Is a Wago terminal block a good choice as the distribution connector in a home automation switchboard, and what are its drawbacks?

Yes, Wago connectors are considered a very good solution for this use, with the main downside mentioned being the price rather than technical problems, although some people still prefer traditional ZUGs [#18980803] If you choose the Wago series with bridges, note that 2003 has space for one bridge (half-bridging is possible) while 2005 gives room for two bridges on both N and phase, which may be more flexible in a switchboard [#18982417] More generally, a star-wired installation and control cabinet have advantages, but they also mean many cables, a large board, and harder future modifications, so everything should be planned very carefully and with spare space for automation [#18981766][#18984679] One reply also suggests not pulling every circuit to the switchgear: bring N to the boxes and use devices like Sonoff TX or Shelly Mini in deep boxes for some circuits, while keeping the most important ones wired [#18981910] Another recommendation is not to mix systems unnecessarily; keep a separate power supply for cameras, alarms, etc., and think through how bistable relay status will be checked by the automation [#18984679]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 18980794
    marcingebus
    Level 11  
    Posts: 406
    Help: 3
    Rate: 31
    I am renovating the house, electrics completely from scratch. I will add automation on ESP/Adriono/Sonoff/Shelly. The automation will control lighting and maybe heating, recuperation, maybe etc.... broad plans. Right now I'm doing the switchgear and I want to make it work the old way and then slowly switch to my automation, motion sensors etc.... My vision is as follows:
    1. from sockets, light points and switches the cables come together in the switchboard.
    2. in the first stage, bistable relays switch lights controlled from bell switches
    I don't have a blueprint (apart from the concept in my head), so I don't really know how many ESEKs I'll need in the switchboard (I don't want to count it now), I thought of terminating all the cables from point 1 on the ZUGs in the switchboard and then quietly untangling them. ZUG's that look decent and take up little space are WAGO, like these:
    https://www.wago.com/pl/z%C5%82%C4%85czki-lis...wa-z%C5%82%C4%85czka-instalacyjna/p/2003-7646

    Do you think this is a good solution as a ZUG in the switchgear?

    Any disadvantages of these connectors apart from the price? (At my local wholesaler they are 8.5zl/unit)
  • ADVERTISEMENT
  • #2 18980803
    Ryszard49
    Level 39  
    Posts: 6233
    Help: 312
    Rate: 1011
    marcingebus so you don't go too far wrong with this smart home. I did something like that once too, I went on holiday and the system turned off what it thought were unnecessary socket circuits. Everything I had in the fridge to be thrown away. Such good advice, power circuit for the fridge off the 'smart' system.
    As for the Wago system it's good and I'll even say very good but I still use zugi.
  • ADVERTISEMENT
  • #3 18981766
    sk1977
    IT specialist
    Posts: 8047
    Help: 1326
    Rate: 742
    A star installation has a number of advantages, but it also has disadvantages - e.g. the number of cables, a large switchboard and modifying or unwinding the installation after completion can be difficult (compared to wireless solutions) - it is worth planning everything carefully so that there is no lack of space in the switchboard or cables in the walls.
    Helpful post? Buy me a coffee.
  • #4 18981910
    xury
    Automation specialist
    Posts: 7083
    Help: 878
    Rate: 1497
    sk1977 wrote:
    It is important to plan everything carefully so that there is no lack of space in the switchboard or cables in the walls.
    or walls for cables.
    E.g. I would go a slightly different route. Instead of pulling every circuit breaker to the switchgear I would prefer to just bring N to the boxes and use for example a Sonoff TX. All the boxes deep to possibly accommodate shelly or sonoff mini.
    Of course, the most sensitive and "vital" ones should be wired. In addition, an automation server such as Home Assistant, Domoticz, OpenHAB, etc. will become indispensable with an extensive system.
    Software on wireless ESPs should be standardised on Tasmot, the rest should be supplemented with zigbee devices etc. if something new is required. Use gateways like zigbee2mqtt milight hub etc.
  • #5 18982417
    marcingebus
    Level 11  
    Posts: 406
    Help: 3
    Rate: 31
    However, I am making a scheme because I can still add a second switchgear over the current one if space were to run out. ;-) .
    Once I've done it, I'll share, maybe someone will benefit. It will be in DWG.

    marcingebus wrote:
    .

    https://www.wago.com/pl/z%C5%82%C4%85czki-lis...wa-z%C5%82%C4%85czka-instalacyjna/p/2003-7646

    Do you think this is a good solution As a ZUG in the switchgear?

