jamrjan 197985 688
Best answers

What is the ecoLINK2 interface used with the ecoNet 300, and is it just a USB/RS485 converter?

ecoLINK2 is basically an RS485 converter, but the ecoNET300 setup uses more than a plain adapter: the controller goes through ecoLINK2 into the ecoNET300, and only that combination establishes communication with the server [#17778027] A normal RS485→USB converter can still let you listen to the controller on a PC, but it does not make ecoNET300 work by itself [#17778027] The controller side uses the G1/G2 RS485 ports; one reply says USB is only for software updates, while G1 is for the ecotouch panel and G2 for ecoNET, with the same data on both buses [#17757514] The interface is tied to FTDI-based hardware; the forum explicitly says ecoLINK2 uses an FTDI chip and that CH340-based converters are not supported by the ecoNET software [#19663291] Even when raw RS485 data is captured, it is not useful without the frame structure/decoder, because the protocol is closed and not Modbus [#17756899]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #331 19845379
    SławekSS
    Level 24  
    Posts: 726
    Help: 34
    Rate: 80
    In the original MR3020 v.3 (important) you first need to upload the openwrt firmware and only then the soft econeta. Nothing else is needed.
  • ADVERTISEMENT
  • USB port may be faulty; how to test it

    #332 19845574
    bymbyn
    Level 10  
    Posts: 12
    Rate: 1
    From my observations it follows:
    after connecting the power supply on the original econet, the power diode flashes, then when it is on, the RX diode flashes on the rs485 converter, and the diode connected with the controller flashes on the econet. After a few seconds, it lights up constantly, i.e. it has connected to the controller, so the TX diode on the converter also flashes from time to time.
    On the other hand, on the MR3020 uploaded by me, after connecting the power supply, the power LED flashes, then when it is on, the RX LED flashes on the converter, and nothing happens on the MR3020, and so on all the time. After connecting to the MR3020 with a LAN cable, the LED of connection with the econet server is on.
    Could it be that the USB port is not working properly? And how to check it?
  • #333 19847885
    Starterek85
    Level 16  
    Posts: 576
    Help: 19
    Rate: 59
    Buddy, the rs485 to usb converter from ftdi works at 100%. Perhaps you have a damaged one?
  • #334 19847890
    SławekSS
    Level 24  
    Posts: 726
    Help: 34
    Rate: 80
    There is also the question of what you want to combine this econet with. Sometimes you need a software dedicated to a given boiler
  • USB port may be faulty despite RS485 power working

    #335 19848083
    bymbyn
    Level 10  
    Posts: 12
    Rate: 1
    So yeah
    I have 2 MR3020 routers - the first working, original Econet, the second router, after downloading the software for Econet when updating the first, uploaded by OpenWrt.
    I also have 2 converters - the first one that was attached to the original Link2 Econet, the second one bought on the auction site
    Both operate on the original Econet.
    They do not work on the second router with the Econet soft loaded.
    The first is for monitoring the heat pump.
    The second I wanted to monitor recuperation.
    Both of the same company.
    The original Econet works both on the heat pump and, after overvoltage, on recuperation, there are appropriate indications on the page, and 2 devices are visible. Now, as active, I can only have one, so I wanted to connect the second router so that both devices were visible, but unfortunately something is missing, or the USB port is broken, only if it was broken, the RS485 converter would not work because it gets power from the router.
    How to check if the USB port is working properly?
  • ADVERTISEMENT
  • MR3020 OpenWrt image and flashing procedure

    #336 19897914
    Jokik_1
    Level 8  
    Posts: 4
    Rate: 1
    bymbyn wrote:
    From my observations it follows:
    after connecting the power supply on the original econet, the power diode flashes, then when it is on, the RX diode flashes on the rs485 converter, and the diode connected with the controller flashes on the econet. After a few seconds, it lights up constantly, i.e. it has connected to the controller, so the TX diode on the converter also flashes from time to time.
    On the other hand, on the MR3020 uploaded by me, after connecting the power supply, the power LED flashes, then when it is on, the RX LED flashes on the converter, and nothing happens on the MR3020, and so on all the time. After connecting to the MR3020 with a LAN cable, the LED of connection with the econet server is blinking.
    Could it be that the USB port is not working properly? And how to check it?





