Why does my BK7231N/CB3S door sensor only wake from deep sleep when it was asleep with the reed open, and how do I make wake-up work in the closed state too?

Set the wake-up edge to match the sensor’s idle level before sleep: the working fix was `DSEdge 1` for the low-level wake-up case, and another user later confirmed that this solved the same problem for them [#20542881][#20826289] For the original reed-switch wiring, the working combination was `DoorSnsrWSleep_nPup` with a forced edge of `0`; for a direct GPIO-to-GND test setup, `DoorSnsrWSleep` with a forced edge of `1` was needed [#20542881] The issue was that the sensor must wake on the same state it will be in after deep sleep, otherwise opening/closing the reed does not generate the expected wake event [#20542881] If you need to set multiple startup commands, use Tasmota-style `backlog ...; ...;` syntax rather than separating commands with plain semicolons [#20543214]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • Wake-up fails if reed switch is closed before sleep

    #1 20534749
    nihildiximus
    Level 9  
    Posts: 32
    Help: 1
    Rate: 23
    Czujnik kupiony na tej aukcji (snapshot): https://allegro.pl/oferta/autonomiczny-czujni...jYmZhMmNmYjk2YTE4NjY3ZWQzOWQ5NDlhYTZmOTgyNTk=

    1. Connected by CH341A programmer. Shorting CEN to GND for a moment allows you to download and save the flash memory.
    2. BK7231GUIFlashTool via mono on linux turned out to be useless and throws the same error every time as in many other forum threads:

    Quote:
    Going to start reading at offset 0x00...
    Reading 0x00... failed with serial.BytesToRead 4095 (expected 4111)
    The beginning of buffer in UART contains 040EFF01E0FCF4061009000000200069 data.
    failed! There was no result to save.

    3. uartprogram with hid_download_py it works without any problem.
    4. Loaded OpenBK7231N_QIO_1.15.668.bin
    5. Leads as in the picture below.

    pin 5 = GPIOP_26 PWM5 - (Btn 1 0) battery case button
    pin 10 = GPIOP_9 = PWM 3 = (LED 0) diode-
    pin 14 = GPIPP_7 = PWN_1 = (DoorSensorWSleep_nPup 0 [regular DoorSensWSleep doesn't work at all]) reed switch

    Using CH341A Programmer for BK7231N/CB3S Door/Window Sensor PB-69W VER 1.3: UART & OpenBK7231N_QIO

    6. The LED lights up after the reed switch is opened, and goes out after the short circuit and the information goes through the MQTT to HomeAssistant. Time until deep sleep is also extended correctly. However, wake-up only works when the sensor has entered deep sleep in the open reed (off) position. When the magnet shorts it (on) and in this state it is put to sleep, there is no possibility of waking up and a reset by turning the power off and on again is necessary.
  • ADVERTISEMENT
  • Try the _pd pin with version 1.15.674

    #2 20535312
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14782
    Help: 659
    Rate: 12920
    Hello, it seems that your device has a slightly different electronically implemented sensor than devices that I had reported as working with the controller. Maybe it's a matter of pull up or down resistors. Does the reed switch have such on the PCB?

    It's hard to say anything more remotely, but I have an idea - if the programmable pull up version and without resistors doesn't work for you, maybe the pull down version will work?

    I uploaded an update. Version 1.15.674. Select the _pd pin and try again:
    Using CH341A Programmer for BK7231N/CB3S Door/Window Sensor PB-69W VER 1.3: UART & OpenBK7231N_QIO
    Helpful post? Buy me a coffee.
  • #3 20535429
    nihildiximus
    Level 9  
    Posts: 32
    Help: 1
    Rate: 23
    p.kaczmarek2 wrote:
    I uploaded an update. Version 1.15.674. Select the _pd pin and try again:


    The reed switch works, but there is no countdown to deep sleep at all. It also shows 0 drivers active instead of 1 driver active (DoorSensor) as before.
  • Manual startDriver fix for DoorSensor autostart bug

    #4 20535432
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14782
    Help: 659
    Rate: 12920
    Ehh, sorry, that's how it is with remote help ... I forgot the condition for autostarting the DoorSensor driver in the case of setting the role of the pin with _pd.
    You either have to manually enter "startDriver DoorSensor" in the commands, at least for a test, once, or wait for the build that has now started (22:25) and download the new version in these 10 minutes, it has it fixed, version 1.15.675.

    Then test it and see if anything works better. If not, we'll think what else could be wrong...

    You can also physically check on the PCB what are the resistances between the reed switch GPIO and ground and 3.3V and give them to me.

    Added after 1 [minutes]:

    One more note, maybe a little helpful:
    nihildiximus wrote:
    there is no possibility to wake up and a reset by turning the power off and on again is necessary.[/b]

    if you set the GPIO of the button as Button, then pressing this button should wake up the sensor anyway. Check and let me know if it works. This is what helps to "emergency" wake up the device.
    Helpful post? Buy me a coffee.
  • ADVERTISEMENT
  • Reed switch shows odd resistance with batteries inserted

    #5 20535478
    nihildiximus
    Level 9  
    Posts: 32
    Help: 1
    Rate: 23
    I had already set the wake-up to reset pin to make it easier, and before I saw the answer, I had already uploaded autoexec.bat to run DoorSensor. However, the result is the same, i.e. it does not wake up after entering sleep when the magnet is applied.
    The GPIO of the reed switch to Vcc has no transition, and strange things happen with GND, because with the sensor off (switch) but with batteries inserted, the meter in the 2000Ω mode shows me 1700Ω, with the 20k setting it shows 4.6kΩ, and in the 200k mode 25.8kΩ. No connection with batteries removed.
  • Suggests trying another firmware version

