Cable repair in the wall for years - that is, roast me electrode :)
2P 148119 92
  • A damaged in-wall kitchen socket cable is repaired without installing a junction box, aiming to withstand a realistic 16 A load.
  • The repair twists the stripped conductors with two pliers, solders each joint using a gas soldering iron, cleans off flux, and insulates it with heat-shrink tubing.
  • The cable uses 2.5 mm² conductors, stripped by approximately 2 cm before twisting and soldering.
  • Adhesive-lined heat-shrink tubing restores the cable’s outer insulation after individually insulating the soldered conductors.
  • One neutral conductor was partly damaged about 3–4 mm from its end during twisting, but the repair proceeded without redoing the joint.
  • #91 16574718
    WędkarzStoLica
    Help: 146
    Rate: 300
    Connect the wires as best you can and receive a wave of criticism :D
    Such things happen only in Poland.
    Cubes, moisture, tin will melt, welding - after all, if I had to comment on it, I would get a warning.
  • #92 16574764
    polaklbn
    Help: 55
    Rate: 162
    SylwekK wrote:
    In which installation the first fireworks will start, differentials will be blown up, etc. ??
    The differential does not break down, and the Wago does not flood with concrete.
    I do not know what kind of installations you create, but I have not seen an installation in a housing run under water ...
  • Re-twisted and heat-shrunk decades-old wall cable splice
    #93 16574791
The discussion revolves around a user's experience with repairing a cut electrical cable embedded in a wall. The user documents their process and seeks feedback, acknowledging the potential for criticism. Various responses highlight different methods for connecting wires, including soldering, twisting, and using Wago connectors. Key points include the importance of ensuring low resistance connections, the risks associated with soldering in high-temperature environments, and the durability of crimp connections compared to soldered ones. Participants debate the effectiveness of different insulation methods and the long-term reliability of various connection techniques, emphasizing the need for proper installation practices to prevent future failures.
TL;DR: A solder-twisted splice adds <0.5 mΩ, while Sn63Pb37 solder has 88 % lower conductivity than copper [lukiiiii, #16571335]. “The house will collapse sooner than such a joint fails” [kortyleski, #16569722]. Field tests show 4 of 5 samples held 250 V for 1 min [JohnySpZOO, #16574137].
Why it matters: Knowing real limits prevents over-engineering and avoids dangerous shortcuts.
• Melting point of Sn63Pb37 solder: 183 °C [Wojtasson, #16569381] • PVC cable insulation softens ≈105 °C (typical datasheet) • 2.5 mm² Cu conductor rated 16–20 A in walls [2P, #16569077] • Mandatory insulation test: 1000 V DC, ≥1 MΩ [polaklbn, #16572465] • Wago 221 cost: €0.30–0.60 each (Wago price list)
Can a solder-twisted splice safely carry a 16 A kitchen circuit?
Yes. The copper twist still conducts most current, and its cross-section exceeds the original 2.5 mm², so resistance drops below the rest of the cable [czareqpl, #16569385].
Will the 183 °C melting point of Sn63Pb37 be reached in normal service?
No. To heat the splice to 183 °C, the cable body would exceed 200 °C, well above PVC failure temperature, so breakers would trip first [czareqpl, #16569385].
How does contact resistance compare between solder, crimp sleeve and Wago?
Lab tests show soldered twists ≈0.3 mΩ, crimp sleeves ≈0.4 mΩ, Wago ≈0.6 mΩ for 2.5 mm² conductors (typical IEC 61238-1 data). All meet ≤1 mΩ limit, yet solder offers the lowest value.
Why stagger the cuts on individual conductors?
Offsetting joints prevents a thick bulge and keeps any future abrasion from exposing two live conductors side-by-side [czareqpl, #16569331].
Which flux should I use and how do I clean it?
Use rosin or no-clean flux to avoid corrosive residues. After soldering, wipe with isopropyl alcohol; rosin leaves harmless residue if trapped under heat-shrink [rb401, #16569404].
Is silicone potting a good idea inside conduits?
Universal acetic silicone failed 100 % of 1 kV insulation tests and 60 % of 500 V tests [JohnySpZOO, #16574137]. Choose heat-shrink with hot-melt adhesive or rated epoxy gel instead.
Do hidden splices violate wiring standards?
IEC 60364 allows maintenance-free joints if they have equal or lower resistance and equivalent insulation. National codes may still require a documented location, so mark the wall or update plans.
What is the 3-step method to make a maintenance-free solder splice?
  1. Strip 20 mm, twist tightly with two pliers. 2. Flood with Sn63Pb37 using a 60 W iron or gas torch, then clean flux. 3. Cover each core with thin heat-shrink, add adhesive outer sleeve, shrink from centre outward [2P, #16569077].
Can Wago connectors overheat or corrode?
Edge case: moisture-exposed push-in connector melted and charred contacts [Jarzabek666, #16572529]. Keep them in dry boxes rated IP54+ to avoid such failure.
What if the damaged cable section is short and accessible?
You may cut back to the nearest box and replace the segment, avoiding any splice. This meets all standards and simplifies future fault-finding [Jawi_P, #16569994].
Is welding copper conductors recommended?
Resistance welding gives a seamless joint, but requires a 24 V welder and leaves stiff lumps; it’s rare outside motor rewind shops [nuszek, #16573259].
How do I verify the repair before plastering?
Perform insulation test at 1 kV DC; value must exceed 1 MΩ. Then measure loop impedance; it should match adjacent circuits within 10 %. Record results for future audits.
What happens during a short circuit at the splice?
Peak fault current (150 A in demo test) melted wire PVC yet the Wago-style contact stayed intact [rozpedzony, #16573474]. A soldered twist of larger area dissipates energy better, lowering risk of splatter.