    Hi I tried it with TP MR3020 v3 link too, uploaded OpenWrt here but it failed which link should I upload to MR3020-OpenWrt and what procedure. Thank you in advance.
  • #337 19898163
    SławekSS
    Level 24  
    Posts: 726
    Help: 34
    Rate: 80
    First you upload openwrt 18.xxx from Luci's GUI and then the binark from post # 96. Do not upload newer openwrt because it may not work.
  • #338 19898390
    bymbyn
    Level 10  
    Posts: 12
    Rate: 1
    OKAY. Or do you have this OpenWRT binary? The official website has version 19 and above
  • #340 19899150
    Jokik_1
    Level 8  
    Posts: 4
    Rate: 1
    Hello everyone, after long efforts econet MR3020 I put it in a pile thank you all.

    Added after 27 [minutes]:

    I still have a question, I want to log in to econet24.com so it will write to me The device is blocked, but the application works, what else should I do
  • #341 19899672
    SławekSS
    Level 24  
    Posts: 726
    Help: 34
    Rate: 80
    Jokik_1 wrote:
    I still have a question, I want to log in to econet24.com so I will write to me The device is blocked, but the application works, what else should I do
    Either wait, they might unlock, or buy an original.
  • #342 19903712
    gigipawel
    Level 15  
    Posts: 155
    Help: 6
    Rate: 17
    Anyone of you have a script to read after RS485 but directly after SERIAL?
    Working.
  • Need correct OpenWrt install order for ecoNet USB driver

    #343 19903756
    bymbyn
    Level 10  
    Posts: 12
    Rate: 1
    SławekSS wrote:

    I am already giving up, I have already uploaded almost everything, SNAPSHOT 18, I was playing with LUCI, I was playing with LUCI, and it didn't help.
    The router cannot see the driver.
    I checked the USB port and it works, because there is a message on the console about connecting the device, but unfortunately it does not want to connect the driver.
    In the original, the LED connected to the controller is blinking, and nothing happens in this
    Am I doing something wrong?
    1.I am uploading openwrt snapshot version 18.
    2. I put the econet binark on the device
    3. I am doing a sysupgrade
    4.I connect to the controller and nothing ..
    I will note that the device is working properly, because I have it connected to the putty after rs and I can see it on the console.
    Do you have to upload something to read from USB?
    Alternatively, I am asking for some instructions on how to do it correctly, what version, what to install, in what order etc.
  • Sysupgrade to full econet firmware

    #344 19904154
    SławekSS
    Level 24  
    Posts: 726
    Help: 34
    Rate: 80
    bymbyn wrote:
    2. I put the econet binark on the device
    3. I am doing a sysupgrade


    I don't really understand if it looks like this:
    you upload openwrt from GUI,
    you turn on the router
    you go to the firmware update tab, select the econet binary from this topic, click Upload or update, I don't remember.
    A red warning will appear on the screen that you are loading a soft that does not match and you can release the router, you ignore it and click yes.

    After all (upload and restart) you have a full econet.
  • Need OpenWrt 18.x image and ecoNet pinout

    #345 19940647
    dido83
    Level 6  
    Posts: 9
    Rate: 2
    Hello,

    I need help / guidance ...

    I have TL-mr3020 v3.20 - I'm uploading bin to it (via TFTP because gui crashes an error - but I've already found somewhere that
    v3 only via TFTP goes) which could be found on the Openwrt website:

    https://downloads.openwrt.org/snapshots/targe...plink_tl-mr3020-v3-squashfs-tftp-recovery.bin

    after uploading I have access to the router only via ssh but after trying to upload econet bin from the command line, I trace all connectivity to the router.
    Here, as I understand it, I use openwrt for the new one and that's probably why it's falling apart ...

    I am loading recovery via TFTP and the router is alive ..


    1) Could someone give the path to version 18.x for mr3020 v3.20
    2) After uploading eco bin, how should this switch 3g / 4g - WISP - AP be set?
    3) Which pins on ecosol 301 are used for transmission ..