    #6 20535553
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14782
    Help: 659
    Rate: 12920
    It's weird. I checked on my board with CB3S in the configuration shorting the GPIO to ground or power and it works for me:
    Using CH341A Programmer for BK7231N/CB3S Door/Window Sensor PB-69W VER 1.3: UART & OpenBK7231N_QIO
    Test layout:
    Using CH341A Programmer for BK7231N/CB3S Door/Window Sensor PB-69W VER 1.3: UART & OpenBK7231N_QIO Using CH341A Programmer for BK7231N/CB3S Door/Window Sensor PB-69W VER 1.3: UART & OpenBK7231N_QIO
    I need to figure out how to reproduce your problem.

    But I have another idea - try using maybe this version:
    Attachments:
    • test-czujnika-drzwi20230411.zip (611.76 KB) You must be logged in to download this attachment.
    Helpful post? Buy me a coffee.
  • Closed reed switch sleep leaves GPIO stuck high

    #7 20535562
    nihildiximus
    Level 9  
    Posts: 32
    Help: 1
    Rate: 23
    It is still the same with this fw, i.e. it wakes up nicely when it falls asleep with the reed switch open, but sleep with the closed one is eternal. Apparently, falling asleep with a closed reed switch does more than falling asleep with an open one.

    I also checked the voltage on the reed switch pin with GND and it is 2.6V when closed, 0 when open (normally and during sleep). But when it goes to sleep, it jumps to 3.3V when closed and after opening, it maintains 3.3V all the time.

    EDIT: However, there is a difference in sleep in the open state, because before the diode was constantly on, and now it goes out and only applying a magnet wakes it up again.

    EDIT: Shorting the GPIO to ground wakes up the sensor dormant in the closed state. However, apparently opening the reed switch does not short GPIO with GND when the sensor was put to sleep in this state.

    EDIT: From what I see it is the same as this: https://www.elektroda.pl/rtvforum/topic3959677.html#20453815 only with me ver. 1.3 and not 1.4.
  • ADVERTISEMENT
  • 10 kΩ pull-down test for wake-up issue

    #8 20535617
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14782
    Help: 659
    Rate: 12920
    Indeed, it looks like you have exactly the same technical problem as @4139ggn . I'm not sure what else I can do at the moment, because basically we can only set the pin to input mode, either input_pullup or input_pulldown, there's nothing else to do here. You could also combine and dynamically set the mode to pullup or pulldown just before the start of sleep, depending on whether we read on pin 0 or 1, but it probably won't do anything.

    I had a similar door sensor but on XR809, and XR809 I desoldered for testing, maybe I can find its board and try to reproduce your problem on a physical device.

    Quote:

    EDIT: Shorting the GPIO to ground wakes up the sensor dormant in the closed state. However, apparently opening the reed switch does not short GPIO with GND when the sensor was put to sleep in this state.

    when testing at home, I short-circuit directly to ground / VDD and therefore I am not able to reproduce your problem. I thought pullingdown with this might help, but apparently it didn't help anyway.... That's the _pd we tested.


    If you have a moment of time and, for example, you have a soldering iron and a resistor, e.g. 10k, you can do an experiment and check whether, for example, soldering 10k between the sensor's GPIO and ground will help wake up from closed mode ...
    Helpful post? Buy me a coffee.
  • Sleep wakeup works only in open position

    #9 20535826
    nihildiximus
    Level 9  
    Posts: 32
    Help: 1
    Rate: 23
    Now it wakes up in the closed state, but no longer wakes up in the open state, so the situation has simply reversed.
    I also checked the soldering of the reed switch directly to GPIO and Vcc and on standby the switching works, but after falling asleep it also cannot be woken up.

    EDIT: For the test, I soldered the switch directly to the free GPIO next to GND and set it to the usual DoorSnsrWSleep (then those don't work). It wakes up from sleep in the open position, and when it sleeps in the closed position it does not.
  • Repository firmware still fails to wake from closed switch

    #10 20536852
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14782
    Help: 659
    Rate: 12920
    nihildiximus wrote:

    EDIT: For the test, I soldered the switch directly to the free GPIO next to and GND and set it to the usual DoorSnsrWSleep (then those don't work). It wakes up from sleep in the open position, and when it sleeps in the closed position it does not.

    Do I understand correctly - the switch is between GND and GPIO, and the DoorSnsrWSleep role is set and it does not wake up anyway?
    Which firmware version - the test private one or the last one from the repository?
    The one from the repository, check it out.
    Helpful post? Buy me a coffee.
  • Reed switch works directly on GPIO and GND

    #11 20536934
    nihildiximus
    Level 9  
    Posts: 32
    Help: 1
    Rate: 23
    p.kaczmarek2 wrote:
    Do I understand correctly - the switch is between GND and GPIO, and the DoorSnsrWSleep role is set and it does not wake up anyway?

    Yes. That's what I did for the test on another GPIO and it wakes up only when it falls asleep on an open one, and not on a short one.
    p.kaczmarek2 wrote:
    Which firmware version - the test private one or the last one from the repository?
    The one from the repository, check it out.

