[CB2S] How to Flash Custom Firmware on Tongou TOVTH-216WTTDA MCB with BK7231N CB2S?

stonacek 261 11
ADVERTISEMENT
  • Helpful post
    #1 21710653
    stonacek
    Level 7  
    This is a teardown and firmware change guide for Tongou DIN mounted MCB temperature and humidity with two 16A switching relay. Model TOVTH-216WTTDA. It has a BK7231N CB2S inside.
    Tongou TOVTH-216WTTDA module with probe cable and connector

    Usage
    The relays can be programmed on the MCU or remotely controlled via TUYA App based on temperature or humidity.
    TUYA app settings screen with relay, temperature, and humidity configurationTUYA app screen showing 17.6°C temperature and 55% humidity readingsTUYA app screen showing relay settings and device control mode options


    Purchased from the Tongou store https://www.aliexpress.com/item/1005009707659555.html
    Tongou relay dimension diagram with display and probe, 82x50x18 mm


    Opening
    Like most MCBs, the rivets/ferrules must be drilled out on one side and pushed through
    Close-up of the back of a Tongou electrical device with markings and mounting hole.

    the faceplate is clipped in on the top and bottom, it will slide out with some gentle prying. The rest of the device will open after this
    Close-up of an electrical terminal block labeled S1 with two wire insertion pointsElectronic module with dual LED displays and three push buttons

    Inside
    Which reveals the CB2S chip and a pair of relays quite tightly packed. There is limited space near the CB2S chip and difficult to get to the VCC, GND, TX, and RX which are on the back of the chip.
    Disassembled electronic module with PCB, relays, and screw terminals visible
    Interior of a smart relay module with visible electronic components


    On the back side is the MCU. The RX and TX traces are again difficult to get to. The MCU's TX (which needs to be disconnected for flashing) isn't visible on the back, and is passed on a VIA hole underneath the MCU.
    PCB with electronic SMD components and four DB9 connectors.

    Disconnecting MCU and flashing
    There are a few options to disconnect the MCU from the CB2S for flashing.
    1. Lift the CB2S - Lifting the chip is usually my preferred method, but it's about 1.5mm space around the tuya chip and other components like the capacitor and relay. I abandoned this method as other components started melting
    2. Lift the TX pin on the MCU. This would probably work fine, but because I can't see how close the TX VIA underneath the MCU is, I decided not to risk it.
    3. the trace traverses underneath the relay, and the only decent opportunity is about 3mm past the relay. Still not a great option, but I did it with two of these without issue.

    Gently scratch the circuit board to reveal the copper trace before the MCU TX VIA. Cut the trace 1mm before the VIA to leave yourself enough room to solder the cut later.
    Close-up of a PCB with highlighted repaired MCU TX trace near CB2S module

    With the MCU disconnected, you can backup and flash the BK7231N as normal with OpenBeken.

    OpenBeken config and tuyaMCU dpids
    DPIDs were captured with the openbeken capture tools, as well as tuya developer json.


    For simplicity, these are summarised in an autoexec.bat below.   
    Updated now using config using SetChannelEnum

    I excluded some configuration for dpid's I'm not using, but have left those ID's in the comments

    autoexec.bat:
    
    /mqtt_broadcastInterval 60
    
    // this large of an autoexec definition currently consumes all heap
    //scheduleHADiscovery 3600
    
    // tuyaMCU store RAW data in /cm?cmnd=Dp must be turned off on this device..
    // it eats memory because the MCU updates the time every 500ms
    setflag 46 0
    
    ntp_setServer 132.163.97.4
    ntp_timeZoneOfs 12:00
    
    startDriver TuyaMCU
    
    tuyaMcu_setBaudRate 115200
    
    // always report paired
    tuyaMcu_defWiFiState 4
    
    // update states any time the temperature changes
    addEventHandler OnChannelChange 27 tuyaMcu_sendQueryState
    
    // 2 switch 1 relay bool - 121 device control must be 2 or 3 (remote mode)
    setChannelType 21 Toggle
    setChannelLabel 21 "Switch 1"
    linkTuyaMCUOutputToChannel 2 bool 21
    