    Thanks a lot for your help ....
  • ADVERTISEMENT
  • TFTP recovery image rejected by stock GUI

    #347 19940709
    dido83
    Level 6  
    Posts: 9
    Rate: 2
    SławekSS wrote:


    and from this link I upload the file via tftp:

    tplink_tl-mr3020-v3-squashfs-tftp-recovery.bin

    none of the three available through the original tplink GUI failed and crashed:

    The uploaded file was not accepted.

    After uploading, I am at this stage that I upload the binary from this thread via ssh eco-mr3020-v3-3.2.3678-em-fda69db834b649919bfeeecd8d955327.bin
    I am doing:

    sysupgrade -v -f /tmp/eco-mr3020-v3-3.2.3678-em-fda69db834b649919bfeeecd8d955327.bin

    but this causes the router to stop assigning addresses from dhcp, rigidly as I set the address from the 192.168.1.x or 192.168.0.x network on the card, I do not find the router's address ...
  • OpenWrt can be flashed via tftp and GUI update

    #348 19940808
    SławekSS
    Level 24  
    Posts: 726
    Help: 34
    Rate: 80
    Through the original GUI you will not play any openwrt.

    You can upload Openwrt with GUI via tftp.
    After uploading openwrt from its GUI, select the update and point to the .bin file with the econeta soft.

    Openwrt will tell you that the wrong file, etc. etc., and whether you really want to upload. You take it and you confirm. Soft econeta is playing.
    You reboot and you have an econet.

    The switch does not work, the router does not allocate addresses because it is no longer a router. Mr3020 takes an IP address that is assigned to it by another router.

    LEDs y have a different function than the factory setting.
  • OpenWrt install leaves only SSH access

    #349 19940996
    dido83
    Level 6  
    Posts: 9
    Rate: 2
    SławekSS wrote:
    Through the original GUI you will not play any openwrt.

    You can upload Openwrt with GUI via tftp.
    After uploading openwrt from its GUI, select the update and point to the .bin file with the econeta soft.

    Openwrt will tell you that the wrong file, etc. etc., and whether you really want to upload. You take it and you confirm. Soft econeta is playing.
    You reboot and you have an econet.


    And here is the problem because after uploading I don't have GUI, I only have ssh access.
    A similar situation to someone here with version v3.20: https://forum.openwrt.org/t/tl-mr3020-after-i...ling-openwrt-no-access-to-the-interface/48505

    SławekSS wrote:

    The switch does not work, the router does not allocate addresses because it is no longer a router. Mr3020 takes an IP address that is assigned to it by another router.


    soft econet after uploading via ssh, reboots and unfortunately does not assign itself any IP from the router.

    Screenshot of the software upgrade process on an OpenWRT router.
  • Wrong econet binary caused the upload issue

    #351 19941080
    dido83
    Level 6  
    Posts: 9
    Rate: 2
    I made a fatal mistake :shocked!: I don't know how I didn't notice it. I uploaded the wrong econet ... I downloaded the binary from my friend's post @kashue Only after I verified what is in the post # 96, I noticed the differences.

    After uploading, the econet rises ... now only connecting to ecosol and we will see if it will work ...
    Thank you for helping everyone ...

    @SławekSS this is the same binary as previously downloaded ... on my version MR3020 v3.20 gui did not want to work .. but flashing via ssh goes flawlessly ....
  • #352 19949998
    bonon14
    Level 1  
    Posts: 1
    Has anyone successfully connected the EcoSol500 to HomeAssistant? anyhow? The topic was scrolled several times in the thread, but there was not too much detail.
  • ADVERTISEMENT
  • #354 19967685
    zASSAz
    Level 1  
    Posts: 1
    Hi,
    I know how to turn on and turn off:
    [ip]/econet/newParam?newParamName=BOILER_CONTROL&newParamValue=1 / - turn on the boiler
    [ip]/econet/newParam?newParamName=BOILER_CONTROL&newParamValue=0 / - turn off

    How to pause via econet local api?
  • #355 20040505
    tmhc
    Level 14  
    Posts: 155
    Rate: 10
    Does anyone have a soft for the Metal Fach controller? Unfortunately, I have "Blocked Device" info, only e-mail alerts come.
  • Disable econet and log in to Plum account

    #356 20040960
    SławekSS
    Level 24  
    Posts: 726
    Help: 34
    Rate: 80
    Since you have such a string, it means that you have a good firmware. If the firmware was bad, Econet would not get along with the boiler controller.
    To get rid of this inscription, you either buy the entire econet from a metal trade or wait. Sometimes a week, sometimes several months, until plum is cleaning up the server.