    Private trial version. I will check with the repo version, but I won't be able to do it until Sunday or Monday. I'll let you know, because if the reed switch works directly connected to the GPIO and GND, it's probably easier to use such a small modification of the system than to combine what's going on there that it doesn't want to work in the original setting. Btw. is there any option to reduce the standby time and/or the time from waking up to sending payload via mqtt?
  • Quick wifi connect and shorter standby timing

    #12 20536977
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14782
    Help: 659
    Rate: 12920
    The private trial version is not authoritative, I just wanted to check something.

    Tomorrow I will check what you write on my dev board, I am convinced that it should work, because in this topic:
    https://www.elektroda.pl/rtvforum/topic3960149.html
    it was working and not moving. In addition, users of smoke detectors made in a similar way reported that they had approx.


    nihildiximus wrote:
    Btw. is there any option to reduce the standby time and/or the time from waking up to sending payload via mqtt?

    There is a "quick wifi connect" flag or something, which will then be permanently enabled, we just had some strange instabilities a year ago when we turned on WiFi too early and therefore it is a flag to be selected (and not enabled by default).

    I'm going to change the standby time so that after the response from MQTT that it received the status, the sensor immediately fell asleep again, but I have to check if there is such an option in the MQTT library used (with LWIP)

    But if you want to artificially shorten the timing time for now, it's no problem for me to give this time to the autoexec.bat command.
    Helpful post? Buy me a coffee.
  • Helpful post

    Opposite wake level needed for deep sleep input

    #13 20542631
    nihildiximus
    Level 9  
    Posts: 32
    Help: 1
    Rate: 23
    flash: OpenBK7231N_1.16.2.rbl
    Reed switch directly soldered to unused GPIO 8 (PWM 2) and GND.
    It correctly signals 1 and 0 with DoorSnsrWSleep and DoorSnsrWSleep_nPup.
    Identical situation - no waking up when it falls asleep with a short circuit, but it wakes up when it falls asleep with a gap and the magnet moves closer.

    EDIT:
    I found a solution by deduction - the same state must be used to wake up:

    new_pins.c
    [syntax=c]
    // door input always uses opposite level for wakeup
    for (i = 0; i < PLATFORM_GPIO_MAX; i ) {
    if (g_cfg.pins.roles[i] == IOR_DoorSensorWithDeepSleep
    || g_cfg.pins.roles[i] == IOR_DoorSensorWithDeepSleep_NoPup
    || g_cfg.pins.roles[i] == IOR_DigitalInput
    || g_cfg.pins.roles[i] == IOR_DigitalInput_n
    || g_cfg.pins.roles[i] == IOR_DigitalInput_NoPup
    || g_cfg.pins.roles[i] == IOR_DigitalInput_NoPup_n) {
    //value = CHANNEL_Get(g_cfg.pins.channels[i]);
    value = HAL_PIN_ReadDigitalInput(i);
    //if (value) {
    // on falling edge wake up
    falling = 1; //
  • Suggesting a flag for door sensor wake polarity

    #14 20542751
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14782
    Help: 659
    Rate: 12920
    Are you sure? If it actually works then good job, I wouldn't have thought of that myself. The above code always sets the wake-up on a falling edge on a given GPIO, so theoretically if the sensor is 0 in the sleep state and 1 appears when the door is opened, then we will have a rising edge and the sensor will not wake up.

    What's most interesting, I'm currently testing with a user who has a door sensor based on a different type of sensor (Hall sensor) and the current solution works for him:
    Using CH341A Programmer for BK7231N/CB3S Door/Window Sensor PB-69W VER 1.3: UART & OpenBK7231N_QIO

    In your version, I would have to add 3 separate DoorSensor roles - because with pull up, pull down, and without.

    Maybe it's better to add a flag for that? In Config->Flags?
    Helpful post? Buy me a coffee.
  • Wakeup polarity flags needed for door sensor modes

    #15 20542881
    nihildiximus
    Level 9  
    Posts: 32
    Help: 1
    Rate: 23
    The situation is that the solution works if you use the direct connection of the switch to a free GPIO and GND. However, with the original setting of the reed switch, no. FW without modification, in turn, does not work either with the original setting or with direct plugging of the reed switch in GPIO and GND. I will test further, because it would be good to run it with the original connection ... Anyway, it's worth adding a flag that would set the same state for waking up regardless of the state of falling asleep, because it may be useful. ;)

    EDIT:

    SOLVED!
    1. For free GPIO GND you need DoorSnsrWSleep and falling =1 hard for both states.
    2. For original connections you need DoorSnsrWSleep_nPup and hard falling = 0 for both states.

    I think it's best to just add two flags in config with the setting of rigidly falling to zero or one, so as not to multiply the number of entries from DoorSnsr and in new_pins.c a conditional instruction that will check if any is selected and if so, then set it rigidly, omitting setting opposite level.

    I guess something like this would suffice:

    Code: C / C++
    Log in, to see the code


    EDIT:
    It would also be good to replace the constant setting_timeRequiredUntilDeepSleep = 60 in driver/drv_doorSensorWithSeepSleep.c with a variable that could be set in autoexec, because a minute is good as a default value for testing, but after configuring the device, a shorter time is enough, which can be changed without need to upload new fw. ;)
  • Door sensor edge handling and sleep timeout variable

    #16 20543157
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14782
    Help: 659
    Rate: 12920
    I added the flag before you edited your post. The build should be ready. Only the flag sets falling = 1 hard. It doesn't support the second situation you wrote about. Ew. I'll give you a second flag...