    // 101 switch 2 relay bool - 121 device control must be 2 or 3 (remote mode)
    setChannelType 22 Toggle
    setChannelLabel 22 "Switch 2"
    linkTuyaMCUOutputToChannel 101 bool 22
    
    // 104 Switch 1 Automatic Mode bool
    setChannelType 24 Toggle
    setChannelLabel 24 "Switch 1 Auto Mode"
    linkTuyaMCUOutputToChannel 104 bool 24
    
    // 105 Switch 2 Automatic Mode bool
    setChannelType 25 Toggle
    setChannelLabel 25 "Switch 2 Auto Mode"
    linkTuyaMCUOutputToChannel 105 bool 25
    
    // 27 current temperature /10 - dpId 20 changes C/F
    setChannelType 1 Temperature_div10
    linkTuyaMCUOutputToChannel 27 val 1
    
    // 46 current humidity
    setChannelType 2 Humidity
    linkTuyaMCUOutputToChannel 46 val 2
    
    //102 online state enum; 0 online, 1 offline
    setChannelType 3 ReadOnlyEnum
    setChannelLabel 3 "Online State"
    setChannelEnum 3 0:Online 1:Offline
    linkTuyaMCUOutputToChannel 102 enum 3
    
    // 118 event RO
    setChannelType 4 ReadOnlyEnum
    setChannelLabel 4 "Event Status"
    SetChannelEnum 4 0:Normal "9:Buttons Locked" "10:Local Mode" "11:Remote Control" "12:Any Control"
    linkTuyaMCUOutputToChannel 118 enum 4
    
    // 121 device control mode enum; 0 local_lock, 1 MCU control, 2 OBK control, 3 MCU and Tuya control
    setChannelType 5 Enum
    setChannelLabel 5 "Device Control"
    SetChannelEnum 5 "0:Buttons Locked" "1:Device Control" "2:Remote Control" "3:Any Control"
    linkTuyaMCUOutputToChannel 121 enum 5
    
    // 106 device Power-On Relay behaviour
    setChannelType 6 Enum
    setChannelLabel 6 "Power-on Behaviour"
    SetChannelEnum 6 0:off 1:on 2:memory
    linkTuyaMCUOutputToChannel 106 enum 6
    
    // 107 Switch 1 Automatic Control Mode
    setChannelType 7 Enum
    setChannelLabel 7 "Switch 1 Control Mode"
    setChannelEnum 7 0:Temp 1:Humidity
    linkTuyaMCUOutputToChannel 107 enum 7
    
    // 108 Switch 2 Automatic Control Mode
    setChannelType 8 Enum
    setChannelLabel 8 "Switch 2 Control Mode"
    setChannelEnum 8 0:Temp 1:Humidity
    linkTuyaMCUOutputToChannel 108 enum 8
    
    // 22 Switch 1 Min Temp Set C -10-99
    setChannelType 10 TextField
    setChannelLabel 10 "Switch 1 Min C"
    linkTuyaMCUOutputToChannel 22 val 10
    
    // 110 Switch 1 Max Temp Set C -10-99
    setChannelType 11 TextField
    setChannelLabel 11 "Switch 1 Max C"
    linkTuyaMCUOutputToChannel 110 val 11
    
    // 113 Switch 2 Min Temp Set C -10-99
    setChannelType 13 TextField
    setChannelLabel 13 "Switch 2 Min C"
    linkTuyaMCUOutputToChannel 113 val 13
    
    // 115 Switch 2 Max Temp Set C -10-99
    setChannelType 15 TextField
    setChannelLabel 15 "Switch 2 Max C"
    linkTuyaMCUOutputToChannel 115 val 15
    
    // un-used dpIds
    // 7 cycle time str
    // 20 Temp Unit Convert enum; 0 C, 1 F
    // 28 current temperature F /10
    // 30 Temp correction; -9 - 9
    // 47 Humidity Calibration val -9 - 9
    // 103 probe/proximity switch bool
    // 41 Switch 1 Min Humidity Set -10-99
    // 111 Switch 1 Max Humidity Set -10-99
    // 21 Switch 1 Min Temp Set F 14-212
    // 109 Switch 1 Max Temp Set F 14-212
    // 112 Switch 2 Min Temp Set F 14-212
    // 114 Switch 2 Max Temp Set F 14-212
    // 116 Switch 2 Min Humidity Set val 0-99
    // 117 Switch 2 Max Humidity Set val 0-99
    // 119 switch 1 alarm settings raw
    // 120 switch 2 alarm settings raw
    
    // refresh tuyaMCU after definitions
    tuyaMcu_sendQueryState
    


    with this config and enum support, the obk and home assistant look like this:
    [CB2S] How to Flash Custom Firmware on Tongou TOVTH-216WTTDA MCB with BK7231N CB2S? [CB2S] How to Flash Custom Firmware on Tongou TOVTH-216WTTDA MCB with BK7231N CB2S? [CB2S] How to Flash Custom Firmware on Tongou TOVTH-216WTTDA MCB with BK7231N CB2S?

    Some points to note:
    1. the MCU controls the relays unless DPID 121 enum is set to 2 or 3. In these modes, openbeken can control the relays
    2. the physical MCU programming is painful and documentation isn't especially clear.
    3. programming the MCU via dpid's is slightly easier. See MCU configuration heading below
    4. DPID 7 for cycling on-off patterns via the MCU is defined by a STR type.  OBK doesn't currently support String channel types. The could be done with TuyaMCU commands, but I personally don't require this so I did not invest time into it... I control the relays from MQTT so I don't need the MCU doing this.
    5. tuyaMCU enums can be passed to homeassistant with SetChannelType Enum if the latest built from PR



    repackaging
    As described in the Tongou MCB smart meter and relay teardown, you can either add new ferrules or use screws. I prefer the M2.5 x 10mm screws since they are easy and repeatable and don't require any special tooling.
    Close-up of Tongou electrical device housing with three black screws

    MCU configuration
    easier than using the physical menus, the switches control can be configure on the MCU
    1) set 'Device Control' (dpid 121) must be set to Buttons Locked (0), Device Control (1), or Any Control (3) - can not be Remote Control (2)
    2) toggle the 'switch auto mode' to ON for the desired switch (1 or 2)
    3) set the Min and Max C values for the switch.  Note the defines a range of temperatures the switch will turn on for.  i.e min=19,max=80 means the switch is only on for temperatures between 19-80C.
    notes:  you can override the switch states with 'Device Control' (dpid 121) set to 'Any Control' (3) or 'Remote Control' (2), otherwise MCU has control of the switches.
  • ADVERTISEMENT
  • #2 21710795
    p.kaczmarek2
    Moderator Smart Home
    Thank you for this interesting presentation! I haven't yet seen that kind of device, especially with 7-segment LED display. I think you did well with autoexec.bat. I am aware about current limitations of enums with OBK, but it can be worked around with some REST page scripting: https://www.elektroda.com/news/news3971355.html

    Do you think is there anything we can improve in OBK? I can add features if you think that something could be useful for your device presented here.
    Helpful post? Buy me a coffee.
  • ADVERTISEMENT
  • #3 21711323
    stonacek
    Level 7  
    thanks for the interest and the offer - I really enjoy working with OBK, I now have over 60 devices running OBK on my network.

    The REST side of things in OBK is quite impressive for such a device, but it isn't particularly high value to me personally since I mostly use OBK get better control of these devices into home assistant.

    I'm not sure if it's really worth increasing the footprint of OBK, but the part I would like to see and have been toying with on my own builds is the ability to adjust what is sent to home assistant's discovery (i.e. enable sending the enum tuyaMCU types as 'select' sensors with 'value_template' mappings to HA via discovery). But I suspect this feature would blow out the size of autoexec.bat files and subsequently impact OTA updates.
  • ADVERTISEMENT
  • #4 21711345
    p.kaczmarek2
    Moderator Smart Home
    I have been thinking about this feature, but I didn't get around making HA discovery JSON for that. Do you have it figured out, can you share?
    Helpful post? Buy me a coffee.
  • Helpful post
    #5 21717508
    stonacek
    Level 7  
    >>21711345

    I noticed your previous work on cmd_newEnums.c. So I expanded on this by adding a ChType_Enum and HA discovery and submitted Pull Request 1130. Please have a look - my first PR with OBK, so hoping I followed your conventions well enough. Happy to discuss what adjustments are required to get this into main branch.

    This PR allows for defining a tuyaMCU enum as a channel Enum on this device like so.
    