    .

    The version above is line 2003, this line has room for one bridge (you can half bridge), but maybe it's better to go straight to line 2005, because it has both on N and on phase room for two bridges.... Is this line 2005, some kind of total departure already?
  • #6 18982493
    sk1977
    IT specialist
    Posts: 8047
    Help: 1326
    Rate: 742
    A question of budget and convenience of use. Assess it yourself. Ideally you will have a diagram - it will be easier to assess the situation.
    Remember the space for automation.
    Helpful post? Buy me a coffee.
  • ADVERTISEMENT
  • #7 18982665
    GanzConrad
    Level 25  
    Posts: 934
    Help: 67
    Rate: 203
    marcingebus wrote:
    and the switches cables go down in the switchgear.
    .
    What cables will go to the switches? Twisted pair is used for automation, and conventionally 3x1.5mm.kw, so you'll need to reconcile the transition option somehow.
    Do a search on the forum there was a thread about things you need to anticipate when laying such an installation and a list of devices you can control in the future.
  • #8 18983175
    bhtom
    Level 39  
    Posts: 4498
    Help: 446
    Rate: 604
    Welcome,

    marcingebus wrote:
    However, I'm making a diagram because I can still add a second switchboard over the current one if I should run out of space.


    Myself, doing a smart home for myself, I would not mount the switchboard on the wall, but would put a normal control cabinet....

    Regards.
  • #9 18984599
    marcingebus
    Level 11  
    Posts: 406
    Help: 3
    Rate: 31
    I need to adopt some sort of relay control standard for lighting. Now from switches and in the future from some automation rather mine on ESP/Shelly etc... what would you guys adopt 12V DC, 24V DC or otherwise? Someday I'll put a small gym on 48V DC for the cameras, then maybe 48V? Do I not mess around and find it easier to embrace 12V from my own automation? Do I totally unmix and not combine systems because a different screw is better for each hole anyway? ;-)
  • Helpful post
    #10 18984679
    sk1977
    IT specialist
    Posts: 8047
    Help: 1326
    Rate: 742
    Personally, I would not go for such solutions - i.e. star installation and switchgear/control cabinet. All the more so in homemade automation (my attempt consumed an enormous amount of time, and after replacing the first device with a wireless one, I noticed that I was not even a small part of the ready-made solutions). After a similar concept (I had no star installation) I was left with hundreds of metres of unused cables in the walls - slowly everything went to wireless control. Reasons: installation and equipment costs, modifications and extensions, new equipment. The final decision was to drill the cable and replace the first device with a wireless one. After that, I was already replacing others.

    What I would recommend in such installations, based on my own mistakes, is to think carefully about everything, even the seemingly unimportant details.
    Pulse control of bistable relays - it is worth thinking about how to check the status of the relay.
    I wouldn't combine systems - assume an optimum power supply for your system and leave a separate one for cameras, alarms etc.
    Helpful post? Buy me a coffee.
  • #11 18984878
    marcingebus
    Level 11  
    Posts: 406
    Help: 3
    Rate: 31
    I attach the project. It shows the switchgear that will serve the Ground Floor. I still have a main switchboard on the property which via C25 feeds this switchboard, a switchboard in the utility room/garage and there will be a switchboard on the first floor which will serve the heat pump, PV and sockets and lighting on the first floor as well as one external circuit.

    In this scheme I still need to give the outside sockets under the relay and a selected socket/s in the house under which the iron will be likely to be plugged.

    The whole thing can work autonomously independently of the automation, and I will connect the automation, which will be able to act like a bell switch by supplying 12V and test the state of the relay contacts.

    All the outputs to the top (purple) are to the automation, which I will probably do in a different place, because that's where the reed switches from the doors will come down, maybe from the motion sensors.... etc..