    Either I clear the flag and give defaultDoorSensorEdge = 2 or 0 or 1

    nihildiximus wrote:

    1. For free GPIO + GND you need DoorSnsrWSleep and falling =1 hard for both states.

    I have this configuration for buttons (more precisely: Button role, it sets pull up and always has falling = 1), but this is assuming that the button is open by default and the user shorts it only for a moment with ground. This is different from a switch that has two states of stability - either open or closed.

    nihildiximus wrote:

    It would also be good to replace the constant setting_timeRequiredUntilDeepSleep = 60 in driver/drv_doorSensorWithSeepSleep.c to use a variable that could be set in autoexec, because a minute is good as a default value for testing, but after configuring the device, a shorter time is enough, which can be changed without need to upload new fw. ;)

    This question has already appeared, I can put it in a variable for now, but ultimately the plan is to check the MQTT response to publish and then turn off.
    Helpful post? Buy me a coffee.
  • Autoexec suggested for exceptional sensor settings

    #17 20543190
    nihildiximus
    Level 9  
    Posts: 32
    Help: 1
    Rate: 23
    p.kaczmarek2 wrote:
    Either I clear the flag and give defaultDoorSensorEdge = -1 or 0 or 1


    All in all, it's probably best to set such things by autoexec, because it will be for exceptional situations anyway. But as for the time to fall asleep, I think it's better to leave the default 60 seconds to avoid problems during configuration, leaving the variable in autoexec, where you can either specify the time, or give e.g. 0 which will only wait for MQTT when everything is checked. But that's just my suggestion. :)
  • #18 20543206
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14782
    Help: 659
    Rate: 12920
    I'll convert the flag to command tomorrow.

    As for 60 seconds, it seems to me that it is very easy to program the DoorSensor controller so that pressing the button on the housing (the one for pairing - always present) turns on the configuration mode, where the sensor falls asleep, e.g. after 120 seconds. Without this press, he would fall asleep as soon as possible.
    Helpful post? Buy me a coffee.
  • #19 20543212
    nihildiximus
    Level 9  
    Posts: 32
    Help: 1
    Rate: 23
    Setting the button is a simple matter, but I'm wondering if someone first sets up mqtt and a reed switch, then they won't lose the ability to enter the configuration in a moment and there won't be a multitude of threads on the forum asking what to do in such a situation. ;)
  • #20 20543214
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14782
    Help: 659
    Rate: 12920
    There is always a safe mode - five quick power on and off. You'd need a battery here.

    Added after 10 [hours] 35 [minutes]:

    Added commands:
    https://github.com/openshwprojects/OpenBK7231T_App/blob/main/docs/commands.md
    DSEdge
    DSTime
    Helpful post? Buy me a coffee.
  • Delayed MQTT after wake loses door events

    #21 20546015
    nihildiximus
    Level 9  
    Posts: 32
    Help: 1
    Rate: 23
    DSTime does not work in startup command when I type: DSEdge 0; DSTime 15;
    When run as a single command on a regular basis it pops up, but after waking up it's 60 seconds again.

    But there is also a critical problem that practically prevents the sensor from working properly…

    Wifi connection after waking up is very slow and it wouldn't be a critical problem (although it's still a big difference with the original fw, because it's a good half a minute and the quick connect flag doesn't change anything, and with the original maybe a second or two) if it wasn't for that when it happens, it will does not send mqtt with information about the state change that occurred before it was established. In other words, the usual opening and closing time of the door behind each other is 2 to max. 5 seconds (longer only if something is brought into the house). The thief will do it even faster. The sensor wakes up as it should with the DSEdge option, but apparently fw only checks the status when connected, instead of doing it immediately and storing the event queue until wifi is connected to send it (here it is necessary to payload with the state and timestamp, not the state itself to have a full chronology of events). Practically in the current situation no simple door opening and closing behind you is recorded at all in the event log and thus the sensor unfortunately becomes completely useless ...
  • #22 20546042
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14782
    Help: 659
    Rate: 12920
    DSEdge and DSTime had one issue due to copy/paste, it was fixed today as the contributor tested it about 15, latest versions should have it working.

    In what format do you want to have a report with time to HA? Does HA even have the ability to accept a report over time?

    Sending the 'first' state is easy to do, but I don't know about the timestamp at the moment.
    Helpful post? Buy me a coffee.
  • Suggesting MQTT timestamp endpoints and queued states

    #23 20546080
    nihildiximus
    Level 9  
    Posts: 32
    Help: 1
    Rate: 23
    I checked DSTime in OpenBK7231N_1.17.8.rbl downloaded maybe an hour ago.

    And as for mqtt, I really do not see that it is possible to enter the time of occurrence of a specific state into HA, but you can probably do a workaround in the form of:

    - queuing states when the connection has not been established and sending them in turn after connection;
    - creating two new mqtt endpoints - in addition to doors/0/get, you can also add doors/0/laston and doors/0/lastoff with a timestamp (separate entities), then even if the connection to wifi is delayed, it will be saved in the logs exact opening and closing times.