    SetChannelType 50 Enum
    SetChannelLabel 50 "Device Control"
    SetChannelEnum 50 "0:Buttons Locked" "1:Device control" "2:Remote Control" "3:Any Control"
    linkTuyaMCUOutputToChannel 121 enum 50
    


    The Enum channels then appear as select boxes on the OBK
    Control panel with switch buttons and dropdown setting menus

    After HA Discovery, the Enum channels appear like this:
    Device control panel with dropdown for Power-on Settings and multiple toggle switches


    stonacek wrote:
    I suspect this feature would blow out the size of autoexec.bat files and subsequently impact OTA updates.

    Regarding my earlier comment about the impact of Enums size of the autoexec.bat... it is certainly still is a concern, especially for the resources available for CB2S. I subsequently found that even on the main branch, before adding Enums to an already large autoexec.bat, the HA discovery already consumes the all the heap and reboots the device. Adding a ChType_Enums certainly doesn't help the situation (appears to consume an extra 1k from the heap on this device), but I don't think it is as big of an impact as I originally suspected.
  • ADVERTISEMENT
  • #6 21717669
    p.kaczmarek2
    Moderator Smart Home
    I think it's acceptable. Just tell me how much the main binary grew, maybe we need to put it behind #if ENABLE wall.

    Can you also add more complete self test for Discovery and read only enums?
    Helpful post? Buy me a coffee.
  • #7 21718994
    stonacek
    Level 7  
    >>21717669

    Added the ChType_ReadOnlyEnum type and expanded the discovery tests.

    The binary size grew 1376 bytes compared to main branch on BK7231N, so not much. I'm wasn't concerned about binary size.
  • #8 21719055
    p.kaczmarek2
    Moderator Smart Home
    Excellent. I really like this change, thank you! I only need opinion on whether to have it enabled by default of via config - what do you think, @insmod ?

    It looks useful for TuyaMCU.

    Can you do autoexecbatexamples update as well, @stonacek ?
    Helpful post? Buy me a coffee.
  • #9 21719264
    insmod
    Level 28  
    >>21719055
    Looks fine after a cursory glance.
    Enums can be useful for more complex devices, like thermostats.
  • #10 21719563
    stonacek
    Level 7  
    p.kaczmarek2 wrote:
    Can you do autoexecbatexamples update as well

    done


    p.kaczmarek2 wrote:
    only need opinion on whether to have it enabled by default of via config

    My biased opinion is on by default. The global g_enums stay uninitialized until the SetChannelLabel command, so almost no heap usage when not used. Total binary increase of less than 0.3%. Many TuyaMCU dpids have Channel Enums and I think this could be used in many places where Enums weren't available before (I am going through all my TuyaMCU commands on other devices and applying it).
  • #11 21719776
    p.kaczmarek2
    Moderator Smart Home
    One nitpick - it seems you didn't add autoexec.bat source, only added manually changed a file that is usually autogenerated.

    No new file here:
    https://github.com/openshwprojects/OpenBK7231T_App/tree/main/docs/autoexecs
    No new entry here:
    https://github.com/openshwprojects/OpenBK7231T_App/blob/main/docs/json/autoexecExamples.json
    Helpful post? Buy me a coffee.
  • #12 21719874
    stonacek
    Level 7  
    >>21719776
    ah yeah, I didn't see that particular .md was autogenerated. probably should have realised that while I was removing all the unrelated changes after running getcommands.js. Raised a new PR for the corrections

    thanks for merging into main!

Topic summary

The discussion centers on flashing custom firmware on the Tongou TOVTH-216WTTDA DIN-mounted MCB, which integrates a BK7231N CB2S MCU. The device features temperature and humidity sensing with two 16A relays controllable locally or via the TUYA app. The teardown process involves drilling out rivets to access the internals. The firmware modification leverages OBK (OpenBK) firmware, with users sharing experiences on managing device control and integration with Home Assistant. Key points include the use of autoexec.bat scripts for configuration, current limitations with enum handling in OBK, and potential enhancements for better Home Assistant discovery support through REST API and JSON configuration. The trade-off between firmware size and OTA update feasibility is noted when considering advanced features like enum-to-select sensor mapping for Home Assistant.
Summary generated by the language model.