    Hint:
    how do you turn off econet and log in to your plumie account
    then you will be able to see the history and a few other things.
  • EcoNet connection resets EcosterTouch panel during mode changes

    #357 20051027
    Sportiva
    Level 11  
    Posts: 7
    Question:
    I realize that this may not be exactly the topic. But for some time now, connecting EcoNet causes me to restart the wired EcosterTouch room panel, this happens both on the original ecoLINK2 and the usual RS485 converter, I have already connected the panel and EcoNet to other power supplies, etc. the problem still appears. It is enough that the EcoNet is disconnected from the bus and everything works as it should.
    Connecting the computer with the use of programs from honorable forum members here also does not interfere with the operation of the boiler and the parameters are read on the computer, connecting EcoNet at the time of changing the boiler operation mode from "heating" to "operation" resets the room panel and automatically resets the boiler operation in automatic mode if work based on EcoSter is set.
    Questions whether any of the forum members has a charge for the Kostrzewa Room Panel newer than: EcoSTER 1 module version: 1.14.73.
    And next: Do you think it is possible to downgrade the software in Econet from ecoNET module version: 3.2.3810 ??
    The equipment purchased together with the boiler is not in the fashion of the above-mentioned topic, but I understand that it does not matter :)
    OVEN: KOSTRZEWA EEI: 24 kW
    Software versions of regulators
    EcoNET module version: 3.2.3810
    Module A version: 16.33.91
    Panel module version: 16.14.175
    EcoSTER 1 module version: 1.14.73
    Module B version: 1.30.11

    Greetings
  • DHW schedule control via econet getSchedule

    #358 20086285
    ufogufo13
    Level 2  
    Posts: 3
    Rate: 1
    Hi,
    I generally follow the thread from the very beginning.
    I launched the econet service on my raspberry. From one of the ecolink throws from this thread. Not important.
    I felt like controlling schedules, or rather turning them on / off.

    Has anyone tried to tame the DHW temperature reduction schedule on / off?

    Get returns
    pi@raspberrypi:~ $ curl xxx/econet/getSchedule
    {"schedulesVer":1,"schedules": {"ecomaxSchedules": {"mixer1TZ": [[0, 1, 255, 255, 255, 240], [0, 1, 255, 255, 255, 192], [0, 1, 255, 255, 255, 192], [0, 1, 255, 255, 255, 192], [0, 1, 255, 255, 255, 192], [0, 1, 255, 255, 255, 240], [0, 1, 255, 255, 255, 240], [1, 4, 0, 20]], "circPumpTZ": [[255, 255, 255, 255, 255, 255], [255, 255, 255, 255, 255, 255], [255, 255, 255, 255, 255, 255], [255, 255, 255, 255, 255, 255], [255, 255, 255, 255, 255, 255], [255, 255, 255, 255, 255, 255], [255, 255, 255, 255, 255, 255], [0, 0, 0, 20]], "cwuTZ": [[0, 0, 0, 0, 63, 224], [0, 0, 0, 0, 63, 224], [0, 0, 0, 0, 63, 224], [0, 0, 0, 0, 63, 224], [0, 0, 0, 0, 63, 224], [0, 0, 0, 0, 63, 224], [0, 0, 0, 0, 63, 224], [1, 6, 0, 20]], "boilerTZ": [[0, 1, 255, 255, 255, 240], [0, 1, 255, 255, 255, 192], [0, 1, 255, 255, 255, 192], [0, 1, 255, 255, 255, 192], [0, 1, 255, 255, 255, 192], [0, 1, 255, 255, 255, 192], [0, 1, 255, 255, 255, 240], [1, 5, 0, 20]], "boilerWorkTZ": [[0, 3, 192, 192, 63, 224], [0, 3, 192, 0, 63, 224], [0, 3, 192, 0, 63, 224], [0, 3, 192, 0, 63, 224], [0, 3, 192, 0, 63, 224], [0, 3, 192, 0, 63, 224], [0, 3, 192, 192, 63, 224], [1, 0, 0, 20]]}}}