    EDIT:
    Isn't it so that the original fw does not disconnect from wifi when entering deepsleep? I guess after waking up it doesn't connect again and doesn't download the dhcp address again and maybe that's why it works faster. Can something like this be implemented?
  • Helpful post

    Quick fix for door state MQTT logging after reboot

    #24 20546210
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14782
    Help: 659
    Rate: 12920
    I just added a quick fix for the issue raised in the post: >>20546015 . At the moment, the soft after reboot remembers the pin state, and DoorSensor sends it via MQTT for the first two seconds (by force) and then sends the current state.

    This solution will ensure that at least one second of door opening (or closing) will be recorded in the logs, only the actual door opening time will be distorted due to the lack of timestamps. Anyway, the trace after closing the door will be, tested now:
    Using CH341A Programmer for BK7231N/CB3S Door/Window Sensor PB-69W VER 1.3: UART & OpenBK7231N_QIO

    Deep Sleep is a complete shutdown of almost everything in the CPU, so even if it didn't "disconnect" it would be dropped by DHCP after the lease expired anyway, so I don't think it would be like that...

    However, today with the contributor we added two small improvements, namely MQTT should connect faster (improvement of the connection logic) and we added the option static IP which also speeds up.

    How fast are you connecting to MQTT? 7 seconds for me:
    
    Info:MAIN:Main_Init_Before_Delay
    Info:CFG:####### Boot Count 67 #######
    Warn:CFG:CFG_InitAndLoad: Correct config has been loaded with 22 changes count.
    Error:CMD:lfs is absent
    Info:MAIN:Started DoorSensor.
    Info:GEN:PIN_SetupPins pins have been set up.
    Info:MAIN:Main_Init_Before_Delay done
    Info:MAIN:Main_Init_Delay
    Info:GEN:CHANNEL_Set channel 0 has changed to 1 (flags 0)
    
    Info:MQTT:Channel has changed! Publishing 1 to channel 0 
    Info:MAIN:Main_Init_Delay done
    Info:MAIN:Main_Init_After_Delay
    Info:MAIN:ssid:qqqqqqqqqqqqq
    Info:MAIN:Using SSID [qqqqqqqqqqqq]
    Info:MAIN:Using Pass [qqqqqqqqqqqqqq]
    Info:MQTT:MQTT_RegisterCallback called for bT obkDoorN/ subT obkDoorN/+/set
    Info:MQTT:MQTT_RegisterCallback called for bT cmnd/obkDoorN/ subT cmnd/obkDoorN/+
    Info:MQTT:MQTT_RegisterCallback called for bT obkDoorN/ subT obkDoorN/+/get
    Info:HTTP:DRV_SSDP_Init - no wifi, so await connection
    Info:MAIN:Started SSDP.
    Info:NTP:NTP driver initialized with server=217.147.223.78, offset=0
    Info:MAIN:Started NTP.
    Error:CMD:LFS_ReadFile: lfs is absent
    Info:CMD:CMD_StartScript: failed to get file autoexec.bat
    Info:MAIN:Main_Init_After_Delay done
    Info:MAIN:Time 1, idle 280330/s, free 73856, MQTT 0(0), bWifi 0, secondsWithNoPing -1, socks 2/38 
    Info:MAIN:Time 2, idle 185265/s, free 73856, MQTT 0(0), bWifi 0, secondsWithNoPing -1, socks 2/38 
    Info:MAIN:Time 3, idle 68683/s, free 73960, MQTT 0(0), bWifi 0, secondsWithNoPing -1, socks 2/38 
    Info:MAIN:Time 4, idle 0/s, free 73960, MQTT 0(0), bWifi 0, secondsWithNoPing -1, socks 2/38 
    Info:MAIN:Time 5, idle 0/s, free 73960, MQTT 0(0), bWifi 0, secondsWithNoPing -1, socks 2/38 
    Info:MAIN:Main_OnWiFiStatusChange - WIFI_STA_CONNECTING - 1
    Info:MAIN:Main_OnWiFiStatusChange - WIFI_STA_CONNECTED - 4
    Info:MQTT:mqtt_userName homeassistant
    mqtt_pass ma1oovoo0pooTie7koa8Eiwae9vohth1vool8ekaej8Voohi7beif5uMuph9Diex
    mqtt_clientID obkDoorN
    mqtt_host 192.168.0.113:1883
    Info:MAIN:Time 6, idle 107681/s, free 74208, MQTT 0(1), bWifi 1, secondsWithNoPing -1, socks 2/38 
    Info:MAIN:Boot complete time reached (5 seconds)
    Info:CFG:####### Set Boot Complete #######
    Info:MQTT:mqtt_connection_cb: Successfully connected
    Info:MQTT:mqtt_subscribed to obkDoorN/+/set
    Info:MQTT:mqtt_subscribed to cmnd/obkDoorN/+
    Info:MQTT:mqtt_subscribed to obkDoorN/+/get
    Info:MQTT:Publishing val 0 to obkDoorN/0/get retain=0
    Info:MAIN:Time 7, idle 176455/s, free 62544, MQTT 1(1), bWifi 1, secondsWithNoPing -1, socks 3/38 
    Info:MQTT:MQTT client in mqtt_incoming_publish_cb topic obkDoorN/0/get
    

    The testers are more or less the same:
    Using CH341A Programmer for BK7231N/CB3S Door/Window Sensor PB-69W VER 1.3: UART & OpenBK7231N_QIO

    Added after 10 [minutes]:

    What you wrote with timestamps separately is also a nice idea, I can add it soon, but not today. We already have NTP, just start the NTP driver and then when it's time from the network, subtract how much has elapsed since the first measurement and send it.