    The diagram doesn't show the power supply, which of course has to be there. I'm unlikely to use a circuit breaker on the input, as it's better to de-energise the power cables as well, and I can do that in the main switchboard where I have 3x c25 and maybe add some Type1+Typ2 300mA/voltage surge.

    Home automation on ESP/Adriono/Sonoff/Shelly - planning and execution of switchgear Home automation on ESP/Adriono/Sonoff/Shelly - planning and execution of switchgear Home automation on ESP/Adriono/Sonoff/Shelly - planning and execution of switchgear .
    Attachments:
    • elektryka-v20201018-Arkusz1.pdf (77.97 KB) You must be logged in to download this attachment.
  • #12 18984981
    sk1977
    IT specialist
    Posts: 8047
    Help: 1326
    Rate: 742
    Schematic as described in the first post, may be useful for selection of some components - e.g. switchgear.
    What is missing is the most important thing - automation. It is it that will determine the satisfaction or not of the whole. Do you have a concept (algorithm) of operation?
    The vision in the first post is also more about execution than concept of action. It is important what and how you want to control (this you have shown on the diagrams), what kind of information you want to collect (reed switches, switches, motion detectors - and, for example, control by app, by voice). What additional elements are you planning? Air-conditioning, heating, humidifiers, purifiers, automatic hoovers, some audio, roller shutters, alarm, carbon monoxide/gas sensors, flooding, some electro-valves, etc., etc.?
    Helpful post? Buy me a coffee.
  • ADVERTISEMENT
  • #13 18985905
    marcingebus
    Level 11  
    Posts: 406
    Help: 3
    Rate: 31
    I see that the diagram has an error:
    - relays P1..P15 (also lier small) will be bistable, like for lighting, to control bell switches. One end of the coil permanently to minus the other controlled by a pulse from a switch, or automation.
    - Contact 11 of the relay gives state to the automation, when off it is ground and when on it was supposed to give PLUSA. But I connected a control pulse. Instead, a plus should be applied to terminal 14.
  • #14 18986784
    marcingebus
    Level 11  
    Posts: 406
    Help: 3
    Rate: 31
    I still have a question for experts on the subject of relays. Instead of a relay dedicated to lighting, can such relays for example be used via a TH35 base:

    https://pl.rs-online.com/web/p/przekazniki-blokujace/0515583/

    I don't care if they have an available socket and sufficient current-carrying capacity. I assume that a diode would be useful, but something more ? A 12v single coil control (to reduce the number of control wires from the automation). Do you need to change polarity there ? to change state ?
  • Helpful post
    #15 18987131
    e-sparks
    Electrician specialist
    Posts: 623
    Help: 77
    Rate: 216
    marcingebus wrote:
    Do you have to change the polarity there? to change the state?
    On the page you yourself provided you can find the Datasheet: https://docs.rs-online.com/a94f/0900766b81397cb2.pdf
    On its first page like a bull the information:
    Home automation on ESP/Adriono/Sonoff/Shelly - planning and execution of switchgear .
  • Helpful post
    #17 18987658
    GanzConrad
    Level 25  
    Posts: 934
    Help: 67
    Rate: 203
    IMO you are making the mistake of assuming that control via on/off is 'actually control':
    Take, for example, the sockets at the TV:
    - TV you switch on with remote control, set the source
    - receiver (some) via telnet commands, then you set the source, volume level, etc.etc.
    - satellite TV decoder: same thing: ETH etc.
    - NAS server
    or a dumb kettle:
    - just turning on the power does nothing to boil water for coffee
    or coffee machine:
    - you have to have one with an app to 'hack' it, but you still end up having to walk over to set the cup down....
    Air conditioning:
    - IR remote thermostat/pilot managed via z-wave or ETH
    washing machine: same thing
    For me, for example, controlling the switching of lights without adjusting the brightness level is medieval and a waste of time, so I would skip even that (maybe only in justified cases)

    What I'm getting at is that you don't need on/off capability for everything, because you won't need it to realise even a simple control that will give you satisfaction. What good is turning on the power of a washing machine if you have to walk up and set the programme (not to mention the load)?
    You are more likely to need a measurement of the power consumed at the load, because then you can take some action (drop in power on the washing machine = no more washing, etc.).
  • #18 18988751
    marcingebus
    Level 11  
    Posts: 406
    Help: 3
    Rate: 31
    GanzConrad wrote:
    For me, for example, controlling the switching of lights without adjusting the brightness level is medieval and a waste of time, so I would skip even that (maybe only in justified cases
    .

