  • #1591 20727583
    arek1313
    Level 12  

    @lesiakjarek give it a rest, such a problem is not a problem. The equipment generally works, it is unlikely to break down, enjoy as I do the low voltage in the network.
    .
  • ADVERTISEMENT
  • #1592 20732067
    rasell_
    Level 11  

    Does anyone have any accurate pictures of the interior of the Sofar 5.5 KTL-X or 6.6 KTL-X?
  • ADVERTISEMENT
  • #1595 20769006
    zdziseek
    Level 10  

    Hi,
    Version 8.8ktlx-g3.
    I had the factory software 608 and just did an update to 611.

    In the menu, there are a lot of new items, of course, despite the setting of the Polish language, some of these new functions are in English.

    Could someone explain what is responsible for these settings in the 611 software?

    How to set the reactive power control? Which settings are responsible for this?

    Here are examples of items that I do not understand, original spelling:

    Section Enter settings:
    -10 SetAntiReflux (OFF ARPC / ON ARPC)
    -12 ScanCurveIV
    -13 PCC Select
    -14 Reflux Mode (CTR TOTAL POWER/CTR PHASE POWER CTR SELLING POWER)
    -17 ReactivePara (ENABLE: POWER FACTOR/FIXED REACTIVE; disable)
    -18 HardReflux (disable ARPC / ENABLE ARPC)
    -19 Set Insulation (Dis Insulation / En Insulation(value 00050K(?))

    Section System info:
    -14 DRMs0 off
    -15 DRMn on
    -19 PV-ISO 693k (?)
    -20 GFCI 3mA
    -22 Reactive Power -10.87kVar
    -23 Power Ratio 1.0 ratio

    In normal mode of the screen, in addition to the menu, there is also a new item. After clicking the down arrow, 'power' disappears and "PF:-0.950p.u. (this value changes with the production power)" appears. The next click down shows only the amount of production "today".

    I'm especially concerned about the reactive power settings, which position and what is this Set Insulation, and whether it should be dis insulation or en insulation (and what value?)

    Thanks in advance for your help.
  • #1596 20769020
    ja_pizgam
    Level 10  

    @zdziseek this PF it looks like "Power Factor", or power factor, and the value given in your case is 95%. By the way, where did you get this soft? Did you write to the manufacturer, or did you find it somewhere on the Internet, or somewhere else?
  • #1598 20769338
    zdziseek
    Level 10  

    Display showing text normalny and power factor PF: -0.947 p.u.

    I don't know if this is the power factor, because first of all there is a minus sign in front and secondly I took the picture with a production of about 5.2 kWh and the max inverter is 8.8 kWh so it wasn't 95%.

    Soft from Sofar website generally available :)


    Anybody anything about these new items in v611 menu?
  • #1599 20771412
    pavvell
    Level 14  

    On the occasion of a power outage, I started the EPS in my HYD 3600 ES. Unfortunately, the power comes on for a few seconds, the alarm lights up for a while, the ID12 event appears, the inverter counts down 60 seconds and so on and so forth. No load on the EPS output. What could it be? Battery charge and discharge current set at 6A (I have small AGM batteries).
  • #1600 20775361
    prose
    Level 35  
    @pavvell Look into the instructions and set up.
  • #1601 20775428
    pavvell
    Level 14  
    Manual sucks, doesn't explain most of the settings
  • #1602 20801275
    szewczo86
    Level 2  

    Hello, I have such a problem. 2 months ago, the company that installed the photovoltaics took away the Sofar inverter (KTL-X, 4.2 kW installation) because I reported a failure, it meant that everything was turned off in it and it did not turn on. After a month, they said it was the DC switch because "we connected it for a short time and everything works." Later they said the complaint was not accepted because I turned the knob and that caused the inverter to burn out, what do you think about it? Even if someone turned the switch, could the inverter burn out? although I'm 100% sure no one touched it Close-up of a burnt electronic component held above an open electronic device. Burnt photovoltaic inverter with visible circuit board damage. Close-up of a damaged inverter with visible burn marks on internal components.
  • #1603 20801288
    ja_pizgam
    Level 10  

    @szewczo86 how? Flipping the DC switch was supposed to cause it to fail?! Are the photos yours or did this company check the inverter every month? And what does "we connected it briefly" mean, did they bypass the switch or what?
  • #1604 20801295
    k_pec
    Level 32  
    @szewczo86

    Hmm, since, as they wrote, " We connected it for a short time and everything works " this means that the inverter was working at that moment, not burned out. And if it was burned out at that time, they should have notified you then.