    for DHW, for example
    "cwuTZ": [[0, 0, 0, 0, 63, 224], [0, 0, 0, 0, 63, 224], [0, 0, 0, 0, 63, 224], [0, 0, 0, 0, 63, 224], [0, 0, 0, 0, 63, 224], [0, 0, 0, 0, 63, 224], [0, 0, 0, 0, 63, 224], [1, 6, 0, 20]]

    we have 7 days with hourly settings and [1, 6, 0, 20]. 1-on / off, 6-step reduction in degrees.

    I tried a million ways to give him the given json but nothing wants to come despite returning OK.
    this is what the functions in the controller look like
    def onsetSchedule(self,params):
      scheduleType=None
      timeOfWeek=None
      scheduleDev=None
      values=None
      if 'scheduleType' in params:
       scheduleType=urllib.unquote(params['scheduleType'][0])
      if 'timeOfWeek' in params:
       timeOfWeek=urllib.unquote(params['timeOfWeek'][0])
      if 'scheduleDev' in params:
       scheduleDev=urllib.unquote(params['scheduleDev'][0])
      if 'values' in params:
       values=[json.loads(item)for item in(urllib.unquote(params['values'][0])).split(",")]
      if not scheduleDev is None:
       tmpValues=values
       values=dict()
       values[scheduleDev]=tmpValues
      self.commThread.addSetSchedule(scheduleType,timeOfWeek,values)
      return '{"result":"OK"}'
     def ongetSchedule(self,params):
      return '{"schedulesVer":'+str(state.scheduleVer)+',"schedules": '+json.dumps(state.getSchedule())+'}'
  • MR3020 v1 compatibility question for ecoNet software

    #359 20091427
    popek9
    Level 14  
    Posts: 104
    Help: 1
    Rate: 26
    Hi everyone,

    I have been following this topic for some time, I have already completed everything and yesterday I was supposed to start uploading openwrt to the mr3020 router. However, I logged on to it and found out that I had bought the V1 version. Unfortunately, I have nowhere found any information whether this version is compatible with the econet software.

    Could someone tell me if this router will work? If not, I will return and look for the V3 version.

    Thanks in advance for your help :)
  • v1 router incompatible due to different processor and memory

    #360 20091611
    ufogufo13
    Level 2  
    Posts: 3
    Rate: 1
    popek9 wrote:

    Could someone tell me if this router will work? If not, I will return and look for the V3 version.


    I made the same mistake. It will not run on v1. There is a different processor and less memory.

    I abandoned the search for v3 and, having dismantled the system image, I took the necessary files out of it and added the missing packages to the raspberry. The same effect, only no connection to the econet24 system.

    Regards

Topic summary

✨ Discussion focused on the ecoNet 300 / ecoLINK2 ecosystem for Plum boiler controllers and how the internet module communicates with the furnace controller over RS485. The module was identified as a modified TP-Link router running custom firmware, with ecoLINK2 acting as more than a simple USB-to-RS485 converter because the controller only works when connected through the original ecoLINK2 chain. Participants intercepted and decoded the RS485 traffic, determined the frame format, CRC method, and serial settings, and mapped many boiler parameters such as temperatures, flame, blower, power, fuel usage, operating times, and ignition counts. Later posts showed that the ecoNet firmware could be extracted from a router image, that the web backend uses scripts and a parser for the controller data, and that the system can be adapted to home automation platforms like Domoticz and RRD. The thread also covered firmware update files, FTP/update access, MAC-based authorization, and hardware compatibility of TP-Link MR3020/OpenWRT-based replacements.
AI summary based on the discussion. May contain errors.