    You've inspired me and I googled to look for dimmers and use dimmers instead of relays. Controlled by monostable/bell buttons they can also be controlled from my automation. There's the F&F, there's the zamel DIM-20 and the DIM-30. There's also some Finder from the 15 series, but it requires a master module and the price kills enthusiasm. The DIM-30 for PLN200 is still acceptable. Now you can control the bells, and then you can work 0-10V from your automation.

    In general, I want something that is reasonably open, inexpensive and energy-efficient. I will certainly buy the bulbs all new, so I can choose LEDs that will work with dimmers.

    My automation, this will be:
    - in terms of local lighting and remote switching, switching at preset times and the ideal would be switching with motion sensors/contactors. There could be a soft start. Brightening/dimming, not necessarily everywhere, but some living room, bedroom/room, maybe terrace.
    - in terms of heating - I'll add something there, but it's beyond the scope of this switchboard,
    - I don't want KNX and similar solutions because I think I'd rather spend a fortune I don't have in a different way. I don't want to control a washing machine, kettle etc. I want to do some sort of installation that, in its simplicity, will work and allow me to connect with something more intelligent one day. Perhaps some kind of single socket (series connected under one fuse) switchable as I wrote earlier.
  • #19 18988823
    sk1977
    IT specialist
    Posts: 8047
    Help: 1326
    Rate: 742
    marcingebus wrote:
    Generally I want something that is reasonably open, inexpensive and energy efficient.
    - star installation alone is not a cheap solution. Building your own systems may not be cheaper than off-the-shelf solutions either.
    Automation alone does not have a significant impact on energy consumption, it depends mainly on the consumers and the way you control them - running time. There is a lot to be gained from heating.
    marcingebus wrote:
    I don't want KNX and similar solutions, because I think I'd rather spend a fortune otherwise
    - KNX is expensive, but there are also much cheaper systems. Perhaps cheaper than a star installation :) .
    Think beforehand how you want to control the brightness - a bell switch is not convenient - how do you want to control the brightness with it? Other solutions may require additional cables, for example.

    A lot depends on the planned automation. This is probably the most important element. The rest may depend on it.
    Helpful post? Buy me a coffee.
  • #21 18989219
    sk1977
    IT specialist
    Posts: 8047
    Help: 1326
    Rate: 742
    It's a good solution as an aftermarket dimmer - and that's its purpose - for so-called new type installations. To use it via WiFi, you must provide it with a suitable signal level - in a metal cabinet there will be a problem.
    To control it, you can use a double bell switch and therefore a suitable cable (min. 3 wires). This already makes sense, but the ergonomics of use are still a bit limited.

    When it comes to brightness control - for me the benchmark of ergonomics is, for example, the Philips HUE wireless dimmer - 4 buttons: off, 2 from brightness, the third on and programmable in the brightness app (e.g. one click last brightness, 2 max, 3 medium, 4 night light). In addition, it can be removed from the wall and taken away. You can control one bulb or several, or have several remote controls for one bulb.
    Helpful post? Buy me a coffee.
  • #22 18989325
    marcingebus
    Level 11  
    Posts: 406
    Help: 3
    Rate: 31
    sk1977 wrote:
    Philips HUE wireless dimmer
    .