    Added after 3 [minutes]:

    EDIT: I think I need to check the download of the door state directly after the reboot. Anyway, I'll look into it in the morning.

    Added after 4 [minutes]:

    EDIT2: ah, I already know, I'm throwing the fix yet.
    Helpful post? Buy me a coffee.
  • Fixed IP reduces HA sensor update delay

    #25 20546258
    nihildiximus
    Level 9  
    Posts: 32
    Help: 1
    Rate: 23
    With the new fw, the symptoms are:

    - Setting "DSEdge 0; DSTime 15;" in "Set/Change/Clear startup command line" doesn't change anything. Still 60 sec. countdown.

    - After setting a fixed IP, the time was significantly shortened - in HA, the open state appears within 6 seconds and the closed state within 9 seconds (it's strange that both states do not pop up at once, one after the other). It's a bit slower than with the original fw (I checked again and it's 1-2 sec. state change in HA via localTuya), but acceptable, although I don't understand where this 3 sec. delay when sending the second state (I test by doing a quick disconnect and reconnection).

    EDIT:
    As for DSTime, the problem is only with the setting from the config level (maybe it ignores the second cmd?), because in autoexec.bat it works without a problem.
  • Need WiFi and MQTT connection timing logs

    #26 20546271
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14782
    Help: 659
    Rate: 12920
    We have Tasmota syntax, I haven't added automatic semicolon separation yet, you have to write backlog cmdA xyz; cmdB abc; etc , in fact, there is even a "use backlog" comment on this page.

    These 3 seconds between sending the first remembered state and the current state are in my driver, it's not a problem. I don't know how HA would react if he received a packet with the value open and then closed at the same time...

    For the rest, in the Web App Log, how long does it take you to connect to WiFi and how long to connect to MQTT? This message obk Time 1, etc etc has further MQTT (1) and WiFi (1) (or 0) tags and can be determined after that.
    Helpful post? Buy me a coffee.
  • MQTT delay needed to preserve message order

    #27 20546280
    nihildiximus
    Level 9  
    Posts: 32
    Help: 1
    Rate: 23
    It seems to me that between sending mqtt a delay, max. 1 sec. because it's just about keeping the order of the messages. This would probably be the last fix and I can start making a full tutorial for this sensor. :)

    EDIT:
    
    mqtt_host 192.168.100.200:1883
    Info:MAIN:Time 6, idle 109507/s, free 73672, MQTT 0(1), bWifi 1, secondsWithNoPing -1, socks 2/38 
    Info:MAIN:Boot complete time reached (5 seconds)
    Info:CFG:####### Set Boot Complete #######
    


    EDIT2:
    After a long sleep, the time increases significantly for some reason:
    
    mqtt_host 192.168.100.200:1883
    Info:MAIN:Time 19, idle 176735/s, free 73568, MQTT 0(1), bWifi 1, secondsWithNoPing -1, socks 2/38 
    Info:MQTT:mqtt_connection_cb: Successfully connected
    
  • Battery setup and MQTT state publishing test results

    #28 20546308
    DeDaMrAz
    Level 23  
    Posts: 621
    Help: 34
    Rate: 130
    Here is what I got by testing build 1.17.10 and this autoexec.bat

    Battery_Setup 2000 3000 1.885 2400 4096
    Battery_cycle 2
    mqtt_broadcastInterval 1
    mqtt_broadcastItemsPerSec 3
    addEventHandler OnHold 20 SafeMode 5
    DSTime 5


    Using CH341A Programmer for BK7231N/CB3S Door/Window Sensor PB-69W VER 1.3: UART & OpenBK7231N_QIO

    Both states are published on mqtt connect, previous and new - this is in an event that sensor activation is done quickly (less than 1s between state changes) and before mqtt connect, so there is a log in HA.
  • Safer safe mode with delayed reboot or longer hold

    #29 20546462
    p.kaczmarek2
    Moderator Smart Home
    Posts: 14782
    Help: 659
    Rate: 12920
    @DeDaMrAz , if you change
    
    addEventHandler OnHold 20 SafeMode 5
    

    to:
    
    addEventHandler OnHold 20 backlog DSTime 6000; SafeMode 5
    

    you will get a bit more fool-proof safe mode, because otherwise device can go to sleep before safe mode will reboot.

    You can also consider:
    
    addEventHandler OnHold 20 DSTime 600
    

    this would just give more time on button hold... maybe it's even better... hm.
    Helpful post? Buy me a coffee.
  • ADVERTISEMENT
  • #30 20546730
    Adi13089
    Level 11  
    Posts: 22
    Rate: 4
    Will there be any config for setting a fixed IP address on the device?
    For some reason the DHCP server doesn't want to assign me an address for the device.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around using the CH341A programmer to interface with the BK7231N/CB3S door/window sensor (PB-69W VER 1.3) and the OpenBK7231N_QIO firmware. Users report issues with the sensor not waking up from deep sleep when the reed switch is closed, despite various firmware updates and configurations. Solutions proposed include adjusting GPIO settings, using different firmware versions, and implementing specific commands like "DSEdge" to manage wake-up behavior. The conversation highlights the importance of correctly configuring pull-up and pull-down resistors and the need for firmware modifications to ensure proper functionality. Users also discuss the challenges of MQTT connectivity and the timing of state changes after waking from sleep.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: Ten FAQ pomaga osobom flashującym PB-69W VER 1.3; klucz to „DSEdge 1” oraz firmware po 1.17.10, bo sensor potrafił spać 60 s i nie budzić się z jednego stanu kontaktronu. [#20826289]

Dlaczego to ważne: Zła krawędź wybudzania lub wyczyszczona partycja RF może zmienić czujnik drzwi w urządzenie, które nie raportuje włamań ani nie łączy się z WiFi.

