715]
How do sand-filled fuses compare with ordinary glass fuses when interrupting high short-circuit currents?
Sand-filled fuses handle high short-circuit currents more safely because the silica or quartz filling helps quench the arc and shorten current flow. A thread participant warned that replacing such a fuse with an ordinary glass type can increase injury risk from flying glass and can also worsen equipment damage because the arc lasts longer. Another reply added that the metal-vapor flashover seen on glass does not occur in a sand-filled fuse. That makes sand-filled designs the safer choice where fault energy is high. [#21026920]
What causes metal vapor to deposit on the inside of a blown glass fuse, and how can that lead to cracking or flashover over the glass surface?
Metal vapor deposits on the inside of a blown glass fuse when heavy current vaporizes the fusible wire during interruption. One reply explained that this conductive coating can let voltage break down across the inside surface, so current then tracks over the glass itself. That extra surface current heats the tube and can crack it. In the thread, users also reported many failed glass fuses with a clear metal coating inside after the event. [#21026812]
What is PU equipment in the context of fuse selection and household power supplies?
PU equipment means ordinary household or domestic equipment in this thread’s terminology. A participant explicitly clarified that it stands for common-use equipment and refers to domestic gear and power supplies. In context, the term was used while explaining why some household power supplies use silica-sand fuses instead of ordinary glass ones. That matters because home equipment can still see fault conditions severe enough to justify better arc extinction. [#21027038]
How do ultrafast aR fuses differ from standard fast-blow fuses in construction and application?
The thread only states that ultrafast aR fuses exist and are distinct from ordinary fast fuses, but it does not describe their internal construction. The author said he had encountered aR fuses and had not been able to verify how their design differed from fast ones. So the only safe conclusion from this discussion is application-level: users recognize them as a separate fuse category used where faster fault interruption matters. The thread provides no verified geometry, filler, or timing data beyond that. [#21027027]
What safety gear should I use when testing or repairing high-energy circuits so I’m protected from exploding fuses, capacitors, and ceramic fragments?
Use eye protection first, then gloves, and add face and body protection when fault energy is high. The thread includes reports of molten metal embedded in safety goggles, ceramic BM fragments described as sharper than glass, and a user who later refused to open LV switchgear without a mask, gloves, dielectric boots, and protective clothing. One practical rule from the discussion is simple: if the circuit stores or can deliver significant energy, treat blast and shrapnel as credible hazards, not edge cases. [#21054845]
How should I set up a dedicated workshop circuit with its own RCD and B16 breaker to limit damage when an electronics project fails?
Set up one separate workshop branch so only that branch trips when a project fails. 1. Put the bench outlets on a dedicated circuit. 2. Protect it with its own RCD and a B16 breaker. 3. Keep experimental loads on that branch, not on the room’s general outlets. The thread recommendation aimed to stop a fault from cutting power to the entire room. It is a containment strategy, not a substitute for proper PPE or correct fuse selection. [#21027306]
What are the main differences between AC and DC fuse testing, especially when it comes to arc extinction and danger level?
DC fuse testing is more dangerous because extinguishing a DC arc is harder once current starts flowing. In the thread, one user proposed an AC-versus-DC comparison specifically to show the arc-extinction problem, and the author replied that DC is “quite a dangerous game” and requires a suitable capacitor bank, a switch that survives several operations, and checks for leftover capacitor voltage. AC naturally passes through zero crossings; DC does not, so the test setup becomes much less forgiving. [#21027447]
How could I build a simple DC fuse test setup using a bridge rectifier, capacitor, and kettles as a current limiter, and what are the main risks?
One proposed setup was bridge rectifier -> capacitor -> two series kettles as current limiter -> tested fuse in series. The aim was to force current without making a dead short. The author immediately pointed out two main risks: the kettles may have to limit capacitor charging current, and the bridge would need to withstand part of the fault current, so it must be powerful. Residual capacitor voltage after the test is another stated hazard. This idea is experimental and was discussed as risky even before construction details were settled. [#21027503]
Why can even a large ceramic BM fuse filled with кварtz sand still burst apart under a severe fault current?
A large ceramic BM fuse can still burst because high fault energy can exceed what even a sand-filled body can absorb and interrupt cleanly. The thread describes 630A BM links blown apart in switchgear and 400–600A BM links rupturing so violently that quartz dust filled the room. Sand helps quench the arc, but it does not make the fuse indestructible. As one comment put it, bigger fuses can mean bigger problems because the arc in a “thicker” circuit is also more severe. [#21054845]
What is a GDT, and why does it reportedly survive DC short-circuit testing better than some other protection components?
“GDT” is a protection component that conducts during an overvoltage event, using a gas discharge path as its key operating element. In the thread, the author said GDTs “stand up well” to DC testing and linked to a demonstration, but he did not provide measured current, voltage, or survival limits in the posts themselves. So the thread supports only a narrow claim: compared with some other tested parts, GDTs were observed to tolerate DC short-circuit-style tests better in that example. [#21027503]
How dangerous are battery-backed DC systems like 48V telecom power plants, UPS strings, or large VRLA banks during a short circuit?
They are extremely dangerous because low voltage does not mean low energy. The thread cites a 48V, 2500A power plant, 2x1200A battery fuses that did not clear during one event, and a 24-cell OPzS 2500Ah battery string. Users described disappearing metal objects, ringing ears for a week, evaporated cable lugs, and explosive splatter from vaporized metal. Another post warned that DC battery strings also raise shock concerns at higher series voltages, alongside the blast hazard from short circuits. [#21054522]
Why do some telecom and radio systems use positive ground or connect the + supply to the chassis, and what practical advantages does that have?
The thread says some telecom and radio systems use positive ground because that arrangement is less sensitive to interference and emits less interference. One participant also stated that older vehicles with positive ground corroded less and suffered less electro-erosion at electrical contacts. The same discussion notes that this convention survives in some licensed-band radio equipment, where the positive supply remains bonded to the chassis. The thread does not add measured EMC figures, but it clearly presents noise reduction and corrosion behavior as the practical advantages. [#21056397]
What protective covers or fuse holders for 5x20 PCB fuses help reduce the risk of shrapnel and accidental contact in electronic devices?
The thread mentions rubber protective sleeves fitted over some 5x20 PCB fuse mounts. One participant noted that these covers reduce the risk of accidental touch and also limit shrapnel if the fuse ruptures. That makes them a simple secondary barrier around a fragile glass fuse. They do not replace correct fuse selection, but they can reduce injury and contamination inside the device when a small fuse fails violently. [#21037568]