    For me, an obvious topic for the Consumer Ombudsman.
  • #1605 20801372
    szewczo86
    Level 2  

    Even if someone did something to the switch, it's probably there to turn it off and on, logical. I'll wait another week. If they don't respond, I'll report it somewhere higher. Best regards and thank you
  • ADVERTISEMENT
  • #1606 20801389
    zdziseek
    Level 10  

    What about your PV installation and production? Have you been on the ice for two months without an inverter? Do they offer anything substitute?
  • #1607 20801520
    Baqo
    Level 16  
    szewczo86 wrote:
    Hello, I have such a problem...


    Do you have two different chains with the same MPPT?
    I read somewhere.
    Two photovoltaic strings must use the same number of photovoltaic modules.
    Quote:
    When the DC switch is turned off, two PV strings connected to the same MPPT are still connected in parallel. In this case, two voltage sources are connected in parallel. When two voltage sources have different electromotive forces, a circulating current is generated.
  • #1608 20819425
    ic3ek
    Level 15  

    Hi all,

    I finally got to the end of reading the entire thread. It took me a while, a whole 54 pages 😊 And it's time to give a little shout-out to all of you who have more knowledge than me.

    Well, I have photovoltaic for several years, on board:

    SOFAR 5.5 KTL-X firmware v2.01
    18x RUNDA 300Wp Full Black which gives a pure-theoretical 5.4kW

    Switched under 2 separate MPPT of 9 Panels

    Analyzing the voltages and currents and power since July this year because there was a change of platform, I conclude that the panels operate in such parameters:
    - PV1 - PV2 voltages oscillate between 250V and 310V of course during operation.
    - Currents PV1 - PV2 do not exceed 10A when it is sunny all day will not exceed 9A
    - Power, which I obtained in the peak MAX is 5.25kW, mostly does not exceed 5kW, by default it oscillates at the limit of 4.3-4.8kW

    - Of course, the time of 3 years has passed since the subsidy where you cannot move anything, and it was time for modifications.

    First inverter up to 6.6kW, of course update to ver firmware 2.20, so that it certainly does not cut, but what next.

    Analyzing my installation, I'm thinking about 2 solutions.

    AD.1

    Connect all panels under 1 string 18x300 of course connected to both MPPT through transitions.
    Recalculating the panels, should all fit, - voltage max 18x40.24V at Voc gives 723 V "limit to 1000V". - current max 9.23A

    Only question is it going to make a difference, will I have better results?
    Because the operating range of the voltage would be higher "2 times higher" i.e. now on 2MPPT are at 290V, and after plugging all together in series and split into 2 MPPT inputs will be 580V.
    This is within the operating limit of the Inverter (240V-850V).
    But will it change anything when it comes to power given to the grid?

    AD.2

    I leave as above all the current panels plugged into one MPPT i.e. 18x300Wp "because they hang on one slope of the roof, and I have no way to add panels there"
    And to the second MPPT, I connect another panels - about 8 pcs. Some 400Wp, paying attention to the maximum current of the inverter, so that the panels do not exceed 11A

    For the day, I would not want to replace the inverter for a larger one, I reckon that in the case of peak operation of the panels in the combination of 18x300Wp + 8x400Wp will be heavily oversized,
    which will involve a power cut above 6.6kW, but in case of anything I count on the surplus on those cloudy days.

    Of course, on the second new string 8x400Wp, I cannot have less because there will not be adequate operating voltage, and the problem is that this string 8x400Wp must be installed on the other slope of the roof. But the alignment relative to the old panels is about the same angle the same insolation.

    Do such modifications make any sense?

    Maybe you can suggest a better solution to the situation?