Metoda / ustawienie Konkret z wątku Efekt
BK7231GUIFlashTool przez mono błąd serial.BytesToRead 4095, oczekiwano 4111 odczyt flash nie zapisuje wyniku
uartprogram + hid_download_py działało bez problemu pozwoliło wgrać OpenBK7231N_QIO
DHCP po deep sleep MQTT nawet po 19 s po dłuższym śnie wolniejsze raportowanie
Statyczny IP stan „open” po 6 s, „closed” po 9 s akceptowalne raportowanie w HA
DSEdge 0 lub 1 jako stała krawędź naprawia wybudzanie w nietypowych układach

Kluczowa obserwacja: PB-69W VER 1.3 wymaga dobrania stałej krawędzi wybudzania, a nie tylko roli GPIO. Dla jednego układu pomogło DSEdge 1, a dla oryginalnego połączenia testowano wariant DSEdge 0.

Quick Facts

  • Czujnik PB-69W VER 1.3 z modułem CB3S/BK7231N został najpierw podłączony przez CH341A, a chwilowe zwarcie CEN do GND pozwoliło odczytać i zapisać flash. [#20534749]
  • Konfiguracja pinów z działającego opisu: pin 5 jako Btn 1, pin 10 jako LED 0, pin 14 jako DoorSensorWSleep_nPup dla kontaktronu. [#20534749]
  • W pomiarach kontaktron miał 2,6 V względem GND po zamknięciu, 0 V po otwarciu, a po wejściu w sleep napięcie dochodziło do 3,3 V i utrzymywało się. [#20535562]
  • Po ustawieniu stałego IP raport w Home Assistant pojawiał się po około 6 s dla otwarcia i 9 s dla zamknięcia; bez tego po dłuższym śnie MQTT połączył się dopiero przy Time 19. [#20546258]
  • Jeżeli flasher wykona Clear all na całych 2 MB flash, urządzenie może stracić partycję RF i dostać domyślny MAC kończący się zerami. [#20546804]

How do I flash a BK7231N/CB3S PB-69W VER 1.3 door/window sensor with a CH341A programmer and OpenBK7231N_QIO firmware?

Flash wykonaj przez UART, po wcześniejszym wykonaniu kopii pamięci flash. 1. Podłącz CH341A do modułu CB3S/BK7231N i chwilowo zewrzyj CEN do GND. 2. Odczytaj oraz zapisz flash; w wątku uartprogram z hid_download_py działał poprawnie. 3. Wgraj OpenBK7231N_QIO_1.15.668.bin, a później zaktualizuj OTA do nowszego .rbl, np. 1.17.10. Nie używaj Clear all, bo kasuje sekcje RF. [#20534749]

Why does BK7231GUIFlashTool on Linux with mono fail with serial.BytesToRead errors when reading BK7231N flash, and why might uartprogram with hid_download_py work instead?

Błąd wynikał z nieudanego odczytu bufora UART w środowisku mono na Linuksie. Narzędzie pokazało serial.BytesToRead 4095, gdy oczekiwało 4111, i nie zapisało wyniku. Ten sam użytkownik odczytał układ bez problemu przez uartprogram z hid_download_py. W praktyce warto traktować ten zestaw jako obejście dla wadliwego odczytu przez mono. [#20534749]

What pin roles should be configured in OpenBeken for the PB-69W VER 1.3 sensor’s button, LED, and reed switch?

Ustaw pin 5 jako przycisk, pin 10 jako LED, a pin 14 jako kontaktron z wariantem bez pull-up. Konkretny opis podał: pin 5 GPIOP_26 PWM5 jako Btn 1, pin 10 GPIOP_9 PWM3 jako LED 0, oraz pin 14 GPIOP_7 PWM1 jako DoorSensorWSleep_nPup. Zwykły DoorSensWSleep nie działał w tej konfiguracji. [#20534749]

What is DSEdge in OpenBeken, and how does it fix door sensor wake-up problems after deep sleep?

DSEdge ustawia stałą krawędź GPIO używaną do wybudzania czujnika drzwi. „DSEdge” jest komendą OpenBeken, która wymusza krawędź wybudzania dla DoorSensor, zamiast wybierać ją automatycznie według stanu pinu przed sleep. W opisanym przypadku DSEdge 1 naprawił brak wybudzania po deep sleep w stanie LOW. [#20826289]

What is DSTime in OpenBeken, and how can it be used to change the time before a door sensor enters deep sleep?

DSTime zmienia czas oczekiwania przed wejściem czujnika drzwi w deep sleep. „DSTime” jest komendą OpenBeken, która ustawia zwłokę usypiania sterownika DoorSensor, zwykle krótszą niż domyślne 60 sekund po konfiguracji. W testach użyto DSTime 5, DSTime 15, DSTime 600 i DSTime 6000. Dla wielu komend w jednej linii użyj składni backlog. [#20546308]

Why does a BK7231N door sensor wake from deep sleep only when the reed switch slept in one state but not the other?

