SOFAR 8kW PV Installation: Opinions, Durability, Failures & Experiences with Inverters

---Ryba--- 489690 1705
Best answers

How reliable are Sofar inverters for an around-8 kW PV installation, and what problems or failures do users report?

Users report mostly acceptable results: one 6.6KTL-X had no problems for over a year, and another 8.8KTL-X owner said a firmware update to v2.20 removed the old clipping around 8 kW and let the inverter reach full peak power [#18112697] [#18662870] [#19158337] The most common problems in the thread were not outright inverter defects but installation/configuration mistakes: too many panels in one string or the wrong input mode caused DC overvoltage errors such as PvOVP, BusOPV or permanent fault, and the cure was to wire the strings correctly and keep each MPPT within its limits [#18322870] [#18323108] [#18359020] [#18360610] [#18699492] Another recurring issue was grid overvoltage: users saw ID01/Grid OVP shutdowns when mains voltage rose to about 253 V, and one case reached 280 V at the customer side; the inverter was behaving as designed in those cases [#18624602] [#18665849] A few users also mentioned Wi‑Fi/software quirks and awkward warranty handling, with the installer, seller, distributor and Sofar service bouncing responsibility between each other [#18306997] [#18322870] [#18323064] [#18331261] [#18772451] There was at least one real hardware failure report, where an 8.8KTL-X tripped AC overcurrent after about a month and then would not restart, so the unit had to go through warranty [#18771167]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1621 20958572
    JEDD
    Level 29  
    In my opinion, it will display an error, will not produce and will cut off the PV input to avoid damaging the IGBT. It`s different with the service, if you tell them that you want FW, they will ask if the inverter is working properly and if you just want newer software, they probably won`t provide it to you... You can upload some from the Internet, as long as the model is correct. When updating, it is worth paying attention to the ARM MCU version, there may be problems with updating the microprocessor to a higher FW. For me it ended with 3.02 and there was only an ARM file error
  • ADVERTISEMENT
  • #1622 20958637
    mysh_daniels
    Level 10  

    I still have a question about whether we want to expand the installation correctly. Of course, it will be done by a company with permissions, I don't want to do it myself, I just want to make sure that we are doing it right.

    Sofar 8.8 KTL-8
    Nameplate of Sofar 8.8 KTL-X inverter with technical specifications.
    Maximum operating current 11A, short-circuit current 14A
    MPPT operating voltage range 160V–960V
    Full power MPPT voltage range 380V-850V
    Maximum input current 1000V.

    I currently have 22 310W panels installed, divided equally into 2 strings of 11 panels each.
    Nominal current 9.43A, nominal voltage 32.88V, open circuit voltage 40.22V, temperature coefficient -0.30%/K
    I want to add panels to this installation, hence the idea to put the old panels on one circuit and add the new panels on the second circuit.
    Wouldn't 22 old panels on one circuit be too much? Can you leave them whole or would it be better to remove 2 for safety and leave 20 of them?
    The new panels have a current of 12.13A and a short-circuit current of 12.9A. Will they work with the Sofar 11A/14A parameters? It's hard to find anyone in the area who has panels below 11A. I would like to add 10 or 12 such panels to the second circuit.

    If I count correctly, theoretically I should not exceed 960V or 1000V. 22 panels x 40.22V open circuit x 12% voltage increase for -15°C temperature. = 991V. The question is whether this can be the case or whether it is safer to use 20 panels and the output will be 901V at a temperature of -15.
    There is no problem regarding the operating voltage, we are within the range, but the open circuit voltage in frosty weather is probably a bit too high or on the limit. And then the question is how it relates to 6200W per MPPT, and if it exceeds it, it will disconnect or cut off.
  • #1623 20976369
    mysh_daniels
    Level 10  

    There have never been any problems with the voltage, always 229-232V, but today the sun and the network increase even to 247-248V. At what voltage will the 8.8 KTL-X disconnect? Is there any option to change it to withstand higher voltage or does it disconnect so as not to be damaged? The high voltage in the network is probably not its fault, when it produces 7-8 kW, the consumption at home is e.g. 12 kW while charging the car and the voltage is still so high
  • #1624 20979851
    maiki00
    Level 10  