    Technical specifications table for SOFAR inverters from model 3.3KTL-X to 12KTL-X. Table with technical specifications of different photovoltaic panel models..
  • #1609 20836256
    AlinaPodgajna
    Level 1  

    >>18111924
    I've had it with the magazine since April. I don't recommend it, every now and then there are some errors, the service seems to have deleted it again after some time, and when needed it didn't work. There was some lack of communication with the warehouse and finally it stopped working completely, the sun was shining, the warehouse was full and there was no electricity, nothing. They are also in no rush to repair it. They last for weeks. A lot of money was spent and... I also have a Foxes - there was also a problem, but they came and took it to the service center in 2 days, sent a new one and it has been working for 2 years without being checked.
  • #1610 20887850
    maciek.mr
    Level 14  
    Hi,

    I have a question about the configuration I want to change. I have a Sofar KTL5.5 inverter and 9 320W panels, which gives ~2.9kW, connected as one string. The voltage is enough to turn on the inverter.
    I am now going to add a second string to the second input on the inverter, but these panels will only be 5x600W -> 3kW.
    They are supposed to be on the same roof surface as the first string. (SW).

    The new panels have U at Pmax - 34V, which with 5 pieces will give me ~150V.

    Will this small number have a negative impact on the operation of the inverter (low voltage on the second string)?
    The inverter has a starting voltage of ~190V, but since the first string provides sufficient voltage to start, I assume that the second string
    does not have to meet this parameter,

    Regards
  • #1611 20887945
    Janusz_kk
    Level 39  
    The Vmax of this KTL is too low, if it is high, connect them all in series, you will have a greater profit.

    Added after 2 [minutes]:

    14* around 40V gives 560 and he probably has 650, so it`s enough. 14*320W gives 4.5kW, so the power is also ok.
  • #1612 20888033
    maciek.mr
    Level 14  
    But the panels have different powers 9x320W and I want to add 5x600W, I will not connect them in series :)
    The question is whether the second input on the KTL inverter is independent and requires 190V to start as well?
  • #1613 20888222
    Janusz_kk
    Level 39  
    maciek.mr wrote:
    But the panels have different powers 9x320W and I want to add 5x600W, I will not connect them in series

    You can connect them, but they will work with weaker power, you should have asked before purchasing.
    In an independent chain they will not work at all or only at noon, do what you want, you have already received advice.
  • #1614 20888269
    maciek.mr
    Level 14  
    😀 I haven`t bought it yet. I`m just planning. But if it works properly with one string, i.e. the inverter turns on, will adding a second string turn it off? I am trying to understand the principle of operation of this inverter. Is the switch-on voltage the voltage when the inverter turns on, or does this voltage only result in a change from DC to AC in a given circuit? And what does the setting of the inverter that connects the circuits do (I don`t remember the name of this option)?
    The first string gives 300V, so there is no problem with it.

    Regards
  • #1615 20888352
    Janusz_kk
    Level 39  
    maciek.mr wrote:
    I`m just planning. But if it works properly with one string, i.e. the inverter turns on, will adding a second string turn it off?

    No, but if added it won`t work.
    maciek.mr wrote:
    Is the switch-on voltage the voltage when the inverter turns on, or does this voltage only result in a change from DC to AC in a given circuit?

    There is a switch-on voltage (160V) and a minimum operating voltage at full power (240V). Because the inverter has to `raise` the voltage to convert it to AC and `push` it into the network, it won`t do it if it is too low. But this lifting also `costs`, the efficiency decreases, so the next parameter is the optimal or rated operating voltage, for this Sofar KTL5.5, when I look at the parameters now, it is 600V. So you can see that it is optimal to connect all panels in series to have the highest possible operating voltage, but not more than 1000V. This means that there is no point in buying a higher power one because it will not be used anyway. You have to buy the same ones as the previous ones or replace all of them.

    maciek.mr wrote:
    And what does the setting of the inverter that connects the circuits do (I don`t remember the name of this option)?

    This is an option for higher power panels, to use higher current, you connect both inputs in parallel in the inverter, i.e. you buy 500W panels, e.g. 14 pieces (because you cannot exceed the power either and this is 7kW max), connect them in series and connect them to the MPPT inputs in in the inverter and in the options you set the connection of inputs so that the current is distributed over both inputs, which the inverter will take care of, otherwise a single input would be overloaded.
  • ADVERTISEMENT
  • #1616 20888623
    maciek.mr
    Level 14  
    Thank you for the full explanation. Now I understand. Ok, I`ll look for 320W,
  • #1617 20956990
    Dudilp
    Level 9  

    I have a photovoltaic installation with a Sofar Solar HYD 6 KTL-3PH inverter and a SOFAR BTS 5K energy storage facility.
    Installation with a power of 7.2 kW with TIGO optimizers.
    I have a problem with the "Warning" code 813 "Charge Forbidden Alarm" appearing, theoretically the entire installation works properly, but these alarms worry me both in the application and in the inverter when I enter the "Event List".

    Do you also have so many events in this tab?
    The alarm doesn`t seem to be displayed, but I think something is not working properly.

    I will add that I reported the error to the installer. First, the Sofar service performed a remote software update, which led to the installation being disabled and, as it later turned out, damaging the control board in the inverter.
    The inverter was dismantled and sent to the service center, where the controller was replaced.
    The inverter came back repaired and with a newer version of the program, because it has more options, but the "events" are still saved.

    Can this be somehow changed in the settings on the device?

    Inverter screen displaying error ID124 BatDiscProhibit. Inverter screen displaying a list of error codes and their occurrence times. Screen showing inverter event list with error codes ID03 and trigger times. Screenshot of an app displaying 813 Charge Forbidden Alarm warnings for inverter SP2ES10. App screen showing photovoltaic alert details with a warning.
  • #1618 20958457
    mysh_daniels
    Level 10  

    So far 8.8 KTL-X
    Max power 8000W
    Max power 1 MPPT 6200W

    If we exceed 8000W of the entire device, the peak will simply be cut off and the device will not provide any more electricity, and what about the overload of 1 MPPT above 6200W? Will it also cut off the top or restart the device?
  • #1619 20958474
    JEDD
    Level 29  
    It will cut when it exceeds 8800W, unless you set the jumpers to e.g. 11000W, it will be cut at 11kW. If the MPPT power is exceeded, it seems to me that the inverter will report an error and cut production.
  • #1620 20958539
    mysh_daniels
    Level 10  

    I'm just reading about jumpers and software updates. If it exceeds and cuts the 6200W on MPPT, I understand it as a power limit from 7000W to 6200W and it will continue to work without any problems, there will be no reset? What do you understand by the term production cuts? Will it limit to 6200 or will it turn off completely?

    Do I have to write to the service center to send the file for software updates? I think I still have v2.0

Topic summary

The discussion centers on experiences with Sofar inverters in approximately 8kW photovoltaic (PV) installations, focusing on technical issues, durability, and configuration challenges. Users report generally stable operation with models like Sofar 6.6KTL-X and 5.5KTL-X over extended periods, though some face connectivity problems, especially with Wi-Fi and software availability. A recurring technical problem involves input voltage exceeding the maximum allowed 600V DC for single-phase Sofar inverters (notably the 4KTLM-G2), causing errors such as PVOVP and BusOPV and inverter shutdowns. This is often due to too many PV panels connected in series on a single string, with 15 Q.CELLS Q.PEAK G4.1 305W panels sometimes exceeding voltage limits, especially in cold conditions where voltage rises. Solutions include splitting panels into two strings (e.g., 8 and 7 panels) connected to separate MPPT inputs, though some users report this does not fully resolve the issue. The maximum recommended panels per MPPT input is around 9 to avoid surpassing power and voltage limits. Users also discuss the need for three-phase inverters for larger installations above 7kW on a single phase due to grid operator restrictions. Software and firmware updates are sought after but not easily accessible, with some users lacking Polish language support. Comparisons with other brands like SMA and Fronius highlight Sofar's cost advantage but raise concerns about long-term reliability and service support, which is still developing in some regions. Network-related errors such as Grid OFP (over-frequency) have been reported, with troubleshooting involving network frequency checks and inverter restarts. Overall, Sofar inverters are considered a cost-effective option with some technical caveats related to system design, installation quality, and support infrastructure.