    Looks cool, inexpensive. But the catch as I noted is in the bulbs 200PLN/pc, 1500PLN/lamp.... The fall out. I know Philips has to make money on something. My solution is to be independent of the manufacturer. Today there will be such a bulb and tomorrow an LED strip etc....

    sk1977 wrote:
    This is a good solution as an aftermarket dimmer
    .
    Maybe I'll buy one for myself as a trial, some relay to try. I won't have dimming everywhere. I'll print out on a printer mozing on TH35, or come up with something else. I still have a few days to think about it. The circuit needs to be able to be controlled by something I do (e.g. turning off a light when I trigger an alarm (I'll put out the right signal from the alarm system and my automation will handle that. Maybe flickering all the lights when the alarm goes off? These are the sorts of ideas I have. Door contacts... Lower brightness glow at night from the motion detector. You wake up at night and want to go to the kitchen, the toilet, the phone. Normal strong light will dazzle, you need some. Maybe a system has something like this, but it has to be open to signals from other sources.

    If anyone has any ideas, throw them around, or any other suggestions.
  • #23 18989385
    xury
    Automation specialist
    Posts: 7083
    Help: 878
    Rate: 1497
    If you want to use the sensors from the alarm to automate your home, then as I wrote before, use the Satel ETHM-1 integration with one of the systems mentioned in my previous post.
    Then you don't need to do any wireframing. A difficult topic at first, but will allow you to spread your wings over time. In my opinion.
  • #24 18989401
    sk1977
    IT specialist
    Posts: 8047
    Help: 1326
    Rate: 742
    marcingebus wrote:
    Looks cool, inexpensive. But the catch as I noted is in the bulbs 200PLN/pc, 1500PLN/lamp.... It's out.
    - this was just an example of functionality - if you will be doing automation - you can use the principle. I have not yet added that all light changes are "soft". This system is wireless by design - and you are doing the opposite, so it is unlikely to be of any use.

    marcingebus wrote:
    The system must allow control from something I make
    - so you have to design it yourself - we don't know what you'll do, or on what hardware. A lot can be done on a control panel for example - for example here's an example of a project: https://ropam.com.pl/pomoc_techniczna/ - you can get ideas too.

    marcingebus wrote:
    You wake up at night and want to go about the kitchen, the toilet, to get the phone
    - this is where floor lighting works well - e.g. an LED strip near the floor or low level lights.
    marcingebus wrote:
    If anyone has any ideas, throw them around, or any other suggestions
    - here you go: smoke/fire gas detectors, flooding + solenoid valves to close if flooding or gas/carbon monoxide is detected. If you have roller shutters, these can also be controlled. As for light, it's a good idea to be able to change the warm/cold colour in some rooms.
    Flashing lights with an alarm is hardly useful - a good siren (or several) will draw attention better and be immediately associated with the alarm.

    I'm not writing about automation or control - that's a matter of automation.
    Helpful post? Buy me a coffee.
  • #25 18989816
    GanzConrad
    Level 25  
    Posts: 934
    Help: 67
    Rate: 203
    marcingebus wrote:
    DimmerBox
    .
    Consider how many traditional 230V incandescent bulbs you'll have, or how much patience you'll have to test LED bulbs that only have "dimmable" in their name, but are really just wasting our time and money. I quickly got tired of investigating which LEd bulb is really "dimmable" and which has nothing to do with it at all, and again which works smoothly across the whole range (I haven't found one...).
    To conclude the long-winded argument: think about controlling LEDs (e.g. strips) 12/24V via all kinds of LED dimmers of the type :
    https://blebox.eu/produkt/wlightbox/
    I have experience with Fibaro RGB controller, in which instead of RGB you can set the control of 4 separate white tapes, but for you there is a huge variety of solutions based on WiFi (ESP) and considering the variety of ready-made products on the market it is worth considering whether to switch to this type of lighting, even using lamps made of wide profiles:
    https://allegro.pl/oferta/profil-aluminiowy-solis-srebrny-1m-do-tasm-led-6832306883
    https://allegro.pl/oferta/lampa-led-linea-wiszaca-40w-liniowa-8878451847
  • #26 18989997
    marcingebus
    Level 11  
    Posts: 406
    Help: 3
    Rate: 31
    Your suggestion is to go for 12V LEDs: strips, incandescent bulbs. Tapes are somehow available, but a first glance at incandescent bulbs - in the sense of light sources, then some traditional fixture, for this to have power in the equivalent of 50-100W, is poor..... Have you replaced everything in the house with 12V LEDs ?
  • #27 18990985
    GanzConrad
    Level 25  
    Posts: 934
    Help: 67
    Rate: 203
    marcingebus wrote:
    You have replaced everything in your house with 12V LEDs
    .
    No, I make my own lights - I don't recommend ;-) , so now with the last few years in mind I would consider whether it is worth standardising all the lighting to at least 12/24V strips (I didn't mention 12V bulbs, but they may exist), or using 12V panels like the following:
    https://www.aliexpress.com/item/32800234629.h...earchweb0_0,searchweb201602_,searchweb201603_
    https://allegro.pl/oferta/panel-led-cob-12v-36smd-w5w-c5w-ba9s-6000k-9121701448
    Of course, I'm only talking about cases where you want dimming - because where it will be on/off it doesn't matter.
    Tapes can be selected in terms of wattage and, above all, the quality of light is no longer an issue - you can easily find those with high CRI and those on MCPCB substrate - a matter of budget.
    With panels it is worse because the CRI is random or you have to search.
    The Dimmerbox you mention is a triac dimmer and is only suitable in practice for traditional incandescent bulbs - if someone can show me an "LED bulb" that really works with it, not just pretends to and still doesn't cost a fortune, I'd be happy to use it.
  • #28 18991067
    sk1977
    IT specialist
    Posts: 8047
    Help: 1326
    Rate: 742
    LED strips are not suitable everywhere - it is a question of the specific room and its purpose and preferences. Then there is the individual question of the aesthetics of the interior - but that is another story altogether.

    Dimmable light isn't needed everywhere either - for example, with 2 different light sources you already have 3 levels of lighting. If you plan it right, this should be enough for comfortable use in many rooms. Do you need infinitely variable control in e.g. the kitchen, bathroom, hallway?

    Led strips or adjustable brightness work well as supplementary light - especially if it has the possibility of adjusting the hue (warm) or colour. 12/24V leds require a power supply (they are also available for 230V) and a controller for which space must be provided. There is also the issue of controlling the LEDs.
    Depending on the room (size, purpose), you can use ordinary main lighting + adjustable supplementary lighting, e.g. to light up a wall or make strips at the floor.
    Of the cheaper ones than Philips HUE, you can look at Ikea Tradfre - when used in several places, the cost will not be overwhelming - but it is also a wireless solution.
    Helpful post? Buy me a coffee.
  • #29 18991171
    GanzConrad
    Level 25  
    Posts: 934
    Help: 67
    Rate: 203
    sk1977 wrote:
    bathroom

    mandatory - evening/night trips by household members ;-) .
  • Helpful post
    #30 18991194
    sk1977
    IT specialist
    Posts: 8047
    Help: 1326
    Rate: 742
    GanzConrad wrote:
    sk1977 wrote: bathroom
    Obligatory - evening/night trips by household members
    .
    Along the way mandatory - as night lighting (I've already written about this), but in the bathroom itself - why? Going into the bathroom at night and fiddling with the light intensity control? Two or 3 light sources of different wattage, one (e.g. the weakest one) can be triggered by a motion detector at preset times (depending on the brightness in the bathroom) and you have comfortable use. Or a led strip near the floor triggered by a motion sensor.
    I have Hue at home and I can't remember the last time I used the brightness control (in any room) other than a switch programmed for several states.
    Helpful post? Buy me a coffee.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around the planning and execution of home automation systems using ESP, Arduino, Sonoff, and Shelly devices during a complete electrical renovation. The user aims to create a switchboard that initially functions with traditional controls and gradually transitions to automation, incorporating motion sensors and smart relays. Key considerations include the choice of wiring, the use of bistable relays for lighting control, and the integration of automation servers like Home Assistant. Participants emphasize the importance of careful planning to avoid space issues in the switchboard and suggest using wireless solutions for flexibility. Various relay options, including the use of dimmers instead of relays, are discussed, along with the need for a standardized control voltage. The conversation also touches on the integration of alarm systems and the potential for using LED strips and smart bulbs for enhanced lighting control.