FAQ

TL;DR: “Roughly 80 % of home-made ecoNET clones trigger the ‘device blocked’ error” [Elektroda, SławekSS, post #18323351] “Only FTDI-based USB-RS485 adapters are accepted” [Elektroda, SławekSS, post #18292233] Stick to genuine UID-MAC pairs or local-only JSON control. Why it matters: wrong hardware wastes time and can lock your controller.

Quick Facts

• Supported buses: RS-485 115 200 8N1, FTDI chip only [Elektroda, miszko, post #18186792] • JSON endpoints: /regParams, /sysParams, /editParams (~350 values each) [Elektroda, maki26, post #19044244] • Typical clone success: <20 % reach full cloud pairing [Elektroda, SławekSS, post #18323351] • Customisation (MAC + brand key) reflash cost: PLN 180 ≈ €40 [Elektroda, Starterek85, post #19657219] • Safe baud fallback: 9 600–115 200 bps; data valid only at 115 200 bps for ecoMAX 9xx [Elektroda, miszko, post #17779586]

How do I wire a USB-RS485 converter to the ecoMAX controller?

Match RS-485 A→D- and B→D+, leave GND unconnected. Most converters label A/B opposite to D+/D-, so connect A→D- and B→D+ [Elektroda, SławekSS, post #19645484]

Which USB-RS485 adapters work?

Only converters using an FT232/FT2232 FTDI chip enumerate as /dev/ttyUSB0 on ecoNET firmware; CH340 or Prolific devices are ignored [Elektroda, SławekSS, post #18292233]

Why does my clone show “device blocked” on econet24.com?

Plum’s server whitelists factory MAC ranges and brand keys. Clones with unknown MACs (or reused ones) are rejected during TLS handshake, returning ‘device blocked’ [Elektroda, cinas, post #18323486]

Can I still monitor the boiler locally when the cloud is blocked?

Yes. Point a browser to http:///econet/regParams. The JSON payload exposes live temperatures, power, pump states and over 300 variables without cloud access [Elektroda, maki26, post #19044244]

How do I change a parameter via HTTP?

Send: http:///econet/newParam?newParamName=CWU_SET_TEMP&newParamValue=44 . The module replies {result:"OK"}. Use rmCurrNewParam?newParamKey=1280&newParamValue=60 for indexed values [Elektroda, OlexandrRom, post #19607120]

The reply says OK but nothing changes—what’s wrong?

EditableParamsVer must be >0. If the controller reports 0 the driver blocks writes; update module-A firmware, then repeat [Elektroda, aurimenas, post #19608553]

How can I log data to Home Assistant or Domoticz?

  1. Install Python on a Raspberry Pi.
  2. Use the econetanalyze script to poll /regParams every 10 s and publish to MQTT [Elektroda, SławekSS, post #19607352]
  3. Add MQTT sensors in HA. A 24 h run logs ~8 000 frames (≈5 MB).

Is firmware update possible without ecoLINK2?

Yes. Copy the *.pfi file to a FAT32 micro-SD, insert it into the touch panel and choose Software > Update. Service USB flashing demands an ecoLINK2 (FTDI) cable [Elektroda, SławekSS, post #19268577]

What statistic shows clone risk?

Forum logs indicate only 1 in 5 DIY MR3020 conversions pass Plum’s server checks, leaving 80 % unusable for remote cloud control [Elektroda, SławekSS, post #18323351]

Edge case: what happens if baud or byte size is wrong?

Frames still appear but contain garbage; recognizable strings like ‘ecoMAX 920’ disappear, misleading users into thinking the bus is silent [Elektroda, miszko, post #18186792]

Can I integrate the ecoLAMBDA oxygen probe data?

Yes, after connecting the probe module the main frame adds lambdaStatus (byte 224) and lambdaLevel (float 226) values [Elektroda, OlexandrRom, post #19607120]

Quick 3-step test to verify bus health?

  1. Connect FTDI RS-485 A/B.
  2. Open serial 115 200 8N1; look for ‘TIME’ packets every second.
  3. Confirm CRC byte = XOR of previous bytes; value 0×2B appears in 300-byte frames [Elektroda, przemo_ns, post #18120336]