    Witam wszystkich, pacjent sofar 15 g3, podczas aktualizacji błąd arm, sprzęt padł błąd SCIcomLose, próbuję ponownie zainstalować oprogramowanie ale nie ładuje jak wcześniej plików tylko pisze aktualizacja i po chwili falownik ponownie się uruchamia, gdy wrzucę na USB inne oprogramowanie wybieram aktualizacja to przeleci że błędne pliki ale jest jakiś proces, a niby odpowiednie jakby się zawiesza? Może ktoś miał podobną sytuację i wie jak z tego wyjść? Pozdrawiam Michał
  • #1625 20996887
    vityok
    Level 1  
    Здравствуйте. Помогите с настройками, инвертор Sofar 8.8KTLX-G3 Отключается при 195 вольт, хочу сделать, чтобы работал от 190 вольт. Где в настройках можно поменять этот параметр? И вообще можно ли такое сделать? Спасибо большое.
  • ADVERTISEMENT
  • #1626 21020844
    grzegorz.d3
    Level 14  
    Hello, I have a 40ktlx-g3 inverter, how many panels should I give for one string of JAM66S30-505/MR_BF panels?
    Or is there someone here who could draw me a diagram.
  • #1627 21029274
    karolc856
    Level 2  

    maiki00 wrote:

    Hello everyone, patient so far 15 g3, during the update there was an arm error, the hardware got a SCIComLose error, I`m trying to reinstall the software but it doesn`t load the files as before, it just writes update and after a while the inverter restarts, when I put another software on the USB I select update and it will pass. incorrect files but there is some process and it seems to be crashing? Maybe someone had a similar situation and knows how to get out of it? Regards, Michał


    Hello,
    I join the question.
    I have an 8.8 KTLX-G3 Inverter (Hardware Version V001, Software ARM V000005, DSPM V000000, DSPS V000000) and I decided to update the software to the latest version because of the multitude of new options compared to those currently available on my inverter.
    I downloaded the update files from the official Sofar website (sofarsolar.com) and performed the update according to the instructions.
    An ARM error occurred during the update and the device was reset after a while. After loading, the SCICommLose error was displayed on the screen.
    Subsequent attempts to update or turn it off for at least 5 minutes do not bring any positive effect. After turning on, the inverter displays an error and that`s it.
    Unfortunately, the website has not yet responded to my inquiry.
    Has anyone had this problem and managed to solve it?
  • #1628 21029553
    maiki00
    Level 10  

    leave only the arm and safety files and run the installation like this
  • #1629 21031441
    karolc856
    Level 2  

    Thanks a lot.
    I did as you wrote and the inverter came back to life.
  • #1630 21064748
    maciek.mr
    Level 15  
    Hello,

    I have an inverter sofar ktlx 5.5, set with jumpers to 6.5. I have one string of panels 6.5kW. And I noticed that after connecting to one input I only have 2,8kW of generated power. I understand that I need to connect both inputs on the inverter and set up parallel operation.
    But since the inverter is set to 6.5kW, why does it cut at 2.8 and not have 3.2?

    Greetings
  • ADVERTISEMENT
  • #1631 21071280
    kolavb
    Level 1  

    Good afternoon,
    I have a question. Does the new software for the inverter 6.6KTLX-G3 introduce a change which gives the possibility of enabling active power curve adjustment in the options? (Reactive power curve adjustment)?

    The Fox inverter has something like this which, in the event of a voltage surge in the mains, allows continuous current production at a reduced value (cuts production e.g. from 3.5kW to 2.0kW) and thus does not switch off.

    I have such a problem that my inverter at high voltages in the network simply gives an error GRID OVP and shuts down, so at that time does not produce energy....
    One installation on Fox (4.5kWp) produces up to 25kW per day and the other 5.35kWp on Sofar only does 16kW under the same lighting conditions.... which is a big loss.

    How can this be remedied? Nameplate of the SOFAR 6.6KTLX-G3 inverter. .
  • #1632 21071913
    shogun
    Level 12  
    @kolavb You need to run the P(U) function on G3. This can be done with the instructions on priv.

    for me it then looks like in the attached screenshots around hr. 11
    Voltage U1 chart in the time range from 9:30 to 11:00.
    .
    Sofar power chart with a green line showing variability over time from 9:30 to 11:00.
    .
  • ADVERTISEMENT
  • #1634 21072073
    jaworsito
    Level 10  

    LordZiemniak wrote:
    You can also send me please :)
    I join the request.
  • #1635 21072137
    iborkim
    Level 13  

    shogun wrote:
    @kolavb You need to run the P(U) function on G3. This can be done with instructions on priv.


    If you can, I will also ask for instructions.
  • #1636 21076538
    zdziseek
    Level 10  

    Yesterday I noticed that in both the mobile app and the Solarman website, even after downloading the inverter log in Excel, there is no temperature value given. Up until about a week ago, all three of these "sites" were displaying two values from the temp sensors.
    Can you check with yourselves if you still have the temp displayed?
    At my Sofar Solar 8.8 ktlx g3.
  • #1637 21076551
    LordZiemniak
    Level 15  
    temperature tab has evaporated :D
    I checked on a dozen installations and this temperature tab is not there :D
  • #1638 21076567
    zdziseek
    Level 10  

    Holy crap. Exactly, there is no whole tab with the temp. And on the page, when you type in the settings to display in the graph also no, I think it used to be called Single plate temperature.
    But you reassured me that this is not only my problem.

    Btw, could you also send me instructions on how to enable this function in the menu when the voltage is too high?
  • #1639 21077414
    JEDD
    Level 29  
    On my 8.8 KTL-X the Solarman website normally displays the temperature

    Screenshot displaying inverter information on the Solarman website, showing temperatures.
  • #1640 21080812
    zdziseek
    Level 10  

    Today, it doesn't even display reactive power, in fact half the data has disappeared.
    Screenshot of the solarmanpv.com panel displaying electricity generation data from a photovoltaic installation.
  • #1641 21081218
    windowsowy27
    Level 11  

    With me it normally shows the temperature further down, the graph is just as available
    Screenshot displaying data on electricity generation and module temperature. .
  • #1643 21081702
    janus_z
    Level 12  

    >>21071913 I will also ask for this instruction
  • #1644 21083148
    LordZiemniak
    Level 15  
    I confirm, appropriate setting of this p(u) in my case does the job :D voltage as it was is too high, but the inverter works, fact with less power but it works :) the difference is significant in production, the only thing left for me is to torment Tauron to bring it to order.
  • #1645 21083162
    janus_z
    Level 12  

    Did you activate this function yourself or did Sofar's service enable you remotely?
  • #1648 21123271
    dark1309
    Level 6  
    Hello
    Sofar Solar 5.5KTL-X 3-phase inverter
    JA SOLAR 420 JAM54S30-HC GR BF 420W panels 13 pieces

    1 -STRING 7 panels 31.80Vx7=222.7V (2.94KW)
    2 -STRING 6 panels 31.80Vx6=190.8V (2.52KW)
    Open circuit voltage (Voc) 37,58V
    Max. power voltage (Vmp) 31.80V

    Biggest sun at 11-13 I give 4.2KW, shouldn't it be 5KW? Maybe convert to 1 String?
    Ground mounted photovoltaic on a rack

    I would be grateful for an answer

    Graph of energy production from a photovoltaic installation on 2024-06-15.
  • #1649 21123306
    k_pec
    Level 34  
    @dark1309
    [letter:4807666891] 1. Catalogued minimum DC input voltage for max power from mppt is 240V, so you have too low string voltages, which can probably reduce the power extracted from the panels by some percentage.
    2. In panels you have about 5.4kWp according to STC, which means in practice in the middle of summer some 4.5...4.9kW in real life, depending on weather conditions.When you add up one with the other these 4.2kW seem to be justified.

    I would try a one string connection to start with, if possible. Optimal inverter operating conditions are specified for a string voltage of 650V
  • #1650 21123336
    dark1309
    Level 6  
    It is possible to pin on 1 String. Thanks for the answer.

Topic summary

✨ The discussion centers on experiences with Sofar inverters in approximately 8kW photovoltaic (PV) installations, focusing on technical issues, durability, and configuration challenges. Users report generally stable operation with models like Sofar 6.6KTL-X and 5.5KTL-X over extended periods, though some face connectivity problems, especially with Wi-Fi and software availability. A recurring technical problem involves input voltage exceeding the maximum allowed 600V DC for single-phase Sofar inverters (notably the 4KTLM-G2), causing errors such as PVOVP and BusOPV and inverter shutdowns. This is often due to too many PV panels connected in series on a single string, with 15 Q.CELLS Q.PEAK G4.1 305W panels sometimes exceeding voltage limits, especially in cold conditions where voltage rises. Solutions include splitting panels into two strings (e.g., 8 and 7 panels) connected to separate MPPT inputs, though some users report this does not fully resolve the issue. The maximum recommended panels per MPPT input is around 9 to avoid surpassing power and voltage limits. Users also discuss the need for three-phase inverters for larger installations above 7kW on a single phase due to grid operator restrictions. Software and firmware updates are sought after but not easily accessible, with some users lacking Polish language support. Comparisons with other brands like SMA and Fronius highlight Sofar's cost advantage but raise concerns about long-term reliability and service support, which is still developing in some regions. Network-related errors such as Grid OFP (over-frequency) have been reported, with troubleshooting involving network frequency checks and inverter restarts. Overall, Sofar inverters are considered a cost-effective option with some technical caveats related to system design, installation quality, and support infrastructure.
Generated by the language model.

FAQ

TL;DR: Field owners report 0–20 % daily energy loss when Sofar inverters trip on 253 V grid peaks; “set Country Code 12 for Poland and the problem goes away” [Elektroda, 3301, post #18624621] Why it matters: one menu setting often fixes most unexpected shutdowns without replacing hardware.

Quick Facts

• Max. DC input voltage 1000 V & MPPT window 240-850 V (Sofar 8.8KTL-X manual [Uri, #18921613]) • Recommended DC/AC oversize ratio ≤ 1.2 : 1 for KTL-X models [Elektroda, BikeBarian, post #18360391] • Country Code list: PL = 12, DE = 07, NL = 05 [Elektroda, Defence & 3301, post #18851696] • Typical firmware: V2.30 (increases AC limit from 4.0 kW to 4.4 kW on 4.4KTL-X) [Elektroda, prose, post #19034268] • Service e-mail: service.pl@sofarsolar.com; hotline +48 22 123 98 58 [Elektroda, AT PRO, post #18772451]

How reliable are Sofar inverters in everyday use?

Most 6–9 kW owners report trouble-free work for 1–3 years [Elektroda, iborkim, #18112697; Elekt...

Which menu code should I select for Polish grid parameters?

Use Country Code 12 (PL). It lifts the over-voltage trip to 253 V/10 min and 264 V/1 s, matching Polish NC-RFG limits [Elektroda, 3301, post #18851696] Selecting 07 (DE) raises the limit to 264 V but violates declaration of conformity.

My inverter shows ID01 ‘GridOFP’ and stops at noon—what now?

Measure L-N voltage; if it rises above 253 V, ask the DSO to lower tap settings or move PV to another phase. Until then, temporarily change Country Code to DE (07) or install a 230 → 220 V autotransformer [Elektroda, MariuszFEG, post #18623709]

What causes PvOVP / BusOPV errors on 4KTLM-G2 units?

Voc exceeds 600 V in cold sun. Split the 15-panel string into two of 8 + 7 or use a 3-phase inverter that accepts 1000 V DC [Elektroda, noja102, post #18323557]

Is the MPPT Scan function worth enabling?

Enable only when partial shading occurs; it rescans the IV curve at user-set intervals. Service says it "improves harvest under shade" but reduces output 1–2 % on clean arrays [Elektroda, 3301, post #18622124]

How do I update Sofar firmware myself?

  1. Copy the /firmware folder to the SD card.
  2. Insert card, choose Menu → 5.Software Update, enter password 0715.
  3. Wait until ‘Update DSP1 OK’, ‘DSP2 OK’, ‘FUSE OK’, then reboot [Elektroda, Grucha383, post #19029218]

The display boots for one second at dawn—is that harmful?

No. The capacitors charge when DC rises above 180 V, then discharge if current is < 20 mA; this soft-start repeats without affecting lifespan [Elektroda, rydzyk673, post #19035241]

Why does Solarman show 0.9 A per phase even at 0 W?

Firmware ≤ V2.30 reports reactive standby current as active. Real clamp-meter reading is ~0.2 A; ignore the dash-board figure until a patch arrives [Elektroda, wilk125, post #19038447]

Edge case: can the inverter fail after a breaker trip?

Yes—one 8.8KTL-X died after a 16 A AC breaker opened; display stayed dark despite correct DC voltage, requiring warranty swap [Elektroda, gotycki1, post #18771167]

How to auto-run a 1.5 kW boiler only on surplus PV?

Install a PR-energised relay with the inverter’s CT loop; set closure above 4.5 kW export so the heater engages only in excess production [Elektroda, 3301, post #19053070]