Czujnik budził się tylko z jednego stanu, bo firmware wybierał przeciwną krawędź wybudzania niż wymagała elektronika kontaktronu. Gdy kontaktron zasypiał otwarty, wybudzanie działało. Gdy zasypiał zwarty magnesem, urządzenie wymagało resetu zasilania. Pomiary pokazały 2,6 V po zamknięciu, 0 V po otwarciu oraz 3,3 V po sleep. Stałe DSEdge rozwiązało ten typ problemu. [#20535562]

How do DoorSnsrWSleep, DoorSnsrWSleep_nPup, and DoorSensorWSleep_nPup differ in OpenBeken?

Te role różnią się głównie obsługą wejścia i pull-up dla czujnika drzwi z deep sleep. DoorSnsrWSleep działał przy bezpośrednim połączeniu wolnego GPIO z GND. DoorSnsrWSleep_nPup sygnalizował stany 1 i 0 przy GPIO 8 i GND. W oryginalnym połączeniu PB-69W potrzebny był wariant DoorSensorWSleep_nPup oraz stała krawędź wybudzania. [#20542631]

What is the difference between using a pull-up, no-pull-up, and pull-down GPIO configuration for a reed switch on BK7231N?

Pull-up, no-pull-up i pull-down zmieniają stan spoczynkowy oraz krawędź widzianą przez BK7231N. „Pull-up” jest konfiguracją wejścia GPIO, która podciąga pin do 3,3 V, gdy zewnętrzny styk go nie wymusza. Wersja _pd miała testować podciąganie w dół, ale początkowo nie uruchamiała sterownika DoorSensor. Autor firmware dodał poprawkę w 1.15.675. [#20535432]

CH341A vs UART flashing tools — which method is more reliable for backing up and flashing a BK7231N CB3S module?

W tym wątku bardziej niezawodny okazał się UART przez uartprogram i hid_download_py. CH341A służył jako interfejs po podłączeniu, a chwilowe zwarcie CEN do GND umożliwiło odczyt flash. Problem pojawił się w BK7231GUIFlashTool przez mono, który zatrzymywał odczyt na serial.BytesToRead 4095. Dlatego najpierw zrób backup, a potem flashuj metodą, która stabilnie czyta układ. [#20534749]

How can I make a BK7231N OpenBeken door sensor report both quick open and close events to MQTT after waking from deep sleep?

Użyj nowszego firmware, który publikuje zapamiętany stan startowy i bieżący stan po połączeniu MQTT. Problem dotyczył typowego otwarcia i zamknięcia drzwi w 2–5 s, zanim WiFi zdążyło wrócić. Poprawka wymuszała publikację pierwszego stanu przez pierwsze 2 s, a potem wysyłała stan aktualny. Tester z buildem 1.17.10 potwierdził publikację obu stanów przy zmianie poniżej 1 s. [#20546308]

Why is WiFi or MQTT reconnection slow after deep sleep on OpenBeken, and how can static IP improve wake-to-report time?

Deep sleep wyłącza prawie cały CPU, więc urządzenie musi ponownie zestawić WiFi i MQTT. Po długim śnie MQTT potrafił połączyć się dopiero przy Time 19. Statyczny IP skrócił raportowanie w Home Assistant do około 6 s dla otwarcia i 9 s dla zamknięcia. Wątek wskazuje też poprawki logiki MQTT w nowszym firmware. [#20546258]

How do I set a fixed IP address in the OpenBeken web interface for a BK7231N device?

Stały IP ustawisz w menu Configure IP, znajdującym się pod Configure Wifi. Opcja pojawiła się dopiero w nowszym firmware, nie w OpenBK7231N_QIO_1.15.699.bin. Zalecana ścieżka aktualizacji to Launch web applicationOTA → pobranie nowszego pliku .rbl, np. 1.17.10, i wrzucenie go przez Drop OTA here. [#20546801]

What is the RF partition on BK7231N, and why can clearing the whole flash cause duplicate MAC address or WiFi connection problems?

Partycja RF przechowuje dane radiowe, w tym adres MAC używany przez WiFi. „Partycja RF” jest obszarem pamięci flash BK7231N, który przechowuje konfigurację radiową urządzenia, w tym unikalny adres MAC potrzebny do poprawnego łączenia z routerem. Operacja Clear all na 2 MB flash może zmienić MAC na domyślny kończący się 0x00, powodując konflikty. [#20546804]

How do I restore the RF partition or MAC address on an OpenBeken BK7231N device after using Clear All in a flasher?

Przywróć partycję RF przez flasher UART albo przez Web Application OpenBeken. W narzędziu UART wybierz Restore RF partition. Alternatywnie otwórz Web Application, przejdź do karty Flash Memory i użyj przycisku Restore RF partition. Ta operacja nadaje nowy losowy MAC i usuwa konflikty po wyczyszczeniu całych 2 MB flash. [#20546804]

What is OpenBK7231N_QIO firmware, and when should I use an RBL OTA update instead of flashing a BIN file?

OpenBK7231N_QIO to wariant firmware OpenBeken dla BK7231N używany przy początkowym flashowaniu plikiem .bin. „OpenBK7231N_QIO” jest obrazem firmware OpenBeken dla układów BK7231N, przygotowanym do startowego wgrywania i dalszej konfiguracji urządzeń Tuya. Po pierwszym uruchomieniu aktualizuj przez OTA plikiem .rbl, bo nowsze wersje dodały DSEdge, DSTime i Configure IP. [#20546801]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT