[Solved] Tuya Zigbee valve controller in a built in boiler. Signal attenuation issue?

palmus 1320 9
Best answers

Why does my Zigbee valve controller go offline when the inspection flap is closed, even though a nearby repeater stays connected?

The problem was the metal construction around the inspection hatch, which was shielding the controller when the flap was closed [#20724656] The controller and its antenna were effectively facing a corner of the hatch with about a 5 cm wide metal strip, so the flap acted like a screen even though the repeater still had a good link to the gateway [#20724656] The suggested causes were the antenna’s radiation pattern plus the flap material and nearby aluminum frame, not just range alone [#20719704] The fix was to remove the extra frame material and cut down the angle bar, leaving only small mounting slots; after that, the link worked [#20724656]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
This content has been translated flag-pl » flag-en View the original version here
  • Aluminium flap frame likely blocks Zigbee signal

    #1 20718946
    palmus
    Level 34  
    Posts: 3974
    Help: 233
    Rate: 751
    Hello
    I have fitted a Tuya valve controller on the water supply to the DHW boiler. That's the one on the left.The boiler in full plasterboard on the rack plus a lot of pipes in the revision:
    View inside CWU boiler housing with installed pipes and valve controller.
    Unfortunately, WiFi didn't get there. So I replaced the controller with Zigbee.It too is offline when the revision flap is closed.The flap looks like this:

    Photo of a wall with a rectangular inspection hatch and a double light switch below.
    The gate ( 5m distance) does not see it.So I inserted a Zigbee repeater inside. And interestingly the signal from the repeater as normal reaches the gate, but from the controller does not.I checked that the controller connects to this repeater, but unfortunately after closing the flap it becomes immediately offline. This is the first conundrum. I looked inside for the optimum place for the repeater, but this did not give anything. The flap has an aluminium frame.From the inside it looks like this:
    Interior view of a revision flap with an aluminum frame and remnants of soundproofing foam.

    These scabs are remnants of a mute sponge which I tore off, thinking that it contributes to signal attenuation. Could this frame on the flap be creating some sort of obstruction? Of course, with the flap open the signal is ok.I've run out of ideas:-( What else can be done?
  • ADVERTISEMENT
  • Clarifying which link fails after closing flap

    #2 20719164
    freebsd
    Level 42  
    Posts: 6791
    Help: 766
    Rate: 2032
    palmus wrote:
    The gate ( 5m distance) does not see it.So I inserted a Zigbee repeater inside. And interestingly the signal from the repeater as normal reaches the gateway, but from the controller does not.I checked that the controller connects to this repeater, but unfortunately after closing the flap it becomes immediately offline.
    Can you describe this a little more clearly?
    When you close the repeater flap what connection works?
  • ADVERTISEMENT
  • #3 20719204
    palmus
    Level 34  
    Posts: 3974
    Help: 233
    Rate: 751
    The repeater<->gateway connection works. With the flap closed. The controller does not. According to the mesh rules, the valve controller should communicate with the repeater as an intermediary ( 20 cm next to it) and send it on, since it can't manage on its own through the walls. With the flap open or even tilted for about 25 cm, everything communicates nicely with the gateway.
  • ADVERTISEMENT
  • #4 20719245
    freebsd
    Level 42  
    Posts: 6791
    Help: 766
    Rate: 2032
    Have you removed and added drivers from Tuya, so as to rebuild the connections?
    Change the power supply to the valve, maybe this one "sows" interference and "nudges" the receiver in the valve.
  • #5 20719498
    palmus
    Level 34  
    Posts: 3974
    Help: 233
    Rate: 751
    Off, 10 sec, on for the controller, quick close of the flip.I check the connections on the gateway and see that the controller is connected with the repeater, the repeater is visible and connected to the gateway and the controller is not.Just a curiosity.
    I will check the power supply.
  • #6 20719619
    freebsd
    Level 42  
    Posts: 6791
    Help: 766
    Rate: 2032
    You can still disconnect all other electrical devices in the vicinity for a test.
    From the photo, I infer that the inspection flap when closed is very close to the valve controller?
  • #7 20719657
    palmus
    Level 34  
    Posts: 3974
    Help: 233
    Rate: 751
    Yes.About 5 cm.Unfortunately I can't turn the valve,and lack of space and possible leakage.I thought maybe cut off/tighten that wide strip of aluminium on the left to the minimum?
  • Helpful post

    Inspection flap material may be blocking Zigbee signal

    #8 20719704
    freebsd
    Level 42  
    Posts: 6791
    Help: 766
    Rate: 2032
    From the photos I estimate that the aluminium strip is away from the valve, although probably less than a wavelength. However, it is possible that the bigger problem is the radiation characteristics of the antenna from the valve and, on top of that, the material from which the flap is made. It sometimes happens that materials such as bathroom tiles on the wall perfectly block the signal of e.g. WiFi. We don't know what the properties of your plasterboard are, as I guess the inspection flap is made of this material. The differences can be very significant, e.g. in Poland and Germany these are boards with different properties (the German one is sort of more "ceramic").
  • ADVERTISEMENT
  • Possible antenna shielding or metal-frame interference

    #9 20719759
    palmus
    Level 34  
    Posts: 3974
    Help: 233
    Rate: 751
    The board is classic plasterboard, on the side plasterboard plus mineral wool, on the opposite side plasterboard plus tiles. I even put the repeater on this controller - nothing.The repeater has a "good" signal, the controller offline.It's possible that the antenna is in such a position that it is shielded by some kind of lich. But why doesn't it want to get out via the repeater???? Some kind of interference when the frame al is brought closer ?
  • Metal inspection hatch was blocking Zigbee signal

    #10 20724656
    palmus
    Level 34  
    Posts: 3974
    Help: 233
    Rate: 751
    It turned out that the door had a frame behind Al 2.5cm wide(!) And on top of that a frame embedded in the wall also 2.5cm.- The controller and the antenna were looking directly at the corner of the inspection hatch - a 5 cm wide strip of metal sheet - so not a bad screen. I tore the whole thing out, cut off the excess angle bar, leaving only a couple of slots for attaching the frame and the filling, the construction became filigree, but it helped.

Topic summary

✨ The discussion revolves around a user experiencing signal attenuation issues with a Tuya Zigbee valve controller installed on a domestic hot water (DHW) boiler. The user initially replaced a WiFi controller with a Zigbee controller due to connectivity problems. Despite installing a Zigbee repeater, the valve controller remains offline when an inspection flap, made of plasterboard and aluminum, is closed. The user notes that the repeater successfully connects to the gateway, but the controller does not, even when positioned close to the repeater. Suggestions include checking the power supply for interference, removing nearby electrical devices, and considering the impact of the flap's materials on signal transmission. Ultimately, the user discovered that the metal frame of the inspection hatch was obstructing the signal, and after modifying the frame, the connectivity issue was resolved.